I cannot plug my M/H into any GFI circuit without blowing the cb! I have managed to isolate 3 circuits that are causing the problem. If I turn off the 3 AC cb's on the panel, then I can plug into a GFI circuit. The 3 circuits are: fridge, a/c & washer/dryer. I have tested the three circuits but no problem found.

Any ideas?

Thanks, Derek

Knightly is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-20-2010, 10:12 AM   #2
Junior Member
Join Date: Nov 2010
Posts: 4

GFI or GFCI breakers are looking at the current on the ungrounded (hot) wire and comparing the current to the grounded wire (neutral). if the comparison is not within tolerance of the GFCI breaker, it will trip.

because of the way GFCI breakers work, the neutral conductor cannot be connected to the equipment ground conductor, or the breaker will see less current on the grounded neutral. the neutral wire could be shorted to ground elsewhere and the same problem would result.

another reason for the GFCI breaker tripping could be moisture in the electrical compartments of the appliances. moisture could introduce a minor short into the circuit and this would cause an imbalance of current on the grounded versus the ungrounded conductors. the short may not be enough to feel to the touch as it may be measured in milliamps. GFCI circuit breakers are manufactured to be very sensitive.

you say you've tested the three circuits; have you tested the appliances also? the GFCI circuit breaker is tripping for a reason. if you can't find the problem yourself, i'd have a qualified electrician have a look.

hope this helps.

hamp is offline   Reply With Quote
Old 11-20-2010, 10:52 AM   #3
Senior Member
don-deb's Avatar
Tiffin Owners Club
Freightliner Owners Club
Join Date: Aug 2010
Location: Mt. Olive Shores North......RV community ( winter )
Posts: 149
You may want to try unpluging all 3 of the appliances......( or disconnecting the load side of the breaker ). Then add each appliance back into the system......and see exactly which appliance is causing the breaker to trip. This will narrow it down to the one troubled appliance.

After you determined which appliance is the problem.......maybe try running a extension cord direct from the GFCI to that appliance.....this will prove .....the appliance is defective or the problem is in the coach wireing.

Hope it helps.
2009 Tiffin Phaeton 40 QTH
2007 Honda CR-V
and our..... Chocolate Lab
don-deb is offline   Reply With Quote
Old 11-21-2010, 01:59 AM   #4
Community Moderator
RV Wizard's Avatar

Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 11,803
If the coach will operate all circuits on a 30 or 50 amp service but trips a 15 or 20 amp GFCI the problem is 90% of the time a bad heating element. There is enough current leakage from the element's filament to frame ground for the GFCI to trip but not enough to trip a standard circuit breaker. Unplug the refrigerator from the receptacle and retry. If the GFCI hold the bad element is in the refrigerator. If not keep checking individual appliances as stated above to find the culprit. Replace the defective element and you should be good to go.
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 11-21-2010, 06:34 AM   #5
Senior Member
paz's Avatar
Join Date: May 2005
Location: Full-timers - Home is where we park it.
Posts: 4,431
In residential wiring, the ground and the neutral are bonded in the electrical box. In an RV, the ground (frame of the RV) and the neutral are supposed to be separate. If someone has done any rewiring in the RV and they have connected the ground and neutral together, that will probably trip a GFCI, especially if the polarity (hot and neutral) are reversed.
2015 DRV Tradition 375KPS
2015 Chevy Duramax 3500HD LTZ Dually
Full-timers...Home is where we park it.
Check out our blog: Living Our Dream
paz is offline   Reply With Quote
Old 11-21-2010, 06:55 AM   #6
Senior Member
roboniko's Avatar
Newmar Owners Club
Solo Rvers Club
Join Date: Mar 2009
Posts: 184
DOn't rule out the GFI either, it could be bad. I have had them overloaded before (due to excessive moisture) and became faulty. Had to change and all was good.
Tim Heinzen
2013 King Aire
'12 Jeep COD MWF
roboniko is offline   Reply With Quote
Old 11-21-2010, 02:06 PM   #7
Senior Member
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Nov 2010
Location: Surrey, B.C.
Posts: 130
Thanks for all the suggestions. I have tested all circuits as mentioned above with help from a technician. That is how I found out which ones were causing the problem. If I turn off the c/b's to the frig, a/c & washer/dryer, then everything else will work fine on the GFI. If any one of these 3 circuits are active, then the GFI blows. It is not a problem when plugged into a regular 15 amp circuit, 30 or 50 amp shore power.
As suggested, I will try to trace the ground and neutral wires of each circuit, to make sure they are separate. I will also try each appliance separately, using an extension cord, to determine if it is the actual appliance or circuit causing a short.

