Originally Posted by HamboneTHW
So the geniuses that wired our house put the panel on the opposite side of the house from the driveway. I want to install a 50 amp receptacle at the house. When measuring, it will be about an 80' run of cord from the receptacle to the coach. Voltage calculations are showing a 1.34 voltage drop for 85' of 6/3 on 2 legs of 120 volts. Will this cause any issues for anything on the coach?
Already pricing power cords... This is gonna suck... But the convenience of being able to plug in at the house the day before leaving... Priceless
|
Although you may never need 50 amps, it should be done right. Therefore, 50 amp draw @ 120 volts with #6 copper the voltage drop is 3.36 which is 2.8%. 50 amp service is 240/120, however campers generally only have 120 volt devices. The loads are distributed across both legs, however it is possible to draw 50 amps on one leg a 0 amps on the other leg... which is the worst-case scenario to account for. Voltage could drop to 116 which is totally fine. This represents the worst case scenario. Drawing current on both legs and/or drawing less than 50 amps, the situation only improves.
The worst part is running the wire.