Quote:
Originally Posted by Vicr View Post
The iron is an inductive load and will draw maximum amps as soon as it is plugged in or turned on. This will cause a drop in voltage at the converter which will cause it to shut down temporarily until the voltage rises to sufficient operating voltage to supply 12v. It's basic OHMs law. It would be prudent though to make sure all electrical connection on the shore power side and in the converter.
I think you might want to re think that. An Iron is a big low value resistor. All it does is make heat. True, the element is a coil of nichrome or similar but the induction is low. Unless it shares the circuit with the converter the rest of the system should be stiff enough to take the iron load. That would have me checking the transfer switch and main panel connections for a loose screw. That is a common problem as the heavy wiring in a screw compression fitting tends to loosen over time. There have been numerous examples posted here of wires eventually failing with a long streak of cooked insulation from the heat generated at the connection.
nothermark is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-19-2017, 10:18 AM   #16
Senior Member
 
Vicr's Avatar
 
Join Date: Dec 2016
Location: Fortuna Foothills, AZ
Posts: 189
Send a message via ICQ to Vicr Send a message via AIM to Vicr
Yes, I meant to say RESISTIVE LOAD.
Vicr is offline   Reply With Quote
Old 10-20-2017, 06:59 AM   #17
Senior Member
 
edge68474's Avatar
 
Join Date: Oct 2017
Posts: 1,937
AHAA. Now I know the go to guy in electrical, IBEW, who lives not too far from me. Hello neighbor. I'm retired equipment operator, 302. I live in Onalaska, Land of the Free, Home of the Brave. Hope we can keep it that way. As you can see I'm new to the boards and learning.
Speaking of irons, we don't use it much around this home, but, when it kicks in the lights dim in the house. Juice robbing little bugger eh.
Have a Good Day.
__________________
Larry & Sheree & KD the CAT
2009 Holiday Rambler Admiral 30SFS Lewis County, Wa.
USN 1964-68, USS LEXINGTON CVS-16
edge68474 is offline   Reply With Quote
Old 10-20-2017, 07:05 AM   #18
Senior Member
 
Join Date: Jun 2017
Posts: 2,807
Quote:
Originally Posted by nothermark View Post
I think you might want to re think that. An Iron is a big low value resistor. All it does is make heat. True, the element is a coil of nichrome or similar but the induction is low. Unless it shares the circuit with the converter the rest of the system should be stiff enough to take the iron load. That would have me checking the transfer switch and main panel connections for a loose screw. That is a common problem as the heavy wiring in a screw compression fitting tends to loosen over time. There have been numerous examples posted here of wires eventually failing with a long streak of cooked insulation from the heat generated at the connection.
Although he said "Inductive" when he meant resistive his reasoning was still correct. The resistance of the heating element is low when cool and increases with temperature so there is maximum current when it is first turned on.
aether_one is offline   Reply With Quote
Old 10-21-2017, 02:53 AM   #19
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
More or less agreed on current, the point is that he should not be taking down more than the branch circuit if that. It's unlikely that would be shared with his converter. That is why I would be looking for loose connections. I squared R does not take a lot of R to make a significant drop and heat when talking irons or other heavy current draws.
nothermark is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ironing board AudreyMS Class A Motorhome Discussions 8 03-07-2017 05:08 PM
Ironing Board Solution Wil Rathke Alpine Coach Owner's Forum 3 06-30-2016 05:57 AM
Country Coach or American Coach or Alpine Coach Troys66 Class A Motorhome Discussions 14 01-04-2015 06:38 PM
Ironing board plans Indian Creek Winnebago Industries Owner's Forum 6 11-25-2009 08:21 AM
New Coach Batteries Not Powering Coach challengerros MH-General Discussions & Problems 14 02-23-2008 07:02 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:05 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.