Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > MOTORHOME FORUMS > Class A Motorhome Discussions
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 09-17-2015, 09:31 AM   #43
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,704
I'm always amazed at the hysteria this question produces. And the misinformation.

The 220 (240) volt diagram is the correct one. The standard 50A RV outlet has 240v available. Just like your house power at home. Just because your RV has no actual 220v or 240v circuits does not mean the power outlet can't have 240v available for use. And some [few] RVs do in fact employ actual 220v circuits and appliances, e.g. an electric stove/oven or residential style clothes dryer.

I think Cooperhawk is thinking of a 30A RV plugged to an older style 30A/240v outlet that was commonly used for welders and old 3-pront-plug dryers. THAT is a no-no, but it has nothing to do with an RV designed for 50A power.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-17-2015, 03:17 PM   #44
Senior Member
 
Cooperhawk's Avatar
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Jun 2013
Location: 5 miles south of Lakeville, Mn
Posts: 3,047
I wire my own, (with inspections), and I am always worried that someone will get the wrong receptacle. Just trying to be cautious.
__________________
Jim and Carol Cooper with Oreo the Kitty
FAA ATC ret, VFW, AL, VVA, NRA
US Army Aviation, MACV Vietnam 65-66
2012 Journey 36M, Cummings 360hp
Cooperhawk is offline   Reply With Quote
Old 09-17-2015, 04:43 PM   #45
Senior Member
Commercial Member
 
Join Date: Aug 2012
Posts: 726
The fundamental problem is that many 240vac welder and home dryer installations have used the standard TT-30R outlet. Therefore before plugging in, you should verify the voltage.

A RV 30amp service is 120vac

Reference: http://www.myrv.us/Imgs/PDF/30-amp%20Service.pdf



Sent from my iPad using iRV2 - RV Forum
TravellingRVDoctor, LLC
__________________
Traveling RV Doctor
https://www.facebook.com/Traveling-R...5780632151951/
shiggs68 is offline   Reply With Quote
Old 09-17-2015, 08:27 PM   #46
Senior Member
 
Papa_Jim's Avatar
 
Outdoors RV Owners Club
Join Date: Oct 2009
Location: Manitoba,Canada
Posts: 2,789
Quote:
Originally Posted by shiggs68 View Post
Here is a link http://www.myrv.us/Imgs/PDF/50-amp%20Service.pdf

And a picture Attachment 107064

And a link to how a standard campground post is wired https://www.google.com/search?q=50am...2_ZHOwFR3mM%3A


Sent from my iPad using iRV2 - RV Forum
TravellingRVDoctor, LLC
To answer the OP's question, are 50Amps 220 Volt? The answer is Yes it can be. If the appliance plugged into the receptacle connects L1 and L2 together, it uses the power as 220V. If the appliance (the RV) does not connect L1 and L2 together, but uses L1 and L2 as separate individual power circuits, then this appliance (the RV) uses the power as 110V.

50 Amp receptacles are the easiest and the safest to set up, with a L1 power line, a L2 power line, a neutral connection and a ground connection. The rest depends on the appliance being plugged into it.

As I stated previously, I have a 50 Amp receptacle set up in my shop. When I plug my coach into it, it uses it as a 110V power supply. When I plug my big shop air compressor or my welder into it, they use it as a 220V power supply.

30 Amp receptacles are a totally different story. They can be set up as 110V or 220V. I don't think the OP is asking about that.

Jim
__________________
2016 Creekside 23RKS
2012 Ram 2500 Laramie 4X4 Cummins 6.7L
Canada, eh?
Papa_Jim is offline   Reply With Quote
Old 09-18-2015, 06:08 AM   #47
Senior Member
Commercial Member
 
Join Date: Aug 2012
Posts: 726
Quote:
Originally Posted by Papa_Jim View Post
To answer the OP's question, are 50Amps 220 Volt? The answer is Yes it can be. If the appliance plugged into the receptacle connects L1 and L2 together, it uses the power as 220V. If the appliance (the RV) does not connect L1 and L2 together, but uses L1 and L2 as separate individual power circuits, then this appliance (the RV) uses the power as 110V.



50 Amp receptacles are the easiest and the safest to set up, with a L1 power line, a L2 power line, a neutral connection and a ground connection. The rest depends on the appliance being plugged into it.



As I stated previously, I have a 50 Amp receptacle set up in my shop. When I plug my coach into it, it uses it as a 110V power supply. When I plug my big shop air compressor or my welder into it, they use it as a 220V power supply.



30 Amp receptacles are a totally different story. They can be set up as 110V or 220V. I don't think the OP is asking about that.



Jim

Papa_Jim, you have partially restated what the above references show.

Your statement "receptacle connects L1 and L2 together, it uses the power as 220V." Is incorrect. When the load is connected to L1 and L2, you have 240vac not connected "together" which would cause a short.

And just FYI, there are RVs on the market today that utilize the 240vac capability for clothes dryers and cook top appliances.

