Onan Gen - starts by itself

I have a Journey Winnebago 2007 with Diesel Gen Set - Onan.

The generator started by itself while I was hooked to RV Park power.

What could cause this and how can I prevent it?

Thanks

(New Full timer - 8 months on the road).

Jim Brickett
jimbrickett is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-12-2015, 04:44 PM   #2
Senior Member
 
lowejug's Avatar
 
Join Date: Oct 2013
Location: st george
Posts: 1,387
I have had the same issue. In a Rv park once we showed up and generator was running and we were plugged in, It is common as I read about others.
They say it has has something to do with lighting storm in the air makes it start. As far as a prevention I never got one so maybe some one else will chime in and say
A remedy
lowejug is offline   Reply With Quote
Old 05-12-2015, 04:52 PM   #3
Senior Member
 
Redridge's Avatar
 
Join Date: Sep 2012
Posts: 1,562
do you have an AGS? Auto Generator Start have a few options... starting the gen if: low battery voltage, high cabin temperature, low amperage detected (ie: to use microwave), loss of shore power... or to cycle it on a schedule. It depends on how it was programmed to turn on...
__________________
Ferdinand,
2014 Thor Palazzo 33.3 (Melody), Folkstone
2017 Jeep Rubicon, Ready Brute Elite & Currie Ent Baseplate
Redridge is offline   Reply With Quote
Old 05-12-2015, 05:17 PM   #4
Senior Member
 
britcon's Avatar
 
Join Date: Mar 2011
Posts: 754
As Redridge said, sounds like Auto Generator Start is set to come on with either AC or low battery voltage
__________________
2014 Newmar Ventana 4037 / 4018
2015 Jeep Grand Cherokee Ltd.
1940 Chevrolet Pickup
britcon is offline   Reply With Quote
Old 05-12-2015, 05:26 PM   #5
Senior Member
 
Bigd9's Avatar


 
Join Date: Jun 2012
Location: The Bluegrass State
Posts: 8,889
There have been reports of moisture from the dash air conditioner dropping on the control board causing the board to short out and starting. On my coach the discharge for the air conditioner has been extended to direct the water away from the generator.
__________________
Good Luck, Be Safe and Above All, Don't Forget To Have Fun
Pete
Central Kentucky
2006 Fleetwood Discovery 35H, 2014 Honda CR-V, M&G Engineering Braking System
Bigd9 is offline   Reply With Quote
Old 05-12-2015, 05:26 PM   #6
Senior Member
 
Qwert66's Avatar
 
Newmar Owners Club
Join Date: Nov 2011
Location: Michigan
Posts: 894
Send a message via Skype™ to Qwert66
if you don't have auto gen start the 2 most likely causes are;

1.Critter climbed up on the genny control panel and stepped on the start button. This can be fixed by taping something under the start side of toggle switch and start from inside the coach.

2.Humidity on/in the gennny main wiring harness connector above and outside the generator. This can be fixed by opening the harness connector, cleaning/drying and applying a SAMLL amount of dielectric grease on the contacts.
__________________
1999 Newmar Mountain Aire MADP 4080, Cummins ISC 8.3L, Allison, Spartan MM IFS, Howard Power Center, Chev Trailblazer LTZ Towed w/ BlueOx rigging, Segway X2.
www.shaw11.com
Qwert66 is offline   Reply With Quote
Old 05-12-2015, 05:47 PM   #7
Junior Member
 
Join Date: Jan 2011
Location: DeLand FL
Posts: 25
Agree. Moisture in the connector from the start button. Known problem. Near the firewall outside.
big katuna is offline   Reply With Quote
Old 05-12-2015, 06:16 PM   #8
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 14,589
There is also a multi wire connector on the side of the generator, in some cases this connector will get moisture/water in it. This could cause the generator to start on it's own. Take the connector apart, spray with a electrical cleaner, and put back together.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Reply

Tags
onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan gen starts on its own! bglewis RV Systems & Appliances 7 05-12-2015 04:13 PM
Onan Quiet Diesel starts, then shuts off dave freitas RV Systems & Appliances 6 03-12-2015 04:52 PM
Onan gen coolant joelyn5 Cummins Engines 4 12-06-2014 05:39 PM
Onan gen blowing fuel pump - auto choke fuse Rockyroad MH-General Discussions & Problems 3 02-22-2014 05:45 AM
Onan Gen and Cummins ISL Oil Filter Number Scepter1 Class A Motorhome Discussions 3 01-20-2014 04:18 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:16 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.