Old 09-01-2014, 05:22 PM   #1
Senior Member
 
Geneandea's Avatar
 
Workhorse Chassis Owner
Holiday Rambler Owners Club
Join Date: Nov 2011
Posts: 128
6.5KW Onan LP generator breaker keeping tripping

Recently I started having problems with my generator starting to oscillate. I have found the breaker tripped (1 of 2) tripped, no AC power inside coach. today I had oscillation but had AC power (the Air conditioner also oscillated. I just turned off the generator. Once home I cycled both breakers and restarted the generator and all seemed fine again. I had the surge proctor replaced as it was identified as being bad on the first go around with the generator. The unit is 15 years old and has 408 hours on it. Thanks in advance.

Gene
__________________

__________________
Gene and Bea
2008 Fleetwood Pace arrow , Allison 6 speed transmission 38P work horse W24 chassis 5.5 KW gas Onan Generator with 2009 Saturn vue.
Geneandea is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-01-2014, 07:07 PM   #2
Senior Member
 
94-Newmar's Avatar
 
Join Date: Nov 2009
Posts: 2,043
By oscillating I'll assume you mean the engine rpm is inconsistent and fluctuating to higher then lower rpm's? If so, we refer to this as "hunting".

Being a 99 model, your generator's voltage output is very dependent upon the engine rpm. If the unit is running too slow the AC voltage will drop which causes the amperage draw by the A/C compressor to increase thus eventually tripping a breaker.

Please post your model number, for now I'll assume it's a BGE/M or NHE/M series:

The can be caused by a few different sources on your generator:
1. Bad governor controller (whether mechanical or electronic)
2. Failing LPG regulator mounted on the generator
3. Failing LPG regulator on the coach LP tank
4. Damaged LPG supply hose from coach LP tank to generator regulator or supply hose from generator mounted regulator to carburetor
5. Vacuum leak in/around carb and intake manifold

If you have a volt/ohm meter check voltages at an outlet when the unit is hunting and when it's not. Check again with both ACs running.

Report back :-)
__________________

__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
94-Newmar is offline   Reply With Quote
Old 09-01-2014, 07:30 PM   #3
Senior Member
 
Geneandea's Avatar
 
Workhorse Chassis Owner
Holiday Rambler Owners Club
Join Date: Nov 2011
Posts: 128
1.Governor/controller. ?
2. Failing Regulator, Gen Regulator was replaced a year ago.
3. Regulator on coach, It doesn't have one liquid up to a two stage regulator on gen.
4. Damage line. / Don't smell anything and the generator will run.
5. Vacuum leak,?

Specs
model ,NHM
Volts 120
current 54.2
watts 6800
Speed 1800
trouble shooting guide for circuit breaker keeps tripping/stalling
1.Check fuel, tank was 85% last Friday (had to reset breaker on genset) ran fine for over an hour. had tank filled over the weekend. still had problem (fuel level is not the problem).


Thanks for the responding
__________________
Gene and Bea
2008 Fleetwood Pace arrow , Allison 6 speed transmission 38P work horse W24 chassis 5.5 KW gas Onan Generator with 2009 Saturn vue.
Geneandea is offline   Reply With Quote
Old 09-01-2014, 07:43 PM   #4
Senior Member
 
94-Newmar's Avatar
 
Join Date: Nov 2009
Posts: 2,043
Can you post the entire model number? I need the SPEC to see if it's a mechanical or electronically governed unit.

1. I'm sure you probably don't have a manometer, but if I were troubleshooting it the first thing I would do is hook mine up to a tap on the regulator and watch flow pressure as the unit is running. If the hunting resulted in the same fluctuations on the manometer then we could look further into the LPG supply.

2. Next look for vacuum leaks in and around the carburetor. Use a spray bottle of water. Remove the air filter and housing. When the unit is hunting, spray a stream of water around the outside of the carburetor where it mates to the intake manifold. If the hunting stops then you've found a vacuum leak - which could be a bad gasket or cracked intake/carb (not unusual).