The proper terminology for the service is "120/240vac/50amp split-phase. Exactly the same as supplied to your S&B house except not the higher amperage.


Sent from my iPad using iRV2 - RV Forum
TravellingRVDoctor, LLC
__________________
Traveling RV Doctor
https://www.facebook.com/Traveling-R...5780632151951/
shiggs68 is offline   Reply With Quote
Old 09-18-2015, 07:43 AM   #48
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by Papa_Jim View Post
To answer the OP's question, are 50Amps 220 Volt?
The answer is Yes it can be. If the appliance plugged into the receptacle connects L1 and L2 together, it uses the power as 220V. If the appliance (the RV) does not connect L1 and L2 together, but uses L1 and L2 as separate individual power circuits, then this appliance (the RV) uses the power as 110V.
50 Amp receptacles are the easiest and the safest to set up, with a L1 power line, a L2 power line, a neutral connection and a ground connection. The rest depends on the appliance being plugged into it.
As I stated previously, I have a 50 Amp receptacle set up in my shop. When I plug my coach into it, it uses it as a 110V power supply. When I plug my big shop air compressor or my welder into it, they use it as a 220V power supply.
30 Amp receptacles are a totally different story. They can be set up as 110V or 220V. I don't think the OP is asking about that.
Jim
Papa_Jim
That is an excellent reply/answer to the OP's question.
Correct and easily understood with no unnecessary technical mumbo-jumbo.

Quote:
Originally Posted by shiggs68 View Post
Papa_Jim, you have partially restated what the above references show.
Your statement "receptacle connects L1 and L2 together, it uses the power as 220V." Is incorrect. When the load is connected to L1 and L2, you have 240vac not connected "together" which would cause a short.
And just FYI, there are RVs on the market today that utilize the 240vac capability for clothes dryers and cook top appliances.
The proper terminology for the service is "120/240vac/50amp split-phase. Exactly the same as supplied to your S&B house except not the higher amperage.
TravellingRVDoctor, LLC
shiggs68
Your comments to Papa_Jim are also correct.

EXCEPT for the fact that some older S&B homes have "120/240vac/50amp split-phase" electrical service from the power company....which IS EXACTLY THE SAME as the electrical service provided by most campground "50A" power pedestal receptacles.

Mel
'96 Safari
mel s is offline   Reply With Quote
Old 09-19-2015, 07:04 AM   #49
Senior Member
Commercial Member
 
Join Date: Aug 2012
Posts: 726
Quote:
Originally Posted by mel s View Post
Papa_Jim
That is an excellent reply/answer to the OP's question.
Correct and easily understood with no unnecessary technical mumbo-jumbo.


shiggs68
Your comments to Papa_Jim are also correct.

EXCEPT for the fact that some older S&B homes have "120/240vac/50amp split-phase" electrical service from the power company....which IS EXACTLY THE SAME as the electrical service provided by most campground "50A" power pedestal receptacles.

Mel
'96 Safari

Not sure what you are saying and I guess I should have been more clear.

Most S&B homes have 120/240vac split-phase service in the 50/60/100/200amp range depending on age of the home and the local codes in effect at the time.

There is nothing special or mysterious about a 50amp RV service. In fact in some areas of the county, the same outlet is required for home clothes dryer installations.

The main point is that before plugging in your RV, you should either have a Surge Protector that checks for correct wiring and voltages or have a meter to manually check yourself and understanding what you are checking. This applies to both 30amp and 50amp RV services. Better safe then sorry.


Sent from my iPad using iRV2 - RV Forum
TravellingRVDoctor, LLC
__________________
Traveling RV Doctor
https://www.facebook.com/Traveling-R...5780632151951/
shiggs68 is offline   Reply With Quote
Old 09-19-2015, 07:26 AM   #50
Senior Member
 
Entegra Owners Club
Spartan Chassis
Join Date: Mar 2009
Location: Kerrville, TX
Posts: 320
Quote:
Originally Posted by leshchat View Post
I'm trying to set up an electric pole for my monaco with a 50 amp service...is that 220 or 110?
The simple answer is that you need 220 volt at the plug pedestal. You split the 220 so you have 110/50 amp to Leg 1 and 110/50 amp leg 2 which will share a common neutral. These two legs are out phase so they can share the common ground. If you put a meter on leg 1 and leg 2 you will get 0 volts. If you look at a 50 amp plug on your unit it has on the top a common neutral pin, on each side is a hot blade (leg 1 and leg 2), and the bottom is the grounds. This has been stated by several members but may seem a little convoluted.
I would recommend you use an electrician. There are several other factors that need consideration such wire run distance from source which will determine wire gauge, etc.
rorr1821 is offline   Reply With Quote
Old 09-19-2015, 08:16 AM   #51
Senior Member
 
