Electrical Question

We are finally getting underground power to my RVport (new word not a garage more like a carport). A licensed electrician is doing the work, BUT he is the first to tell you he know nothing about RVs. He purchased the receptacle through a RV source. After reading some of the threads I made sure it was correct for a motorhome. We are going to use the 30amp service that services our well. The electrician will tie into the 30 amp line prior to the well so the RV will have continuous service as the well is only live when the tank needs filling. (I hope I’ve explained that correctly) We would prefer to run a separate 30 or 50 amp line but due to other structures and constraints it is not possible without tremendous cost.



My question: The RV will be set like it is at many campgrounds for the 30 amp service. There will be very limited use of power in the RV but when we do use it ….If the basement HVAC is on and the well comes on…both being on the same 30 amp service is there a chance of damage to the RV or well or will the breaker kick and that is all that will happen?



The electrician thinks the breaker kicking or a dimming of RV interior lights but I want to be sure. The basement AC is a bigger issue than the heat.


Thanks for your expertise on this...
__________________

__________________
Sandi
Loving My RV
2005 Dolphin 6355 LX WH24
lenjen is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-30-2013, 06:34 PM   #2
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 11,807
What is the start and running power consumption of the pump?
__________________

__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 08-30-2013, 06:35 PM   #3
Member
 
binspector's Avatar
 
Join Date: Jun 2013
Location: Bay St Louis, MS
Posts: 91
Not being an electrician, I would say that the worse thing would be the breaker would trip. I was hooked up to 30 amp at a campground and tried using the micro wave while both A/C units were on and all that happened was the campground breaker tripped. No harm done.
__________________
binspector is offline   Reply With Quote
Old 08-30-2013, 06:39 PM   #4
Senior Member
 
palehorse89's Avatar


 
Newmar Owners Club
Join Date: Oct 2009
Posts: 7,777
If I had to bet your well is setup with a 30 amp. breaker and the amp. draw on the wire is going to be in the mid 20 amp. range, so yes, if using you rv shut down your well so it does not come on.
__________________
2000 Newmar MADP 4060, 350ISC, Spartan MM, IFS 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006Ultra & 1989 Springer
palehorse89 is offline   Reply With Quote
Old 08-30-2013, 06:42 PM   #5
Senior Member
 
Join Date: Nov 2006
Location: Centerville, Iowa
Posts: 241
New Electrician

No disrespect to your electrician, but he should be able to calculate all of these things, if he truly is an electrician. You should never knowingly set up an electrical situation where an overload can occur. Without knowing your situation, and because I am a master electrician, you need to get a second opinion from another electrician, not one of his buddies, but a real electrician. Last thing you want to do is burn down your rv or your home... That sounds like where you are headed, just based on your description..
__________________
Mike Thomas is offline   Reply With Quote
Old 08-30-2013, 06:48 PM   #6
Senior Member
 
lenjen's Avatar
 
Join Date: Mar 2011
Location: Conyers, GA
Posts: 549
Quote:
Originally Posted by vsheetz View Post
What is the start and running power consumption of the pump?
I'll check that out.
__________________
Sandi
Loving My RV
2005 Dolphin 6355 LX WH24
lenjen is offline   Reply With Quote
Old 08-30-2013, 06:55 PM   #7
Senior Member
 
docj's Avatar
Official iRV2 Sponsor
 
Join Date: May 2011
Posts: 3,720
Quote:
Originally Posted by Mike Thomas View Post
No disrespect to your electrician, but he should be able to calculate all of these things, if he truly is an electrician. You should never knowingly set up an electrical situation where an overload can occur. Without knowing your situation, and because I am a master electrician, you need to get a second opinion from another electrician, not one of his buddies, but a real electrician. Last thing you want to do is burn down your rv or your home... That sounds like where you are headed, just based on your description..
X2; my last sticks & bricks had a 240V well pump. Does your so-called electrician know that your RV only uses 120V?
__________________
Joel Weiss--WiFiRanger RV Ambassador
RVParkReviews administrator
2000 40' Beaver Patriot Thunder Princeton CAT C-12
docj is offline   Reply With Quote
Old 08-30-2013, 06:58 PM   #8
Senior Member
 
