Go Back   iRV2 Forums > MOTORHOME FORUMS > Class A Motorhome Discussions
Click Here to Login
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 08-02-2013, 03:13 PM   #1
Senior Member
 
lenjen's Avatar
 
Join Date: Mar 2011
Location: Conyers, GA
Posts: 569
2 30 to make 50

This probably has been discussed many time but it is not coming up in my search. My coach is 50 amp, most RV CG's we go to are 30 amp. I use a short dog bone to reduce to 30 amp. I haven't had an issue but I'm very careful not to run AC/Microwave/ hair dryers/ etc at the same time.

Am I understanding this ad correctly? Ad shows the Y with one 50 amp end and two 30 amp ends. As some sites have two 30 amp receptacles, would this allow me to operate like normal 50 amps service?

50 Amp 125/250V RV Female - (2) 30 Amp RV Male Plus Y-Adapter with Powersmart LED's - Furrion F5431RY-SB - Electrical Cords - Camping World

thank you for any input...
Sandi
__________________

__________________
Sandi
Loving My RV
2005 Dolphin 6355 LX WH24
lenjen is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-02-2013, 03:24 PM   #2
Senior Member
 
Join Date: Oct 2009
Posts: 248
1. 2 30's doesn't make 50 - a 50Amp connection gives you 2 * 50amp supplies = 100amps - just be aware of that when powering up on the circuits

2. The Y connection will only work if the 2 30amp connections that feed it are on SEPARATE phases and do not have a Earth Leakage Circuit Breaker - that means that on about 50% of pedestals it won't work.

When allowed, in the past I have been given permission to use the 30amp from one pedestal and use a 30amp extension to connect to the next sites pedestal - when they wire up the CG then tend to use different phases for each lot space and it makes it possible to use the Y

I have had one for about 6 years and maybe used it on 3 occasions!
__________________

steveclv is offline   Reply With Quote
Old 08-02-2013, 04:07 PM   #3
Senior Member
 
lenjen's Avatar
 
Join Date: Mar 2011
Location: Conyers, GA
Posts: 569
Steveclv, thank you. The most I know about electricity is you plug in and it works. So anything the least bit technical is beyond me.

The sites where I thought this might be possible would be where 2, 3 or 4 RV's can use the same post with up to 4 receptacles per box.

If I understand your reply the above sites probably would not give me the extra 20 amps. Correct?

Sandi
__________________
Sandi
Loving My RV
2005 Dolphin 6355 LX WH24
lenjen is offline   Reply With Quote
Old 08-02-2013, 04:43 PM   #4
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 3,859
The most you're ever going to get using that is 2x30amps = 60amps. Not the 2x50amps = 100amps for a real 50amp connection. The major downside is that if the two plugs you connect to are on the same phase, you're going to do a major overload on the neutral wiring and burn something up. Unless you're absolutely sure you'll be able to test the plugs to make sure they're on opposite phases, don't do it.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 08-02-2013, 04:49 PM   #5
Senior Member
 
lenjen's Avatar
 
Join Date: Mar 2011
Location: Conyers, GA
Posts: 569
Thank you, FlyingDiiver. I saw the ad and thought the product might be a good thing... but 2 negative replies are enough for me to not buy or attach it to my RV.
__________________
Sandi
Loving My RV
2005 Dolphin 6355 LX WH24
lenjen is offline   Reply With Quote
Old 08-02-2013, 04:56 PM   #6
Senior Member
 
Ramblin's Avatar
 
National RV Owners Club
Workhorse Chassis Owner
Ford Super Duty Owner
Carolina Campers
Join Date: Aug 2011
Posts: 2,253
I have one and have used it successfully a few times.
__________________
2002 National Dolphin LX 6356
Workhorse W-22 chassis
Don't believe everything you think.
Ramblin is offline   Reply With Quote
Old 08-02-2013, 05:02 PM   #7
Senior Member
 
BFlinn181's Avatar


 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 17,913
In addition to the above, you have to know how your RV is wired for 50 amps. Two hot leads of 50 amps come into the coach. The alternating current is in opposite phase so not to overload the shared neutral wire. The the RV, each leg is used to power part of the rig. One might power the front A/C, the front TV, and the coffee pot. The other phase might cover the rear A/C, the Converter/Inverter, bathroom outlet (hair dryer) etc. If you hook one leg to 20 amps and need 23, you'll trip a breaker. If one is hooked to 30 amp and is only using 15, you'd need to switch plugs at the pedestal. Many times the 20 amp circuit on the pedestal is GFI protected, it will trip when combined with the 30 amp circuit. In addition, ask at the office if it's O.K. to hook up to more than one outlet in the pedestal, many will want to charge more.

At minimum I'd be sure to have an EMS so I could monitor amp usage and protect the RV.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 08-02-2013, 05:43 PM   #8
Senior Member
 
clyon51's Avatar
 
Monaco Owners Club
Join Date: Mar 2012
Location: Arizona West RV Park, Yuma, Az
Posts: 4,188
Quote:
Originally Posted by FlyingDiver View Post
The most you're ever going to get using that is 2x30amps = 60amps. Not the 2x50amps = 100amps for a real 50amp connection.


