Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > MOTORHOME FORUMS > Class A Motorhome Discussions
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 04-19-2018, 09:21 PM   #1
Senior Member
 
sCarycary's Avatar
 
Ford Super Duty Owner
Join Date: Sep 2010
Location: Valley Springs, CA.
Posts: 166
Generac Q55G 146VAC output

My genny is putting out 146V. It should be closer 120V. The genny stays running but my outlets shut down for a monute or so and then resets and I get power back for a short while. I suspect the voltage regulator on the genny. What do you think it is?
Cary
__________________
Cary McHugh & Stacey Fairchild
Valley Springs , CA
1999 Rexhall Aerbus 3250BSL
sCarycary is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-20-2018, 08:15 AM   #2
Senior Member
 
sCarycary's Avatar
 
Ford Super Duty Owner
Join Date: Sep 2010
Location: Valley Springs, CA.
Posts: 166
This morning it was putting out 118VAC while I was making coffee. I suspect an electronic component that heats up and is breaking down.
__________________
Cary McHugh & Stacey Fairchild
Valley Springs , CA
1999 Rexhall Aerbus 3250BSL
sCarycary is offline   Reply With Quote
Old 04-20-2018, 08:19 AM   #3
Senior Member
 
Join Date: Oct 2013
Posts: 191
Is the 146v a no load voltage? Some generators run “wild” on voltage until a load is applied.
joshuajim is offline   Reply With Quote
Old 04-20-2018, 08:26 AM   #4
Senior Member
 
Join Date: Jun 2004
Posts: 1,361
The governor needs to be adjusted. It's normal for the voltage to be lower under load (i.e making coffee). If I recall the no load is supposed to be around 130VAC and as mentioned it will be lower under load. The specs are in the service manual. If you can't get it to adjust properly then the governor spring may need to be replaced. Also clean and lube all the linkage points.
__________________
2014 Southwind 32VS
2013 Nissan Xterra PRO-4X
PbdBlue is offline   Reply With Quote
Old 04-20-2018, 11:20 AM   #5
Senior Member
 
sCarycary's Avatar
 
Ford Super Duty Owner
Join Date: Sep 2010
Location: Valley Springs, CA.
Posts: 166
Quote:
Originally Posted by joshuajim View Post
Is the 146v a no load voltage? Some generators run “wild” on voltage until a load is applied.
Yes that was no load. It was cycling off & on with 146v output. This morning, no load was 118v, 5v drop with toaster & microwave running. I'll run it for a longer period of time today and see if it acts up.
__________________
Cary McHugh & Stacey Fairchild
Valley Springs , CA
1999 Rexhall Aerbus 3250BSL
sCarycary is offline   Reply With Quote
Old 04-20-2018, 02:07 PM   #6
Senior Member
 
Charlie 5320's Avatar
 
Join Date: Mar 2017
Posts: 698
Quote:
Originally Posted by sCarycary View Post
Yes that was no load. It was cycling off & on with 146v output. This morning, no load was 118v, 5v drop with toaster & microwave running. I'll run it for a longer period of time today and see if it acts up.
Take it to a Generac dealer to have it serviced. You don't have a way to set the rpm of the generator head. It needs to be set to a certain RPM, then the voltage regulator can be adjusted. DON'T start messing with the governor. If you take the plastic cover off around the switches, the regulator is in there. It has 5 or 6 wires going to it, there is a little blue and white pod that can be adjusted for voltage. Set it to 123 to 128 vac unloaded, then load it up. You don't want it to go below 118 vac loaded. If you can't get this vac take it to a service dealer, you WILL be money ahead. The generac does NOT have a fast warm up like onans do.
__________________
1996 Challenger 313

2003 Dolphin 5320 sold
Charlie 5320 is offline   Reply With Quote
Old 04-20-2018, 03:07 PM   #7
Senior Member
 
Bob Hyatt's Avatar
 
Tiffin Owners Club
Join Date: Apr 2018
Location: Pelham (Birmingham) AL
Posts: 400
Quote:
Originally Posted by PbdBlue View Post
The governor needs to be adjusted. It's normal for the voltage to be lower under load (i.e making coffee). If I recall the no load is supposed to be around 130VAC and as mentioned it will be lower under load. The specs are in the service manual. If you can't get it to adjust properly then the governor spring may need to be replaced. Also clean and lube all the linkage points.
The governor is ONLY about frequency (60 hz). The generator part of the genset produces the voltage as demanded by internal settings. Not quite sure how you would get that high a number even unloaded. I have a 7.0 in my coach, and a 7.5 generator (Westinghouse) at home. Neither has that kind of an issue. Only problem with any of these is that unloaded, the generator spins easier, and that will screw up the frequency a bit, making it higher since it is spinning faster than the existing number of poles on the armature should spin to produce 60hz. That is why cheaper generators are a problem in that voltage fluctuates, frequency fluctuates, and some electronics fail to see any humor in those conditions.

