^^^ Never a good idea to get snippy (pardon the pun). But I'm with ya - L1 - L2 - G and N on 50 amp all the way. If anyone weren't needed - they wouldn't be there. Simple as that. It's not like folks are running needless lines for the fun of it.
__________________
Steve & Annie (RVM2)
2008 Fleetwood Bounder 38F ~ 325 ISB Turbo ~ Freightliner XC 2014 CR-V ~ Invisibrake / Sterling All Terrain
Sioux Falls, SD (FullTime Since Nov 5th 2014)
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
08-03-2013, 11:27 AM
|
#128
|
Senior Member
National RV Owners Club Workhorse Chassis Owner Ford Super Duty Owner Carolina Campers
Join Date: Aug 2011
Posts: 2,266
|
Quote:
Originally Posted by WDK450
So if I cut the Neutral wire in my RV's shore power cord, everything will work O.K. since: "There is only one wire used in any circuit. One portion of the wire is connected to the power source and the "hot" side of the load. The other portion is connected to "neutral" side of the load and finds its way to ground by design, the same ground as the source (hot) uses. One wire per circuit. Load in the path."
|
I think his point was that the neutral is the 'return' part of his 'one wire concept'. Hence, if you cut the neutral, you interrupt the circuit.
__________________
2002 National Dolphin LX 6356
Workhorse W-22 chassis
Don't believe everything you think.
|
|
|
08-03-2013, 04:15 PM
|
#129
|
Senior Member
Newmar Owners Club
Join Date: Oct 2009
Posts: 10,310
|
I think if Benjamin Franklin was alive........he sure would be interested in this thread, especially the dog-bone.......
__________________
2012 Essex 4544 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006 Ultra & 1989 Springer, 2003 Harley-Davidson
FLHR Road King Anniversary
|
|
|
08-03-2013, 04:20 PM
|
#130
|
Senior Member
Fleetwood Owners Club iRV2 No Limits Club
Join Date: Sep 2012
Location: Rainbow Riding
Posts: 18,574
|
Never a Nikola Tesla when ya need one.
__________________
Steve & Annie (RVM2)
2008 Fleetwood Bounder 38F ~ 325 ISB Turbo ~ Freightliner XC 2014 CR-V ~ Invisibrake / Sterling All Terrain
Sioux Falls, SD (FullTime Since Nov 5th 2014)
|
|
|
08-04-2013, 07:41 AM
|
#131
|
Senior Member
Winnebago Owners Club
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 3,958
|
WDK450: WRONG!!! back at yea! The coil (can't write the name because of spelling) between the ground and neutral detects the micro-current difference and trips the gfci. Devices are parallel on the circuit but each device is in series from source to return. This is a loop. That is the only way it can work. As each load is added in parallel the current in the hot and return increases. If, on a gfci, the ground detects current it trips.
__________________
Rick & Melissa Young, 2011 Itasca Meridian 40U, Frtliner XCL, Cummins ISL 380HP/DEF, Allison 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox, EEZ TPMS, TruCenter steering control
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
|
|
|
08-04-2013, 07:49 AM
|
#132
|
Member
Join Date: May 2009
Posts: 38
|
Quote:
Originally Posted by flaggship1
^^^ Never a good idea to get snippy (pardon the pun). But I'm with ya - L1 - L2 - G and N on 50 amp all the way. If anyone weren't needed - they wouldn't be there. Simple as that. It's not like folks are running needless lines for the fun of it.
|
Needless and fun good electrical terms, maybe add safety duplication for G and N being that they come from the same source.
|
|
|
08-04-2013, 08:22 AM
|
#133
|
Senior Member
Damon Owners Club Ford Super Duty Owner
Join Date: Apr 2008
Location: NAS Pensacola, FL
Posts: 349
|
Quote:
Originally Posted by jerichorick
WDK450: WRONG!!! back at yea! The coil (can't write the name because of spelling) between the ground and neutral detects the micro-current difference and trips the gfci. Devices are parallel on the circuit but each device is in series from source to return. This is a loop. That is the only way it can work. As each load is added in parallel the current in the hot and return increases. If, on a gfci, the ground detects current it trips.
|
Jerichorick.
YOUR PUTTING OUT BAD INFO!
The typical GFCI (like purchased at Lowes or Home depot) is designed to protect not only loads plugged into it but also the branch loads connected to the load output terminals; it protects all slaved outlets on a branch. A GFCI detects an imbalance of current passing through receptacle’s HOT and NEUTRAL lines. A GROUND line is not required for the GFCI to function. An imbalance can occur when current leaks (a fault) from the HOT or NEUTRAL to a ground line or earth ground or through an individual to earth ground. An imbalance can also occurs due to an inductive kick (e.g., a collapsing magnetic field from a motor, etc.) when an electrical device is turned off. The GFCI limits the fault current to sensed current of about 5 mA. JM2¢...
__________________
Ted & Diane Fulltiming in the DreamCatcher a
2008 Challenger 371PE on F53 w/ 2013 Kia Soul+ the DreamChaser
R'V there yet?
|
|
|
08-04-2013, 08:34 AM
|
#134
|
Member
Join Date: Mar 2013
Posts: 38
|
Quote:
Originally Posted by jerichorick
WDK450: WRONG!!! back at yea! The coil (can't write the name because of spelling) between the ground and neutral detects the micro-current difference and trips the gfci. Devices are parallel on the circuit but each device is in series from source to return. This is a loop. That is the only way it can work. As each load is added in parallel the current in the hot and return increases. If, on a gfci, the ground detects current it trips.
|
If I was wrong, I apologize.
