2 x 20 amp to 50 amp connection

I'm trying to find more than 20 amps for my 2005, 45' Country Coach when I'm visiting someone's home. Would it work if I used two separate 20 amp circuits from the home and wired them to my 50 amp RV cord? An electrician showed me how to do it. He said to make sure the two home circuits are separate so they add up to 240 V. Would these two 20 amp, 120 V legs work? I've seen another thread where there is a 30a/20a to 50a conversion cord, so I'm thinking this may work.

Thanks, Doug
__________________

__________________
backagain is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-29-2016, 09:32 PM   #2
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 14,108
Done correctly you can power up both legs of your 50 amp coach systems.
BUT, you will only have 20 amps on a 50 amp circuit . RV site plug supplies 50 amps to each side , so power use management is in order.
And that's if the two circuits you plug into are 20 amps , you'll have to go back to the circuit breaker panel to check , as most older homes will only be 15 amps per circuit , and you'd need to check for all other loads in the house.
Could be a lot of tripping of C/B s going on.
__________________

__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 09-29-2016, 09:48 PM   #3
Senior Member
 
bdpreece's Avatar
 
Monaco Owners Club
Join Date: Mar 2000
Location: Woodburn Oregon USA
Posts: 2,505
I am not sure I would do that to my worst enemy. For starters you have to think that maybe the home owners may also be using these circuits to run things in their home. Next you will have to run extension cords after finding two separate circuits. The longer the run the more voltage drop and these cords need to be good heavy duty probably 12/3 wire which will run you in the neighborhood or $100 each. You really don't want to burn down their house do you.
__________________
Brian, Loretta & Daisy (Golden Retriever)
2008 Holiday Rambler Endeavor 40 PDQ , ISL 400
2014 Ford Explorer toad
bdpreece is offline   Reply With Quote
Old 09-29-2016, 09:51 PM   #4
Senior Member
 
Join Date: Sep 2016
Location: Woodstock GA
Posts: 249
I agree. You have to know your usage balance to know if it is going to do you any good. As long as you have breakers that limit the pull to not exceed the wire you can put any plug you want. The limit is the breakers, and I would also suggest spending $20 and putting in fresh breakers for such an "implementation". Remember that just because something is rated for 50 does not mean it is using 50. Limit your inputs and as long as your needs do not exceed it you are fine.

It is not the optimal solution but depending on the rig needs is possible if you are ABSOLUTELY SURE on the wire and limit the inputs based on the wire.
__________________
imob is offline   Reply With Quote
Old 09-29-2016, 10:09 PM   #5
Senior Member
 
Join Date: Jul 2014
Posts: 8,433
What you propose will work but you shouldn't have make sure they add up to 240 volts.

If you find 2 separate circits, even on the same leg, you will only be supplying 40 amps, so you won't be overloading the shared neutral line.

Modern homes, 1980s and up, wire kitchens and dinning rooms with, at least 2, 20 amp circuits. Then you can try the laundry room for a 20 amp circuit.

As pointed out, you may have some breaker tripping, sharing the loads with the house. That would be the case using only one circuit anyway.

Another option is to adapt to a 240 volt electric dryer outlet, if it's a 4 prong plug. You would have more power and could go to generator when laundry needs to be done.
__________________
twinboat is online now   Reply With Quote
Old 09-29-2016, 10:17 PM   #6
Junior Member
 
Join Date: Aug 2016
Posts: 25
Quote:
Originally Posted by Skip426 View Post
...most older homes will only be 15 amps per circuit , and you'd need to check for all other loads in the house.
Could be a lot of tripping of C/B s going on.
If the home owner will let me, and they're not already loading up those circuits, two 15 amp lines are better than one
__________________
backagain is offline   Reply With Quote
Old 09-29-2016, 10:22 PM   #7
Junior Member
 
Join Date: Aug 2016
Posts: 25
Quote:
Originally Posted by bdpreece View Post
The longer the run the more voltage drop and these cords need to be good heavy duty probably 12/3 wire which will run you in the neighborhood or $100 each. You really don't want to burn down their house do you.
Ha ha. I bought a thick $100 cord about 10 years ago. Finally I have a use for it. I'll have to make the second cord a short run. The breaker should prevent an overload and possible fire.
__________________
backagain is offline   Reply With Quote
Old 09-29-2016, 10:30 PM   #8
Senior Member
 
