Old 07-03-2015, 02:47 PM   #1
Member
 
Join Date: Mar 2015
Posts: 83
89 Pace

I have an onan emerald 3 6.5kw. Here's the question shore power run ac's on pulse on high max cold works great no sweat. Oh and that's 30 amp.
Try to run one ac on low with lowest cold setting trips 20 amp circuit. This makes little to no sense to me. On shore or generator the circuit should see the same load. Not the generator runs like new also new circuit in fuse panel. The only thing I changed was went to a duel 20 amp because they don't make the 30/20 split .
Solutions? Questions? Getting damn hot boondocking. Thanks ahead of time
diesel1204 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-03-2015, 04:38 PM   #2
Senior Member
 
Monaco Owners Club
Freightliner Owners Club
Join Date: Mar 2015
Posts: 169
Check your voltage from the generator low voltage drives amps up fast if voltage is ok post back someone will help figure it out Mike
__________________
lead follow or get out of the WAY
1998 HR Endeavor 5.9 Cummins
redtail is offline   Reply With Quote
Old 07-04-2015, 07:20 AM   #3
Member
 
Join Date: Mar 2015
Posts: 83
Voltage is good
diesel1204 is offline   Reply With Quote
Old 07-05-2015, 05:43 AM   #4
Senior Member
 
Monaco Owners Club
Freightliner Owners Club
Join Date: Mar 2015
Posts: 169
????

well now we are both confused now i will think on it and get back hope someone familiar with Ac jumps in . Mike
__________________
lead follow or get out of the WAY
1998 HR Endeavor 5.9 Cummins
redtail is offline   Reply With Quote
Old 07-12-2015, 06:25 AM   #5
Member
 
Join Date: Mar 2015
Posts: 83
It's all about amps and load. I also have a 89 pace 38' duel duo therms. Think of it this way, when running genset in the perfect world brand new out of the box in the company's test center. The techs crank that baby to the max BOOM and that's what they stamp on the generator 6.5 kw @ 4000 was 120 volts and 33.3 amps. You will never ever get that. Your ac draws 30 amps at min cool so when you crank up the ac you also increase your load to your generator. What's in line is your fuse panel which has a 30 20 amp circuit, and the 20 pops.
On shore power you get a regulated power supply just like you home. So you get for the lack of a better word clean steady power. Generator is not clean regulated power. Another way to look at it think of a garden hose smaller hose to much pressure pop evertime. Large 2.5 fire fighting hose nice regulated flow.
If you really want to test this out, try running a ac , coffee pot and blow dryer at the same time off you generator. The do the same thing off shore.
I hope this helps sometimes I give to much information
You could always think of inverters and more batteries, a little spendy but long-term works great and saves fuel on generator .6 gal an hour adds up when boondocking.
diesel1204 is offline   Reply With Quote
Reply

Tags
ace



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
1984 Fleetwood Pace Arrow Eleganza ifsmithy Vintage RV's 39 07-14-2019 07:06 AM
2006 Pace Arrow 37C - thinking about purchasing meant2shop Fleetwood Owner's Forum 74 05-22-2017 11:29 PM
1990 Fleetwood Pace Arrow Battery Connections? HavocSun Fleetwood Owner's Forum 14 04-18-2015 11:27 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:19 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.