The major downside is that if the two plugs you connect to are on the same phase, you're going to do a major overload on the neutral wiring and burn something up. Unless you're absolutely sure you'll be able to test the plugs to make sure they're on opposite phases, don't do it.
I agree FD. What I question is, or would like clarification, the 50a portion neutral of the adapter is capable, and I would assume so are the 2 30a portions are capable. So you are saying the neutral in the pedistal box (on the same phase) would be under overload, not the adapter or coach cable, correct?

Not that it should mean go ahead, 'cause it aint a gonna hurt my stuff' of course Just curious. Also, how can one determine separate phases on two outlets. Never had to worry about that before.
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
clyon51 is offline   Reply With Quote
Old 08-02-2013, 06:26 PM   #9
Senior Member
 
BFlinn181's Avatar


 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 17,913
If you were using the full 30 amps of each leg on the same phase, the neutral would be carrying 60 amps. It is only rated for 50 amps. Your shore cord, connectors in the ATS, plugs, etc. could be over heated.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 08-02-2013, 06:36 PM   #10
Senior Member
 
Jim_HiTek's Avatar
 
Join Date: Nov 2011
Location: Full time RV'er
Posts: 1,760
Of course you have a digital volt meter, right?

With that set at over 240Vac scale, you plug one lead into the hot of one 30a outlet, and the other lead into the hot of a different 30a outlet. If you read 240Vac, then they are out of phase (a good thing). The same would be true if you plugged one lead into the hot of a 20A outlet on the same pedestal. But as has been mentioned, there may be a GFI system installed and it won't allow you to 'Y' the circuits to the same RV. Other times, you'd be fine.

As far as using the Y adapter on two 30A systems that are IN-PHASE, you would measure Zero volts between the hots. As mentioned, you could potentially have 60A running through your 50A RV cord neutral if you connect up that way. Not likely if you're conservative and don't try to run to many devices at once. And of course, things like a 240V oven wouldn't work in that case. The panel would light up, but there wouldn't be enough voltage to run the burners...only a concern if you have an all electric rig.

Some times you'd be able to happily connect up that way, and that would probably be in newer parks with no neighbors other times probably best to just use your 50A to 30A adapter.
__________________
'02 Winnebago Journey DL, DSDP, 36' of fun.

Visit my RV Travel & Repair Blog at : http://chaos.goblinbox.com
Jim_HiTek is offline   Reply With Quote
Old 08-02-2013, 06:46 PM   #11
Senior Member
 
lenjen's Avatar
 
Join Date: Mar 2011
Location: Conyers, GA
Posts: 569
Quote:
Originally Posted by Jim_HiTek View Post
Of course you have a digital volt meter, right?

.
Are you asking me... the OP? You must be kidding! Did you read my second post. No I would not know how to use one if I had it. I do have a surge protector. With the replies above, I'll stay with my one cord with a reducer from 50 to one 30.
__________________
Sandi
Loving My RV
2005 Dolphin 6355 LX WH24
lenjen is offline   Reply With Quote
Old 08-02-2013, 06:50 PM   #12
Senior Member
 
clyon51's Avatar
 
Monaco Owners Club
Join Date: Mar 2012
Location: Arizona West RV Park, Yuma, Az
Posts: 4,188
Quote:
Originally Posted by BFlinn181 View Post
If you were using the full 30 amps of each leg on the same phase, the neutral would be carrying 60 amps. It is only rated for 50 amps. Your shore cord, connectors in the ATS, plugs, etc. could be over heated.
Ok, so it would be correct to say the single neutral in the 50a cord would only carry 50a max (even if 100a is being used) because the 2 phases cancels out one of the 50a legs?

In other words, if 60a were being used in this case, the neutral would carry the 60a on the rated 50a neutral?

Where I'm still confused is modern power is 3 phase. And were talking the 2 inbound legs from the power company as being 2 phases. I guess that's something I need to investiage myself. I didn't mean to muddy up the thread.
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
clyon51 is offline   Reply With Quote
Old 08-02-2013, 07:00 PM   #13
Senior Member
 
BFlinn181's Avatar


 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 17,913
Quote:
Originally Posted by clyon51 View Post
Ok, so it would be correct to say the single neutral in the 50a cord would only carry 50a max (even if 100a is being used) because the 2 phases cancels out one of the 50a legs?

In other words, if 60a were being used in this case, the neutral would carry the 60a on the rated 50a neutral?
Alternating current goes from 120 v (+) to 120 (-) 60 times (cycles) a second. In an RV 50 amp outlet, as one leg is decreasing, the other leg is increasing, so the neutral leg never 'sees' more than 50 amps. If the two 30 amp circuits were being supplied in the same phase (common in one pedestal) then they are both supplying 30 amps at the same instant. The neutral would then carry the combined 60 amps.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 08-02-2013, 07:34 PM   #14
Moderator Emeritus
 
RustyJC's Avatar


 
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
Quote:
Originally Posted by clyon51 View Post
Where I'm still confused is modern power is 3 phase. And were talking the 2 inbound legs from the power company as being 2 phases. I guess that's something I need to investiage myself. I didn't mean to muddy up the thread.
50 amp 120/240V service uses only 1 phase from the power company. That phase powers a center-tap neutral transformer to provide split-phase 120/240 V output. The ground conductor is not shown in the following diagram.



Rusty
__________________

__________________
2016 Ram Longhorn 3500 Dually 4x4 CCLB, 385/900 Cummins, Aisin AS69RC, 4.10
2014.5 DRV Mobile Suites 38RSSA #6972
Come join us on a TEXAS BOOMERS rally!
RustyJC is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:38 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.