3. Depending upon which SPEC unit you have, the governor is the next logical item to visit.
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
94-Newmar is offline   Reply With Quote
Old 09-02-2014, 09:11 AM   #5
Senior Member
 
Geneandea's Avatar
 
Workhorse Chassis Owner
Holiday Rambler Owners Club
Join Date: Nov 2011
Posts: 128
a basic question, do I have to totally remove all AC loads prior to starting the Generator? Heat pump and I have a belly refer box (Which was on) at start up. I will get the model soon, thanks
__________________
Gene and Bea
2008 Fleetwood Pace arrow , Allison 6 speed transmission 38P work horse W24 chassis 5.5 KW gas Onan Generator with 2009 Saturn vue.
Geneandea is offline   Reply With Quote
Old 09-02-2014, 11:06 AM   #6
Senior Member
 
Hooligan's Avatar
 
Freightliner Owners Club
Join Date: Apr 2002
Location: Pensacola
Posts: 2,202
Quote:
Originally Posted by Geneandea View Post
a basic question, do I have to totally remove all AC loads prior to starting the Generator?
Normally a good idea. Onan recommends allowing the generator to warm up prior to connecting electrical load. (2 minutes in cold wx) Also possible the circuit breaker is faulty. But that would not cause oscillations...
__________________
Hooligan, Pensacola, Fl -U.S. Coast Guard 1956-1985
2016 Thor Siesta Sprinter 24ST diesel
Our Pug "Lily" & "George" the Newfoundland
Hooligan is offline   Reply With Quote
Old 09-02-2014, 12:50 PM   #7
Senior Member
 
Geneandea's Avatar
 
Workhorse Chassis Owner
Holiday Rambler Owners Club
Join Date: Nov 2011
Posts: 128
its 95 degrees right now later this evening I will get the rest of the info you requested. Not knowing how the circuit breakers are wired its always been the bottom breaker (maybe its weak not many run hours on it though). We are leaving to go to Nova Scotia Thursday this week, I can live with the problem for the time we are gone. Hopefully its the load issue and I certainly don't give it two minutes prior to loading. I will make the changes you mention, get the tag information. Thanks so much, so much to know about so many things. Gene
__________________
Gene and Bea
2008 Fleetwood Pace arrow , Allison 6 speed transmission 38P work horse W24 chassis 5.5 KW gas Onan Generator with 2009 Saturn vue.
Geneandea is offline   Reply With Quote
Old 09-02-2014, 03:36 PM   #8
Senior Member
 
Hooligan's Avatar
 
Freightliner Owners Club
Join Date: Apr 2002
Location: Pensacola
Posts: 2,202
My 99 Onan NHM 6500 LP service manual is here: http://www.cumminsonan.com/www/pdf/m.../965-0531B.pdf
__________________
Hooligan, Pensacola, Fl -U.S. Coast Guard 1956-1985
2016 Thor Siesta Sprinter 24ST diesel
Our Pug "Lily" & "George" the Newfoundland
Hooligan is offline   Reply With Quote
Old 09-03-2014, 01:42 PM   #9
Senior Member
 
Geneandea's Avatar
 
Workhorse Chassis Owner
Holiday Rambler Owners Club
Join Date: Nov 2011
Posts: 128
I do believe the problem is my failure to remove initial loads and maybe the warm up. I have tried several time and had no problems. However just in case here is the infor you wanted.

Model # FA/26445H, Sn # FQ80763515 and it is liquid propane the regulator was replaced year or so ago.

Thanks Gene
__________________
Gene and Bea
2008 Fleetwood Pace arrow , Allison 6 speed transmission 38P work horse W24 chassis 5.5 KW gas Onan Generator with 2009 Saturn vue.
Geneandea is offline   Reply With Quote
Old 09-03-2014, 02:10 PM   #10
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by Geneandea View Post
just in case here is the infor you wanted
Model # FA/26445H, Sn # FQ80763515 and it is liquid propane the regulator was replaced year or so ago.
Thanks Gene
Gene
The "VOLTAGE regulator" or the "PROPANE regulator"?

Here is a link to excellent Onan trouble shooting guides:
Troubleshooting and Cross-Reference Guides | Flight Systems, Inc

BTW, when my genset was giving me Flight Systems' "technical department", (717-590-7330), was very helpful.

Mel
'96 Safari, 6.3kw LP Onan
__________________

__________________
mel s is offline   Reply With Quote
Reply

Tags
generator, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Would you replace a 23 yr old Onan? Pexring RV Systems & Appliances 8 08-13-2014 06:14 AM
Air conditioner Tripping Breaker budtee RV Systems & Appliances 10 06-17-2014 07:00 PM
Onan Generator Issues NevadaM1 iRV2.com General Discussion 7 05-11-2014 02:20 PM
Onan Gen and Cummins ISL Oil Filter Number Scepter1 Class A Motorhome Discussions 3 01-20-2014 05:18 PM
onan Emerald Plus 4000 tom41 RV Systems & Appliances 4 09-04-2013 02:20 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 09:01 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.