Burnt receptacle Face plate
We have an older MH Winnebago 92 model.This winter we parked it next to our garage and plugged it into the 20 amp garage. I kept a electric oil filled rad heater plugged in for some heat. For about one week it got down in the single digets, so I used another heater same type but only turned it on 600 watts. All seemed fine for a day or two. Checked one morning and they were not working. Breaker in MH was flipped. I unplugged one of the heaters, reset breaker, everything was fine. Never used both heaters again at the same time. Getting ready to start a trip and noticed that the wall plate where I had the heater plugged into was burnt on the outside(not good). beside changing the wall recepticle what else should I check for? Thanks
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
03-02-2018, 08:06 AM
|
#2
|
Senior Member
Winnebago Owners Club
Join Date: Dec 2015
Location: Jacksonville, Fl
Posts: 3,542
|
Check the wiring behind the plug, any wiring that looks like it's been hot needs to be replaced (or just cut off, if the bad part is short enough that will leave you enough wire to make a connection).
__________________
2013 Winnebago Sightseer 36V
|
|
|
03-02-2018, 08:10 AM
|
#3
|
Senior Member
Monaco Owners Club
Join Date: Jan 2016
Location: New Hampshire
Posts: 593
|
When you change the receptacle, check the condition of the wires. If they look OK, then it was probably high resistance in the plug contacts causing the burning. If the wires look charred or melted downstream, then I'd worry.
Walt
__________________
Walt & Bonnie
2006 Monaco Camelot 40PAQ, Cummins 400 ISL
'22 Ford Escape PHEV, Roadmaster BP, Sterling towbar
|
|
|
03-02-2018, 08:36 AM
|
#4
|
Senior Member
Monaco Owners Club
Join Date: Aug 2017
Location: Orlando, Florida
Posts: 5,819
|
Also, check to see if the connections to the receptacle are made by "friction fit" where the wire is just pushed into a hole in the back of the receptacle. The receptacle will have screw terminals and the push-in friction retention holes).
This is seen in a lot of production built homes because its faster. But the wire is also looser (than when using the screw terminal) and more prone to overheating at his connection.
If you replace the recipictals take the time to wrap the wire around the screw terminals and don't use the hole in the back.
|
|
|
03-02-2018, 08:44 AM
|
#5
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,785
|
With one heater on 1500 watts and the other one on 600 watts, you would be pulling about 17 amps. If anything else in the RV was pulling any current, you could have easily overloaded the 20 amp circuit. I would use two heaters that you can set on 600 watts each!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
03-02-2018, 08:45 AM
|
#6
|
Senior Member
Join Date: Mar 2017
Location: Oakville, Ontario
Posts: 168
|
Most RV receptacles and switched use a press in connection for the wiring.
This method just cuts into the wire insulation to make contact with the copper.
It is not the greatest method of connection wires, but there is no other option with the way they design these devices to fit into the narrow wall cavities. Wrapping the copper wire around a terminal screw is preferred or a crimp connection, provided that it is installed correctly (correct style crimp for solid or stranded conductor and correct termination tool used)
Other issue that cause hot spots is worn out receptacle contact and cord caps.
As current flows through the connection it heats up and can cause the terminals to loose their spring tension resulting in a poor contact that may start to arc slightly. This arcing can cause a high resistance contact between the cord and the receptacle resulting in increased heat.
Change the device, check wire for damage (wire should still be flexible and not crack when you move it)
Make sure the plug on the heater fits snugly into the wall receptacle, if it does not replace the cord end if you can. On some male cord ends, the blades are made of a piece of metal (not sure exactly what metals) that is folded back on itself. There is a slim joint between the 2 pieces that you can slip a very tiny slot screw driver into and spread the to pieces, this will make the blade of the plug wider and it will make better contact in the receptacle.
Any time you have a cord that is loose in the receptacle it is not a good idea to use it as the connection is not the best.
As mentioned in previous posts, replace the receptacle and check the wiring.
Hope this helps
__________________
Doug and Katherine
2005 Dutchstar 3810 370hp Spartan
pushed around by 2017 Explorer
|
|
|
03-02-2018, 08:52 AM
|
#7
|
Junior Member
Tiffin Owners Club
Join Date: Sep 2016
Posts: 29
|
We smelled something burning as we were going down the road...
