Old 10-28-2014, 06:33 AM   #71
Senior Member
 
Steve N Sal's Avatar
 
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 5,590
You know I've stayed away from this thread for some obvious reasons but maybe it's time to share something. Maybe some of you have not had the safety training and if you have maybe you slept thru the course (I don't know). This is a dangerous trade and respect of it is of the utmost importance. I have always taken it seriously not just for myself but for anyone who works alongside of me or any customers that I have serviced.
It's been mentioned that maybe I was "LUCKY" to have found the contacts in a breaker sticking. No it wasn't LUCK, I was just doing what each an everyone of you should do. NOT TAKE ANYTHING FOR GRANTED. I don't know if I mentioned this before but I have found this more then once. Do you really think that everything is fail safe? If you do you're badly mistaken. For this to happen a breaker does NOT have to be in a industrial environment nor does it have to be struck by lightning. It can happen just in the process from the manufacturer as a faulty item. I'm not a roll of the dice electrician. If you are so be it but don't ever condemn someone who is thorough in there work. I'll leave it at that and I'm including a page from one of my safety classes. Take the time to read first two paragraphs. You can click the image to enlarge it. Take care and be safe!
Attached Thumbnails
Click image for larger version

Name:	Electrical Hazards 001.jpg
Views:	82
Size:	281.7 KB
ID:	77681  
__________________

__________________
Steve & Sally / HiTee & Hudson Our Little Poms / Heidi & Houston Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert
Michigan (Summer) Florida (Winter)
Steve N Sal is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-28-2014, 07:01 AM   #72
Senior Member
 
tagcat's Avatar
 
Monaco Owners Club
Join Date: Dec 2013
Location: west fork arkansas
Posts: 270
I live in an area that has had several power outages.The really only safe way is to install a switch over box at the panel in the house.Mine has 10 emergency breakers,for lights ,frig tv,etc(no 220 v) then you have to have an heavy duty cord to go from gen to switch over box.I finely did get a 5500 watt at home depo.With the switch over box protects you and linemen ,you do not feed power down line.
You can wire the coach to feed this panel ,but do it right if not you can cause a fire or kill your self.Just be safe.The extension cord with 2 male ends ,not a good idea.
__________________

__________________
tagcat is offline   Reply With Quote
Old 10-28-2014, 08:15 AM   #73
Senior Member
 
Join Date: Jun 2013
Posts: 175
Quote:
Originally Posted by Steve N Sal View Post
You know I've stayed away from this thread for some obvious reasons but maybe it's time to share something. Maybe some of you have not had the safety training and if you have maybe you slept thru the course (I don't know). This is a dangerous trade and respect of it is of the utmost importance. I have always taken it seriously not just for myself but for anyone who works alongside of me or any customers that I have serviced.
It's been mentioned that maybe I was "LUCKY" to have found the contacts in a breaker sticking. No it wasn't LUCK, I was just doing what each an everyone of you should do. NOT TAKE ANYTHING FOR GRANTED. I don't know if I mentioned this before but I have found this more then once. Do you really think that everything is fail safe? If you do you're badly mistaken. For this to happen a breaker does NOT have to be in a industrial environment nor does it have to be struck by lightning. It can happen just in the process from the manufacturer as a faulty item. I'm not a roll of the dice electrician. If you are so be it but don't ever condemn someone who is thorough in there work. I'll leave it at that and I'm including a page from one of my safety classes. Take the time to read first two paragraphs. You can click the image to enlarge it. Take care and be safe!

From one sparky to another well said
__________________
middleman210 is offline   Reply With Quote
Old 10-28-2014, 09:48 AM   #74
Senior Member
 
BFlinn181's Avatar


 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 12,944
I agree Steve N Sal, the chances of energizing the lines is not worth the convenience of flipping a switch. In a power outage, move into the RV and string a couple of extension cords to refrigerators or freezers. Also, if needed, a space heater to keep things from freezing. To expect to run your house from a 120 v RV generator is a bit extreme.

Used to be people went camping to enjoy 'roughing it' so they could appreciate the comforts of home when they returned. Now with RVs tricked out fancier than 98% of the world's population living conditions some folks can't handle the inconvenience of a short term power outage.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 11-04-2014, 03:56 AM   #75
Senior Member
 
Ford Super Duty Owner
Join Date: Nov 2013
Posts: 206
Quote:
Originally Posted by tricotec View Post
What I haven't seen here is the fact that the RV's power system and generator are not the same as the average home. Your home has a three-wire 220VAC feed with two hot wires and a grounded neutral and the 110V circuits are taken from both sides of that feed to the neutral wire. The RV is 110VAC only. While it might be possible to feed certain circuits in the home from an RV generator, none of the 220VAC equipment would work (AC, water heater, Range, Dryer etc), and feeding certain 110VAC loads would require some complex electrical equipment to do safely.

It would almost surely cost more in modifications to the RV and the home's electrical system to tie in the RV safely to a home than to just buy a 220VAC generator for the home and power the whole thing. Even if you did, several of your major 220VAC load could not be supplied.
I agree and that's coming from being an instrument/electrician for 40 years
__________________
flangley is offline   Reply With Quote
Old 11-04-2014, 09:06 AM   #76
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 21,485
I will point out this: I have read posts from people who say something like "I will never forget to pull the main breaker before I backfeed cross my heart and hope to die" Well bully for them.. But let me paint a picture (of death).

They are out and about, Perhaps at a doctor's appointment or at work (Seems power fails always happened when i was at work, or in one case church).

