30A to 50A Adapter Causes MH Fire

I was camping with our local WIT club this weekend. One of our club members had a fire in his 2000 Itasca Meridian at about 12:30am Saturday morning.

Apparently the 30A to 50A adapter shorted while in his electrical bay, resulting in a ball of fire inside the compartment.

They were in bed, but heard a loud 'pop'. The coach quickly filled with smoke, and they immediately got out of the motorhome. The owner used a fire extinguisher and got the flames down, and the fire truck shortly arrived. Their smoke alarm did go off.

Next door neighbor was a retired sheriff deputy, and quickly helped out. Thanks to him, they are both safe.

First picture shows the shorted 30A to 50A adapter which apparently caused the fire.

Second picture shows the damage to the electrical compartment. There was significant damage to the coach, and of course smoke damage inside.

Here are my learnings:

1) Always use the shortest length of shore supply cord to the power pedestal, starting with your 50A shore power cord, to run to the power post. If necessary, use the 30A to 50A adapter at the pedestal; DO NOT keep it coiled up inside your coach, and simply run a 30A extension cord to the power post.

Use the adapter outside of the coach. If it does short out, apparently as happened in this situation, it will happen outside of the coach.

Don't keep extra lengths of extension cords on your shore cord if you don't need them. 30A plugs have a habit of getting hot and melting the connections. The longer the run of wire, the more resistance, potentially causing heat build-up at the connections.

2) 30-to-50A adapters cost about $14. Replace them every few years.
Attached Thumbnails
Click image for larger version

Name:	Scorched Adapter.jpg
Views:	773
Size:	391.1 KB
ID:	43161   Click image for larger version

Name:	MH Electrical Fire.jpg
Views:	755
Size:	230.5 KB
ID:	43162  

__________________

__________________
Don
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
Pusherman is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-28-2013, 02:35 PM   #2
Senior Member
 
Join Date: Oct 2009
Posts: 248
I'm confused - did they run a long 30A cable from the pedestal to the compartment?

Typically we use dog bones at the pedestal.

Thank goodness they were safe!
__________________

__________________
steveclv is offline   Reply With Quote
Old 07-28-2013, 02:38 PM   #3
Senior Member
 
Pusherman's Avatar
 
Join Date: Oct 2006
Location: Rochester NY
Posts: 2,544
Quote:
Originally Posted by steveclv View Post
I'm confused - did they run a long 30A cable from the pedestal to the compartment?

Typically we use dog bones at the pedestal.

Thank goodness they were safe!
Yes, they kept the 50A shore cord coiled in the electrical bay, adapted it with the dog-bone inside the electrical bay, and ran the 30A extension cord to the pedestal. They could have made it to the power pedestal with their 50A cord, and used the dog bone at the power pedestal.

Would have kept any fire from a shorted dog-bone adapter outside of the coach.
__________________
Don
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
Pusherman is offline   Reply With Quote
Old 07-28-2013, 02:40 PM   #4
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 13,686
Thanks for the pictures and admonition about using under-sized cords and multiple cords.
In the 2nd picture, is that water filters seen in the left side of the compartment? If it is, it was a very poor choice to put water in the electrical bay. Also, in the 1st picture it appears like the 30A cord had been repaired with a replacement end. I repaired one that way; it lasted for about a year until the wire-nuts got hot from current and allowed the wires to touch. Thankfully it was all outside our 5er. Decided right then to never attempt a cord repair again.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA."We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution. "Abraham Lincoln"
Ray,IN is offline   Reply With Quote
Old 07-28-2013, 02:43 PM   #5
Senior Member
 
Pusherman's Avatar
 
Join Date: Oct 2006
Location: Rochester NY
Posts: 2,544
Quote:
Originally Posted by Ray,IN View Post
Thanks for the pictures and admonition about using under-sized cords and multiple cords.
In the 2nd picture, is that water filters seen in the left side of the compartment? If it is, it was a very poor choice to put water in the electrical bay.
Yes. Interesting observation. Mine's the same way on my winnie, but the wet bay and electrical bay, both behind one door, are divided by a metal divider. Ray -- good points.
__________________
Don
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
Pusherman is offline   Reply With Quote
Old 07-28-2013, 02:46 PM   #6
Senior Member
 
Join Date: Oct 2009
Posts: 248
Gotchaa - sometimes I guess 'common sense' grows wings and flies away
__________________
steveclv is offline   Reply With Quote
Old 07-28-2013, 03:01 PM   #7
Senior Member
 
Join Date: Sep 2010
Posts: 278
First thing that comes to mind is that was not a 50 down to a 30 ,it was a 50 trying to use a 30 with what looks like a homemade cord .any time u try to draw 50 amps thru a 30 amp receptacle you will over heat the connection .common sense tells you anytime you use a adaptor of any kind you should check it to see if the cord is getting warn-hot and if it is you are at risk for a fire on't I say Don't go to sleep when you have this risk unplug the damn thing.you might get hot during the night but not fire and smoke hot
__________________
swampdog is offline   Reply With Quote
Old 07-28-2013, 03:10 PM   #8
Senior Member
 
