Old 05-18-2016, 08:27 PM   #1
Senior Member
 
Join Date: Dec 2014
Posts: 102
Onan 7500 Diesel gen problem

2003 Onan diesel 7500 with 250 total hours. The generator was serviced by Cummins 2 months ago including oil, both filters, and coolant. It was running just fine before and after service and would fully power coach. After running for approx 1 hour only powering one A/C a few days ago, it quit. Will restart and run smoothly for about 45 seconds and quit - about the time it actually picks up a load. If I start it with the breaker in the off position, it runs fine but when I turn the breaker on, generator quits. Oil and coolant levels are right on. Any ideas?
MikeandJan is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-18-2016, 08:50 PM   #2
Senior Member
 
FIRE UP's Avatar


 
Join Date: Dec 2009
Location: Out there, somewhere
Posts: 9,941
Quote:
Originally Posted by MikeandJan View Post
2003 Onan diesel 7500 with 250 total hours. The generator was serviced by Cummins 2 months ago including oil, both filters, and coolant. It was running just fine before and after service and would fully power coach. After running for approx 1 hour only powering one A/C a few days ago, it quit. Will restart and run smoothly for about 45 seconds and quit - about the time it actually picks up a load. If I start it with the breaker in the off position, it runs fine but when I turn the breaker on, generator quits. Oil and coolant levels are right on. Any ideas?
MikeandJan,
Well, the very first thing you need to do is, when that generator quits, the start toggle switch, located on the generator itself, will "blink" in a code. It will blink in a series and, have a pause, then it will blink a second series. It will present something like this:

Blink-Blink-blink...........Blink-blink-blink........ start all over again.

That series of blinks is, 3....pause, 3.

The code is, "33".

You then need to look up, in your Onan Generator manuals (service and owners) to find out what that code represents.

Now, this is an example. It could be any code. So, try and read what that switch is telling you.

Scott
__________________
2004 ITASCA HORIZON 36GD, 2011 GMC Sierra 1500 4x4 Toad '20 Honda NC750X DCT
2018 Goldwing Tour DCT Airbag
Retired-29.5 yrs, SDFD, Ham - KI6OND
Me, Karla and the Heidi character, (mini Schnauzer)!
FIRE UP is offline   Reply With Quote
Old 05-18-2016, 09:31 PM   #3
Senior Member
 
Davdeb1's Avatar
 
Monaco Owners Club
Freightliner Owners Club
iRV2 No Limits Club
Join Date: Jan 2011
Location: Avon Lake, Oh
Posts: 2,958
If it's a 36, it's fuel. ( plugged gas filter or fuel pump). 33 means coolant temp
__________________
2000 HOLIDAY RAMBLER ENDEAVOR
40 FT--330HP CAT
2 SLIDES-TOAD 2012 focus
Fulltime-Home is where we park it.
Davdeb1 is offline   Reply With Quote
Old 05-18-2016, 09:50 PM   #4
Senior Member
 
Dtwallace's Avatar
 
Join Date: May 2014
Posts: 1,368
How much fuel do you have in your main tank?


Low fuel will shut the gen down so you don't run out by accident....


DTW
__________________
Dan & Loretta, US Army Retired Aero Scout Pilot
2012 Fleetwood Providence 42P Class A/DP
Spartan Chassis, 8.9L Cummins 450HP
Dtwallace is offline   Reply With Quote
Old 05-19-2016, 06:42 AM   #5
Senior Member
 
Sky_Boss's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Spartan Chassis
Join Date: Apr 2012
Location: ON THE ROAD...SOMEWHERE
Posts: 6,973
Quote:
Originally Posted by Davdeb1 View Post
If it's a 36, it's fuel. ...
Maybe, maybe not. Good odds it might be but Per may 7.5 QD circa 2006...

Code 36 is "Engine stopped without command by controller"

Corrective Action:
1. Check fuel level. (Note: The genset fuel pickup is probably higher than the vehicle engine pickup.)
2. Prime the engine fuel system by holding the control switch down in its Stop position for at least 1 minute.
3. Check the engine air filter and remove any blockage (Page 16).
4. Check for mechanical damage.
__________________
Don, Sandee & GSD Zeus. Guardian GSDs Gunny (7/11/15) & Thor (5/5/15)
2006 2015 DSDP 4320 4369, FL Chassis, 2013 CR-V 2020 Jeep Overland, Blue Ox Avail, SMI AF1.
[SIGPIC][/SIGPIC]
Sky_Boss is offline   Reply With Quote
Old 05-19-2016, 07:00 AM   #6
Senior Member
 
Sky_Boss's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Spartan Chassis
Join Date: Apr 2012
Location: ON THE ROAD...SOMEWHERE
Posts: 6,973
Quote:
Originally Posted by MikeandJan View Post
2003 Onan diesel 7500 with 250 total hours. The generator was serviced by Cummins 2 months ago including oil, both filters, and coolant. ...
When you say "both filters" you have 3. Fuel, air and oil. Which 2 were changed?

