07-07-2010, 07:39 AM
|
#1
|
Junior Member
Join Date: Aug 2009
Posts: 4
|
MH is using house batteries while plugged in
I have a 1999 Allegro Bay motorhome with a Ford V10 engine. It is 32'.
The last time I went camping everything worked fine for the first day but on the second when we came back to rv from baseball games the lights were dim on the inside of mh. The AC would not work, refrig quit as well. If I turn the ignition key to on everything gets bright and works but as soon as I turn it back to off, they all go off again although the lights will be dim. It appears that it puts a little charge in the house batteries. If I drive I guess it charges the house batteries and it works again for a little while till they go dead.
What would cause the converter to not be working when on shore power? Shouldn't it work off of that and not the house batteries when on shore power? Any ideas would be appreciated. We are leaving Saturday for a week in Florida.
Thanks!
Scott
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-07-2010, 07:53 AM
|
#2
|
Senior Member
Join Date: Jul 2005
Posts: 5,996
|
Check the main breakers in the coach and out at the pedestal. Good luck!!
__________________
TandW
|
|
|
07-07-2010, 07:59 AM
|
#3
|
Senior Member
Join Date: Aug 2009
Location: CT
Posts: 378
|
Quote:
Originally Posted by smorgan
What would cause the converter to not be working when on shore power? Shouldn't it work off of that and not the house batteries when on shore power? Any ideas would be appreciated.
|
Not sure about your's, but my converter plugs into the 120v electrical system . . . I'd start there . . . see if you have power to the converter? . . . it probably has a thermal breaker of sorts, have you blocked the airflow to it?
Worst case, I upgraded my converter earlier this year . . . relatively inexpensive and easy to do. Good luck!
__________________
2005 National Dolphin 6376 LX
bought used in 2017
|
|
|
07-07-2010, 08:26 AM
|
#4
|
Senior Member
Join Date: Sep 2006
Location: Ottawa, Ontario
Posts: 272
|
I would also look at the converter. My 1999 converter finally crapped out this spring, after I took it our of storage. In my case nothing worked. Replaced it with a 50 amp converter and it works fine.
__________________
2004 CRV
Brake Buddy Blue Ox Aventa II
|
|
|
07-07-2010, 08:29 AM
|
#5
|
Senior Member
Join Date: Jul 2005
Posts: 5,996
|
The OP states AC is not working.
__________________
TandW
|
|
|
07-08-2010, 08:17 AM
|
#6
|
Senior Member
Join Date: Aug 2009
Location: CT
Posts: 378
|
Quote:
Originally Posted by TandW
The OP states AC is not working.
|
Ahhh! . . . but does he mean the 110v alternating current or the air conditioning?
__________________
2005 National Dolphin 6376 LX
bought used in 2017
|
|
|
07-08-2010, 08:32 AM
|
#7
|
Senior Member
Newmar Owners Club
Join Date: Apr 2010
Posts: 460
|
If none of your 110 vac appliances or outlets work its a good place to start. Try starting the gen. if the A/C etc. works from gen. it could be the switching contactor that switches from shore power to gen. output or 110 vac input from the shore panel.
If you have no power from gen. either you'll have to start measuring from the source forward.
|
|
|
07-08-2010, 08:34 AM
|
#8
|
Senior Member
Join Date: Jul 2005
Posts: 5,996
|
Sorry, but the OP mentions both Shore Power and AC. Good luck!!
__________________
TandW
|
|
|
07-08-2010, 08:40 AM
|
#9
|
Moderator Emeritus
Nor'easters Club Workhorse Chassis Owner iRV2 No Limits Club
Join Date: Oct 2004
Posts: 30,785
|
I agree with Ken & Bigsky he's lost his 110, needs to check 110 supply,circuit breaker in load center, outlet for converter where is it.
His transfer switch could have dirty contacts on the relay, should start Gen and see if he gets power and converter works from its 110 outlet with Gen working.
Need to start coach engine for starting Gen because house batteries probably can't.
Once Gen going shut off engine of coach.
Refridgerator needs the 12v for control board to work either off converter or 12v house batteries. May have to charge house batteries with a 12v battery charger.