Thanks for all the tips. Derek (now in Charleston, SC)
Knightly is offline   Reply With Quote
Old 11-21-2010, 09:04 PM   #8
Join Date: Jun 2010
Posts: 46
I had a similar issue. Whenever I turned on the rooftop A/C the GFCI would trip. To make along story short, the cause was the heating element in the refrigerator. Once it was isolated, and subsequently replaced, no more GFCI trips.
TT = 2007 Jayco Jay Flight 27bh TV = 2006 F-350 CCLB DRW 6.0
Macrosill is offline   Reply With Quote
Old 11-21-2010, 09:10 PM   #9
Ford Super Duty Owner
Join Date: Jul 2010
Posts: 82
I had the same problem on an Itasca Suncruiser. I thought it was a moisture problem, because the appliances worked fine when plugged into non-GFI circuits, but would always trip the GFI if it was present.

I found that it was loose neutral where power enters the rig at the switch box. Tightened it, and no more problems. Then, I took the cover of the c/b panel, and tightened all the lugs on the buss bar and the breakers. Found alot of loose connections here too. The danger with the loose connections is that they build up very high resistance, and can ultimately cause a fire. I found several that showed signs of over-heating.

Good luck.

INSPECTORBOB is offline   Reply With Quote
Old 11-22-2010, 10:29 AM   #10
Join Date: Jan 2010
Posts: 48
I had the ground and neutral mix up in the box where the gen wires meat house wires 4by4 in. 30 amp. I add a 12 amp wire for rear air, works good.
National Dolphin 35Ft. 1995 slide Ford 460
Banks SYSTEM Best thing I did. 6.5 MPG at 65MPH with toad.
gary peterso is offline   Reply With Quote
Old 11-23-2010, 02:42 PM   #11
Senior Member
Join Date: Apr 2005
Posts: 309
Mine was tripping the GFI. I isolated it to the microwave. With an extension cord, the microwave was fine. It turned out that the outlet the microwave plugged into was full of dead ants. So small I had to use powerful magnifying lenses to see them. We were in really humid weather and they absorbed enough moisture to conduct electricity. Cleaned them out and all has been fine since. Good Luck, HarveyP
94 Holiday Rambler Endeavor LE

HarveyP is offline   Reply With Quote
Old 11-24-2010, 09:56 AM   #12
Join Date: Nov 2010
Posts: 47
Aye, Laddie

If you be Irish it might be Leprechauns dat be haunting you.

If you are running power from a secondary power panel, you may not be wired correctly.

Older homes and outbuildings have three wire circuits where the ground and neutral are combined in one wire. Pre GFI days.

Also, all secondary panels should not be grounded, except back at the main panel.

What I am trying to say, is that you need a separate neutral wire running from the main power box.

Neutral returns unused juice to main box and back out to utility system. If using three wire configuration, the GFI picks up on the unused juice and snaps off................

Now..............the ground and neutral are bonded together in the main power box. It doesn't seem logical, but, apparently it works.

I discovered my outside panel was a three wire set up.

Had to pay out serious "geeters" to add separate # 6 neutral wire.

Three wire will work for 220v only.

If you try to use one leg to tap 110 v you are looking for trouble.

96 Dolphin 36' 454

trpwire is offline   Reply With Quote

Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
30 amp to 50 amp Electrical Upgrade mikwallace Winnebago Industries Owner's Forum 17 11-30-2009 10:17 AM
electrical problems peter1 MH-General Discussions & Problems 8 11-27-2009 06:19 AM
Installation of a New Open Grill Partition in the Electrical Compartment SteveG Winnebago Industries Owner's Forum 0 10-14-2009 06:46 PM
Help with electrical problems prpickett Newmar Owner's Forum 7 09-26-2009 06:31 PM
more electrical problems Buddy and Beverly Alpine Coach Owner's Forum 8 06-10-2007 11:18 AM

» Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities

Copyright 2002-2015 Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:51 AM.

Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, vBulletin Solutions, Inc.