Onan 8000 generator giving 30 amps only
Hi everyone,
I have an Onan Quiet 8000 generator which starts very well and runs fine but it only gives 30 amps of power instead of the full 50 amps. The smart energy system display panel displays 30 amps and the service type 30 amps indicator is lit. The service type gen/set indicator should be lit instead
The fuel tank is at 3/4 and the motorhome is unplugged.
Any ideas?
Thanks
__________________
Natalie & Yves
00 Itasca Horizon 36LD
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-15-2019, 12:45 PM
|
#2
|
Senior Member
Country Coach Owners Club Solo Rvers Club iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
|
That's all it will ever have. You need a 10.5 or 12.5 KW to give you both legs of a 50 amp service and only the 12.5 gives you a full 50 amps.
8000 watts = 66.6 amps but only on L1.
10,000 watts = 83.3 amps divided between L1 and L2
12,000 watts = 100 amps divided between L1 and L2.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
|
|
|
07-15-2019, 12:50 PM
|
#3
|
Senior Member
Official iRV2 Sponsor
Join Date: May 2011
Posts: 8,305
|
Quote:
Originally Posted by Yogi26
The smart energy system display panel displays 30 amps and the service type 30 amps indicator is lit. The service type gen/set indicator should be lit instead
|
With all due respect, I think you're worrying too much about an indicator that doesn't actually "control" the power you're getting from the generator. As noted in the previous post, your generator looks like a 30A connection to the control system because it has only one power "leg." The fact the panel lights up as 30A rather than "genset" doesn't mean the generator isn't providing the full 8kW it's capable of producing.
Joel (AKA docj)
__________________
Joel (AKA docj)--
RV Technology Specialist
|
|
|
07-15-2019, 01:16 PM
|
#4
|
Junior Member
Winnebago Owners Club
Join Date: Feb 2014
Posts: 17
|
According to the Operator’s manual and specs on the generator itself, the AC output rating is 66.7 amps for model 8HDKAK 1046K which I have. See attached photo.
__________________
Natalie & Yves
00 Itasca Horizon 36LD
|
|
|
07-15-2019, 01:20 PM
|
#5
|
Junior Member
Winnebago Owners Club
Join Date: Feb 2014
Posts: 17
|
Thanks,
So I understand what your saying, the generator could be setup using one leg instead of two hence providing 30 amps only?
__________________
Natalie & Yves
00 Itasca Horizon 36LD
|
|
|
07-15-2019, 02:15 PM
|
#6
|
Senior Member
Official iRV2 Sponsor
Join Date: May 2011
Posts: 8,305
|
Quote:
Originally Posted by Yogi26
Thanks,
So I understand what your saying, the generator could be setup using one leg instead of two hence providing 30 amps only?
|
Your generator (and mine) are 120V devices and, by definition, they only deliver "one leg" at 120V. Some larger MH's have generators that produce >10kW and those usually are setup to produce 240V power with two 120V legs.
__________________
Joel (AKA docj)--
RV Technology Specialist
|
|
|
07-15-2019, 02:29 PM
|
#7
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
Its delivering 2-120 volt legs, just not at 240 volts so the device thinks its 30 amp service.
Your generator has a double 30 amp breaker. You will have 60 amps avalable, 30 on L1 and 30 on L2.
Turn on 2 air conditioners and the microwave. If they all run, that's the proof.
The signal that the generator is running may be missing from the indicator and that's why its showing 30 amps.
|
|
|
07-15-2019, 02:34 PM
|
#8
|
Senior Member
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
|
Quote:
Originally Posted by twinboat
Its delivering 2-120 volt legs, just not at 240 volts so the device thinks its 30 amp service.
Your generator has a double 30 amp breaker. You will have 60 amps avalable, 30 on L1 and 30 on L2.
Turn on 2 air conditioners and the microwave. If they all run, that's the proof.
|
There ya' go
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
|
|
|
07-15-2019, 03:26 PM
|
#9
|
Junior Member
Winnebago Owners Club
Join Date: Feb 2014
Posts: 17
|
Quote:
Originally Posted by twinboat
Your generator has a double 30 amp breaker. You will have 60 amps avalable, 30 on L1 and 30 on L2.
Turn on 2 air conditioners and the microwave. If they all run, that's the proof.
The signal that the generator is running may be missing from the indicator and that's why its showing 30 amps.
|
Thanks for the explanation. I can’t run all three together. I also checked on the generator and it only has one 35 amps breaker. Having a generator which could get to 66 amps, I am wondering why two breakers (35 and 30 amps) were not installed by the manufacturer.
I know now with the reading shows 35 amps. Thanks to you all.
__________________
Natalie & Yves
00 Itasca Horizon 36LD
|
|
|
07-15-2019, 04:09 PM
|
#10
|
Senior Member
Official iRV2 Sponsor
Join Date: May 2011
Posts: 8,305
|
Quote:
Originally Posted by Yogi26
. I can’t run all three together. I also checked on the generator and it only has one 35 amps breaker. Having a generator which could get to 66 amps, I am wondering why two breakers (35 and 30 amps) were not installed by the manufacturer.
|
FWIW my 7.5kW Onan generator can power both A/C's and the microwave. Something does seem odd with how yours MH was wired.
__________________
Joel (AKA docj)--
RV Technology Specialist
|
|
|
07-15-2019, 04:14 PM
|
#11
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
Quote:
Originally Posted by Yogi26
Thanks for the explanation. I can’t run all three together. I also checked on the generator and it only has one 35 amps breaker. Having a generator which could get to 66 amps, I am wondering why two breakers (35 and 30 amps) were not installed by the manufacturer.
I know now with the reading shows 35 amps. Thanks to you all.
|
The single breaker handle controls 2 breakers.
If you can power all of the MH, rather then 1/2, of the breakers, all is correct.
If some of the stuff has no power, you have a problem.
What happens when you switch on 2 ACs and the microwave. Why can't you do it ?
|
|
|
07-15-2019, 04:19 PM
|
#12
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
Here is your specs.
|
|
|
07-15-2019, 05:42 PM
|
#13
|
Junior Member
Join Date: Jul 2019
Location: Claremont NC
Posts: 12
|
The amp rateing is the maximum the generator can supply, the actual delivered amps is based on the load the generator ‘sees’.
|
|
|
07-17-2019, 06:39 AM
|
#14
|
Junior Member
Join Date: Jul 2019
Posts: 1
|
Try resetting the 35 amp breaker on the generator. You should feel it click twice, once around the midway point and the 2nd at the fully on position.
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|