Old 12-28-2012, 09:08 PM   #1
Member
 
Overland Owners Club
Join Date: Nov 2012
Location: Menifee, CA
Posts: 74
Genset Starting with Load

I am relatively new Class A owner, and have a '98 Overland 40, with Onan 7.5. I also have a houseboat, and the electrical system is nearly identical. The houseboat has a Westerbeke 15k genset. Westerbeke says it will damage the genset if it is started or shutdown with the load on. I have searched both the Overland owner's manual and the Onan manual, and neither mentions this possibility. It seems logical to me that if they expect you to start the generator with the load off, there would be a convenient way to turn load on and off at the drivers console. There isn't, so ........ Anyone have any inputs? Thanks, Grzly03, Dick.
__________________

__________________
Grzly03 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-28-2012, 09:22 PM   #2
Senior Member
 
Twomed's Avatar
 
Monaco Owners Club
Join Date: Oct 2009
Location: On the road
Posts: 1,354
Start and shut down with no load. Run for several minutes without load on start up and shutdown. You gen will love you and you won't be blowing expensive control boards.
__________________

__________________
Happy Trails,
06 Dynasty Countess III ISL//3060
07 Hummer H3// Suzi 650 Thumper
Twomed is offline   Reply With Quote
Old 12-28-2012, 09:29 PM   #3
Senior Member
 
Damon Owners Club
Join Date: Jul 2010
Location: Annapolis,MD
Posts: 1,195
Amen !
__________________
macandphyl is offline   Reply With Quote
Old 12-28-2012, 09:30 PM   #4
Moderator Emeritus
 
RickO's Avatar


 
Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 10,530
Welcome to the forum.

General practice is to try to have minimal loads on when switching from one power source to another to avoid slamming the relays involved in the change over. I believe it's the transfer switch but got that confused once and got chastised so I'll leave the specifics to the experts.

No, there's no way in most rigs to shut down the load (Air Conditioner for example) from the cockpit.

Good luck.

Rick
__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
RickO is offline   Reply With Quote
Old 12-29-2012, 03:24 AM   #5
Senior Member
 
Join Date: Dec 2012
Posts: 105
I have a 7.5 Onan QD. In the manual it tells the owner to let the genset stablize before putting a load on the genset.

One of the first things I have noticed about the MH industry is that it seems this taken care of when I go outside and un-plug the power cord from the genset recepticle. So, here is what they expect; Either sit in the drivers seat, open the front access panel, or stand in the kitchen; start the genset; go outside and shut off the main breaker; plug in the power cord; turn on the main breaker. To shut down; go outside; shut off the main breaker; unplug the cord from the genset, go back inside and shut down the genset.

So, what do I do? Leave the cord pluged into the genset and start the genset with load applied. What I do is full of potential problems the first of which was the display of the microwave did not like this. $75.00 just for the part.

Here is what I did, next to the genset power connection I installed a small electricial box, In that box there is a contactor (large relay) also a timed delay timer. The contactor breaks the two 120vac lines to the genset recepticle that the MH cord is pluged into. The delay relay is controling the coil of the contactor. current draw is less than a night light. The control voltage for the contactor is sourced from the genset. Granted when I start the genset the electronic delay timer is on the genset output it draws about the same as a LED. The delay timer is a "delay on make" so as the genset starts the timer starts its count down, 90 seconds (1 and 1/2 minutes) later it turns on the contactor.

The result is that the genset will start with only the delay timer connected and 1 1/2 minutes later it connects the coach to the genset. As soon as the voltage drops below the accepticle output it removes the coach from the genset.

Now I just start up the genset at any start station. The bother is that I have to wait for a minute and a half to reheat the cup of coffee.

To protect the genset and the coach it now takes me twice as long to heat up a cup of coffee.
__________________
glenn allen is offline   Reply With Quote
Old 12-29-2012, 06:49 AM   #6
Senior Member
 
hogdriver's Avatar


 
Entegra Owners Club
Join Date: Jan 2012
Location: Wintering-Orange Beach AL
Posts: 2,915
Transfering electrical loads

I recently traded a 02 Monaco that had a 10.0 kw Onan in it. The manual discussed running the genset at no load for a while before shutdown, but not much about Transfering the load. This past summer I pulled into a campground in Kansas when it was 100deg with both air conditioners running and plugged in to the post....no power. I checked everything and told the manager it was the pedestal. Three sites later I discovered it was not the shore power. I was able to park but had to go to a remote area and run the generator all night. It had run for 48 hrs continuously across the scorching Midwest. Turns out I blew the power transfer switch. Those relays do not like Transfering with 30-50 amps on them. My new RV says turn everything off when Transfering. I guess that makes more sense than dropping $500 to replace a transfer switch in the heat of summer!
__________________
Dave & Debbie
2014 Anthem 44B
2012 Jeep Rubicon toad
2016 Ford Edge toad
hogdriver is offline   Reply With Quote
Old 12-29-2012, 08:24 AM   #7
Senior Member
 
rvfunhunter's Avatar
 
Join Date: May 2012
Posts: 114
Wink How I do it!

