AC / Heating issue

Hi All,

We have a 2004 Winnebago Adventure 35U with basement air.

When we bought it in March 2015 both of the compressor's worked ( is that the right way to say that )
a about a month ago a strange electrical type smell started coming through the vents in the ceiling. When I flip the breaker to turn off the 2nd compressor the smell goes away.
I tested the power last night by unplugging from shore power and starting the generator. With no ac on it shows 6Amps, turn on the 1st ac it stays at 19Amps. When I turn on the 2nd compressor it jumps to 56Amps and doesn't start. (then rests at 19Amps again) it cycles through trying to start every 20Sec or so.

If any of this makes no sense let me know. Or if more info is needed !

Thanks
Dave
__________________
2004 Winnebago Adventure 35U
2005 Ford Focus ZX5
#publinontour #fulltimerv
Publin is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-21-2015, 08:14 AM   #2
Senior Member
 
Workhorse Chassis Owner
Join Date: Apr 2010
Location: Casa Grande AZ
Posts: 246
Basement air/heat pump units have a switch located in the main shore power bay that selects 30 or 50 amp power connection. when on 30 power, switch to "off" position, on for 50. when in "off", only one compressor will run. If you are hooked to 50 amp, check the switch, it may be trying to use both compressors then switch tells it NO. good luck.
__________________
Alleyman; 2004 Dolphin 5355; Banks Power Pack, Ottominder; 405 Watts Solar, 2010 Explorer XLT Toad. four month boondockers!
Alleyman is offline   Reply With Quote
Old 10-21-2015, 08:30 AM   #3
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,400
---56 amps sounds like a locked compressor......time for a new unit.....??????
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 10-21-2015, 08:34 AM   #4
Senior Member
 
Cooperhawk's Avatar
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Jun 2013
Location: 5 miles south of Lakeville, Mn
Posts: 3,047
Our second compressor quit working but was able to get it fixed without replacing. Lot cheaper.
__________________
Jim and Carol Cooper with Oreo the Kitty
FAA ATC ret, VFW, AL, VVA, NRA
US Army Aviation, MACV Vietnam 65-66
2012 Journey 36M, Cummings 360hp
Cooperhawk is offline   Reply With Quote
Old 10-21-2015, 10:52 AM   #5
Senior Member
 
Falcon190's Avatar
 
Winnebago Owners Club
Join Date: Sep 2011
Location: Camas, WA
Posts: 872
Quote:
Originally Posted by Alleyman View Post
Basement air/heat pump units have a switch located in the main shore power bay that selects 30 or 50 amp power connection. when on 30 power, switch to "off" position, on for 50. when in "off", only one compressor will run. If you are hooked to 50 amp, check the switch, it may be trying to use both compressors then switch tells it NO. good luck.
I've got basement air (heat pump) and never heard of that switch. Not sure I'd even have it cos on my rig, if I'm plugged into 30Amps instead of 50Amps, it automatically switches to only run one compressor.
Falcon190 is offline   Reply With Quote
Old 10-21-2015, 12:48 PM   #6
Junior Member
 
Publin's Avatar
 
Join Date: Oct 2013
Location: Where the sun is shining
Posts: 28
Quote:
Originally Posted by Cooperhawk View Post
Our second compressor quit working but was able to get it fixed without replacing. Lot cheaper.
Thanks for all the info,

Cooperhawk: can you remember how it was fixed / what was wrong ?

Thanks
Dave
__________________
2004 Winnebago Adventure 35U
2005 Ford Focus ZX5
#publinontour #fulltimerv
Publin is offline   Reply With Quote
Old 10-22-2015, 08:52 AM   #7
Senior Member
 
Cooperhawk's Avatar
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Jun 2013
Location: 5 miles south of Lakeville, Mn
Posts: 3,047
Yes, a coolent pipe had cracked and it lost it's freon. The tech at ABC Bus soldered it, filled it up, pressure checked it and reinstalled it. The unit drops right out of the rig and can be serviced right on the floor of the shop. Cost was a few hundred dollars and the unit is still working.
__________________
Jim and Carol Cooper with Oreo the Kitty
FAA ATC ret, VFW, AL, VVA, NRA
US Army Aviation, MACV Vietnam 65-66
2012 Journey 36M, Cummings 360hp
Cooperhawk is offline   Reply With Quote
Old 10-22-2015, 09:14 AM   #8
Senior Member
 
