Old 11-02-2015, 11:56 AM   #1
Member
 
dmcquinn's Avatar
 
Tiffin Owners Club
Join Date: Jul 2012
Location: Pensacola, Florida
Posts: 62
Is generator always req'd for Wolf Induction 220v

Our order for an all-electric Tiffin Phaeton 40 QBH coach is almost ready to be assembled.

Due to the poor reviews of the standard Summit Induction Cooktop, we have ordered it to be replaced with a 220v Wolf Induction cooktop.

Now someone has told us that, due to the fact that it is 220v, we will have to run the generator even if we are hooked to shore power any time we wish to cook.

Does anyone know if that is the case? If so we need to change our order very quickly.

Thanks for any information that you can give us!
__________________

__________________
dmcquinn is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-02-2015, 12:05 PM   #2
Senior Member
 
Dennis_K's Avatar
 
Monaco Owners Club
Join Date: Jun 2007
Location: Lake Havasu City, AZ
Posts: 1,085
If you are connected to a correctly wired 50amp service (240v across L1 and L2) and the cooktop is wired correctly it should work fine.
__________________

__________________
2012 Monaco Knight 36 PFT
2014 Jeep Grand Cherokee Overland
2005 Jeep Rubicon Unlimited on 2007 16' Car Hauler trailer
Dennis_K is offline   Reply With Quote
Old 11-02-2015, 12:17 PM   #3
Member
 
dmcquinn's Avatar
 
Tiffin Owners Club
Join Date: Jul 2012
Location: Pensacola, Florida
Posts: 62
Thank you so much for the quick reply!
This is our first MH so that is the reason for the basic questions.
Do the hookups at the campground always supply 50 Amp?
If it is 50 amp service, will it always support the 220v cooktop?
If it is not a 50 amp service, will it be possible to still use the Wolf Induction cooktop?
__________________
dmcquinn is offline   Reply With Quote
Old 11-02-2015, 12:33 PM   #4
Senior Member
 
Algonquin's Avatar
 
Join Date: Apr 2015
Posts: 209
You will not be able to use the cooktop without a 50 amp supply. The problem is not so much the amperage, but 30 amp service is only 110 volts, without the capability of supplying 110 or 220 volts like 50 amp service.
__________________
2011 Itasca Meridian 34Y
2014 Honda CR-V
Algonquin is offline   Reply With Quote
Old 11-02-2015, 12:52 PM   #5
Junior Member
 
Join Date: Aug 2015
Posts: 12
NO NOT ALL CAMPGROUNDS HAVE A 50 AMP SUPPLY. MOST PRIVATE PARKS WILL BUT STATE , NATIONAL AND LOCAL PARKS MAY NOT. GOOD LUCK WITH THE NEW RIG.
__________________
vstanz is offline   Reply With Quote
Old 11-02-2015, 04:23 PM   #6
Senior Member
 
Winepress's Avatar
 
Join Date: Jul 2012
Posts: 570
Make sure your generator is also 220v.
__________________
2018 Dutch Star 4369
Try to live up to your dogs opinion of you.
Winepress is offline   Reply With Quote
Old 11-02-2015, 04:29 PM   #7
Senior Member
 
Mr_D's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 28,382
Quote:
Originally Posted by Winepress View Post
Make sure your generator is also 220v.
You will need at least a 12,000W generator to supply the correct amount of amps.
Our dryer is a 220 volt only, which I like as it works faster but have to have a 50 amp RV service or run our 12.5 KW gen set.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is offline   Reply With Quote
Old 11-02-2015, 07:58 PM   #8
Member
 
dmcquinn's Avatar
 
Tiffin Owners Club
Join Date: Jul 2012
Location: Pensacola, Florida
Posts: 62
oh oh that really worries me. The Tiffin Phaeton 40' QBH only has a 10 kw that comes with it...
Will we even be able to use the Wolf 220 Induction cooktop with this smaller generator.
__________________
dmcquinn is offline   Reply With Quote
Old 11-02-2015, 08:05 PM   #9
Senior Member
 
bluepill's Avatar
 
Join Date: Jan 2011
Location: Pensacola, FL
Posts: 2,246
Ask the factory if a "Load Shedding" device is part of your electrical equipment. This allows more flexibility is appliance use. If not, you may have to watch your usage a bit - i.e. not run all the high wattage appliances at the same time. Not a big deal, as many of us have gotten used to doing it.

