50 amp service at home.

I'm having a service installed at home and was wondering if there is a way to verify the ground and neutral aren't swapped at the box if all the wire is the same color.
__________________
2001 Newmar Mountain Aire 3798
maneddi is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-30-2015, 03:51 PM   #2
Senior Member
 
Bigd9's Avatar


 
Join Date: Jun 2012
Location: The Bluegrass State
Posts: 8,886
I just found this post:
http://www.myrv.us/Imgs/PDF/50-amp%20Service.pdf

Can't tell you if it is accurate or not, but it looks pretty.
__________________
Good Luck, Be Safe and Above All, Don't Forget To Have Fun
Pete
Central Kentucky
2006 Fleetwood Discovery 35H, 2014 Honda CR-V, M&G Engineering Braking System
Bigd9 is online now   Reply With Quote
Old 09-30-2015, 03:53 PM   #3
Senior Member
 
mmartin's Avatar
 
Join Date: Apr 2013
Location: Long Beach, Calif.
Posts: 220
you could run a tracer on both and verify at the box. Was wondering why your neutral isn't white and your ground is green. Normal installation is 6 gauge red, 6 gauge black and 6 gauge white and ground can be 6, 8 or 10 gauge. You can also wrap them in a colored elect. tape at both ends to help identify the ground and the neutral.
__________________
Travel Supreme 03 40DS03
Cummins 400 HP ISL 8.9
2010 Jeep Wrangler JK
mmartin is offline   Reply With Quote
Old 09-30-2015, 03:57 PM   #4
Senior Member
 
hdossett's Avatar
 
Join Date: Mar 2009
Location: N. Central AZ
Posts: 548
I'm not an electrician, but I did sleep and a Holiday Inn Express once upon a time...

If all wire have the same color insulation, they should be marked with tape at each end i.e., white, red, black, and green. (or what ever color)

I think code call for this!

This is exactly what I did. Bought a 500' spool, cut the lengths needed and put colored tape on the ends, before pulling, to identify them.

H
__________________
'01 National RV Tropi-Cal, Ford V10, '01 Suzuki GV 4X4 Blue Ox Tow Bar,300 Watts Solar, 2500 Watt '458' Inverter, NO TVs, Most light fixtures upgraded to LEDs

hdossett is offline   Reply With Quote
Old 09-30-2015, 03:58 PM   #5
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
Quote:
Originally Posted by maneddi View Post
I'm having a service installed at home and was wondering if there is a way to verify the ground and neutral aren't swapped at the box if all the wire is the same color.

If an electrician installed then you should have no worries. The 4 wire 50 amp double pole breaker is wiring 101. The hots should be black & red, the neutral is white and the ground is bare copper. These wire colors should be visible in the box that houses the breaker.


Steve Ownby
Full time since '07
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 09-30-2015, 04:10 PM   #6
Senior Member
 
Join Date: Jun 2012
Posts: 170
Yeah..he's using all same color wire and I'm not sure if he's going to flag the ends. I'm not there and am researching while away. I know how to use a meter to check the pedestal for correct voltage but as far as I know only a visual inspection can tell if ground and neutral are swapped and you can't tell if they aren't marked.
__________________
2001 Newmar Mountain Aire 3798
maneddi is offline   Reply With Quote
Old 09-30-2015, 04:24 PM   #7
Junior Member
 
rvrlyle's Avatar
 
Winnebago Owners Club
Join Date: Jun 2012
Posts: 19
If the electrician did not color code the wiring, then the only way to verify is to disconnect the ground at the new receptacle and check continuity back to the panel feeding the receptacle. If all of the wires are the same size and the circuit is being fed from a 'Main' panel then there should not be a problem since the neutral and ground are bonded at a 'Main' panel. If the circuit is being fed from a 'Sub' panel then it is imperative that the neutral and ground be properly identified.
rvrlyle is offline   Reply With Quote
Old 09-30-2015, 04:29 PM   #8
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
FWIW I am not sure it matters. Assuming there is no sub panel in the path the place the neutral and ground are connected together is the main panel box. If he is pulling 4 wires that are the same color and the hot's are correct either of the other wires can go to ground and the other go to neutral as they will be the same at the panel.

