2003 5.5K Onan Generator Code 45
2003 Fleetwood Southwind, bought used with 55,000 miles and little to no maintenance. Generator would not start after Coach fuel pump replacement (tank had to be dropped). 3/4 tank fuel, oil is full, primes for 30 seconds, will not start after cranking. 2010 RJay suggested "checking slip rings for corrosion." More information would be helpful, or is this an"authorized Onan dealer" visit?
Thank you.
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
04-28-2014, 12:32 PM
|
#2
|
Senior Member
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
|
Don't know exactly what generator model you have, but Onan has a pretty complete website if you Google your model, I'm sure you'll find exactly what code 45 means for your generator.
__________________
Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
|
|
|
04-29-2014, 05:19 AM
|
#3
|
Senior Member
Join Date: Nov 2009
Posts: 2,043
|
Randy,
Error 45 is s speed sense fault - which can be 3 different things. But first you mention a potential fuel issue.. Pull the fuel line off the carb inlet, aim the line into a can then push and hold STOP to engage the fuel pump only. Are you getting any fuel? If not and the fuel pump is running, you can always get a 1 gal can of fuel and a seperate fuel line and while looking underneath the genset you can attach your own fuel supply to the INLET side of the fuel pump. This will help determine if you have pick-up issues in the coach tank or not.
Back to the 45 error code.... can be caused by brushes, belt or stator:
Pull the brush block assembly (2-10mm bolts - EASY access) and inspect the brushes.. should freely move up and down against the springs in the brush holder. Check slip rings that the brushes ride against. Should be clear copper in color - dark black means they need cleaned. (very common - can be repaired while unit is in the coach)
With the brush block out, push START momentarily and make sure the slip rings are spinning with the engine. If not, either broken belt or frozen/seized tensioner. (common - requires removing genset from coach)
If the brushes are ok, slip rings are ok and the rotor/slip rings are turning true with the engine cranking, then it could be a shorted stator. The speed sense circuit is obtained thru the stator and if it's shorted anywhere in the windings it will cause a 45 error. (rare - requires removing genset from coach, separating alternator from engine)
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
|
|
|
05-03-2014, 01:09 PM
|
#4
|
Junior Member
Join Date: May 2013
Posts: 5
|
Found leaking in-line filter at Float bowl, replaced. No gas from Coach fuel tank line. Dropped generator fuel line into portable gas can, primed and generator started. Warmed-up, then loaded with an air conditioner. Generator stumbled but continued to run.
Any advise on Fuel Pickup line, other than drop the Tank?
|
|
|
05-03-2014, 01:14 PM
|
#5
|
Senior Member
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
|
Quote:
Originally Posted by Randy_Miller
Found leaking in-line filter at Float bowl, replaced. No gas from Coach fuel tank line. Dropped generator fuel line into portable gas can, primed and generator started. Warmed-up, then loaded with an air conditioner. Generator stumbled but continued to run.
Any advise on Fuel Pickup line, other than drop the Tank?
|
You could try compressed air blown back up line to fuel tank. If it's just a little crud blocking the screen it will be blown off. Be sure to have gas cap off. If it works, you'll know the tank needs cleaning. If it doesn't work, it might mean a kink in the fuel line.
__________________
Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
|
|
|
05-03-2014, 04:30 PM
|
#6
|
Senior Member
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 5,931
|
Follow the line back to the tank. It is hard to see, but you can usually take a mirror and flashlight and check that the generator fuel line was hooked back up. Also check to see if it looks like the connection was tightened.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2014 Honda CRV toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
|
|
|
05-04-2014, 07:17 PM
|
#7
|
Member
Winnebago Owners Club
Join Date: Mar 2012
Posts: 63
|
whoever did the fuel pump replacement messed up the generator pickup line
|
|
|
07-19-2015, 12:18 PM
|
#8
|
Senior Member
Join Date: May 2006
Location: SoCal
Posts: 1,123
|
The stumbling is exactly normal when a load is applied. It only lasts at most a second, then operates as normal with load.
__________________
2020 Grand Design Reflection 315RLTS
2019 GMC Sierra Denali Duramax
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|