Join Date: Sep 2016
Location: Woodstock GA
Posts: 249
Quote:
Originally Posted by backagain View Post
Ha ha. I bought a thick $100 cord about 10 years ago. Finally I have a use for it. I'll have to make the second cord a short run. The breaker should prevent an overload and possible fire.
Though it does not sound like an issue in this case note should be taken that a 100' braided (flexible) cord and a 100' of solid wire cord are completely different. The reason we only use braided cord on short segments and that it requires a much thicker wire is because of the energy loss. Solid wire which is not flexible can safely carry much more power then the same gauge wire if braided.
__________________
imob is offline   Reply With Quote
Old 09-29-2016, 10:31 PM   #9
Junior Member
 
Join Date: Aug 2016
Posts: 25
Quote:
Originally Posted by imob View Post
You have to know your usage balance to know if it is going to do you any good.
By "usage balance", do you mean what each leg of the 50 amp RV cord supplies in the coach? This would be a good question. For example, if one leg just supplies the A/C units (I have 3), and it's cool like where I am now (Canada), then this might not help much cause I don't need the A/C. But in a warmer climate, I may be able to run 1 A/C unit on the one leg.
__________________
backagain is offline   Reply With Quote
Old 09-29-2016, 10:36 PM   #10
Junior Member
 
Join Date: Aug 2016
Posts: 25
Quote:
Originally Posted by twinboat View Post
What you propose will work but you shouldn't have make sure they add up to 240 volts.

Another option is to adapt to a 240 volt electric dryer outlet, if it's a 4 prong plug. You would have more power and could go to generator when laundry needs to be done.
Yes, the electrician told me to test the 2 black wires (small prongs) for 240 V.

Good idea about the electric drier outlet. Might be more difficult to access.
__________________
backagain is offline   Reply With Quote
Old 09-29-2016, 10:39 PM   #11
Junior Member
 
Join Date: Aug 2016
Posts: 25
Quote:
Originally Posted by imob View Post
Though it does not sound like an issue in this case note should be taken that a 100' braided (flexible) cord and a 100' of solid wire cord are completely different. The reason we only use braided cord on short segments and that it requires a much thicker wire is because of the energy loss. Solid wire which is not flexible can safely carry much more power then the same gauge wire if braided.
Mmm... the cord is thick and not that flexible. How can I tell if it's solid or braided?
__________________
backagain is offline   Reply With Quote
Old 09-29-2016, 10:40 PM   #12
Senior Member
 
Join Date: Sep 2016
Location: Woodstock GA
Posts: 249
"Balance" can mean many things depending on your rig and configuration and you need to know that before you wire it. It could mean something as simple as do not run both AC and the clothes washer at the same time or you need a special schema. At the end of the day the critical piece is know the source wire and make sure you can not exceed its limits.
__________________
imob is offline   Reply With Quote
Old 09-29-2016, 10:42 PM   #13
Senior Member
 
Join Date: Sep 2016
Location: Woodstock GA
Posts: 249
Quote:
Originally Posted by backagain View Post
Mmm... the cord is thick and not that flexible. How can I tell if it's solid or braided?
That's an easy one. If you strip the cover and it is one wire.. that is solid. If you strip it and it is "many" wires that you can "twist" around.. that is a braided/standed wire.

Example: http://www.cableorganizer.com/images...-wire-core.png
__________________
imob is offline   Reply With Quote
Old 09-30-2016, 05:40 AM   #14
Senior Member
 
Tiffin Owners Club
Appalachian Campers
Mid Atlantic Campers
Coastal Campers
Freightliner Owners Club
Join Date: Jan 2015
Posts: 1,113
No, as an electrical engineer....this will not work. I'll give you a short summary, and then the more detail info if your stomach is up for it.

The reason this won't work is because of the GFCI circuits that you will be plugging into. The GFCI breakers will trip and turn the power off.

By code, to avoid electrocutions, any outlets that are near water, outside, garages, etc are protected by a GFCI breaker. The two common installations are either a GFCI circuit breaker in your circuit breaker box (which then protects all of the sockets downstream on that breaker), or the outlet which has the two little buttons on them and a light which are typically found in bathrooms (which also then protect all downstream sockets that are daisy chained off of them).