I never start or stop the generator under load. Mine seems to have a delay at startup before the power is applied to the rv so this has not been a problem. Whenever I shut down I turn things off to reduce the load as much as possible, wait about 1 minute and then shut the gen set off.
The main power relay on mine did blow the second year I owned the rv. Mine has an electrical circuit that delays the generator power input at startup as I mentioned. This type of relay normally has an over lock to ensure they don't try to activate if a second power source is detected. When I first purchased the rv I had no idea of how the shore/generator power was set up. At one time I tried to transfer from one power source to the other without stopping one first and then starting the other. The double input burned up the switch. When I finally had a good look at the set up I found that only one side of the power relay had an overlock!
I reinstalled a new switch in the same way the manufacturer had done it, but now I ensure to always disconnect one power source before connecting the other and no load during this operation.
Two minutes without power can't be that bad!
__________________
1992 GullfStream TourMaster
Painted and looking good!!
rvfunhunter is offline   Reply With Quote
Old 12-29-2012, 08:29 AM   #8
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 17,150
Blog Entries: 21
Not only is starting or stopping the generator with a load bad for the generator, it is bad on the driven equipment. During starting and stopping, the frequency and voltage take wide swings which ca kill certain users. It is really easy to shut off the loads, A/C, microwave, TV, etc and let the set run with minimal load for a couple of minutes.

Think how you would feel if you were tucked into a nice cozy warm bed and some one cane up, booted you out of bed and dropped a 100# pack on you back and were told to take of running up hill...RIGHT NOW.

Ken

ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is offline   Reply With Quote
Old 12-29-2012, 08:47 AM   #9
paz
Senior Member
 
paz's Avatar
 
Join Date: May 2005
Location: Full-timers - Home is where we park it.
Posts: 4,716
Quote:
Originally Posted by Grzly03 View Post
I am relatively new Class A owner, and have a '98 Overland 40, with Onan 7.5. I also have a houseboat, and the electrical system is nearly identical. The houseboat has a Westerbeke 15k genset. Westerbeke says it will damage the genset if it is started or shutdown with the load on. I have searched both the Overland owner's manual and the Onan manual, and neither mentions this possibility. It seems logical to me that if they expect you to start the generator with the load off, there would be a convenient way to turn load on and off at the drivers console. There isn't, so ........ Anyone have any inputs? Thanks, Grzly03, Dick.
I don't know about damaging the genset, but starting and stopping the generator under a high electrical load will certainly damage the transfer switch. High load will cause the contacts to arc and burn. Sometimes the contacts will get hot enough to fuse. Burned contacts also have high resistance which can cause overheating and possibly start a fire.
__________________
2015 DRV Tradition 375KPS
2015 Chevy Duramax 3500HD LTZ Dually
Full-timers...Home is where we park it.
Check out our blog: Living Our Dream
paz is offline   Reply With Quote
Old 12-29-2012, 10:19 AM   #10
Member
 
Overland Owners Club
Join Date: Nov 2012
Location: Menifee, CA
Posts: 74
Genset Starting with Load

Thanks for all the inputs, confirming the principle. In the houseboat, all the controls, breakers, genset starting/stopping functions are on the electrical panel at the helm. At some time in the future a mod to the MH might be in order. Grzly03, Dick.
__________________
Grzly03 is offline   Reply With Quote
Old 12-29-2012, 10:43 AM   #11
Member
 
Teachrz's Avatar
 
National RV Owners Club
Join Date: Jun 2010
Location: Caledonia, MS
Posts: 97
Wouldn't an EMS delay the load while the genny spun up?
__________________
Tim Wilcox
Caledonia, MS
1999 National Tropi-Cal V10 - 2008 Volvo C70 toad
Teachrz is offline   Reply With Quote
Old 12-29-2012, 11:03 AM   #12
YC1
Senior Member
 
YC1's Avatar


 
Holiday Rambler Owners Club
Join Date: Jun 2011
Posts: 5,579
Quote:
Originally Posted by Teachrz View Post
Wouldn't an EMS delay the load while the genny spun up?
Mine does on startup but can still put a very heavy load on quickly if I left the AC's in the run position.

I agree with all about letting it warm up a couple of minutes before adding loads and especially cooling down for just a couple of minutes at idle. At idle they draw lots of air and cool quickly.

Here are a couple of paragraphs out of my manual.
Attached Files
File Type: pdf Pre start.pdf (133.1 KB, 33 views)
File Type: pdf Stopping.pdf (42.5 KB, 27 views)
__________________
Myron & Deborah
08 HR Endeavor 40 SKQ
2012 Ford Edge Limited FWD 3.5L
Aluminator tow bar, Demco base plate
YC1 is offline   Reply With Quote
Old 12-29-2012, 11:13 PM   #13
Senior Member
 
Monaco Owners Club
Join Date: Jan 2012
Location: Durant, Ok
Posts: 339
What happens with the "auto-start" gennies?
__________________
2002 38' Diplomat
Keith & Shirley
Durant, OK
ruffian is offline   Reply With Quote
Old 12-30-2012, 02:59 AM   #14
Senior Member
 
Join Date: Dec 2012
Posts: 105
Most likely start under load.

Transfer relays generally are rated for the connected load. None of them are likely to be rated to transfer connected load. The difference?

It all has to do with the mass of the power contacts of the relays. If they are closed they are in the normal rating position. They must carry the rated load without overheating and burning out.

If you try to transfer the rated load then arcing takes place (arc welding) This arcing under load will cause the surface of the contacts to burn and in time the entire contact area can burn.

My genset is rated at 30 amps per leg. When I picked a contactor to delay loading the genset on start up I picked one rated at 100 amps per leg. I live in the MH during the summer without grid power. This contactor has been transfering load for two summers now and shows no sign of overheating. But in time it will need replacement. If it fails to soon I will pick the next replacement with a larger rating. Even so, in time it will fail and require a replacement set of contacts or a new contactor.

About the only device that the average owner can get to transfer a load is a breaker. That is why your 50 amp service in a MH has a main breaker rated at 50 amps. Even so if you turn it on and off enough you will visit the hardware store for a new one. Repacement is the nature of transfering a load.
__________________

__________________
glenn allen is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:20 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.