Heat pump switches from electric to LP?

Cold night in FL, front heat pump on electric runs for 5-10 minutes then switches on it's own to LP ? Rear HP works fine on electric? Anybody had this happen, any help would be greatly appreciated. Thanks in advance!!!
Coleman 15K units
__________________
Tom & Liz
South Carolina
2009 Allegro Red 36 QSA
Topcat95 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-11-2017, 12:37 PM   #2
Senior Member
 
gljurczyk's Avatar
 
Join Date: Mar 2016
Posts: 420
Quote:
Originally Posted by Topcat95 View Post
Cold night in FL, front heat pump on electric runs for 5-10 minutes then switches on it's own to LP ? Rear HP works fine on electric? Anybody had this happen, any help would be greatly appreciated. Thanks in advance!!!
Coleman 15K units
It very well could be that your front unit either went into the defrost cycle, or it is set to switch auto to propane when the temp outside drops to a set point such as 40 degrees. Is your front stat the master or a slave? I don't know how they have it wired, but those are conditions that can cause it. Need a little bit of more info, what is the stat modle# and heat pump model #. Then I can tell you the sequence. If your unit is doing what I said your in very good shape....Merry Xmas and safe and warm travels[emoji319]🤙
gljurczyk is offline   Reply With Quote
Old 12-11-2017, 12:51 PM   #3
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Most heat pumps quit producing heat between 40° and 35°, then switch over to aux heat, in this case probably the furnace.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 12-11-2017, 01:13 PM   #4
Senior Member
 
timekeeper's Avatar
 
Join Date: Mar 2014
Posts: 289
Quote:
Originally Posted by Topcat95 View Post
Cold night in FL, front heat pump on electric runs for 5-10 minutes then switches on it's own to LP ? Rear HP works fine on electric? Anybody had this happen, any help would be greatly appreciated. Thanks in advance!!!
Coleman 15K units
We have had this happen occasionally to our heat pumps, almost always when it was marginal as to weather they could actually produce any heat. They would flip over into propane and not untill temperature outside was a little warmer did they return to "normal".
__________________
New Aire 2022 3543 picked up @ North Trail 10/22
New Aire 3343 Picked up @ Nappanee 4/18 (traded)
2006 Fleetwood Bounder 34 Pusher (traded) 9/17
timekeeper is offline   Reply With Quote
Old 12-11-2017, 01:58 PM   #5
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,704
On mine the auxiliary heat (LP furnace) will come on any time the set temperature is 5 or more degrees above the actual room temperature (as seen by the thermostat). The assumption is that doesn't happen unless the heat pump is not providing adequate heat, but it also handy for faster warm-ups
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 12-11-2017, 02:11 PM   #6
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
If the heat pump cannot meet the temperature rise demand called by the thermostat the propane furnace (or Oasis/Aquahot) will be added. Normal operation.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 12-11-2017, 02:20 PM   #7
Senior Member
 
Join Date: Aug 2012
Posts: 1,325
Quote:
Originally Posted by vsheetz View Post
If the heat pump cannot meet the temperature rise demand called by the thermostat the propane furnace (or Oasis/Aquahot) will be added. Normal operation.
Except the OP has two heat pumps, and one is switching over to propane while the other continues working fine on electric. The answer will have to address why one is acting one way and the other is acting another way.
oatmeal is offline   Reply With Quote
Old 12-11-2017, 02:31 PM   #8
Senior Member
 
paddler1954's Avatar
 
Fleetwood Owners Club
Freightliner Owners Club
Join Date: Mar 2017
Location: Georgia
Posts: 477
Quote:
Originally Posted by oatmeal View Post
Except the OP has two heat pumps, and one is switching over to propane while the other continues working fine on electric. The answer will have to address why one is acting one way and the other is acting another way.
One heat pump is still producing enough heat to satisfy the thermostat. The other heat pump is not as efficient and has allowed the inside temperature to drop 4-5 degrees below the thermostat set point, thus the propane furnace fired up.

