ONAN 5500 blowing hot air into bedroom

On my last trip I was running the generator to run the roof A/C's. Everything was fine as I have done this on all my trips. I stopped at a rest area and walked to the bedroom and under the vanity there is a return air vent for the furnace. There was hot air blowing through this vent like the furnace was on. This never happened before. It was not an extremely hot day, maybe 85%. I shut off the generator and headed straight to my RV guy. He pulled out my drawers next to the vanity and seen that there was a furnace vent under the drawer. His conclusion was that it must have been windy outside, which it was not, and the wind was blowing the air across the generator into the bedroom. Needless to say, I'm looking for a new RV repairman!!!! Has anyone ever experienced anything like this?
Thanks,
Rendon
__________________
RENDON
Pass Christian, MS Retired
2004 Itasca Sunrise, Full Timer
Rendon is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-14-2017, 09:32 AM   #2
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,269
Questions ?

Did the hot air flow stop when you shut the gen set off ?

Where is the gen set , in relation to the point where the hot air flow was felt ?

Can you duplicate this condition every time the get set is in operation ?
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 01-15-2017, 08:01 AM   #3
Senior Member
 
Rendon's Avatar
 
Join Date: Feb 2014
Location: Pass Christian, MS
Posts: 135
Yes the hot air stopped once I turned off the generator. It is located in the back left outside compartment which is directly under the bedroom closet and the drawers are under the closet. About 5 feet from the genny to where the air was blowing thru the return vent in the bedroom. This has never happened before and I've traveled many miles with the genny running to operate the roof A/C's as the dash air does not work. When I arrived at my RV guy, he had me fire up the genny and turn on the A/C's. They ran for a good hour and no hot air came thru that vent in the bedroom. This vent is located close to the floor. I have a 2004 Itasca Sunrise 32v.
__________________
RENDON
Pass Christian, MS Retired
2004 Itasca Sunrise, Full Timer
Rendon is offline   Reply With Quote
Old 01-15-2017, 09:28 AM   #4
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 5,926
Since the generator is air cooled and has a big fan to move the air, It is logical that the cooling air for the generator is going into the coach. After dark, place a bright light in the return air cavity. check for light at the generator. I am sure you will find a opening somewhere.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2014 Honda CRV toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
ga traveler is offline   Reply With Quote
Old 01-15-2017, 10:20 AM   #5
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
Another suggestion.

Place a lit candle next to vent and have helper watch it.

Get outside with leaf blower and blast everywhere and see if the candle flickers.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 01-16-2017, 10:18 AM   #6
Senior Member
 
Rendon's Avatar
 
Join Date: Feb 2014
Location: Pass Christian, MS
Posts: 135
Thank you both for this info. Still doesn't quite make sense to me but I'll try those suggestions. I wonder why it's never happened before. It was obvious that the hot air was blowing in the vent while I was traveling. How long do you think it would continue to blow that air thru the vent? It was not an extremely hot day and I've traveled in July with no issues!
__________________
RENDON
Pass Christian, MS Retired
2004 Itasca Sunrise, Full Timer
Rendon is offline   Reply With Quote
Old 01-16-2017, 10:30 AM   #7
Senior Member
 
4x4van's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Apr 2011
Location: SoCal
Posts: 1,510
There should be no possible pathway from the generator to the furnace ducting, so there has to be a breach in your furnace ducting near the generator. The suggestions about using light or a candle are good to verify that.

Not sure if yours is the same, but my 04 Itasca Sunrise M30W has the furnace mounted under the floor at the rear of the coach right in the middle. That puts it right next to the generator, which is in the left rear corner.

Again, there has to be a breach in the furnace ducting in that area, but I'm not sure how you would access it.
__________________
You don't stop playing because you grow old...You grow old because you stop playing!
2004 Itasca M30W
'20 Can Am X3 X RS Turbo RR, '85 ATC250R, '12 Husky TE310
4x4van is offline   Reply With Quote
Old 01-17-2017, 07:36 AM   #8
Senior Member
 
Rendon's Avatar
 
Join Date: Feb 2014
Location: Pass Christian, MS
Posts: 135
My furnace is located in the same spot as yours. I haven't tried those two suggestions yet but I will. This last trip I took, I traveled over the worst roads ever in my life. I was quite surprised that the whole MH didn't fall apart! Perhaps something got jarred loose and is causing this issue. I'm planning another long trip come April. I don't think I'll have to use my AC as I am heading north but I def want this issue corrected! Thanks again for the replays!
Rendon
__________________
RENDON
Pass Christian, MS Retired
2004 Itasca Sunrise, Full Timer
Rendon is offline   Reply With Quote
Old 01-17-2017, 12:49 PM   #9
Senior Member
 
J. Frank's Avatar
 
Join Date: Apr 2016
Location: Moulton, Alabama
Posts: 189
Any chance the furnace got turned on accidently? It could have coincidently shutdown about the same time as a you shut down the generator.
__________________
Jerry
2016 Gulfstream/Ameri Lite 268BH
/2006 Ford Expedition
J. Frank is offline   Reply With Quote
Reply

Tags
onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
5500 Onan vs 7000 Onan HUGHP MH-General Discussions & Problems 10 07-16-2016 07:09 PM
Onan 5500 Marquis dies in hot weather joedaddy805 RV Systems & Appliances 39 12-02-2015 10:17 PM
Onan bgm 5500 blowing gas through air intake Cheepjeep80 RV Systems & Appliances 6 07-22-2011 12:21 PM
Onan 5500 surges and stops in hot weather abarkl RV Systems & Appliances 8 11-16-2009 09:54 AM