Old 05-21-2016, 05:40 PM   #1
Moderator Emeritus
 
barmcd's Avatar


 
Monaco Owners Club
Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 13,426
Onan 7.5Kw Quiet Diesel Generator Turns Off

It was running fine. I ran it four hours in March and April with the AC running to give it some exercise. Then at the end of April, I noticed the number of hours on the meter was higher than it should be and Katherine told me she'd heard it running in the middle of the day. I turned the auto-start feature off on the inverter and the generator stopped starting by itself.

I needed to do a complete service on the unit--change coolant, oil, filter, fuel filter, and air filter. I started by draining and replacing the coolant, then moved on to the oil and filter. I started the generator to warm up the oil and it quit after about two minutes. It started and ran at fast idle, then idled down for a few seconds and then quit.

I started it several times with the same results. The longer I waited between attempts, the longer it would run.

I completed the service and started the generator and it ran for about 5 minutes, then stopped.

First, is there anything I could have done at the inverter remote that could cause this behavior?
__________________
Dennis and Katherine
2000 Monaco Dynasty
barmcd is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-21-2016, 06:09 PM   #2
Senior Member
 
slemnah's Avatar
 
Join Date: Jan 2011
Location: Santa Clarita, CA
Posts: 929
Did you start it from the switch on the dash or or at the generator or did you start it from the generator panel? Try starting it from the generator panel and it may stay running. The inverter shuts it off if started from the dash switch unless you reprogram the panel.
Steve
slemnah is offline   Reply With Quote
Old 05-21-2016, 07:33 PM   #3
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 14,608
Have you checked for blink codes to see why it is shutting down. Press the stop button down 3 times within 5 seconds. If there was a fault it will provide a blink code, note the number of blinks. Check your operating manual troubleshooting section and it explains the blink codes.

Hold the prime button down on the generator for ~1 minute, it may have some air in the system.

If mine sits for a long time it seems to want to do the same thing unless I prime for a long time.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 05-21-2016, 08:20 PM   #4
Moderator Emeritus
 
barmcd's Avatar


 
Monaco Owners Club
Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 13,426
I'll purge it and check to see if there are any codes.
__________________
Dennis and Katherine
2000 Monaco Dynasty
barmcd is offline   Reply With Quote
Old 05-22-2016, 09:13 AM   #5
Moderator Emeritus
 
barmcd's Avatar


 
Monaco Owners Club
Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 13,426
I get 33 when I push the stop generator button so I'm assuming I have a bad temp sensor. Can anyone point me to where it's at on the unit?
__________________
Dennis and Katherine
2000 Monaco Dynasty
barmcd is offline   Reply With Quote
Old 05-22-2016, 09:54 AM   #6
YC1
Senior Member
 
YC1's Avatar


 
Join Date: Jun 2011
Location: FL
Posts: 11,452
It may have an air bubble. Watch this video for information. It is towards the end where it talks about overheating due to air.

Attached Files
__________________
Certified Senior Electronic Technician, Telecommunications Engineer, Telecommunications repair Service Center Owner, Original owner HR 2008

.
YC1 is offline   Reply With Quote
Old 05-22-2016, 10:57 AM   #7
Moderator Emeritus
 
barmcd's Avatar


 
Monaco Owners Club
Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 13,426
Thanks Myron, the overflow tank had the right level in it so I didn't think to actually look in the radiator. It took nearly a full quart of antifreeze and has been running for 15 minutes now so I think that did it.
__________________
Dennis and Katherine
2000 Monaco Dynasty
barmcd is offline   Reply With Quote
Old 05-22-2016, 01:44 PM   #8
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 14,608
How much coolant did you drain out??

It takes more then 1 quart for the entire system.

When you filled the coolant did you pull the radiator fill cap completely out of the front cover???? It pulls out ~1 foot.

I know this because I made a huge mistake, I thought I had pulled it out enough but didn't and the hose was kinked. It would not take anymore coolant, when I started it did the same thing. I kept forcing it (I removed the heat sensor plug, BIG Mistake) and I actually got it hot and failed the engine. Had to replace generator with a used one $5K.

The temperature sensor is on top of the engine, passenger side, you have to remove the top cover to get to it. Located next to the thermostat.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 05-23-2016, 05:36 AM   #9
Senior Member
 
Coma's Avatar
 
Monaco Owners Club
Join Date: Nov 2010
Location: The Emerald Coast
Posts: 1,759
Make sure the auto shut down is selected to manual.
__________________
Jim and Jennie, Cats=Bittles and Potter, 2000 Dynasty 350 ISC
2013 Silverado 4x4 Towed with R1200GS in bed.
PROV23:4 Do not wear yourself out to get rich; have the wisdom to show restraint.
Coma is offline   Reply With Quote
Old 05-23-2016, 06:41 AM   #10
Moderator Emeritus
 
barmcd's Avatar


 
Monaco Owners Club
Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 13,426
Quote:
Originally Posted by jacwjames View Post
How much coolant did you drain out??

It takes more then 1 quart for the entire system.

When you filled the coolant did you pull the radiator fill cap completely out of the front cover???? It pulls out ~1 foot.

I know this because I made a huge mistake, I thought I had pulled it out enough but didn't and the hose was kinked. It would not take anymore coolant, when I started it did the same thing. I kept forcing it (I removed the heat sensor plug, BIG Mistake) and I actually got it hot and failed the engine. Had to replace generator with a used one $5K.

The temperature sensor is on top of the engine, passenger side, you have to remove the top cover to get to it. Located next to the thermostat.
I drained out most of a gallon and thought I put in about the same. I bought a gallon container of coolant and couldn't get all of it into the generator so I put the old coolant in an empty 1 gallon bleach bottle. Normally I'd know exactly how much I took out and how much I put in, but since I didn't reuse the same container I didn't know exactly. In retrospect I probably took out almost a gallon and put in a little over three quarts.

I did pull the radiator cap and hoses all the way out. The large hose does tend to kink where it comes out of the frame and stop you from putting more coolant in the radiator.

I ended up running it a full two hours under load for it's monthly exercise. I like having a generator, but I don't know if we'll really ever use it since we don't boondock at all right now.

I'm glad it has an overheat shutoff because I sure would have burned it up if it didn't.
__________________
Dennis and Katherine
2000 Monaco Dynasty
barmcd is offline   Reply With Quote
Old 05-23-2016, 06:43 AM   #11
Moderator Emeritus
 
barmcd's Avatar


 
Monaco Owners Club
Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 13,426
Quote:
Originally Posted by Coma View Post
Make sure the auto shut down is selected to manual.
I have it on manual start and stop now.
__________________
Dennis and Katherine
2000 Monaco Dynasty
barmcd is offline   Reply With Quote
Reply

Tags
diesel, generator, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
1999 Diplomat 7.5kw onan quiet diesel no switch poer PCB Camper Monaco Owner's Forum 16 10-19-2016 01:59 PM
Whirlpool washer turns on lights flash then turns off SuzzyQ Entegra Owner's Forum 17 06-21-2015 07:46 AM
Onan 7.5kw quiet diesel wont stop cranking redtail RV Systems & Appliances 11 05-26-2015 03:56 PM
Broken dipstick in Onan 5.5kw diesel generator Netmxer RV Systems & Appliances 2 01-21-2013 06:27 PM
Starting issue with 7.5KW Quiet diesel Gen FIRE UP Winnebago Industries Owner's Forum 5 02-06-2012 01:54 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:17 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.