Old 04-25-2011, 12:52 PM   #15
Moderator Emeritus
 
Mike Canter's Avatar


 
Join Date: Apr 2008
Location: Freeport, ME
Posts: 4,707
Perry, there is no way to put your finger down there are touch the level float switch on these models. The original switch is plastic so I would be awful careful of breaking it by putting anything down there.

My Low Temp Cutoff switch is always on and like I said before that is normal on my model.

My concern would be that the boiler tank really is low on anti-freeze and that is why the light is really on. You should open up the radiator cap on the top of the unit and see if it is full or not. If not full then pour in a 50/50 mix of boiler anti-freeze. I think that when I opened mine I had all the thermostats calling for heat so all the ciculating pumps were running and the anti-freeze was up in all the lines then I filled it to the top.

The hot water faucets being on or off makes no difference because the boiler is heated and held to a fixed temp for both the hot water and the heaters.
__________________

__________________
Mike Canter
"Gunner" USN Retired, Airdale
2004 Monaco Signature 44' Conquest. Detroit 60
Mike Canter is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-25-2011, 01:18 PM   #16
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,191
Guys, thanks for all the good suggestions. I did put my finger in after filling it with a 50/50 solution and the liquid was within an inch of the bottom of the neck. I did have to put a hose in and fill it via a funnel on the end of the hose, and as per Mike's concern, I may have broken the float if it is that fragile - I didn't even consider that you could break something that way.

I used 1/2 inch clear plastic tubing and shoved about 5 inches of it down the neck to fill it.

Now since the boiler and the filler neck are about 2 feet back inside the belly of the coach and there is only about 4 inches of clearance, there is no way to look down inside to see if it is broken. What is the easiest way to tell if the float is broken and how to you replace it?
__________________

__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 04-25-2011, 01:42 PM   #17
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
Use a mirror and a flashlight. If it's broke call Hydro Hot and they can tell you if it's repairable or if you have to buy another tank.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 04-25-2011, 01:47 PM   #18
Moderator Emeritus
 
Mike Canter's Avatar


 
Join Date: Apr 2008
Location: Freeport, ME
Posts: 4,707
You can bypass the float level switch and see if that fixes the problem and the light goes out. Just pull the two wires off the float switch and join them together and tape them up. If the light goes out and the diesel furnace fires up then you need to spend the $120 to get the brass one. You also need to fix the drain valve to an all brass one since you have to totally drain it anyhow. There is no problem reusing the anti-freeze. I filtered it through a paint filter and used it again. I drained the anti-freeze into three six gallon containers and had a spare one standing by.
__________________
Mike Canter
"Gunner" USN Retired, Airdale
2004 Monaco Signature 44' Conquest. Detroit 60
Mike Canter is offline   Reply With Quote
Old 04-25-2011, 02:00 PM   #19
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,191
Again thanks for the great input. I don't think a mirror and flashlight will do the trick, you can hardly get a hand in there to take off the cap. I'll do as you suggest, Mike, and bypass the switch and see if that is the issue, then proceed from there.
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 04-26-2011, 09:20 AM   #20
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,191
Tech support at Aqua-Hot send me a useful link:

RV Hydronic Heater Repair - Downloads
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 04-26-2011, 09:48 AM   #21
Senior Member
 
Roger Berke's Avatar
Commercial Member
 
Join Date: Apr 2007
Posts: 175
Aqua-Hot Won't Fire

Paul

Sorry that I am slow in responding. I have been busy.

Your float switch has probably failed. If the switch has failed, it thinks that the boiler is low on coolant and shuts everything down. It is not uncommon for the plastic to crack, especially if the coolant gets low and the plastic is exposed to the air in the tank. The replacement float is mostly made out of brass and is much more robust.

Aqua-Hot gave you a link to a couple of the troubleshooting guides that I have written. To jumper the float switch you need “How to defeat the float switch”. If you choose to replace the float switch yourself, read “How to replace float switch”. There are a number of online parts sources for Aqua-Hot parts. Search for “RV Hydronic Heater Parts”.