I homed in on the "there is only 1 wire" statement. I think it could be very misleading for the AC electrical novice. There is so much energy and danger to human life in those AC wires, that it is imperative that people get it right.
I spent a 30 year career in as a Hospital Biomedical Electronics Technician primarily ensuring that the febrile patient/neonate in an ICU/NICU bed was surrounded by SAFE electrical equipment that accurately helped treat and report the patient's condition to the medical staff. That is where my zeal comes from.
|
|
|
08-05-2013, 03:37 PM
|
#135
|
Senior Member
Winnebago Owners Club
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 3,958
|
Quote:
Originally Posted by WDK450
If I was wrong, I apologize.
I homed in on the "there is only 1 wire" statement. I think it could be very misleading for the AC electrical novice. There is so much energy and danger to human life in those AC wires, that it is imperative that people get it right.
I spent a 30 year career in as a Hospital Biomedical Electronics Technician primarily ensuring that the febrile patient/neonate in an ICU/NICU bed was surrounded by SAFE electrical equipment that accurately helped treat and report the patient's condition to the medical staff. That is where my zeal comes from.
|
I hope we are only discussing and not being disgusting . I suffer with an old associate degree in electronics/electrical. I spent several years designing and building control circuits for emergency power generators used by the phone company in New England. My way of thinking and expressing myself is from this background. Forgive me if I have caused confusion.
I agree with the load side of a Ground Fault Circuit Indicator device being protected. Yes, the GFCI will trip if the hot and neutral are not balanced and no ground is wired to the GFCI. But in most cases the ground is present and current on it will also cause a trip. Then we have the arc fault device. I don't even want to go there !
When the GFCI is wired as designed it works fine and protects people first and equipment second. Isn't that all that counts???
__________________
Rick & Melissa Young, 2011 Itasca Meridian 40U, Frtliner XCL, Cummins ISL 380HP/DEF, Allison 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox, EEZ TPMS, TruCenter steering control
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
|
|
|
08-06-2013, 05:47 AM
|
#136
|
Senior Member
Winnebago Owners Club Coastal Campers
Join Date: Oct 2009
Location: Marathon, Florida
Posts: 2,909
|
Quote:
Originally Posted by jerichorick
I spent several years designing and building control circuits for emergency power generators used by the phone company in New England.
|
Another telephone company guy. Should we create a phone company thread to trade stories?
Me 32 years, DW 23, My dad 43, mom 17, FIL 34. We even met at work.
Now that I am retired I can share some of our antics because they can't fire me anymore
Back on topic. I would bet that corrosion or wear on one of the plugs was the cause of the failure.
__________________
Mark & Nancy
2004 Winnebago Vectra 40KD
Shep dog, R.I.P. Kenzie dog Toad 2015 Jeep Wrangler Willys Wheeler
|
|
|
08-06-2013, 02:54 PM
|
#137
|
Senior Member
Monaco Owners Club
Join Date: Feb 2011
Posts: 260
|
RVJIMMY SO what do you have AGAINST the cord reels?
|
|
|
08-07-2013, 10:39 AM
|
#138
|
Junior Member
Coastal Campers
Join Date: Aug 2011
Location: Ormond Beach, FL
Posts: 4
|
Was using a 25 ft 30A cord with dogbone. Recently noticed the plug on the cord turning black-looked burned. Also noticed smoke coming from plug when plugging in. No harm done though-just lucky I guess. Thanks for the heads up!!!!
|
|
|
08-07-2013, 10:43 AM
|
#139
|
Registered User
Join Date: Mar 2007
Location: Somewhere I guess?
Posts: 453
|
I moved to a KOA which wasn't always one. It's a mixture of mobile homes and RVs. Some spots had mobile homes, converted for RV use. This spot I'm at has a 60A breaker and the manager refers to it as 50A since it has a 50A outlet.
So.... yes. At this moment, I am in a 30A RV (which the manager knows, he said I'd need an adapter for this spot) plugged into a 50A outlet with a 60A breaker... at a KOA.
Of course they made me sign something saying I won't hold them liable for any losses due to staying here... but they make EVERYONE sign that who's monthly. (There is other terms on the form like agreeing to pay the metered electric, etc). There are travel trailers on both sides of me that are probably 30A plugged into 60A breakers as well.
|
|
|
08-07-2013, 10:52 AM
|
#140
|
Senior Member
Tiffin Owners Club Freightliner Owners Club
Join Date: Apr 2012
Posts: 2,079
|
Quote:
Originally Posted by Cubey
I moved to a KOA which wasn't always one. It's a mixture of mobile homes and RVs. Some spots had mobile homes, converted for RV use. This spot I'm at has a 60A breaker and the manager refers to it as 50A since it has a 50A outlet.
So.... yes. At this moment, I am in a 30A RV (which the manager knows, he said I'd need an adapter for this spot) plugged into a 50A outlet with a 60A breaker... at a KOA.
Of course they made me sign something saying I won't hold them liable for any losses due to staying here... but they make EVERYONE sign that who's monthly. (There is other terms on the form like agreeing to pay the metered electric, etc). There are travel trailers on both sides of me that are probably 30A plugged into 60A breakers as well.
|
very ineresting post. basically an accident waiting for a time to happen. Thank you for your post. I am not a big fan of KOA so I rarely stay there. That increases the odds against me being parked next to you. Good luck to you and your fellow tenants in your park. I hope you dont have any bad luck from your electrical connections.
|
|
|
|
|