We have an Astoria PE 3772, Can I safely run the generator while connected to shore power? Here's the situation, most small campgrounds only provide 30 amps. There are times I need to run the A/C, the microwave and a toaster oven all at the same time. I would like to start the gen set (for 50 amps) while cooking, and then shut it down and return to 30amps. I have been told that this practice will burn out coach electronics. I shut off the A/C while returning back to 30 amps. (To prevent brown out.) Any Ideas?
__________________
We both retired at 50, sold the house and are now living in a 2008 Damon Astoria PE
We LOVE It!
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
09-12-2008, 05:17 AM
|
#2
|
|
Junior Member
Join Date: Feb 2008
Posts: 6
|
We have an Astoria PE 3772, Can I safely run the generator while connected to shore power? Here's the situation, most small campgrounds only provide 30 amps. There are times I need to run the A/C, the microwave and a toaster oven all at the same time. I would like to start the gen set (for 50 amps) while cooking, and then shut it down and return to 30amps. I have been told that this practice will burn out coach electronics. I shut off the A/C while returning back to 30 amps. (To prevent brown out.) Any Ideas?
__________________
We both retired at 50, sold the house and are now living in a 2008 Damon Astoria PE
We LOVE It!
|
|
|
|
| |
|
09-12-2008, 09:01 AM
|
#3
|
|
Senior Member
Join Date: Apr 2007
Location: Hurricane, Utah
Posts: 177
|
You can do it but it is not a good idea. Very hard on the transfer switch and generator.
Sam
__________________
2004 315 Damon Challenger
Ford F53 20,500
|
|
|
|
| |
|
09-12-2008, 11:49 AM
|
#4
|
|
Senior Member
Join Date: Oct 2000
Location: Livingston, Texas
Posts: 124
|
There is a pigtail you can get at Camping World for your 50 amp plug, which allows you to plug into two 30 amp recepticles or a 30 and a 20 to run your AC. (need to insure that the 20 and 30 are separate circuits or it wil blow a campground fuze)
__________________
Kayo
2004 Damon 348 Workhorse W22 8.1 Vortec
USMC 0302 Semper Fi
|
|
|
|
| |
|
09-12-2008, 01:48 PM
|
#5
|
|
Senior Member
Join Date: Apr 2007
Location: Hurricane, Utah
Posts: 177
|
They also will not work if the 20 amp outlet is a GFI which has been required since the 70s.
Sam
__________________
2004 315 Damon Challenger
Ford F53 20,500
|
|
|
|
| |
|
09-12-2008, 05:32 PM
|
#6
|
|
Senior Member
Join Date: Jan 2007
Location: Hampton Falls, NH
Posts: 359
|
Tom and Diane...When you are using the shore power and start the genset, it automatically switches the load from the shore side to the generator side. The transfer switch has a set of contacts that simply move from one position to another. If a load is present, they will arc...both breaking and making. This will pit the contacts and shorten their life. Also, if you are running the genny and shut it off while a load is present, there could be a voltage spike that could fry your controller board on the generator. (I know, I did it)
The best way to do this is a pain but will ensure you have no problems. Shut the power off at the pedestal before starting the generator or, at the least shut everything you can off in the coach, especially the A/C. Then start the genset. Shut everything off again before you push "stop" on the generator.
If you go to your generators website this may be covered under their frequently asked questions section.
Hope this helps.
Chandler
__________________
2002 Damon Challenger 348
Wife, Dee
|
|
|
|
| |
|
09-13-2008, 06:31 AM
|
#7
|
|
Senior Member
Join Date: Apr 2007
Location: Hurricane, Utah
Posts: 177
|
Good post Chandler. It is also a good idea to let the gen run for at least a few minutes without a load both on startup and shutdown. This allows the engine to warm up and cool down gradually.
Sam
__________________
2004 315 Damon Challenger
Ford F53 20,500
|
|
|
|
| |
|
09-19-2008, 11:55 AM
|
#8
|
|
Senior Member
Join Date: Dec 2006
Location: Atlanta, GA. , South Beach, FL. Naples, Fl , Coral Gables,FL.
Posts: 1,109
|
last 2 posts says it all. good jobs guys!!!!!!!!
__________________
|
|
|
|
| |
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|