Join Date: Jul 2014
Posts: 35,442
Quote:
Originally Posted by rorr1821 View Post
The simple answer is that you need 220 volt at the plug pedestal. You split the 220 so you have 110/50 amp to Leg 1 and 110/50 amp leg 2 which will share a common neutral. These two legs are out phase so they can share the common ground. If you put a meter on leg 1 and leg 2 you will get 0 volts. If you look at a 50 amp plug on your unit it has on the top a common neutral pin, on each side is a hot blade (leg 1 and leg 2), and the bottom is the grounds. This has been stated by several members but may seem a little convoluted.
I would recommend you use an electrician. There are several other factors that need consideration such wire run distance from source which will determine wire gauge, etc.
L1 to L2 volts will equal 240. See the diagrams.
twinboat is offline   Reply With Quote
Old 09-19-2015, 08:23 AM   #52
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
Quote:
Originally Posted by rorr1821 View Post
The simple answer is that you need 220 volt at the plug pedestal. You split the 220 so you have 110/50 amp to Leg 1 and 110/50 amp leg 2 which will share a common neutral. These two legs are out phase so they can share the common ground. If you put a meter on leg 1 and leg 2 you will get 0 volts. If you look at a 50 amp plug on your unit it has on the top a common neutral pin, on each side is a hot blade (leg 1 and leg 2), and the bottom is the grounds. This has been stated by several members but may seem a little convoluted.
I would recommend you use an electrician. There are several other factors that need consideration such wire run distance from source which will determine wire gauge, etc.

I think you understand the configuration but you had a brain fart. Under the above conditions, if you measure between L1& L2, you will measure 240 VCA if the service is installed correctly and L1 & L2 are out of phase. If this measurement is zero, then the service is wired with L1 & L2 in phase and there is a real possibility of over current on the neutral leg.

In reality you are not splitting 220 (240) you are just never using them both in the same circuit. Some coaches use 240 for a dryer or one element in an AquaHot. The capacity is present and all that's necessary to utilize a 240 circuit is installing a double pole breaker and sizing the wiring on that circuit appropriately.


Steve Ownby
Full time since '07
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 09-19-2015, 10:30 AM   #53
Senior Member
 
Algonquin's Avatar
 
Join Date: Apr 2015
Posts: 331
Quote:
Originally Posted by Steve Ownby View Post
I think you understand the configuration but you had a brain fart. Under the above conditions, if you measure between L1& L2, you will measure 240 VCA if the service is installed correctly and L1 & L2 are out of phase. If this measurement is zero, then the service is wired with L1 & L2 in phase and there is a real possibility of over current on the neutral leg.

In reality you are not splitting 220 (240) you are just never using them both in the same circuit. Some coaches use 240 for a dryer or one element in an AquaHot. The capacity is present and all that's necessary to utilize a 240 circuit is installing a double pole breaker and sizing the wiring on that circuit appropriately.


Steve Ownby
Full time since '07

Yes, you are splitting the single phase 220 (240) by using a center tap on the distribution (utility power pole) transformer output windings so that only 110 (120) volts are seen between L1 or L2 and the center neutral tap.
__________________
2011 Itasca Meridian 34Y
2014 Honda CR-V
Algonquin is offline   Reply With Quote
Old 09-19-2015, 02:22 PM   #54
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,704
Semantics? "Split phase" is technically correct but mere techno-babble as far as practical usage at the power pole is concerned. If you connect the load between L1 & L2, it's 240v. No matter how you describe it.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 09-19-2015, 02:59 PM   #55
Senior Member
 
NMRVer's Avatar
 
Thor Owners Club
Freightliner Owners Club
Join Date: Jul 2014
Posts: 352
x2 skip nailed it. get answer
__________________
2018 Thor Aria 3901
Toad: 2022 GMC Canyon CC LB
NMRVer is offline   Reply With Quote
Old 09-20-2015, 08:15 AM   #56
Senior Member
 
HD4Mark's Avatar
 
Winnebago Owners Club
Coastal Campers
Join Date: Oct 2009
Location: Marathon, Florida
Posts: 2,909
Honestly I had no idea any MH actually used 240V. This must be a new thing with the advent of all electric coaches. The way I looked at it, even though there was 240 available, it was never intended to be used in a MH. There was just two 120 feeds to supply enough power for all the goodies inside a big house on wheels.

So the answer in my eyes is just wire it correctly and who cares how you look at it as long as it is safe and works.
__________________
Mark & Nancy
2004 Winnebago Vectra 40KD
Shep dog, R.I.P. Kenzie dog Toad 2015 Jeep Wrangler Willys Wheeler
HD4Mark is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
15th ANNIVERSARY CELEBRATION RALLY Madame Boomer Texas Boomers 31 05-19-2015 03:36 PM
110/ 220 volt question SDCOToyhaul Toy Haulers Discussion 16 05-05-2015 03:21 AM
12 Volt Problems garymunson Class A Motorhome Discussions 6 04-23-2015 07:52 AM
New 6 volt 220 amp bats what charger? edsperfect MH-General Discussions & Problems 8 03-15-2015 02:54 PM
Amps per hour? Horsepower per hour? BatteryPro Going Green 5 02-23-2015 06:04 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:40 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.