If your wires looks like this...you definitely need to find the problem. Ours was that the wire got against the refrig vent pipe and melted the insulation and shorted out the circuit. The circuit was not on a fuse, direct wire to the battery supply. I rewired the circuit, and put a fuse in the circuit. Lucky for me it was only a single line circuit and easy to get to. Replaced everything while boondocking.
|
|
|
03-02-2018, 08:54 AM
|
#8
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,785
|
Quote:
Originally Posted by Speck
We smelled something burning as we were going down the road...
If your wires looks like this...you definitely need to find the problem. Ours was that the wire got against the refrig vent pipe and melted the insulation and shorted out the circuit. The circuit was not on a fuse, direct wire to the battery supply. I rewired the circuit, and put a fuse in the circuit. Lucky for me it was only a single line circuit and easy to get to. Replaced everything while boondocking.
Attachment 194302
Attachment 194303
|
WOW! That's scary!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
03-02-2018, 09:33 AM
|
#9
|
Community Administrator
Tiffin Owners Club
Join Date: Sep 2013
Location: DFW, Texas
Posts: 21,565
|
in addition to what's been mentioned about replacing the receptacle and checking the wiring at that end, check the wiring at the circuit breaker. If the circuit has been overloaded to the point of kicking the breaker, the wiring there could be burned.
__________________
2017 Phaeton 40IH XSH Maroon Coral - Power Glide Chassis with IFS
Previous '15 Tiffin Allegro RED 38QRA and '06 Itasca Sunrise 35A
'16 Jeep JKU Wrangler Sahara or '08 Honda Goldwing
|
|
|
03-02-2018, 12:29 PM
|
#10
|
Senior Member
Join Date: Aug 2015
Posts: 271
|
OP didn't mention whether both heaters were plugged in to one outlet - that would make the situation worse. Could be that when the heaters thermostat cycles them on there is some surge, so if they both happened to cycle on together...
In any case, sounds to me like connections to the outlet were loose - you'd need some resistance to create enough heat to char the outlet cover. This is what's behind the problem with aluminum wiring in homes back in the late '60s - the aluminum 'flows' a bit so the contact between wire and outlet becomes loose, and that resistance can create enough heat to set the wall on fire. In other words you might look to see if the wire is aluminum or copper.
__________________
2017 Coachmen Leprechaun 319MB towing a 2013 CR-V AWD away from San Diego
|
|
|
03-02-2018, 02:30 PM
|
#11
|
Senior Member
Winnebago Owners Club Freightliner Owners Club
Join Date: Oct 2009
Location: E WA or S TX
Posts: 4,058
|
Quote:
Originally Posted by Speck
We smelled something burning as we were going down the road...
If your wires looks like this...you definitely need to find the problem. Ours was that the wire got against the refrig vent pipe and melted the insulation and shorted out the circuit. The circuit was not on a fuse, direct wire to the battery supply. I rewired the circuit, and put a fuse in the circuit. Lucky for me it was only a single line circuit and easy to get to. Replaced everything while boondocking.
Attachment 194302
Attachment 194303
|
Go buy a LOTTO ticket! Luck is with you!
__________________
04 Horizon QD, 12 Ford Flex, Excalibar, Brakemaster, Winter Texan, RVin! since 1974
Norm, Donna & Tinker Kat(RIP) 01 Z3
Life is a Timed Event, you only get One Go Around!
|
|
|
03-02-2018, 04:59 PM
|
#12
|
Senior Member
Join Date: Dec 2010
Posts: 1,084
|
the extension cord you are using may have to small of wire or is to long to carry the load.
size 12 minimum and size 10 would be better
|
|
|
03-03-2018, 06:28 AM
|
#13
|
Senior Member
Join Date: Jan 2017
Posts: 122
|
Quote:
Originally Posted by beaverfever
the extension cord you are using may have to small of wire or is to long to carry the load.
size 12 minimum and size 10 would be better
|
10 GA
|
|
|
03-03-2018, 06:29 AM
|
#14
|
Senior Member
Join Date: Jan 2017
Posts: 122
|
Quote:
Originally Posted by mwkingsd
op didn't mention whether both heaters were plugged in to one outlet - that would make the situation worse. Could be that when the heaters thermostat cycles them on there is some surge, so if they both happened to cycle on together...
In any case, sounds to me like connections to the outlet were loose - you'd need some resistance to create enough heat to char the outlet cover. This is what's behind the problem with aluminum wiring in homes back in the late '60s - the aluminum 'flows' a bit so the contact between wire and outlet becomes loose, and that resistance can create enough heat to set the wall on fire. In other words you might look to see if the wire is aluminum or copper.
|
two outlets thanks
|
|
|
|
|