Old 09-24-2009, 01:29 PM   #1
Junior Member
 
Workhorse Chassis Owner
Join Date: Jul 2007
Posts: 24
120 Volt Problem

I noticed my plug in type polarity checker shows HOT/Neutral Reversed when plugged into shore power at the campground and again when I plugged in at my house. That scared me.

I disconnected and turned on the genny. The meter shows O.K. No problem. Both lights are yellow. Then I plugged into shore power again, the meter showed the same Hot/Neutral Reversed lights. That is, one amber and one RED.

I checked all receptacles for opens, loose wires, and nothing wrong. I do notice my male 30 Amp connector is showing age (2002) because the blades feel loose. I opened the connection from the other end of the cord to the entrance of the MH junction box. All looks correct and tight.

Should I start by replacing the end male connector or replace the entire cord? Or, am I having some other gremlin to look for? Thank you.

Steve
__________________

__________________
spat is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-24-2009, 01:48 PM   #2
Community Administrator
 
Route 66's Avatar


 
Newmar Owners Club
Retired Fire Service RVer's
Spartan Chassis
Join Date: May 2000
Location: Newark, DE
Posts: 25,614
A reversed hot/neutral is definitely not good.

Since more than one shore power is reversed and the generator is OK, I would check the power cord connections at the transfer switch for proper polarity.

Here is the correct wiring and color code for 30 amp service.
__________________

__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, previously 4 years as a fulltimer in a '07 DSDP

Route 66 is offline   Reply With Quote
Old 09-24-2009, 02:12 PM   #3
Senior Member
 
Dmiles's Avatar
 
Appalachian Campers
Forest River Owners Club
Ford Super Duty Owner
Join Date: May 2009
Location: Suffolk, VA
Posts: 473
I don't know of any way that loose blades would cause a reversed polarty reading, but from what you describe there could be a possibilty that somewhere along the line in the past, someone could have replaced your 30 amp power cord, and possibly got the wires reversed.

If you have a voltage meter that can read 120V AC (or can borrow one) there is a way that you can tell for sure whether your wiring is reversed or not. If you look closely at a 120V AC recepticle, you will see that one of the "slots" (for lack of a better term) that the blades plug into is bigger than the other. When you put one probe on ground (the one on the bottom that is shaped like an upside down "U") you should read incoming line voltage at the smaller slot, and nothing (or a very low, nominal reading) on the larger one.

If you find these readings reversed, you have a potentially dangerous situation that you should have looked at by an electrician that is familiar with RV wiring.
__________________
2011 Winnebago Vista 30W
Duane, Precy, 9 year old son Matt, and Abby, our American Eskimo.
Dmiles is offline   Reply With Quote
Old 09-24-2009, 02:12 PM   #4
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 18,085
Assuming your shore cord is the original (no replacement plug on the end), my guess is that the hot and neutral leads of your shore power cord have been reversed where they connect to the transfer switch. It would be all but impossible for the cord itself to fail in a way that swapped the hot and the neutral and did not cause a short.

But if the male plug on the shore cord has been replaced once, then somebody miswired it at that end. Just replace it and do it right.
__________________
Gary Brinck
Former owner of 2004 American Tradition
Home is in the Ocala Nat'l Forest near Ocala, FL
Summers in Black Mountain, NC
Gary RVRoamer is offline   Reply With Quote
Old 09-24-2009, 07:27 PM   #5
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,820
I will second the suggestion you check your shore power cord

IN this case. I would use a multimeter

This site links to all the diagrams you could possible need

nema plugs and socket wiring diagrams - Google Images

This is the 30 amp RV outlet

http://www.dasplace.net/RVWiring/DSC...0AmpSocket.jpg

And here is a standard wall outlet

http://www.leadsdirect.co.uk/images/...ng%20300px.gif

So the WIDE slot on the outlet is NEUTRAL

And as you look at the RV's plug with the round pin at the top the one on the LEFT is also neutral.. An ohmmeter between the two should show "Short" You will (of course) be UNPLUGGED when you do this (Since you are holding the plug in your hand)
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 09-24-2009, 09:21 PM   #6
Senior Member
 
skigramp's Avatar
 
Join Date: Sep 2005
Location: HOME: Oshkosh, WI
Posts: 2,102
easy way to further isolate ..

Here is an easy way to further isolate your problem ... buy a 30 amp male to 15 amp female adapter ... (Walmart or your local RV store)

Then plug your same polarity checker into the adaptor ... and then plug that adaptor into the pedestal ...

That will tell you whether the polarity is correct on the pedestal ...

I carry one of these and use it frequently .... particularly if there are any signs of recent activity around the pedestal ... or if I see an electricians truck on the premises ...
__________________
2012 Buick Enclave
Present At home Home: Oshkosh, WI

former owner 2004 Winnebago Journey 39W
skigramp is offline   Reply With Quote
Old 09-25-2009, 03:21 AM   #7
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,062
Quote:
Originally Posted by skigramp View Post
Here is an easy way to further isolate your problem ... buy a 30 amp male to 15 amp female adapter ... (Walmart or your local RV store)

Then plug your same polarity checker into the adaptor ... and then plug that adaptor into the pedestal ...

