30 to 50 AMP Question

Well, the coach is in back at the dealer again. We have noticed some electrical issues, one caused the automatic transfer switch to require replacement. Another, issue is the AC causes the generator to flip the breaker. When we are plugged in to electricity breakers pop for no apparent reason. We have talked to the service people about this. They have suggested to us that we buy a 30 to 50 amp converter and plug into the 50 amp service whenever possible. Our coach is wired for 30 amp service and we could not find any literature that says this is the right thing to do. Anyone out there ever done this as a regular practice?
__________________

__________________
sharksgirl21 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-03-2012, 10:33 PM   #2
Member
 
GuitarLefty's Avatar
 
Join Date: Jul 2012
Posts: 77
I would get a local electrician involved, breakers could be aged, they are designed only to carry only 80% of it's rated capacity. So either the equipment is (non-professional opinion) in disrepair, or the breaker has weakened, or a combination of the two factors.
Going to 50 amp might really cause someone serious harm, the breaker is actually designed to sense and react to heat created by electrical current
__________________

__________________
GuitarLefty is offline   Reply With Quote
Old 09-03-2012, 10:42 PM   #3
Senior Member
 
Mr_D's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 28,382
Going to a 50 amp connection would not help anything if it's the breakers going off inside the rig. There is some other problem.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is offline   Reply With Quote
Old 09-04-2012, 12:21 AM   #4
Senior Member
 
historyljc's Avatar
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Feb 2008
Location: Pensacola, Florida
Posts: 5,173
If this coach isn't under warranty, I'd find someone else to look for the cause. What is your dealer recommended is pure BS.
__________________
Travel well, travel safe,
Jim
2006 Tiffin Phaeton - 2011 Cadillac SRX
historyljc is offline   Reply With Quote
Old 09-04-2012, 04:09 PM   #5
Member
 
Join Date: Mar 2007
Posts: 74
Run don't walk and find another dealer or a good mobile tech.
__________________
st687, 97 Foretravel U270
08 Saturn Vue
University of Parris Island class of 66
st687 is offline   Reply With Quote
Old 09-04-2012, 04:49 PM   #6
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Remember one important characteristic of a RV salesperson is that they don't know diddly squat about how a RV operates or runs. The ONLY thing that they are really sure of is the profit margin on a new or used coach which allows them to know exactly how much they can squeeze out of a potential buyer.

Talk to a professional and in this case listen to people who have hooked up to thousands of RV pedestals around the country with both 30 and 50 amp service.

Bottom-line, your coach only needs 30 amp service. There are some parks that ONLY offer 50 amp service where they will loan you a 50-30 amp adapter to use while there.

Dr4Film ----- Richard
__________________
Dr4Film is offline   Reply With Quote
Old 09-04-2012, 05:07 PM   #7
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 16,208
Using a plug adaptor is not going to change the amount of electricity flowing into the RV. That is the most asinine suggestion I've heard from a dealer in quite a while!

Check that all wire connections in circuit breaker panel are tight. This is not something to ignore, fires do happen.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 09-04-2012, 05:27 PM   #8
Senior Member
 
awwall's Avatar
 
Join Date: Jul 2012
Location: Biloxi, Ms
Posts: 199
Transfer switch replacement may be a clue. Sounds like something is loose. Probably a loose main neutral. A loose neutral will cause all kinds of strange events, including a FIRE. I would have a qualified electrician do a once over on the electrical system. Also, I would not be powering the thing up until I found the problem.
__________________
Wayne and Susan
2012 Georgetown 351 DS | 2012 Ford Focus-Brake Buddy
awwall is offline   Reply With Quote
Old 09-04-2012, 05:48 PM   #9
Junior Member
 
