Old 05-09-2015, 12:50 PM   #15
Community Administrator
 
JohnRR's Avatar


 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Sep 2010
Location: Marquette, Michigan "Da UP" & Lehigh Acres Florida
Posts: 21,827
I'd opt to have the 120 plug put in as well the cost would be minimal when done with the 50 amp hook up, you never know when it might come in handy.

I leave mine plugged in all winter without being used, just remember to check your house battery fluid level every so often just in case. After a while you'll have an idea how often to check it.
__________________
John & Cathy R.
06 Pace Arrow 38L Workhorse W24
08 14 Lincoln MKX AWD 06 Lincoln Mark LT 4X4, 2020 Lincoln Corsair
See My Pace Arrow Upgrades
JohnRR is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-09-2015, 12:58 PM   #16
Senior Member
 
Golfer Guy's Avatar
 
Monaco Owners Club
Newmar Owners Club
Join Date: Dec 2014
Location: out west
Posts: 1,061
Any idea what the ball park cost is to have a 50 amp plug added to the parking pad 50" from the house?
__________________
2017 Dutchstar 4369 Spartan Chassis, 2200W Solar, 1200AH Lithium Batteries, Active Air
2022 Jeep Grand Cherokee, Roadmaster Sterling, AF1
Golfer Guy is offline   Reply With Quote
Old 05-09-2015, 01:36 PM   #17
Senior Member
 
Falcon190's Avatar
 
Winnebago Owners Club
Join Date: Sep 2011
Location: Camas, WA
Posts: 872
50 Amp service install on side of house questions

The 50 amp circuit is two separate 120 volt circuits, with two individual circuit breakers. Sure, there's 240 volts available but motorhomes use the two 120 volt circuits. My wiring passed inspection and actually exceeded code. I have done electrical work since I was ten years old and don't need to defend myself (though apparently I just did &#128527.

My cost was 15 feet of 6 gauge wire at about $6 a foot and the rest was about $35. Labor? Free!
Falcon190 is offline   Reply With Quote
Old 05-09-2015, 01:41 PM   #18
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
Quote:
Originally Posted by Golfer Guy View Post
Any idea what the ball park cost is to have a 50 amp plug added to the parking pad 50" from the house?
Too many variables. Overhead, underground, type of soil, landscaping, location, existing utilities or structures, etc.

This is what I used and it was surprisingly inexpensive and had everything, breakers and all. 50/30/15.
Attached Thumbnails
Click image for larger version

Name:	IMAG0551.jpg
Views:	162
Size:	147.8 KB
ID:	93823   Click image for larger version

Name:	IMAG0550.jpg
Views:	126
Size:	163.4 KB
ID:	93824  

__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Lifeline AGM's
2019 F250 King Ranch 4x4 Powerstroke - SOLD
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Old 05-09-2015, 03:04 PM   #19
Senior Member
 
dabrooks's Avatar
 
Tiffin Owners Club
Join Date: Sep 2012
Location: Maryland
Posts: 1,437
Quote:
Originally Posted by Falcon190 View Post
The 50 amp circuit is two separate 120 volt circuits, with two individual circuit breakers. Sure, there's 240 volts available but motorhomes use the two 120 volt circuits. My wiring passed inspection and actually exceeded code. I have done electrical work since I was ten years old and don't need to defend myself (though apparently I just did &#128527.

My cost was 15 feet of 6 gauge wire at about $6 a foot and the rest was about $35. Labor? Free!
I am not sure you are correct. I have a 50 amp circuit for my RV and have had it for at least 3 years and it is a 50 amp 240 double pole breaker. Of course each leg is 120 volts but between the two hot legs it is 240 volts.
dabrooks is offline   Reply With Quote
Old 05-09-2015, 03:19 PM   #20
Senior Member
 
rosspam's Avatar
 
Join Date: Feb 2012
Posts: 116
Plugged in all time here. Just make sure you have multistage battery charger sobyou don't cook the batteries.
rosspam is offline   Reply With Quote
Old 05-09-2015, 03:35 PM   #21
Senior Member
 
Pusherman's Avatar
 
Join Date: Oct 2006
Location: Rochester NY
Posts: 2,706
Quote:
Originally Posted by Falcon190 View Post
The 50 amp circuit is two separate 120 volt circuits, with two individual circuit breakers. Sure, there's 240 volts available but motorhomes use the two 120 volt circuits. My wiring passed inspection and actually exceeded code. I have done electrical work since I was ten years old and don't need to defend myself (though apparently I just did &#128527.
If you have it wired to 2 individual 50A single pole breakers, you are in violation of the National Electrical Code. This service must be wired to a 50A double pole breaker, so that if one leg trips, the other will too.