A socket has three wires to it, the power leg (black or red), a neutral leg (white), and a ground (green or bare copper). The alternating current normally goes out the power leg to the item being powered, and then returns on the neutral leg going back to the breaker box. The ground should have no current on it, and ties the frame to earth ground. Electrocutions occur when the power is able to find it's way to/thru your body to earth ground, a path different than thru the cable. The way a GFCI breaker works, is that it very closely monitors the current of both the positive leg and the neutral leg. If it detects that those two current streams are different, it quickly trips the breaker at a current less than will kill you, and quick enough so that it doesn't. If the current coming out the positive leg, does not match the current coming back on the neutral leg, then it must have found a path to ground somewhere other than it should have, and the GFCI is tripped.

Here's your proposed connection on a 50amp RV: A 50 amp plug has two power legs, one neutral leg, and one ground cable. When you make your cabling dongle that you are talking about, you would have to bring together two circuits, each comprised of a pos/neut/grnd. Pos #1 would connect to Leg#1 of a 50amp plug. Pos#2 would connect to Leg#2 of the 50amp plug. Both Neu#1 and Neu#2 would have to connect together and attach to the single neutral of the 50 amp plug. Both Grnd#1 and Grnd#2 connect together and are attached to a single ground lug on the 50 amp plug.

Here's why it won't work in operation: Once connected, you turn something on (a lamp) in the coach, and lets say it happens to be a circuit that is getting powered from your house cable #1. The Alt Current flows from your house circuit breaker box out on the positive leg #1, thru GFCI#1 in your garage, to your dongle, thru the coach power cord, to the coach circuit breaker box, and to the lamp. That same current returns on the neutral headed back to the house. When it reaches your dongle, it will get to where you tied the two neutrals together, and current will always take the path of least resistance, effectively splitting it's current. Half the current will go back towards your house thru GFCI#1, half thru GFCI#2. When the GFCI sees the minutest difference in current ("all" of the positive leg lamp current vs. "some" of the negative return lamp current), it will trip to prevent electrocution. You will never legitimately get this dongle to work under the electrical code standards.

What you CAN do, is use one house/garage socket to connect a normal 20amp to 30amp dongle, and then a 30amp to 50amp dongle, then connect your coach power cord. Then run a separate extension cord out to the RV from a different house/garage circuit, thru the slide to the kitchen area, and plug the refrig or microwave into it (make sure the extension cords are rated at 20 amps). Remember however, the extension cords will have an internal resistance to them, and using high current devices will result in a drop of voltage at the device (V=i x r). Incandescent lamps don't care if the voltage isn't high, electronic control boards and motors do.

You may say....but wait, the house and socket I'm plugging into is circa 1940 and doesn't have any grounded outlets or GFCI sockets, and I'd like to plug into it. Then you take your (and your spouse/kids) life into your own hands. Don't be a fool, the GFCI's are made to protect your life.

As a side note, if you read the fine print of that 20a/50amp dongle that you referenced in the very first post, you will see that it will say does not work with GFCI sockets. Unless you are at a VERY old campground which isn't up to electrical code standards, it won't work. For example: "This versatile adapter enables RV users with 50-Amp service to run more appliances when 50 amp service is not available. Simply plug the 50 AMP Adapter Cheater Box into a 120 volt/30 amp and a 120 volt/20 amp source on two separate circuits to achieve a 240 volt/50 amp output. "Will not operate on a gfci circuit." Includes a 30 amp to 20 amp adapter and is made of high impact plastic. For outdoor use, and comes with a one year warranty. Features & Specifications 1 year warranty Plugs into a 30 amp and a 20 amp source Great for RVs Requires two separate circuits Able to run more appliances"
__________________

__________________
DaveB, Raleigh, NC
2015 Tiffin RED 33AA
2014 Honda CRV
Kiawah is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50 amp connection how can you hook up an RV with a 50 amp plug to a generator with 30 Luds RV Systems & Appliances 9 04-15-2015 05:57 PM
Fleetwood 50 amp power cord connection problem Hammer48 Fleetwood Products Owner's Forum 25 07-01-2012 09:51 PM
Help on cell phone purchase & Internet Connection werv2go Technology: Internet, TV, Satellite, Cell Phones, etc. 6 09-05-2010 01:10 PM
30 vs 50 Amp Connection Maxie iRV2.com General Discussion 10 12-23-2007 01:47 AM
30 amp connection Cookieman Excel Owner's Forum 10 06-04-2007 02:37 PM

» Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:07 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.