Has to get fixed, fridge going to take a day to cool down or delayed trip to FL.
|
|
|
07-08-2010, 08:31 PM
|
#10
|
Senior Member
Join Date: Feb 2010
Posts: 4,654
|
Measure voltage...Divide and defeat
Get a voltmeter, a few bucks at harbor Freight or Radio shack.
Divide and defeat is a troubleshooting term, divide the system into 2 parts, make a mesurement to determine which way to go, continue until fault located, repair.
Start it shore line connection, is it you are the pedestal?
Next check the load center, open the panel and measure the connections to the breakers.
If breakers hot then go to appliance, if dead go towards shore line, if you transfer switch is between the shore line and the load center then you may have a contactor that is not seated.
The contactor (switching device) is normally resting in the shore line position and activates in the generator mode, the contactor may not have closed properly the last time you had the generator running, the voltmeter will show exactly where the power stops.
|
|
|
09-13-2010, 09:35 PM
|
#11
|
Junior Member
Join Date: Sep 2010
Posts: 6
|
power out to receptacles
Having similar problem. No power to any of my receptacles. If there is no power to the 30 amp breaker in the control panel for the inverter, would that prevent my receptacles from working?
|
|
|
09-14-2010, 07:19 AM
|
#12
|
Senior Member
Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 13,599
|
Hi nanor,
If the circuits in questions are powered by your inverter the answer is yes. It matters not if you are on shore power or battery power. No power to the inverter means no power to outlets powered by the inverter.
__________________
Gary
2005 Newmar KSDP 3910 + GMC ENVOY XUV 37K lbs Moving Down The Road
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
|
|
|
09-14-2010, 07:21 AM
|
#13
|
Moderator Emeritus
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,713
|
Yes it will - none of the outlets that are powered through the inverter would work in that case.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
|
|
|
09-14-2010, 10:57 AM
|
#14
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
|
By AC do you mean 120vac (Alternating Current) outlets or do you mean A/C (Air Conditioning)
In either case this sounds like a 120 volt issue, not a 12 volt issue.
I have found MANY Rvers have a few screws loose.
Here is the test program You will need a test light (Drop cord will do for the first step) or other device which can test the park outlet.. Also a how ever many to 15 amp outlet.. A digital volt meter, not a bad investment. (One of these days I'm going to build a break-out box I have some of the parts now)
NOTE: this is easier on a 30 amp outlet
30 amp: Plug in a 30 to 15 adapter, plug drop cord or other 50-100 watt light into outlet and see if it works.. NO LIGHT: Problem found. No power at outlet.
LIGHT.. Ok, Put that stuff away and go to "NEXT"
50 amp.. This time you are going to have to use a volt meter (We need it in next anyway) this is not as good.. I would start by using a 50-30 and 30-15 and lamp as above (this tests one leg under load) but using the voltmeter set to a range (if needed) that can take 130 volts measure from the CENTER flat blade to either side. Should see about 115-125 volts. Exact voltage not important.
Measure center to round/U-shaped opening, should be ZERO.
NEXT:
Without plugging in the motor home.. Go to the main breaker box.. Open it and look around.. Grab the proper screwdriver and tighten EVERY SCREW IN SIGHT and if you can find a few hidden screws.. Tighten them too. Some of mine were very very very loose (Recall I said "A few screws loose.. These are the screws)
Now, Plug in, CAREFULLY measure from the white bus bar to the main breaker (30 amp) or both of the main breakers (50 amps) the screw with the wire... Again, should be 115-125.. Got it, good.
Now keeping one probe on the white bus.. Check each of the breakers All should show 115-125 (or whatever you had back at the post)
Possible other loose screws include.
Power inlet (if exist) Power cord plug (if not welded on) and outlet (IF Marineco) ATS if exists, and of course any other connection.
IF You have an EMS. and your 12 volt batteries are dead, it might be disconnecting you as well. (NOTE: MIGHT)
But I'd make sure you have 120vac to the converter 1st.. If not 120 fix that.
__________________
Home is where I park it!
|
|
|
|
|