How old is your coach? 250 hours is not a lot of hours if your coach is over a few years old. While I don't think a 33 code is directly related to lack of running it would be something to look into for the long term health of the generator. The only direct connection might be the fuel filter if it has been in there a long time.
__________________
Don, Sandee & GSD Zeus. Guardian GSDs Gunny (7/11/15) & Thor (5/5/15)
2006 2015 DSDP 4320 4369, FL Chassis, 2013 CR-V 2020 Jeep Overland, Blue Ox Avail, SMI AF1.
[SIGPIC][/SIGPIC]
Sky_Boss is offline   Reply With Quote
Old 05-20-2016, 06:17 AM   #7
Junior Member
 
mintysmiley's Avatar
 
National RV Owners Club
Join Date: May 2012
Location: Wingate, NC
Posts: 2
99 national trade wind diesel pusher, with propane generator. generator not turning over, slide not working. seems like an electrical problem. any ideas
mintysmiley is offline   Reply With Quote
Old 05-20-2016, 06:17 AM   #8
Senior Member
 
Join Date: Dec 2014
Posts: 102
Thanks for the clear explanation of how to get the error code. I was only getting the first digit - 3. Full code is 31, which I believe is engine overspeed. Engine sounds normal to me, in fact it shuts off when the engine bogs down slightly when it picks up the load. Only corrective action I can find in the manual is to take it to authorized Cummins/Onan repair. I'm actually sitting at Alliance in Wildwood but they no longer do generator repairs. Go figure - Cummins is only 30 minutes away but I can't drive there because I'm missing a window that is out for repair until next week. Thanks everyone - I'm amazed how much you guys know about these things.
MikeandJan is offline   Reply With Quote
Old 05-20-2016, 10:06 AM   #9
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,697
You apparently have a speed governor problem - the engine goes overspeed under load, when the governor tries to open the throttle to maintain the rpms as the load increases. For most of us, that means a visit to a Cummins/Onan shop. You can get an Onan7500 service manual if you want to tackle it yourself, though. I picked up an inexpensive CD version on Ebay.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 05-20-2016, 04:35 PM   #10
Senior Member
 
Join Date: Nov 2009
Posts: 148
Take a look at the transfer switch box. I had a similar issue and found melted wires in the box.
Fixed the wiring and the generator was fine.

Mike
__________________
2004 Holiday Rambler Endeavor 40 PDQ 330 Cummins
S/N 1RF42464342027368
Mtn.Mike is offline   Reply With Quote
Old 05-21-2016, 09:23 AM   #11
Senior Member
 
Winnebago Owners Club
Join Date: Jan 2016
Posts: 199
I have a onan 7500 like u.It has 1600 hours run fine last year and sit over the winter and wouldnt start got it started run wide open.Took it to a local guy and shouldnt!He had it a month.Picked it up yesterday and it not fixed now charged me 680.00 for labor and he said that it is governor actuator?Got to pull gen out of camper to fix,He said!!but he sure ant going to do it!! A$$ hole.But that is where iam at!!Ifigured a month he could have it fixed plus iam going to missouri had to pick it up or not go!! and ant no telling what the damn bill would have been!
sewerdog is offline   Reply With Quote
Old 06-11-2016, 10:24 AM   #12
Senior Member
 
Join Date: Dec 2014
Posts: 102
I wanted to followup with everyone who tried to help with my generator problem. The generator was throwing a 31 code - engine overspeed - and the corrective action is to see an authorized Onan dealer. I took it to Register RV in Brooksville, FL, where I already had an appointment to have StoneVos slide toppers installed. In addition to the 31 code, their tech also got a 28 code one time. The corrective action for both is to replace the controller/inverter on the generator - $1,850 for the part and about 4 hours labor. When the tech removed all the covers on the way to the controller, a large part of a magnet was laying there stuck to the frame and small bits of magnet were all over. The cooling fan, rotor, and stator were all damaged and had to be replaced. No one had any idea why the magnet came loose - they are "bonded", i.e., glued in place. Total cost parts and labor came to $3,000. The good news is that the controller/inverter was good and we didn't have to install a new one.

The folks at Register were super and the tech took a lot of time explaining the system to me. The controller senses the generator load requirement and adjusts the power output of the engine by adjusting fuel flow. In my case the generator couldn't produce power so the controller would ask for speed up to the max of 2100 RPM at which time it would shut down the engine. After the repair, they ran it for 5 hours with no problem I also ran it 10 hours all the way back to North Carolina and it performed just fine. Thanks again for your ideas.
__________________
Mike and Jan
'03 Monaco Camelot
MikeandJan is offline   Reply With Quote
Old 06-11-2016, 10:35 AM   #13
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
Thanks for the update !!
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Old 06-12-2016, 09:29 AM   #14
Senior Member
 
Dtwallace's Avatar
 
Join Date: May 2014
Posts: 1,368
Very educational,
Thank you for the update.


DTW
__________________
Dan & Loretta, US Army Retired Aero Scout Pilot
2012 Fleetwood Providence 42P Class A/DP
Spartan Chassis, 8.9L Cummins 450HP
Dtwallace is offline   Reply With Quote
Reply

Tags
diesel, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan 7500 Diesel Generator Problem xchp3912 RV Systems & Appliances 4 07-05-2012 12:33 PM
Onan Gen Set HDKAJ 7500 watt lpray1 RV Systems & Appliances 0 06-17-2012 10:30 AM
Onan 7500 diesel Gen problem? Hillbillyjoe Class A Motorhome Discussions 7 07-12-2011 03:45 PM