Starsekr's Avatar
 
Join Date: Feb 2014
Posts: 381
Have the same 54 Amp locked rotor condition on my 1st stage compressor. Unhooked the power from the circuit board to 1st stage, taped the wire and running it with just the second stage until it gets fixed.
Possibilities are bad "hard start" capacitor/PTCR (Positive temperature coefficent relay) or main capacitor <$20 and $10 respectively on eBay> or an acutal motor problem.
Look at the circuit board area for burnt wires. Some recent posts and pictures of this condition, do a search.
__________________
Jim and Valerie, 2005 Winnie Adventurer 37B, 2014 Subaru Forester Toad, hitches, brakes, anti-sways, autopilot, gourmet food on a Social Security budget.
"Wave as you go by."
Starsekr is offline   Reply With Quote
Old 10-22-2015, 10:50 AM   #9
Senior Member
 
National RV Owners Club
Join Date: Jun 2010
Posts: 4,581
Quote:
Originally Posted by Alleyman View Post
Basement air/heat pump units have a switch located in the main shore power bay that selects 30 or 50 amp power connection. when on 30 power, switch to "off" position, on for 50. when in "off", only one compressor will run. If you are hooked to 50 amp, check the switch, it may be trying to use both compressors then switch tells it NO. good luck.
Maybe some but not all. FYI Mine does not have that switch.
__________________
Bob & Sandi, dogs Tasha a Frenchie and Tiki a Skipperkey
SW OREGON 2005 34 foot DolphinLX
If towing: a bright red 2016 Mini Cooper on a tow dolly.
1ciderdog is offline   Reply With Quote
Old 10-22-2015, 04:21 PM   #10
Community Administrator
 
Lt Dan's Avatar


 
Tiffin Owners Club
Join Date: Sep 2013
Location: DFW, Texas
Posts: 21,565
Your excessive power draw could be something as simple as a bad start capacitor. I would try replacing that first before digging deeper. The electronics are located in a box accessible from the front without having to remove the unit. Here is a service manual for one of the AirXCel units like yours. This is the model I had in my '06 Itasca.
Attached Files
File Type: pdf AirXCel 6535 Service Manual.pdf (935.4 KB, 19 views)
__________________
2017 Phaeton 40IH XSH Maroon Coral - Power Glide Chassis with IFS
Previous '15 Tiffin Allegro RED 38QRA and '06 Itasca Sunrise 35A
'16 Jeep JKU Wrangler Sahara or '08 Honda Goldwing
Lt Dan is offline   Reply With Quote
Old 10-26-2015, 08:33 PM   #11
Junior Member
 
Publin's Avatar
 
Join Date: Oct 2013
Location: Where the sun is shining
Posts: 28
Thanks for the info Lt Dan, I found the Hard Start capacitor to be a melted mess lol, I've order 1 and should be here in the next few days. I'll update once I have it fitted and tested.
__________________
2004 Winnebago Adventure 35U
2005 Ford Focus ZX5
#publinontour #fulltimerv
Publin is offline   Reply With Quote
Old 10-29-2015, 01:02 PM   #12
Junior Member
 
Publin's Avatar
 
Join Date: Oct 2013
Location: Where the sun is shining
Posts: 28
UPDATE:

The "Hard Start Kit" I order arrived and was fitted last night. So far all is working

I ordered 2 of these kits as in other posts I found that they are known to go bad, for an easy fix and only $30 ish I'm not going to be without.

Just on a side note, I've noticed that the other Hard Start unit is not original !


Thanks again to everyone for there help ! Saved us $$$$$ by not having to call out a tech.
__________________
2004 Winnebago Adventure 35U
2005 Ford Focus ZX5
#publinontour #fulltimerv
Publin is offline   Reply With Quote
Reply

Tags
heat, heating



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2015 Ventana Cummins Engine Stalling Issue cstar5634 Cummins Engines 8 10-21-2015 08:59 PM
Slight oil leak...Issue or non Issue? Speedjester Cummins Engines 6 09-03-2015 07:17 AM
Fuel issue solved Elandan85 Class A Motorhome Discussions 4 07-07-2015 04:45 AM
Onan Genset power production issue Globetrotter Monaco Owner's Forum 4 05-23-2015 10:20 AM
Strange Electrical Issue baldtat MH-General Discussions & Problems 18 01-13-2014 06:44 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:34 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.