palehorse89's Avatar


 
Newmar Owners Club
Join Date: Oct 2009
Posts: 7,721
There might of been a problem with the 30 amp. breaker???? even on a 50 cord when the Coach drew 30 amps or more the 30 amp. breaker should of tripped, I have this problem when I hook up to a 30 amp. outlet and try to run to much as we all have run into with a 50 amp. setup. I believe the problem was to long of a cord and to many plug in connections and the connection at the 30 amp. side of the dog-bone was not a good connection and developed heat with the amp. draw. Good news that no one was hurt!
__________________
2000 Newmar MADP 4060, 350ISC, Spartan MM, IFS 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006Ultra & 1989 Springer
palehorse89 is offline   Reply With Quote
Old 07-28-2013, 03:19 PM   #9
Senior Member
 
rvjimmy's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Join Date: Mar 2011
Location: Almond, Wisconsin
Posts: 1,455
Glad they are safe, but leaving any power cord coiled is never a good idea. A coil always creates heat. JMHO. Jim
__________________
2002 Newmar Dutch Star DP3569 330 CAT - Toad Jeep Liberty, DW is the Nagivator. Work to travel and everything revolves around the price of diesel.
rvjimmy is offline   Reply With Quote
Old 07-28-2013, 03:24 PM   #10
Community Moderator
 
Petro's Avatar


 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Dec 2003
Location: Weyauwega, WI US
Posts: 5,787
Pusherman;

I also would like to thank you for taking the time to post the pictures and the expert advice. This brings up another question to my mind. I have a 50 Amp Portable Surge Guard locked to the plug on my power cord. I would have installed the 50 amp to 30 amp adapter between my Surge Guard and the pedestal. Do you think the Surge Guard would have sensed a problem and shut down the power before a fire broke out? We had a lightning storm one time that burned out the coil on the transfer switch and that is when I purchased a Surge Guard.

I also am happy nobody was hurt.

Don
__________________
Don & Bev Morgan Weyauwega WI, 05 Itasca Horizon 40KD, 400 HP Cummins, Delorme GPS LT 40, Toad 07 Saturn Vue AWD, Air Force One, TST 510 TPMS, Mayor of Weyauwega 2007 - 2013, Waupaca Co Board Supervisor 2010 - 2014
Petro is offline   Reply With Quote
Old 07-28-2013, 03:30 PM   #11
Registered User
 
Join Date: Mar 2007
Location: Somewhere I guess?
Posts: 453
Sounds stupid and lazy how they did it, just asking for trouble. Glad they are ok without any extensive damage based on the photos.

I have a 30A motorhome and use a dogbone style adapter at the pedestal as needed. Where I am now, it's a 50A hookup so I have a 50A male to 30A female adapter. In the past I have used a 20A adapter and just monitored the adapter at the plug to be sure it wasn't getting too hot.

I leave NO excess cable in the compartment, it lays on the ground under the van.
__________________
Cubey is offline   Reply With Quote
Old 07-28-2013, 03:43 PM   #12
Senior Member
 
Ramblin's Avatar
 
National RV Owners Club
Workhorse Chassis Owner
Ford Super Duty Owner
Carolina Campers
Join Date: Aug 2011
Posts: 2,253
I always extend my 50A cable as far as it will go towards the power source, then adapt and extend as needed. Not because I had the brilliant foresight to foresee this sort of failure, but just because it seems like the logical thing to do.
__________________
2002 National Dolphin LX 6356
Workhorse W-22 chassis
Don't believe everything you think.
Ramblin is offline   Reply With Quote
Old 07-28-2013, 04:21 PM   #13
Senior Member
 
RedWing Nut's Avatar
 
Vintage RV Owners Club
Holiday Rambler Owners Club
Join Date: Sep 2012
Posts: 605
I have 50 amps and use a portable surge guard that I plug the power cord into. I leave the cord coiled in the bay. Then I run a 50 amp extension cord from the surge guard to the pedestal. The whole setup stays cool to the touch. The blades show no black marks.

I do it to keep the surge guard out of the weather and the hands of thieves. If there is only 30 amp service, I put the converter at the pedestal.
__________________
Steve, Mary & Buddy our 2-year-old Chihuahua mix
1995 36' HR Endeavor, 460 w/Banks, 2005 PT Cruiser
Fulltimers originally from Michigan, hanging out in Oregon for a spell.
RedWing Nut is offline   Reply With Quote
Old 07-28-2013, 04:38 PM   #14
Senior Member
 
gemini5362's Avatar
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Apr 2012
Posts: 2,078
Quote:
Originally Posted by Cubey View Post
Sounds stupid and lazy how they did it, just asking for trouble. Glad they are ok without any extensive damage based on the photos.

I have a 30A motorhome and use a dogbone style adapter at the pedestal as needed. Where I am now, it's a 50A hookup so I have a 50A male to 30A female adapter. In the past I have used a 20A adapter and just monitored the adapter at the plug to be sure it wasn't getting too hot.

I leave NO excess cable in the compartment, it lays on the ground under the van.
I hope I misunderstand your post. You said you have a 30 amp motorhome. do you have a 30 amp cable with a 30 amp male end for the shore pedestal. Do you then take a 50 amp male adapter which you plug into the 50 amp shore pedestal. Does this 50 amp male adapter plugged into the 50 amp shore pedestal have a 30 amp female on it which you plug your 30 amp cable from the coach into. I hope I have that explained clearly. In simpler terms is the cable from your coach rated at 30 amps and is it plugged into a 50 amp receptacle with 50 amp breakers. If this is what you have it is extremely dangerous and you would be a major candidate for a fire somewhere in your coach.
__________________

__________________
gemini5362 is offline   Reply With Quote
Reply

Tags
ada



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:44 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.