Onan propane generator won't start

Onan Marquis 6500 Propane generator. We had quite a bit of trouble with it last year, involving several rounds of repairs. By the time we put the coach into storage last fall, we felt the generator problems were finally behind us because it was running like an absolute champ.

Today I took the coach out of storage. The generator started OK, but it was lazy. It took about ten minutes to finally get up to speed, then after about ten minutes of charging, the engine began missing and slowing down. I shut it down before it died.

My troubleshooting efforts today involved changing spark plugs, testing spark plug wires. Initially, the engine would start, but behave as if it was missing. Now, the situation has deteriorated. The engine now will fire, but not start. As long as I hold the starter button, the engine will continue to fire and kind of roll along with the starter. As soon as I release the starter button, the engine simply dies. Tomorrow I thought I'd test coil and ignition. The propane tank is more than 1/2 full, and I do smell propane a little while trying to start the engine.

Any thoughts or advice are greatly appreciated.
__________________
2016 Creekside 23RKS
2012 Ram 2500 Laramie 4X4 Cummins 6.7L
Canada, eh?
Papa_Jim is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-13-2012, 07:39 PM   #2
Senior Member
 
Join Date: Feb 2012
Location: Baton Rouge, LA
Posts: 1,202
We had a similar problem many years ago on a 4K Onan gas generator. Turned out to be the condenser. I changed both the points and the condenser, and all was well. The points and condenser are located on the top center of the generator on the gas unit if I remember correctly. The other problem I am aware of with Propane generators is the fuel regulator gets clogged with oil from the Propane. I have been told you can remove the regultor and clean it out, but I have never doen that. Good luck.

Jim
__________________
Jim and Lynda, (Sophie, Jake, attack trained killer Shi-Tzus :-))

2003 Fleetwood Expedition 38N 2005 Saturn Vue
jlfbatonrg is offline   Reply With Quote
Old 03-13-2012, 09:03 PM   #3
Senior Member
 
Hooligan's Avatar
 
Freightliner Owners Club
Join Date: Apr 2002
Location: Pensacola
Posts: 2,728
After starting, when the starter is released, the control board needs voltage from the generator to operate and it needs the oil pressure switch to close the "run relay". Or the generator will stop. (low oil level?) Hard start or no start can be the fuel solenoid sticking. You can check the solenoid by applying 12 volts and listen for a click.
Besides the regulator gumming up, There is a fuel filter next to the solenoid that can be cleaned. Probably dealer items, The propane in that area is at full tank pressure and has to be purged before it is safe to open the lines. A lot of propane can escape.
Troubleshooting:
http://www.flightsystems.com/pdf/onanrvtshootgd608.pdf

Onan has a service manual for the 6500 generators, as I remember it's reasonable.
They recommend starting the generator monthly and running under load for and hour or 2. Keeps everything fresh and dries moisture in the generator windings. (probably hard to do in storage)
Hope this helps
__________________
Hooligan, Pensacola, Fl -U.S. Coast Guard 1956-1985
2016 Thor Siesta Sprinter 24ST diesel -1972 Moto Guzzi
2008 Suzuki Grand Vitara TOAD
Hooligan is offline   Reply With Quote
Old 03-13-2012, 10:40 PM   #4
Senior Member
 
Join Date: Apr 2010
Posts: 691
first check the tube under the regulator that it is not blocked. Had a mud dobber plug mine in one day. Ran a long screwdriver up and cleared the mud and installed a screen over it. Secondly if it will run only while you hold the start switch in then the brushes probably have built up carbon around them and on the communtator shaft or brushes are worn out, Remove the brushes/check and clean. Tape a piece of steel wool on a screwdriver and hold it against the commentator shaft while turning the engine over to clean it. DO NOT lose the steel wool down inside while doing this. Also the regulator has a drain plug on the bottom that needs to be removed to allow any oil/water that may have came from the propane to drain out. Manual requires this on a regular basis. I do it once annually with oil change
RVhauler is offline   Reply With Quote
Old 03-14-2012, 05:10 PM   #5
Senior Member
 
Papa_Jim's Avatar
 
Outdoors RV Owners Club
Join Date: Oct 2009
Location: Manitoba,Canada
Posts: 2,789
I found the problem today. It didn't take too long to determine it wasn't fuel. The propane system on my Onan is a vapor system, not a liquid.

I went into ignition system checking, using the Onan service manual I'm
fortunate enough to own, and was able to determine that the ignition module has failed.

So, over the next few days, I'll be removing the generator from the coach and taking it apart. The generator has to be removed from the engine to replace the ignition module.