I would check the hots are at the right place before I plugged in! Nothing personal but too many years of proving Murphy was an optimist. ;-)

FWIW2 I would not expect a home installation to be wired like a park installation. Looking at the way parks are wired they should have a ground rod at the pedestal and connect neutral and ground there. For a home installation I would expect a relatively short run without the extra ground rod to avoid ground looping.
nothermark is offline   Reply With Quote
Old 09-30-2015, 04:50 PM   #9
Senior Member
 
SpaceNorman's Avatar
 
Monaco Owners Club
Join Date: Jan 2004
Posts: 1,188
I'd be highly suspicious of any work done by an "electrician" who didn't use properly color coded wires. Plain and simple - an installation that isn't color coded fails to meet not only the letter of the code - but more importantly, the intent of the code. I'd keep my checkbook in my pocket until the job was done right.
__________________
SpaceNorman
2012 HR Endeavor 43' DFT, 2022 Jeep Wrangler
SpaceNorman is offline   Reply With Quote
Old 09-30-2015, 05:00 PM   #10
Senior Member
 
Steve N Sal's Avatar
 
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 5,692
If he didn't color code the wires then I wouldn't call him an electrician. My gosh I don't know of an electrician that doesn't carry marking tape with him.
__________________
Steve & Sally / Hudson Our Little Pom / Heidi, Houston & HiTee Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert
Michigan (Summer) Michigan (Winter For Now)
Steve N Sal is offline   Reply With Quote
Old 09-30-2015, 05:05 PM   #11
Senior Member
 
Join Date: Jul 2015
Location: Watertown NY USA
Posts: 6,440
Is the installer really an electrician or a friend who thinks they know what they are doing?
Lynn
__________________
2002 Fleetwood Storm 30H on Workhorse P32 chassis 8.1 gas.
LETMGROW is online now   Reply With Quote
Old 09-30-2015, 05:33 PM   #12
Member
 
Join Date: Mar 2015
Posts: 73
Pull the cover off and take a look. Set the breaker to off first.
__________________
2003 Fleetwood Expedition 34W
2000 Thor Hurricane 29D Motor Home
2011 Lance 1050S Truck Camper
JumboJet2 is offline   Reply With Quote
Old 09-30-2015, 07:47 PM   #13
Senior Member
 
Join Date: Jul 2015
Location: Athol, Id
Posts: 126
Quote:
Originally Posted by maneddi View Post
I'm having a service installed at home and was wondering if there is a way to verify the ground and neutral aren't swapped at the box if all the wire is the same color.
If the ground and Neutral are the same color RUN as an IDIOT wired it.
Ground = Green or Bare copper
Neutral = White or possible light gray.
Hot wires can be Black, Red, Blue,
Did he even use the correct gauge wire?
#6 copper for 50 amp
Ground can be #10
Per NEC

Retired Real IBEW Electrician!!!!!
__________________
2008 Dutch Star 4035
Retired IBEW Local 595
Dutchstar08 is offline   Reply With Quote
Old 09-30-2015, 08:16 PM   #14
Senior Member
 
HVAC Bill's Avatar
 
Join Date: Oct 2013
Posts: 284
As said in previous reply, electrically and code wise, as long as last 4-6" is marked with the proper color tape all is good. One very important feature that I have not heard mentioned is this plug is considered for outdoor use, therefore make sure your breaker is a ground fault breaker. Expensive, but many are killed with a lot less amperes.
2013 Palazzo 33.3
HVAC Bill is offline   Reply With Quote
Reply

Tags
service



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using 30 amp service hwbuck Travel Supreme Owner's Forum 16 10-10-2015 05:39 AM
Can 30 AMP Service run AC unit ? chrisgolden RV Systems & Appliances 8 06-24-2015 03:32 PM
50 amp service?? bettertogeth Fleetwood Owner's Forum 10 04-12-2015 06:48 PM
Storing w/ 50 amp service Ron & Kerrie Newmar Owner's Forum 27 12-28-2014 04:40 PM
50 amp service for RV Rog1965char iRV2.com General Discussion 19 05-18-2014 02:09 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.