You may find that carrying a 120 volt portable counter top induction cooktop will be a good back-up for when only 120 volt hook-ups are available.
__________________
2008 Itasca Meridian 37H & 2015 Flagstaff T12RBST
2011 & 2012 Len & Pat's "One lap of America"
27K miles & 41 states in 13 months - Woo Woo
Yellowstone Lake 6-1-2012
bluepill is offline   Reply With Quote
Old 11-02-2015, 08:10 PM   #10
Senior Member
 
Oldrtrcr's Avatar
 
Tiffin Owners Club
Join Date: Jan 2008
Location: Warren, PA
Posts: 303
I don't have a problem running my 220 volt induction cooktop with a 10K generator. Do not believe any manufacturer would install inadequate generator for the equipment on board.
__________________
Bill Mahan
2012 Allegro Bus 43 QGP
Oldrtrcr is offline   Reply With Quote
Old 11-02-2015, 08:13 PM   #11
Senior Member
 
Clayobx's Avatar


 
Fleetwood Owners Club
Join Date: Dec 2011
Location: Willow Lakes RV & Golf Resort, FL
Posts: 3,116
According to Mr. D, no. I really don't know of any production coach other than top of the line than come with 12.5 KW generators? Maybe Tiffin will upgrade but it will be very expensive. I would just upgrade to another high line reviewed 110 volt induction top other than summit. Lot less hassle. JMO.
__________________
Clay & Pebble.. Miss Butter our sweet Goldie (Jan. 2005-Jan. 2015) Sissy our Border Collie
2012 Providence 42 M. Spartan Chassis, 450 ISL
Ford Edge toad, RM All Terrane, TST TPMS, SMI Air Force One, RVM95....
Clayobx is offline   Reply With Quote
Old 11-02-2015, 08:38 PM   #12
"Formerly Diplomat Don"
 
Dutch Star Don's Avatar
 
Newmar Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 9,278
Unless I'm missing something here, it really doesn't matter what generator he has or 50 amp power. The Tiffin isn't going to come with a wired connection for a 220 cooktop. Even if it did, custom wiring would have to be installed from the generator to the cooktop. Depending on the amps required for the cooktop, it would require a 30 amp, 40 amp or 50 amp dedicated circuit just for the cooktop. That would pretty much use up the campground 50 amp circuit, just for the cooktop.

Some of the high end coaches using 220 volt require 100 amp campsites.
__________________
Don & Mary
2014 Newmar Dutch Star - All Electric - 450 ISL
2016 GMC Canyon 4WD Crew Cab
Dutch Star Don is offline   Reply With Quote
Old 11-02-2015, 08:39 PM   #13
Senior Member
 
Melmoses's Avatar
 
Tiffin Owners Club
Join Date: Aug 2010
Location: Montgomery, AL
Posts: 1,196
You should have no problem using the Wolf on 50 amp service. Just be sure not to use a lot of heavy draw appliances at one time. The 10K genset handles it just fine. Just be aware not to run a bunch of high amp things at the same time. The coach sheds loads to keep things right so if you have the Wolf going and 2 ac's kick in while on genset the coach will shut down one ac. No worries. Great cook top!
__________________
Mel (Melanie) and Harry
2009 Tiffin Phaeton 40QTH
2014 Jeep Wrangler Sport
Melmoses is offline   Reply With Quote
Old 11-02-2015, 08:57 PM   #14
Senior Member
 
Timon's Avatar
 
Join Date: Jul 2014
Location: Tustin, CA
Posts: 980
Quote:
Originally Posted by dmcquinn View Post
oh oh that really worries me. The Tiffin Phaeton 40' QBH only has a 10 kw that comes with it...
Will we even be able to use the Wolf 220 Induction cooktop with this smaller generator.
Quote:
Originally Posted by Oldrtrcr View Post
I don't have a problem running my 220 volt induction cooktop with a 10K generator. Do not believe any manufacturer would install inadequate generator for the equipment on board.
Both the 10K & 12.5K gens come in 120/240V. In addition you can get the 5.5K and 7.5K gens in 120/240V but only in the commercial line. They are the same size and sound levels as the RV versions but the warranty is only one year instead of tow.
__________________

__________________
John (N6BER), Joyce, Lucas (Golden Retriever mix), Bella (Great Pyrenees) and Lance (Great Pyrenees).
Tustin, CA
Timon is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Conversion to All Electric - Induction Cooktop Install Dutch Star Don Newmar Owner's Forum 31 10-10-2017 11:47 PM
True Induction, which one to use? HHIDan RV Systems & Appliances 7 04-19-2015 11:37 AM
Induction Cook Top Michman66 Newmar Owner's Forum 46 10-30-2014 10:31 AM
Induction Cooktop v. Electric Cooktop Deek Newmar Owner's Forum 23 04-13-2014 12:19 AM
Induction Cooktop in Newmar Coaches saydiver Newmar Owner's Forum 8 11-29-2013 12:22 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 04:26 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.