Reason: with 2 individual breakers it is possible to insert them both on the same leg of the panel. In this case, the neutral wire may be pulling double the amps, which will overheat the wire and possibly cause a fire. When wired to a double pole breaker, it is guaranteed that you are tapping in to both legs of the panel, which causes the amperage pulled through the neutral wire to cancel each other on a balanced load, thus not pulling too much current for 2 positive 120V legs through 1 neutral wire. This is because the opposite legs of the panel are 180 degrees out of phase with each other, cancelling out the neutral draw on a balanced load. Remember, this is a 4-wire service (2 hots, 1 neutral, 1 ground), not a 5-wire (2 hots, 2 neutrals, 1 ground) service.

I am guessing you have the 2 breakers on opposite sides of the panel based on your experience, so it's not doubling the amperage on the neutral wire, but what if the next guy comes along and moves the breakers around in the panel and puts them both on the same leg of the panel. This now becomes a fire hazard.
__________________
Don
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
Pusherman is offline   Reply With Quote
Old 05-09-2015, 04:10 PM   #22
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 4,054
Quote:
Originally Posted by Falcon190 View Post
The 50 amp circuit is two separate 120 volt circuits, with two individual circuit breakers. Sure, there's 240 volts available but motorhomes use the two 120 volt circuits. My wiring passed inspection and actually exceeded code. I have done electrical work since I was ten years old and don't need to defend myself (though apparently I just did &#128527.

My cost was 15 feet of 6 gauge wire at about $6 a foot and the rest was about $35. Labor? Free!
You're wrong, because some motorhomes actually do use 240V circuits. Ours does, we have a 240V dryer.

So you can't say that the RV outlet is two 120V circuits. That implies that they don't have to be out of phase. They do. So it's a 240V circuit using a NEMA 14-50R plug.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 05-09-2015, 07:33 PM   #23
Senior Member
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Nov 2014
Location: Island Park , NY
Posts: 629
Quote:
Originally Posted by FlyingDiver View Post
You're wrong, because some motorhomes actually do use 240V circuits. Ours does, we have a 240V dryer.

So you can't say that the RV outlet is two 120V circuits. That implies that they don't have to be out of phase. They do. So it's a 240V circuit using a NEMA 14-50R plug.
I have never seen a 50 amp single pole breaker , and per NEC it MUST be on a double pole breaker, I don't know what inspector would pass that, Bobby
FastGlassMan is offline   Reply With Quote
Old 05-09-2015, 07:37 PM   #24
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 4,054
Quote:
Originally Posted by FastGlassMan View Post
I have never seen a 50 amp single pole breaker , and per NEC it MUST be on a double pole breaker, Bobby
Why did you quote me? I didn't write anything about breakers.

FWIW, here's a 50amp single pole breaker: Square D QO 50 Amp Single-Pole Circuit Breaker-QO150CP - The Home Depot

Don't know what you'd use it for, but it exists.

But you're right, the feed for the RV connection needs to be a 50 amp double pole breaker.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 05-10-2015, 07:53 AM   #25
Senior Member
 
LakeKerrGuy's Avatar
 
National RV Owners Club
Florida Cooters Club
Freightliner Owners Club
Join Date: Mar 2013
Location: Salt Springs, FL
Posts: 453
Like I said in post #12, some folks should not do any electrical work.
__________________
Jack & Beverly
1999 National Tradewinds 7371; Cat 3126; 6 Speed Allison; 7.5 KW Onan; MS-2012,
2014 Jeep Patriot on a EZE Tow
LakeKerrGuy is offline   Reply With Quote
Old 05-10-2015, 08:31 AM   #26
Senior Member
 