lenjen's Avatar
 
Join Date: Mar 2011
Location: Conyers, GA
Posts: 549
Quote:
Originally Posted by Mike Thomas View Post
No disrespect to your electrician, but he should be able to calculate all of these things, if he truly is an electrician. You should never knowingly set up an electrical situation where an overload can occur. Without knowing your situation, and because I am a master electrician, you need to get a second opinion from another electrician, not one of his buddies, but a real electrician. Last thing you want to do is burn down your rv or your home... That sounds like where you are headed, just based on your description..
This is a real, Georgia licensed electrician that is has done many new homes and commercial jobs. He has been an electrician for over 30 years. His company is well respected. I can not think if he thought for one second that there was a chance of fire he would consider doing this.
__________________
Sandi
Loving My RV
2005 Dolphin 6355 LX WH24
lenjen is offline   Reply With Quote
Old 08-30-2013, 07:09 PM   #9
Senior Member
 
palehorse89's Avatar


 
Newmar Owners Club
Join Date: Oct 2009
Posts: 7,777
Again, when your well or anyone's is installed (I have a well and the pump is 240 vac) the breaker is installed to operate the pump and nothing else. I find it hard to believe a licensed electrican would tap into the wires on a water well to run a service for a persons RV. I would go another route for power if it were me.
__________________
2000 Newmar MADP 4060, 350ISC, Spartan MM, IFS 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006Ultra & 1989 Springer
palehorse89 is offline   Reply With Quote
Old 08-30-2013, 07:12 PM   #10
Senior Member
 
mhudson's Avatar


 
American Coach Owners Club
Join Date: Jun 2012
Location: Ninety Six SC
Posts: 227
Most well pumps are 220v. If your RV is wired for 30 amp service major problem if he wires the rv outlet for 220v. Will toast most everything electrical in the RV. The rest I'm sure he understands.
__________________
mhudson is offline   Reply With Quote
Old 08-30-2013, 07:34 PM   #11
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,829
First. I always recommend if you are hiring the job done put in a 50.. Why... Well less likely he will mess it up.

Now... IF he uses wire heavy enough (I am very fond of "one size larger" by the way) then if the Basement A/C kicks in and trys to draw like 40 amps on a 30 amp line the breaker will trip. Then the lights will dim (Since they run on 12 volt and will now be seeing 12.5 instead of 13.6) till you reset the breaker.

There will be no damage to the RV

Damage to the RV, by the way, would be to the motors in the air conditioner. and would only happen if the electrician uses wire too small for the length of the run so the voltage drop is excessive.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 08-30-2013, 07:34 PM   #12
Senior Member
 
lenjen's Avatar
 
Join Date: Mar 2011
Location: Conyers, GA
Posts: 549
thank you for your replies, I will go over all of the issues noted with the electrician before we go any further with this.
__________________
Sandi
Loving My RV
2005 Dolphin 6355 LX WH24
lenjen is offline   Reply With Quote
Old 08-30-2013, 07:57 PM   #13
Senior Member
 
Gulf Streamers Club
Join Date: Jan 2009
Location: Charlevoix, Michigan
Posts: 215
Make sure the well Pump is NOT a 240 Volt system. Most every well pump I know of in my area run on 240 volt power. If you hook that up to your RV you will let a lot of the Magic Smoke out of a lot of your equipment. A RV 30 Amp plug is 120 Volts only. Make sure your electrician knows that.
__________________
GSMC(SW) U.S. Navy (RETIRED) 1967-10-03 to 1993-11-01
1995 Gulf Stream Scenic Cruiser, Cummins B5.9, Allison MD3060, Toad: 2005 Focus ZXW SES Wagon
Sundancer268 is offline   Reply With Quote
Old 08-30-2013, 08:04 PM   #14
Senior Member
 
TurtleKent's Avatar
 
Tiffin Owners Club
Winnebago Owners Club
Freightliner Owners Club
Join Date: Feb 2011
Location: The Buckeye State
Posts: 492
Send a message via AIM to TurtleKent
Quote:
Originally Posted by Sundancer268 View Post
Make sure the well Pump is NOT a 240 Volt system. Most every well pump I know of in my area run on 240 volt power. If you hook that up to your RV you will let a lot of the Magic Smoke out of a lot of your equipment. A RV 30 Amp plug is 120 Volts only. Make sure your electrician knows that.
x18
Pump is 240v, 30amp RV outlet is 120v.
__________________

__________________
Kent & Sue & Pecos
2010 Allegro Bus 43QRP
Formerly 2004 Itasca Horizon 40AD
TurtleKent is offline   Reply With Quote
Reply

Tags
electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:50 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.