SO, that being said, check the frequency it is producing. Too high, governor is improperly adjusted which will also screw up voltage. Frequency correct means it is not a generator fault. Just always check with a reasonable load, otherwise the generator will tend to overspeed a bit under no-load conditions and give you too much of both. If you spin it at (say) 3600 for a 6 pole alternator, you will get exactly 60hz and exactly the voltage the field coils were wound for (125v for any I have measured).
__________________
Bob Hyatt
2018 Tiffin Allegro 32SA
Bob Hyatt is offline   Reply With Quote
Old 04-20-2018, 07:56 PM   #8
Senior Member
 
Charlie 5320's Avatar
 
Join Date: Mar 2017
Posts: 698
Quote:
Originally Posted by Bob Hyatt View Post
The governor is ONLY about frequency (60 hz). The generator part of the genset produces the voltage as demanded by internal settings. Not quite sure how you would get that high a number even unloaded. I have a 7.0 in my coach, and a 7.5 generator (Westinghouse) at home. Neither has that kind of an issue. Only problem with any of these is that unloaded, the generator spins easier, and that will screw up the frequency a bit, making it higher since it is spinning faster than the existing number of poles on the armature should spin to produce 60hz. That is why cheaper generators are a problem in that voltage fluctuates, frequency fluctuates, and some electronics fail to see any humor in those conditions.

SO, that being said, check the frequency it is producing. Too high, governor is improperly adjusted which will also screw up voltage. Frequency correct means it is not a generator fault. Just always check with a reasonable load, otherwise the generator will tend to overspeed a bit under no-load conditions and give you too much of both. If you spin it at (say) 3600 for a 6 pole alternator, you will get exactly 60hz and exactly the voltage the field coils were wound for (125v for any I have measured).
Best not to give information when you clearly don't have knowledge of said equipment.

The generac in question is a 2 pole generator.

The engine speed should be 2570 to get a rotor speed of 3600 RPM.
Adjustment of the regulators " voltage adjustment" potentlometer must be done only when the unit is running at it's correct governed no-load speed. Speed is correct when the units no-load AC output frequency is about 61-63 hertz. At the stated frequency, AC output voltage should be about 122 to 126 volts.

This is directly from the service manual for this generator.

The easiest way to screw the generator up is start messing with the governor.

Don't do it.
__________________
1996 Challenger 313

2003 Dolphin 5320 sold
Charlie 5320 is offline   Reply With Quote
Old 04-20-2018, 09:10 PM   #9
Senior Member
 
Join Date: Jun 2004
Posts: 1,361
Quote:
Originally Posted by Bob Hyatt View Post
The governor is ONLY about frequency (60 hz). The generator part of the genset produces the voltage as demanded by internal settings. Not quite sure how you would get that high a number even unloaded. I have a 7.0 in my coach, and a 7.5 generator (Westinghouse) at home. Neither has that kind of an issue. Only problem with any of these is that unloaded, the generator spins easier, and that will screw up the frequency a bit, making it higher since it is spinning faster than the existing number of poles on the armature should spin to produce 60hz. That is why cheaper generators are a problem in that voltage fluctuates, frequency fluctuates, and some electronics fail to see any humor in those conditions.