ronjhall's Avatar
 
Join Date: Oct 2011
Posts: 3,356
I have a 50amp Box similar to this. Installed on the side of my barn. Sure is nice to have all three different hookups. We have visitors that hook up to the box. Most of the time I am hooked to the 20amp receptacle. Just to keep batteries charged. But when getting ready to go on a trip I hook into the 50amp to run both AC's or heaters. I did have to replace the GIF receptacle with a standard 20amp receptacle.
__________________
2004 Endura 6340D SOLD
2012 Chevy Captiva toad SOLD
ronjhall is offline   Reply With Quote
Old 05-10-2015, 09:07 AM   #27
Senior Member
 
the trainguy's Avatar
 
Newmar Owners Club
Nor'easters Club
Join Date: Jul 2014
Location: upstate new york
Posts: 241
PLEASE READ!

I am a licensed and insured commercial electrician , been doing electrical all of my 50+ years.

I usually stay out of these threads but this one screams for clarification.

Pusherman's explanation is mostly correct.

The main reason for a 2 pole breaker is SAFETY!

Most of the NEC code was written because of people getting killed(electrocuted) or fires from inadequate/unsafe wiring.

If you use 2 individual single pole breakers on this 4 wire 50 amp installation there is the distinct possibility of of only ONE of the single pole breakers tripping leaving the other circuit live.

If you PROPERLY used a 2 pole breaker then if you had that issue of tripping one side of the line it would trip the ENTIRE 2 pole breaker.

This is required so that you don't have PART of the outlet still LIVE which could result in someone thinking the breaker is tripped so the outlet MUST be dead resulting in a potential life threatening situation!

A breaker feeding an electrical appliance(or receptacle) MUST be able to isolate(disconnect) that appliance per NEC.

And yes single pole breakers do exist in 25/30 and 50 amp sizes as there are a few applications that require that amperage in a 120 volt application.

No offense meant to anyone here but PLEASE leave something as important as a 50 amp 120/240 volt branch circuit wiring job to a qualified electrician.

The electrical service to a lot of homes is still only 100 amps,would you allow your buddy "who knows how to do electrical work" to work on it for you?

Also as far as "electrical inspectors" goes I have had to "school" a few over the years as in a lot of locales the electrical inspector is also the building inspector and contrary to what the title implies they sometimes OK things that are not correct.

Bob
__________________
Bob and Karen and Penny R.I.P. 3/4/2019(our faithful wonderdog)
2014 Ventana LE
2012 Ford FX4 twin turbo / Air Force One / Blue Ox LX 10K tow bar
the trainguy is offline   Reply With Quote
Old 05-10-2015, 10:02 AM   #28
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
Read what a 50 amp connection is...

It is not 50 amp at 120 vac...

It is 50 amp at 240 vac meaning 4 conductors with L1, L2, Neutral and Safety ground...simple as that.

Read the instructions and follow them...

We picked up a square d 50 amp dual pole grount fault breaker the other day at an estate sale...was intended for an rv connection so there are more options for safe connections.

The proper installation can be done by a teenager...assuming they can read the instructions and do the process correctly.

Problem is most folks fail to read the instructions and listen to folks who have no clue and then make assumed choices then do unsafe work.

For those who have not performed any electrical work and who may not have the tools to properly do the work and it is a one time event they are best served by waiting and saving up to have a licensed person to do the work and that includes pulling a permit to be certian that work is inspected and the existing work is also checked as part of the package.

For others do your proper homework and if you feel capable of doing the work you should proceed but please be sure to have the means to properly test your work (voltmeter) and have a helper so you can get help if needed.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Reply

Tags
service, install



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30Amp to 50 Amp service dscotty99 National RV Owner's Forum 4 07-20-2015 03:56 PM
What is forum member experience service from non-selling dealer, but same mfr? BeHappy MH-General Discussions & Problems 16 06-08-2015 01:06 PM
50 amp service?? bettertogeth Fleetwood Owner's Forum 10 04-12-2015 06:48 PM
House battery questions Steeler34 Class A Motorhome Discussions 13 03-23-2015 10:58 AM
50 Amp service in garage. Now what? Gonna_Wander Winnebago Industries Owner's Forum 20 08-16-2014 01:18 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:21 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.