Thanks for your help.
__________________
2016 Creekside 23RKS
2012 Ram 2500 Laramie 4X4 Cummins 6.7L
Canada, eh?
Papa_Jim is offline   Reply With Quote
Old 03-15-2012, 02:26 PM   #6
Senior Member
 
Hooligan's Avatar
 
Freightliner Owners Club
Join Date: Apr 2002
Location: Pensacola
Posts: 2,728
Jim- thanks for the update.. Does not sound like an easy fix....
__________________
Hooligan, Pensacola, Fl -U.S. Coast Guard 1956-1985
2016 Thor Siesta Sprinter 24ST diesel -1972 Moto Guzzi
2008 Suzuki Grand Vitara TOAD
Hooligan is offline   Reply With Quote
Old 03-16-2012, 02:55 PM   #7
Senior Member
 
Papa_Jim's Avatar
 
Outdoors RV Owners Club
Join Date: Oct 2009
Location: Manitoba,Canada
Posts: 2,789
Well, I can do it. Been a diesel mechanic and machinist all of my life. It's not that difficult, just that the generator has to be completely torn apart to get at that little module.

We have had a lot of trouble with this generator. Last fall we thought we finally had it fixed. Running like a champ. Hope this is the last problem we have with it for a long time.
__________________
2016 Creekside 23RKS
2012 Ram 2500 Laramie 4X4 Cummins 6.7L
Canada, eh?
Papa_Jim is offline   Reply With Quote
Old 05-04-2012, 12:31 PM   #8
Registered User
 
Monaco Owners Club
Join Date: Oct 2010
Posts: 28
Good info Jim, thanks for the followup.

Yesterday I finally fixed my propane powered Kohler generator in my '94 Dynasty...

Symptoms: started hard, ran few minutes, hunted for correct RPM then quit. Restarted and it would do the exact same thing.

After many hours of diagnosing servo boards, fuel pressure, brushes, load problem... Called a Pro!

Fix: new plugs!

My generator tech noted that propane powered generators are very sensitive to miss fire caused by plug wires or worn/dirty/badly gaped plugs.

He explained that generator governor servo's circuits usually get their RPM signal input from the crankshaft sensor voltage. Even the most minute reduction in RPM causes the servo to open the carb butterfly a bit... then when the RPM exceeded specs carb closed a bit. At a point an over voltage circuit shut the generator down.

In my case there was no audible indication of an intermittent single plug misfire. But the rear cylinder plug was badly burned. The rear cylinder compression was 120 lbs. The front was 130.

Tech also suggested replacing air filter, checking exhaust tip to make sure no restrictions after long layup. Also consider de-carbon'ing the heads at 500+ hours.

Larry
wheato22 is offline   Reply With Quote
Old 05-05-2012, 02:06 PM   #9
Senior Member
 
Papa_Jim's Avatar
 
Outdoors RV Owners Club
Join Date: Oct 2009
Location: Manitoba,Canada
Posts: 2,789
Cool

Larry,
Good to know you've got it running.

I learned something a while ago about our propane generators. The propane regulators can be problematic for the oil in the propane plugging them up. Mine isn't quite so bad, I guess because it's a propane vapor system. Some however are propane liquid systems. On water cooled engines, there is a water coolant passage running through the regulator, so the regulator is always at engine operating temperature. Apparently this helps to make sure the oil in the propane stays liquid and remains easy to draw through the system and burned up by the engine. With our air cooled engines, there is no way to heat the regulator. To compensate for this, the regulator on my Onan is mounted right beside the muffler, in the hope that the heat from the muffler will heat up the regulator enough to keep the oils dissolved.

Here's the catch. If I don't run the engine for long enough periods of time, the regulator doesn't get a chance to get hot, so the oils slowly collect and solidify into a gelatin like substance that eventually plugs the regulator until the system just can't work properly.

So, I make sure to run that generator for about two hours each time I start it. It seems to be working. I had the regulator apart when I fixed the ignition module, and it was clean.
__________________
2016 Creekside 23RKS
2012 Ram 2500 Laramie 4X4 Cummins 6.7L
Canada, eh?
Papa_Jim is offline   Reply With Quote
Reply

Tags
generator, onan, propane



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Video noise glitching on tv while on generator power RichKimball Technology: Internet, TV, Satellite, Cell Phones, etc. 4 05-28-2012 10:53 AM
Airbags won't inflate lmcgill Fleetwood Owner's Forum 2 03-26-2012 07:01 PM
First start after winter ninos Caterpillar Engine Forum 7 03-22-2012 10:48 AM
Generator Door wont open MICJAC Tiffin Owner's Forum 5 03-20-2012 03:26 PM
generator hrs gilunionhall RV Systems & Appliances 4 03-12-2012 08:22 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:24 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.