Winnebago Owners Club
Join Date: Jun 2012
Location: Gilroy, CA
Posts: 17
Thanks to all the comments. The coach is brand new. 2012 Itasca Sunstar purchased at the end of May. Still scratching my head about the service tech suggestion. Will definitely take all these suggestions to heart and get a certified electrician to provide an alternate opinion. Thanks again.
__________________
sharksgirl21 is offline   Reply With Quote
Old 09-04-2012, 06:19 PM   #10
Senior Member
 
clyon51's Avatar
 
Monaco Owners Club
Join Date: Mar 2012
Location: Arizona West RV Park, Yuma, Az
Posts: 4,113
Quote:
Originally Posted by sharksgirl21
Well, the coach is in back at the dealer again. We have noticed some electrical issues, one caused the automatic transfer switch to require replacement. Another, issue is the AC causes the generator to flip the breaker. When we are plugged in to electricity breakers pop for no apparent reason. We have talked to the service people about this. They have suggested to us that we buy a 30 to 50 amp converter and plug into the 50 amp service whenever possible. Our coach is wired for 30 amp service and we could not find any literature that says this is the right thing to do. Anyone out there ever done this as a regular practice?
A transfer switch going bad is far from unusual. The AC unit could have a bad capacitor, also not unusual, easy to fix and cheap. If this is the rear AC, it is powered solely by the genny, so it could be a bad capacitor or perhaps a bad 20a breaker on the genny.

Now coach breakers popping before reaching their rated load is rather unusual but they do go bad. You of course realize you cannot run the front AC, say an elec water heater and micro at the same time.

Using a 50a outlet will do nothing for your 30a coach. If your coach reaches 30a ( or say 16a on a 15a circuit) you will pop a breaker in the coach. *If* you were popping breakers at the pole, that *may* make a slight difference. The bottom line though is, if coach breakers are popping, plugging into 50a will do nothing to fix your problems.
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
clyon51 is offline   Reply With Quote
Old 09-04-2012, 06:29 PM   #11
Senior Member
 
clyon51's Avatar
 
Monaco Owners Club
Join Date: Mar 2012
Location: Arizona West RV Park, Yuma, Az
Posts: 4,113
Quote:
Originally Posted by sharksgirl21
Thanks to all the comments. The coach is brand new. 2012 Itasca Sunstar purchased at the end of May. Still scratching my head about the service tech suggestion. Will definitely take all these suggestions to heart and get a certified electrician to provide an alternate opinion. Thanks again.
Since you're under warranty, you might as we'll let the dealer try to correct. But telling you to use 50a service certainly gives me pause on their expertise. If they don't correct everything with a reasonable cause, I would contact the factory and have them pay for a good independent RV electrician.
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
clyon51 is offline   Reply With Quote
Old 09-04-2012, 06:48 PM   #12
Senior Member
 
calhyatt's Avatar


 
Newmar Owners Club
Freightliner Owners Club
Join Date: Mar 2012
Location: Weston, Fl.
Posts: 914
Quote:
Originally Posted by sharksgirl21 View Post
Well, the coach is in back at the dealer again. We have noticed some electrical issues, one caused the automatic transfer switch to require replacement. Another, issue is the AC causes the generator to flip the breaker. When we are plugged in to electricity breakers pop for no apparent reason. We have talked to the service people about this. They have suggested to us that we buy a 30 to 50 amp converter and plug into the 50 amp service whenever possible. Our coach is wired for 30 amp service and we could not find any literature that says this is the right thing to do. Anyone out there ever done this as a regular practice?
Run;;;;;;; Don't walk away from that and get a professional involved with this. You will end up a very unhappy guy if you continue on the path your dealer wants you to travel down. A real electrical wizard will find your loose neutral or ground and fix it. You don't need te 50 amp service..
__________________
2003 Newmar Kountry Star 3905, Freightliner XC chassis with CAT 330. Winnie the black lab, pretty Airbus captain wife, retired airline pilot with 11 grandkids. UH-1 pilot (Huey) U.S. Army 1967-1983. RVN 68-69. Northern Idaho my summer home.
calhyatt is offline   Reply With Quote
Old 09-04-2012, 07:19 PM   #13
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,787
You said breakers tripping, The "theory" behind using the 50 amp adapter is better wireing on the 50 amp outlet, Likely a false theory as the wires are often the same but the outlet may be better.

That said Many RVers have a few screws loose, I tightened one of the screws in my power distribution panel (Breaker box) over 2 full turns before it started to offere resistance... NOTE do this when not plugged and not running generator.

Generator breakers will trip, generator off, just from bouncing down the road.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 10-10-2012, 02:55 PM   #14
Member
 
Join Date: Jan 2012
Posts: 60
I have a 2012 sunstar and it has a 50 amp service. Why do you need a 30 amp
adapter? Just plug in the 50 amp cord.
__________________

__________________
steve258 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 12:34 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.