This happens on ours also, part of the issue is the big single pane windshield sucks the heat out of the front of the coach. Putting an insulated solar shield on the inside of the windshield will help reduce the heat loss.
__________________
Steve & Margo
Bonaire, Georgia
2018 Fleetwood Discovery 40D LXE "Alice"
paddler1954 is offline   Reply With Quote
Old 12-11-2017, 03:29 PM   #9
Senior Member
 
Tom-NC's Avatar
 
Winnebago Owners Club
Ford Super Duty Owner
Carolina Campers
Join Date: Dec 2002
Location: Murphy, NC, USA
Posts: 1,117
Hi,

Usually Zone 1 is connected to propane furnace when not enough heat outside. Zone 2 is not defaulted to propane furnace. It may run as a fan but does compressor kick in?
Another point is with heat pump you should also move the thermostat only 2 degrees at a time and if you move more than propane furnace will kick in.
One last solution, when it is cold outside cuddle with your partner under an afghan.

__________________
2014 Winnebago Adventurer 35P,Ford F-53, V-10
2011 Ford Escape,2000 Roadmaster Tow Dolly
"Have a Great Day, Enjoy RVing."
Tom-NC is offline   Reply With Quote
Old 12-11-2017, 03:57 PM   #10
Junior Member
 
Join Date: Jun 2015
Posts: 24
Thank you all for the help! Will try it tonight as far as temp drop is concerned. Seems it may be doing just fine. Thanks Again!!
__________________
Tom & Liz
South Carolina
2009 Allegro Red 36 QSA
Topcat95 is offline   Reply With Quote
Old 12-11-2017, 04:38 PM   #11
Senior Member
Commercial Member
 
Join Date: Aug 2012
Posts: 726
Heat pump switches from electric to LP?

Quote:
Originally Posted by Topcat95 View Post
Thank you all for the help! Will try it tonight as far as temp drop is concerned. Seems it may be doing just fine. Thanks Again!!


Since you said Coleman A/C units, you probably have this thermostatClick image for larger version

Name:	IMG_0690.JPG
Views:	268
Size:	105.9 KB
ID:	185440

Notice the word Diff indicating the set point is too many degrees beyond the actual room temperature. In which case the gas heat will come on.
__________________
Traveling RV Doctor
https://www.facebook.com/Traveling-R...5780632151951/
shiggs68 is offline   Reply With Quote
Old 12-12-2017, 04:13 AM   #12
Junior Member
 
Join Date: Mar 2017
Posts: 1
Mine kept doing the same thing, and after having it checked out, it was to have a frozen reversing valve. Since the roof units are NOT servicable, the whole heat pump/ac had to be replaced. Big Bucks!
happyretired is offline   Reply With Quote
Old 12-12-2017, 05:02 AM   #13
Junior Member
 
Join Date: Oct 2017
Posts: 11
That’s what it’s designed to do. I had that happen and read my manual. It’s normal.
Randeye52 is offline   Reply With Quote
Old 12-12-2017, 05:06 AM   #14
Senior Member
 
gatorcq's Avatar
 
Freightliner Owners Club
Join Date: Apr 2004
Location: Show Low Az
Posts: 1,325
t-stat, can only be raised every 4 degrees from room temperature
__________________
Dale&Susan, 08 Alfa Gold, DaGirlsRv Blog
2015 F-150XLT_2000W Solar_800 AmpHr Lithium
Magnum_MSH 3012 & PT100
gatorcq is offline   Reply With Quote
Reply

Tags
electric, heat, heat pump, switch



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Water Pump Switches Downsizer RV Systems & Appliances 3 01-19-2017 01:38 PM
Rear air switches to Heat Pump midasman Class A Motorhome Discussions 1 08-17-2011 08:53 PM
To heat pump or not heat pump Bruce and Jenna Excel Owner's Forum 17 04-15-2009 10:20 PM
Heat Pump - No Electric Heat Drifterpilot MH-General Discussions & Problems 3 04-11-2009 07:13 PM
Electric Water Heat Switches FenceMan Winnebago Industries Owner's Forum 5 11-03-2006 04:17 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:25 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.