Inverter power loss when generator shuts down
10-13-2011, 05:35 PM
|
#1
|
|
Junior Member
Join Date: Sep 2010
Location: Seal Beach, CA
Posts: 10
|
When I'm using my inverter to watch TV, and I turn on my generator with the inverter on, when I turn off the generator I expierence power loss for a short time at the time I turn the gererator off. Then the inverter restores power to my TV and everything has to reboot. IS THIS NORMAL?
I have had other coaches that if you have the inverter on before turning off the generator you do not interupt the 115V power.
__________________
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
10-13-2011, 05:51 PM
|
#2
|
|
Community Administrator
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,593
|
An inverter usually has an internal transfer switch that senses the presence of another source of AC and if present goes into bypass. The transfer is almost instantaneous, yours just may be a little slow or may be acting up.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
|
|
|
|
| |
|
10-14-2011, 06:58 AM
|
#3
|
|
Member
Monaco Owners Club
Join Date: Apr 2009
Posts: 43
|
I have a Xantrex inverter/charger and it does not transfier instantly back to inverter power. When external power is applied it is instant, but when removed it always drops for a couple of seconds, just enough time for everything electronic to quit and need to restart. I think this is normal for the Xantrex product.
__________________
34' Holdiay Rambler Neptune
Solar and Jeep
|
|
|
|
| |
|
10-15-2011, 09:27 AM
|
#4
|
|
Senior Member
Monaco Owners Club
Join Date: Oct 2009
Location: On the road
Posts: 382
|
Seems to be "normal" on the Magnum 2800 too!! I have played with settings recommended by factory "techs" for four years, frustrating!! My old Heart 2000, circa '99, never lost power. Will love to see answers on this if anyone has one that works.
__________________
Happy Trails 
06 Dynasty Countess III
07 Hummer H3
|
|
|
|
| |
|
10-15-2011, 09:58 AM
|
#5
|
|
Community Administrator
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,593
|
I found this in my Xantrex inverter manual. It descrbes the time delay when going from the inverter to the generator. I haven't found anything about the time delay going from the generator to the inverter.
There is a minimum 5-second delay from the time the inverter senses that AC is present at the input terminals to when the transfer is made. This delay is built in to provide time for a generator to spin-up to a stable voltage and avoid relay chattering. The inverter will not transfer to generator until it has locked onto the generator’s output. The inverter’s AC input is internally connected to the inverter’s AC output while in the battery charger mode.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
|
|
|
|
| |
|
10-15-2011, 10:57 AM
|
#6
|
|
Senior Member
Join Date: Dec 2006
Location: Santa Clarita, CA.
Posts: 1,585
|
My Dimensions was like that, but I now have a Magnum MS-2000 that gives me control of transfer times. I have it set for a fast transfer, or what they call 'UPS Mode'. There is zero (well, 16ms per spec.) drop when killing shore power or the gen.
__________________
_______________________________
Jeff - WA6EQU
'06 Itasca Meridian 34H, CAT C7/350
|
|
|
|
| |
|
10-15-2011, 03:13 PM
|
#7
|
|
Senior Member
Workhorse Chassis Owner Damon Owners Club
Join Date: Mar 2009
Posts: 8,078
|
Not really normal... Your inverter is slow to kick in... I do not know if it's a problem
On mine (Prosine 2.0) I have a florescent lamp that is 120 volt that does blink off.
When I had Dish Network the dome antenna would re-seek the bird.
But with DirecTV it did not, Televisons and computers seem not to notice.
__________________
Home is where I park it!
|
|
|
|
| |
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|
Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 12:02 AM.