Someone else remembers "Last power fail dad did this" and plugs in the death cord. Fires up the genny and ZAP. Kills a line man, or the generator, or both, because they FORGOT to pull the breaker.

Do it right or do not do it at all.. I described right in another post but to recap.

On house: Install a proper transfer system.. There are many to choose from, one goes between the meter and the meter box so the power company does the actual install for you (takes like 2 minutes).

use a proper cord with an OUTLET on the house end to plug into the INLET on the house.

And play safe.

I used a transfer panel so I could select which loads transfered, this allowed me to not transfer 240 volt loads (Since the RV was 120 only) and to not transfer a key indicator light we almost never used (Save during power fails) so i could tell when power was restored.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 11-05-2014, 11:53 AM   #77
Senior Member
 
Join Date: Jul 2012
Posts: 111
Quote:
Originally Posted by Steve N Sal View Post
The reason this could happen is because the contacts within the breaker may stick on one side or possibly both sides and not open the circuit.
Does the NEC allow Interlocks in all 50 States or the majority thereof?
__________________
2002 Monaco Knight
fortisi876 is offline   Reply With Quote
Old 11-05-2014, 05:28 PM   #78
Senior Member
 
Join Date: Jun 2013
Posts: 175
Quote:
Originally Posted by fortisi876 View Post
Does the NEC allow Interlocks in all 50 States or the majority thereof?

The Nec is just the guid line that each local governments use to set there standard. Some have rules that are stricter. None that I know have rules that are less than Nec.
__________________
middleman210 is offline   Reply With Quote
Old 11-05-2014, 05:38 PM   #79
Senior Member
 
palehorse89's Avatar


 
Newmar Owners Club
Join Date: Oct 2009
Posts: 6,800
Cool Very simple....

This subject is very simple to sort out.......
The OP has a Motorcoach....$$$$$$$$
FORGET the Coach to "power your house"!
If needed, use the Fridge..........
"Buy" A GENERATOR to properly power your house or the needed outlets up during a power failure......and install the "PROPER" automatic transfer switch to eliminate "human" Failure........
You will have a lot less money in this backup....setup, than you have tied up in your Motorcoach........and you won't have to rely on it to do a job it was not designed to do......... JMHO......
__________________
2000 Newmar MADP 4060, 350ISC, Spartan MM, IFS 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006Ultra & 1989 Springer
palehorse89 is online now   Reply With Quote
Old 11-05-2014, 05:57 PM   #80
Senior Member
 
Join Date: Sep 2012
Posts: 4,255
Off hand it rather depends on both how big your MH and house are and how often you expect to need it. If I lived somewhere where long power outages were fairly frequent I might invest in a transfer switch an a genset for the house. As it stands if the power goes off for more than a day I will probably go down an pop out a couple of breakers so I can power up the furnace, a few lights and the freezer and refrigerator. It's been 15 years since I last needed to think about it so no hurry. The camper has everything I need the first day and most days. ;-)
__________________
nothermark is offline   Reply With Quote
Old 11-05-2014, 06:46 PM   #81
Senior Member
 
Join Date: Jul 2012
Posts: 111
Quote:
Originally Posted by middleman210 View Post
The Nec is just the guid line that each local governments use to set there standard. Some have rules that are stricter. None that I know have rules that are less than Nec.
Poorly worded on my part, what I meant to ask/say is if the NEC is the minimum guideline for every State and they approve the Interlock as an option, then I don't know why people are getting so pigheaded about this version/option of backfeeding.
__________________
2002 Monaco Knight
fortisi876 is offline   Reply With Quote
Old 11-05-2014, 07:38 PM   #82
Senior Member
 
BFlinn181's Avatar


 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 12,944
Quote:
Originally Posted by nothermark View Post
Off hand it rather depends on both how big your MH and house are and how often you expect to need it. If I lived somewhere where long power outages were fairly frequent I might invest in a transfer switch an a genset for the house. As it stands if the power goes off for more than a day I will probably go down an pop out a couple of breakers so I can power up the furnace, a few lights and the freezer and refrigerator. It's been 15 years since I last needed to think about it so no hurry. The camper has everything I need the first day and most days. ;-)
Here's a video that shows how to hook up your home furnace to your RV generator when needed. It does take a bit of preparation, but not much in the way of parts, so I wouldn't wait until the power was out a few days.



It's a long video, but thorough. NOTE: Since your RV generator is 120 v, you can NOT power a home electric furnace, heat pump, or whole house air conditioner. Those types of heat are 240 v. Also make sure your home thermostat is powered from a transformer powered through the furnace. If it is wired differently, the thermostat will not have power to control the furnace.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 11-05-2014, 08:05 PM   #83
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 12,416
Quote:
Originally Posted by vsheetz View Post
A dead man's cord is a very dangerous thing to have around.
And that "method" is against the law in most states. To use a genset to power the entire house a separate disconnect device must be installed and used on the incoming power line. Simply throwing the main panel breaker is not sufficient.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member."We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert theConstitution. "Abraham Lincoln"
Ray,IN is offline   Reply With Quote
Old 11-06-2014, 04:13 AM   #84
Senior Member
 
Join Date: Jun 2013
Posts: 175
Quote:
Originally Posted by fortisi876 View Post
Poorly worded on my part, what I meant to ask/say is if the NEC is the minimum guideline for every State and they approve the Interlock as an option, then I don't know why people are getting so pigheaded about this version/option of backfeeding.

Me either other than money. My self if and when we loose power I just run cords to the things I need
__________________

__________________
middleman210 is offline   Reply With Quote
Reply

Tags
generator, power


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:39 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, vBulletin Solutions, Inc.