Onan 75K generator question

Generator will not start....get error code 19...checked power connection, three fuses under radiator cap all checked good. When I checked the starter with a volt meter at the point where the ignition switch lead plugs on the starter test showed grounded now that it's being determined that the starter is bad.....next step was to test for voltage on the ignition wire when the starter switch was pressed ...no voltage...read on previous thread that one of the members found a problem with a relay that was under the generator cover...can the cover be removed on 2003 Monaco without removing the generator if yes need instructions
aidachry2003 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-22-2014, 08:38 PM   #2
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 14,608
What model Monaco do you have, is the generator on a slide.

You pretty much have to have full access to the generator to remove the cover. There are bolts all the way around the top.

A friend just had the same problem (code 19), turned out to be wiring going to the governor. This is a common problem with the vibration. He took it to a Onan service shop, they found it. The parts were cheap with ~1 hrs labor but his generator was on a slide.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 10-23-2014, 05:23 AM   #3
Senior Member
 
94-Newmar's Avatar
 
Join Date: Nov 2009
Posts: 2,043
The starter switch does not run directly to the starter, therefore you will not see any voltage at the starter posts when pushing the START/STOP button. The voltage present at the start/stop switch itself is merely control voltage and cannot be used to verify anything.

An Error 19 has nothing to do with the starter, nor the start circuit at all. An error 19 can only occur when the unit is running. I suggest this error was set during a previous run.

Disconnect the remote harness, top corner of the genset. This will disconnect all other start/stop switches except the one right on the front of the genset.

When you push and hold STOP can you hear the fuel pump run?

While pushing and holding STOP and if the fuel pump is running, check the DC voltage going into the generator. Does it drop below 10 volts?

If you push and hold START does the light flash quickly? If so, push and hold START for up to 60 seconds - the glow plug circuit should be energized during this period... does the starter circuit begin to engage? If not, repeat the process with a voltmeter in the DC line.. what is the voltage dropping to when the glow plugs are trying to heat?
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
94-Newmar is offline   Reply With Quote
Old 10-23-2014, 06:52 PM   #4
Member
 
aidachry2003's Avatar
 
Join Date: Nov 2013
Location: Fairfield, Alabama
Posts: 32
Quote:
Originally Posted by 94-Newmar View Post
The starter switch does not run directly to the starter, therefore you will not see any voltage at the starter posts when pushing the START/STOP button. The voltage present at the start/stop switch itself is merely control voltage and cannot be used to verify anything.

An Error 19 has nothing to do with the starter, nor the start circuit at all. An error 19 can only occur when the unit is running. I suggest this error was set during a previous run.

Disconnect the remote harness, top corner of the genset. This will disconnect all other start/stop switches except the one right on the front of the genset.

When you push and hold STOP can you hear the fuel pump run?

While pushing and holding STOP and if the fuel pump is running, check the DC voltage going into the generator. Does it drop below 10 volts?

If you push and hold START does the light flash quickly? If so, push and hold START for up to 60 seconds - the glow plug circuit should be energized during this period... does the starter circuit begin to engage? If not, repeat the process with a voltmeter in the DC line.. what is the voltage dropping to when the glow plugs are trying to heat?
I Have a Monaco Diplomat 40PBDD with chassis mount generator
Will Go thru test procedure that was outlined by 94-Newmar this weekend
aidachry2003 is offline   Reply With Quote
Old 10-25-2014, 02:36 PM   #5
Member
 
aidachry2003's Avatar
 
Join Date: Nov 2013
Location: Fairfield, Alabama
Posts: 32
The starter switch does not run directly to the starter, therefore you will not see any voltage at the starter posts when pushing the START/STOP button. The voltage present at the start/stop switch itself is merely control voltage and cannot be used to verify anything.

An Error 19 has nothing to do with the starter, nor the start circuit at all. An error 19 can only occur when the unit is running. I suggest this error was set during a previous run.

Disconnect the remote harness, top corner of the genset. This will disconnect all other start/stop switches except the one right on the front of the genset.

When you push and hold STOP can you hear the fuel pump run? YES

While pushing and holding STOP and if the fuel pump is running, check the DC voltage going into the generator. Does it drop below 10 volts? NO

If you push and hold START does the light flash quickly? YES If so, push and hold START for up to 60 seconds - the glow plug circuit should be energized during this period... does the starter circuit begin to engage?NO If not, repeat the process with a voltmeter in the DC line.. what is the voltage dropping to when the glow plugs are trying to heat? DROPS FROM 13.62 DOWN TO 13.22 THEN TO 13.62 BACK TO 13.62

Thanks ...what's my next step?
aidachry2003 is offline   Reply With Quote
Old 10-26-2014, 05:02 PM   #6
Registered User
 
Redsoxfan1's Avatar
 
Tiffin Owners Club
Join Date: Jun 2014
Posts: 32
Mine did the same thing, I checked the fuses under the rocker switch and ended up pulling the cover on top of the genset.

I had a sensor wire lose. Tightened it and it fired up immediately.

Good luck
Redsoxfan1 is offline   Reply With Quote
Reply

Tags
generator, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Winnebago and the Onan EC 30 pokgunner RV Systems & Appliances 19 07-16-2016 08:55 AM
Onan code 33 ldfeat Country Coach Owners Forum 7 10-11-2014 09:37 AM
Onan 5500 filter questions Bilgerat RV Systems & Appliances 3 10-07-2014 11:00 AM
Would you replace a 23 yr old Onan? Pexring RV Systems & Appliances 8 08-13-2014 05:14 AM
Onan Gen and Cummins ISL Oil Filter Number Scepter1 Class A Motorhome Discussions 3 01-20-2014 04:18 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:57 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.