SO, that being said, check the frequency it is producing. Too high, governor is improperly adjusted which will also screw up voltage. Frequency correct means it is not a generator fault. Just always check with a reasonable load, otherwise the generator will tend to overspeed a bit under no-load conditions and give you too much of both. If you spin it at (say) 3600 for a 6 pole alternator, you will get exactly 60hz and exactly the voltage the field coils were wound for (125v for any I have measured).
My mistake. I misread the title. Thought we were talking about an older Onan. On the older Onan’s the voltage is dependent on the governor setting. There is no separate voltage regulator. The frequency varies with the voltage.
__________________
2014 Southwind 32VS
2013 Nissan Xterra PRO-4X
PbdBlue is offline   Reply With Quote
Old 04-23-2018, 10:44 PM   #10
Senior Member
 
sCarycary's Avatar
 
Ford Super Duty Owner
Join Date: Sep 2010
Location: Valley Springs, CA.
Posts: 166
Current plan is to replace the voltage regulator in the generac. I measured the voltage at the main AC breaker at 156V during fault condition. The rpm sounds the same wether the voltage is 118 or 156.
__________________
Cary McHugh & Stacey Fairchild
Valley Springs , CA
1999 Rexhall Aerbus 3250BSL
sCarycary is offline   Reply With Quote
Old 04-24-2018, 09:55 AM   #11
Senior Member
 
Charlie 5320's Avatar
 
Join Date: Mar 2017
Posts: 698
Quote:
Originally Posted by sCarycary View Post
Current plan is to replace the voltage regulator in the generac. I measured the voltage at the main AC breaker at 156V during fault condition. The rpm sounds the same wether the voltage is 118 or 156.
Use a meter to find out the HERTZ, if 60 to 62 use the pod on the regulator to adjust the voltage. You need to down load the service manual for your generator. I found them on line while working on my own generac. Chances are a new regulator will need to be adjusted also. Every one I've replaced needed to be adjusted. I have a generac NP66 set up for an emergency generator for my house.
__________________
1996 Challenger 313

2003 Dolphin 5320 sold
Charlie 5320 is offline   Reply With Quote
Old 05-06-2018, 06:43 PM   #12
Junior Member
 
Join Date: Jul 2012
Posts: 2
Generac np-66g voltage problem

I've started having problems with my generator transferring. After starting it will shortly transfer but the voltage is very high. It drops to zero after a moment, but the engine continues to run but zero voltage. The only thing I could guess it might be is a voltage regulator failure. Has there been a problem with voltage regulators failing. My generator is 20+ years old. I don't run it much other than to exercise it every 2 or 3 months. Lately I have been having some problem with the transfer switch not operating every time. That's what I was going to address when the voltage problem started. As I started to check in the generator panel I found some other problems that I need to fix before I continue to find the voltage problem. The shock vibration mounts on the control panel have failed. Found some and ordered. Any thoughts where to start would be appreciated.
Frank
ssiron is offline   Reply With Quote
Old 05-06-2018, 11:04 PM   #13
Senior Member
 
sCarycary's Avatar
 
Ford Super Duty Owner
Join Date: Sep 2010
Location: Valley Springs, CA.
Posts: 166
Quote:
Originally Posted by ssiron View Post
I've started having problems with my generator transferring. After starting it will shortly transfer but the voltage is very high. It drops to zero after a moment, but the engine continues to run but zero voltage. The only thing I could guess it might be is a voltage regulator failure. Has there been a problem with voltage regulators failing. My generator is 20+ years old. I don't run it much other than to exercise it every 2 or 3 months. Lately I have been having some problem with the transfer switch not operating every time. That's what I was going to address when the voltage problem started. As I started to check in the generator panel I found some other problems that I need to fix before I continue to find the voltage problem. The shock vibration mounts on the control panel have failed. Found some and ordered. Any thoughts where to start would be appreciated.
Frank
I replaced the voltage regulator on the generator. The voltage going into my convertor/inverter was high(140-150VAC) intermitenrly. The motor speed was steady. The voltage regulator was the most likely bad part. About $100 to replace.
__________________
Cary McHugh & Stacey Fairchild
Valley Springs , CA
1999 Rexhall Aerbus 3250BSL
sCarycary is offline   Reply With Quote
Reply

Tags
generac



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generac Q55G Low Voltage Sunvoyagee RV Systems & Appliances 5 07-30-2017 05:45 PM
Generac Q55G Starter Motor replacement Kevin J RV Systems & Appliances 4 10-26-2016 06:58 AM
Generac Q55G manuel radmn1 Class A Motorhome Discussions 1 08-01-2015 12:47 PM
Generac Q55g jlyon69 RV Systems & Appliances 3 11-27-2011 11:42 AM
Generac Q55G Generator fuel pump mx08453 RV Systems & Appliances 0 08-04-2011 07:32 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:10 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.