Dometic Comfort Control Center System
I have a 03 Dutchstar. We were operating the front A/C unit when the unit stopped working and the CCC was going blank and not showing all the functions of Zone 1 or Zone 2 units. We replaced the CCC and now the front AC works fine but nothing on the bedroom unit will work. We have reset the CCC and still nothing. I called a RV repair and they said that Zone 2 needed to be set up. I can't find any directions on how to do this. Right now, the CCC shows every mode available for Zone 2 but nothing will come on - not even the fan. Any help?
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-08-2019, 08:55 AM
|
#2
|
Registered User
Monaco Owners Club
Join Date: Mar 2018
Location: Blairsville, GA & WPB, FL
Posts: 3,993
|
There are dip switches that need to be set...look inside your old unit.
|
|
|
07-08-2019, 09:29 AM
|
#3
|
Junior Member
Join Date: Jan 2016
Posts: 7
|
The only dip switches that I know of are in the air conditioning unit itself. Why would those change if all we did was replace the CCC? There are no dip switches on the thermostat that we could see. Thanks.
|
|
|
07-08-2019, 09:42 AM
|
#4
|
Senior Member
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
|
Quote:
Originally Posted by xbbloader
The only dip switches that I know of are in the air conditioning unit itself. Why would those change if all we did was replace the CCC? There are no dip switches on the thermostat that we could see. Thanks.
|
There is nothing to set in the CCC. The most likely cause is lost communication between rooftop unit 1 and unit 2 or poor communication between unit 1 and CCC (or both) . Depending on your units, you will most likely need to go on the roof, remove the big cover, locate the control board, locate the communication cables (look like telco), unplug and examine for corrosion, replug and try units .... repeat for all units.
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
|
|
|
07-08-2019, 09:46 AM
|
#5
|
Senior Member
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,492
|
In the " Files " drop box ; in the blue bar just to the right of your " User CP " go to the heating and cooling section and download the " Duo Therm CCC " pdf with the troubleshooting guide.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
|
|
|
07-08-2019, 09:57 AM
|
#6
|
Senior Member
Join Date: Nov 2015
Posts: 26,845
|
Yes ----dip switches are in the control box
Need to do a system reset
System Reset
After setting the dip switches in the electronic control, do a system reset.
a. Reconnect the 12 VDC and 120 VAC power supplies.
b. Make sure the CCC 2 thermostat is in the OFF mode.
c. Simultaneously press the MODE and ZONE buttons. The LCD will display “IniT” and all available zones.
d. Release the MODE and ZONE buttons.
e. Press the ON/OFF button to exit system set up.
f. When a dip switch is turned on after initial con-figuration, a system reset will need to be done before the CCC 2 thermostat will recognize the updated selection.
System Checkout
Verify that all features of the installed system work. See CCC 2 thermostat Operating Instructions or User’s Guide. Check fan speeds, cooling mode, heat pump mode, and furnace mode (if connected).
If the features do not work disconnect the 12 VDC and 120 VAC power supplies and verify that all wiring is correct and that the correct dip switches have been turned on.
DIP SWITCHES
1) Ext. Stage.OFF
2) zone 2-----------------------------ON
3) zone 3.....OFF
4) zone 4.....OFF
5) Stage ....OFF
6) Heat Strip--------------------------ON (if equipped)
7) Heat Pump------------------------ON (if equipped)
8) Furnace----------------------------ON
9) Dehumidify....OFF
10) Gen Start....OFF
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
|
|
|
07-09-2019, 06:55 AM
|
#7
|
Senior Member
Monaco Owners Club Vintage RV Owners Club Holiday Rambler Owners Club
Join Date: Jul 2012
Location: Lexington, SC
Posts: 2,820
|
Here's the pdf on the CCC2 troubleshooting/setup guide
__________________
Vera & Ken
1998 Holiday Rambler Imperial, RR8S Chassis
Cummins 6C8.3 mechanical engine, 325HP, 3060 Allison
Towing 2014 Ford Explorer
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|