Leg A of my 2002 Beaver 120 volt system works fine. Leg B has no voltage at any of the coach 120 volt outlets. Breakers are all showing good. GFI's will not test as there is no voltage at any of the outlets. Is there a fuse or breaker that I am missing?
__________________

dennismartin is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-28-2013, 02:05 PM   #2
Senior Member
 
Chuck48's Avatar
 
Join Date: Mar 2012
Posts: 134
Check your transfer switch. Power not getting through on leg B. probably damaged contacts in transfer switch. GFCI will not test or reset without power to them.
__________________

Chuck48 is offline   Reply With Quote
Old 10-28-2013, 04:41 PM   #3
Senior Member
 
jerichorick's Avatar
 
Winnebago Owners Club
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 3,430
At your transfer sw, open the cover and carefully measure the voltage on the terminals. From the shore cord connections you should see 240VAC black to red and 120VAC black OR red to white or ground.

If the shore power checks correctly measure the voltage in the same manner on the feed going to the power panel. If the voltage check is not identical there is a problem in the switch. Unplug the shore power and tighten all of the connections in the transfer switch, clean the contacts on the plug and lube with anti-oxide grease. If no loose connections are found or a problem with the plug the transfer switch needs to be replaced.
__________________
Rick & Melissa Young, 2011 Itasca Meridian 40U, Frtliner XCL, Cummins ISL 380HP/DEF, Allison 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox, EEZ TPMS, TruCenter steering control
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 10-28-2013, 04:48 PM   #4
Senior Member
 
beaverfever's Avatar
 
Join Date: Dec 2010
Posts: 829
have you checked the circuit breakers on your inverter?
beaverfever is offline   Reply With Quote
Old 11-11-2013, 11:58 AM   #5
Junior Member
 
Join Date: Nov 2012
Posts: 3
Quote:
Originally Posted by jerichorick View Post
At your transfer sw, open the cover and carefully measure the voltage on the terminals. From the shore cord connections you should see 240VAC black to red and 120VAC black OR red to white or ground.

If the shore power checks correctly measure the voltage in the same manner on the feed going to the power panel. If the voltage check is not identical there is a problem in the switch. Unplug the shore power and tighten all of the connections in the transfer switch, clean the contacts on the plug and lube with anti-oxide grease. If no loose connections are found or a problem with the plug the transfer switch needs to be replaced.
Voltage is 120 in the transfer box at both switches on the power side. Leg 1-2-3 on bottom switch has 120 volt on back side of switch, Leg 4-5-6 on top switch has zero volts on the back side. A transformer box feeding into the transfer switch box is humming but I can't determine which of the 4 transformers (2 signal, 2 ring type instrument) are humming. Is this normal? Hate to buy a new transfer box if it is a small transformer prior to the transfer switches.
dennismartin is offline   Reply With Quote
Reply

Tags
beaver



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 12:01 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.