If you have questions you can post on my Yahoo group.

- Roger Berke -
Moderator - HydronicRVHeating : Hydronic-RV-Heating
__________________
Roger Berke is offline   Reply With Quote
Old 04-26-2011, 10:24 AM   #22
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,191
Roger,

No worries, I have not had time to get back to the coach. I will follow the "How to defeat the float switch" instructions today. If that gets it going, I'll order some parts and have a go at it following your other instructions.

I didn't realize that you had written them as there is no obvious credit, but I am quite grateful that you did so.

Thank you and I'll post my results.

Paul.
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 04-26-2011, 03:55 PM   #23
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,191
Tested it today but was silly and didn't take a small enough screw driver so I could only hold the jumper in place for a few seconds, not enough to fire the burner but long enough to see the light go out. I'll go back later with a small screw driver and see if I can fire it.
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 04-27-2011, 07:56 AM   #24
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,191
Thanks everyone - I did get it to fire last night. It needs a float switch and I think I now have enough info to change it.
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 04-27-2011, 08:25 AM   #25
Senior Member
 
Roger Berke's Avatar
Commercial Member
 
Join Date: Apr 2007
Posts: 175
RE: Aqua-Hot Won't Fire

Paul

Check the drain valve for your Aqua-Hot. If it still has any plastic parts on it you should use replace those parts with brass while you have the coolant out.

Your model of Aqua-Hot was built with short brass pipe nipple that connects with the plastic parts. Replace with 1/2" brass coupling, 2" or 2 1/2" pipe nipple, then use 1/2" brass ball valve.

- Roger Berke -
Moderator - Yahoo Hydronic RV Heating Group
HydronicRVHeating : Hydronic-RV-Heating
__________________
Roger Berke is offline   Reply With Quote
Old 04-28-2011, 06:01 PM   #26
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,191
Last question (for now) - how full should the tank be? I ran it until it had pushed some fluid into the overflow tank, and it did pull about the same amount back when it cooled down completely, but if I am not mistaken it won't actually fill itself that way if it was short to begin with. I have it filled to about an inch below the bottom of the main tank filler neck.
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 04-28-2011, 06:08 PM   #27
Moderator Emeritus
 
Mike Canter's Avatar


 
Join Date: Apr 2008
Location: Freeport, ME
Posts: 4,707
Paul, you already have the float switch installed?

Read this on bleeding the system of air
Aqua-Hot Heating Systems Inc.
__________________
Mike Canter
"Gunner" USN Retired, Airdale
2004 Monaco Signature 44' Conquest. Detroit 60
Mike Canter is offline   Reply With Quote
Old 04-28-2011, 11:48 PM   #28
Senior Member
 
Roger Berke's Avatar
Commercial Member
 
Join Date: Apr 2007
Posts: 175
RE: Aqua-Hot Won't Fire

The model of Aqua-Hot that is in Paul's coach is an AHE-100-04S, which has 'self priming' pumps.

There will be about 1/2 gallon of coolant that will 'overflow' out of the boiler tank to the overflow bottle as the unit heats to operating temperature. Let unit cool for at least 1/2 hour, then remove radiator cap. Should be full right to neck.

- Roger Berke -
Moderator - Yahoo RV Hydronic Heating Group
HydronicRVHeating : Hydronic-RV-Heating
__________________

__________________
Roger Berke is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gurgurling sound from Aqua Hot Casa Ruby Class A Motorhome Discussions 8 02-02-2011 08:59 AM
Service on Aqua Hot FLYING BUTCH Monaco Owner's Forum 10 10-29-2010 09:37 AM
Aqua Hot Service Rgrafty Jayco Owner's Forum 3 09-18-2009 10:26 AM
aqua hot zones and slide adjustments electricks Travel Supreme Owner's Forum 8 11-03-2008 06:05 PM
Aqua Hot Thermostadt Zones DCTENT Monaco Owner's Forum 14 05-03-2008 07:04 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:28 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.