That will tell you whether the polarity is correct on the pedestal ...

I carry one of these and use it frequently .... particularly if there are any signs of recent activity around the pedestal ... or if I see an electricians truck on the premises ...
I would recommend the use of a Surge Guard or similar service entrance protection device. This will automatically check the pedestal before letting power into the coach as well as other benifits.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 09-25-2009, 08:30 AM   #8
Junior Member
 
Workhorse Chassis Owner
Join Date: Jul 2007
Posts: 24
120 Volt Problem

Thank you all for your response. The thing that's odd about my Hot/Neutral Reversed condition is that nothing was changed or replaced. I went from a normal condition, to a Hot/Neutral situation for no reason. I always keep a plug in polarity checker in a receptacle that I can visually observe at all times. So I went from normal to the abnormal for no obvious reason. Nothing (as far as 120 volt electrical) was replaced or changed for the past two years of my ownership of this RV. Could this condition be tied to the Switch Box? If so, can anyone tell me how to go about trouble shooting the switch box. I have two of them in the trunk area. Thank you.
Steve
__________________
spat is offline   Reply With Quote
Old 09-25-2009, 09:39 AM   #9
Moderator Emeritus
 
RustyJC's Avatar


 
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
Although I personally haven't run into this so I don't know if your particular circuit analyzer would give such an indication for this problem, but I wonder if you might not have developed a loose or floating neutral.

I would think that the circuit analyzer, upon detecting any voltage between neutral and ground (as would happen with a loose or floating neutral), might think that the neutral lead is "hot" and, thus, the hot and neutral leads are reversed.

(For clarification, I understand that the neutral and ground leads are bonded at/before the shore power pedestal.)

Rusty
__________________
2016 Ram Longhorn 3500 Dually 4x4 CCLB, 385/900 Cummins, Aisin AS69RC, 4.10
2014.5 DRV Mobile Suites 38RSSA #6972
Come join us on a TEXAS BOOMERS rally!
RustyJC is offline   Reply With Quote
Old 09-25-2009, 12:45 PM   #10
rek
Member
 
rek's Avatar
 
Join Date: Sep 2009
Posts: 85
This may have nothing to do with your problem but after Catrina I had to stay in someones back yard with a home wired 50 amp receptacle. They had forgotten to connect the neutral at the pole disconnect so I had two hots with no neutral for power and everything still worked.....for awhile. After 2 weeks my converter blew. The neutral return had been my trailer frame and the earth. Your neutral may not be good.
__________________
Rodger & Brenda, our big babys, Abbie (Irish Wolfhound) and Jack (Otter Hound)
06 Keystone Challenger 35RFQ, 7.3L 03 F350 Dually
rek is offline   Reply With Quote
Old 09-25-2009, 09:21 PM   #11
Senior Member
 
Workhorse Chassis Owner
Join Date: Feb 2005
Location: western wa.
Posts: 539
make sure your inverter isn't on.
__________________
2007 NRV DOLPHIN LX 6342

WORKHORSE W-22
cannon man is online now   Reply With Quote
Old 09-26-2009, 04:06 AM   #12
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,062
Steve, have you verified that you receptacle tester is good?
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 09-26-2009, 11:36 AM   #13
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,820
Quote:
Originally Posted by rek View Post
This may have nothing to do with your problem but after Catrina I had to stay in someones back yard with a home wired 50 amp receptacle. They had forgotten to connect the neutral at the pole disconnect so I had two hots with no neutral for power and everything still worked.....for awhile. After 2 weeks my converter blew. The neutral return had been my trailer frame and the earth. Your neutral may not be good.

I had the same thign in my HOUSE of all places (Before I got the MH) the neutral on the drop from the pole went bad and as a result it was floating, the Ground return was via the safety ground (Water pipe back then... New ground rod and water pipe now) and what's worse the bypass cable on the plastic water pump.. the idiots at water & sewer left the screws loose so it was not a good ground

Thankfully a nice man from Detroit Edison with an insulate screwdriver tightened those down.. Then a few more nice men came out and replaced the drop
__________________

__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hazard Flasher Problem Ms. Jean Thor Industries Owner's Forum 17 08-28-2014 05:54 PM
97 madp electrical problem Glen M Newmar Owner's Forum 5 09-20-2008 12:08 PM
Dip/Endeavor Wiper Problem Resolved Robin_M Monaco Owner's Forum 21 01-28-2008 08:59 PM
A Rather Odd A/C Problem ( a bit long) gasbag MH-General Discussions & Problems 7 10-16-2007 11:10 AM
No power to 120 volt outlet on slide..and the solution Chandler Damon 2 08-03-2007 02:19 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:47 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.