Originally Posted by ottffss View Post
Really? I'd find a new "electrical specialist" as RV 120VAC wiring - by RVIA mandate - follows national electrical code and a xx amp outlet/circuit in that code will run xx amps all day/night/year without issue. It's corroded or poor assembly that causes the long run time overheating.

Th OP is correct in how many inverters "bypass" shore power sort-of through (not completely around) the inverter and that the inverter "bypass" current IS limited to its feed amperage (usually 20/30amps) which also must power the charger side within those feed amps.

The REAL reason to install heater OFF the inverted outlets is that in the event of a power failure while you are out you won't run the batteries down to the inverter kick-off voltage and then find you still have no shore power, your batteries are dead and you can't start the genset. Now, that's a real problem as everything starts to freeze and you have NO recourse. You might not be able to turn over the big motor without the bat boost if real cold.

There are non-inverted outlets on most rigs - garym114 has the easy way to find them. Usually, the washer, a basement plug or two, maybe an under-sink plug, a central vacuum, the engine block heater, are OFF the inverter and IDEAL elec heater outlets. (If you need an extension cord, please make a 12ga short extension cord using commercial grade plugs on both ends)

And by ALL MEANS do what

Because it is an excellent preventive issue measure!!!!!!
I agree that we wouldn't be allowed to buy RV's that don't meet the National Electric Code. I think the warnings offered by this technician are a little extreme.

There is a bypass relays in inverters, when plugged into shore power, bypass all the circuitry in the inverter (other than the relay). For the 2000W inverters, the bypass relay is generally rated at 30A.

A 30A 120V circuit delivers 3600 watts of power. That would be the 30A relay capacity.

Then there's the issue of having too much wattage on any 15A (1800 watts) or 20A (2400 watts) branch circuit to the receptacles. Overload it and the circuit breaker will pop.

Common sense prevails. I would not use a plug-in heater unattended in my home or my RV. I do use them periodically, where I can monitor their performance. For example, feel the cord. If it's hot, there's a problem. Turn it off.

The anal electrician in me does agree that a direct circuit from the auxiliary heater to the panel box bypassing the inverter is a good idea, as this bypasses any additional mechanical relays which can add resistance to the circuit. But, I also trust the National Electric Code, which our RV's are theoretically built by.

'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
Pusherman is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-19-2012, 05:38 PM   #16
Senior Member
Monaco Owners Club
Join Date: Apr 2011
Location: Scottsdale, AZ
Posts: 255
Trap... good to hear your experience. I think running 750 makes a lot of sense indeed.

Don... I'm going to look into a dedicated circuit which bypasses the inverter altogether just for running a space heater. But I also agree that it "seems" reasonable to trust the circuit that runs through a recent manufactured inverter, particularly when sticking to a moderate 750 watts.

"Be kind... everyone you encounter in life is fighting battles that you have no awareness of."
2016 Newmar Bay Star 3124 w/ 2016 Jeep Wrangler Rubicon Unltd Hard Rock
DHart is offline   Reply With Quote
Old 02-19-2012, 05:50 PM   #17
Senior Member
smiller's Avatar
Join Date: Jul 2011
Posts: 1,298
One way to safely run a 1500-watt space heater would be to install a dedicated outlet near the breaker panel and run 12-gauge Romex (probably just a matter of a few feet) directly to it. In this case you should be about to draw the heaters full rated load indefinitely without excessive supply wire heating.
smiller is online now   Reply With Quote
Old 02-19-2012, 09:39 PM   #18
Join Date: Nov 2006
Posts: 69
What about the relays in the automatic transfer switch that sources power from generator or shore power. Do they heat up?
rvndonm is offline   Reply With Quote
Old 02-20-2012, 12:49 AM   #19
Senior Member
Freightliner Owners Club
Join Date: Apr 2007
Posts: 411
I had the transfer switch inthe inverter burn up using 2 1500 watt heaters when the unit was about 7 yrs old, So to fix the problem I ran 3 new 20 amp #12 wired outlets from the main box just for my winter heater use No hot wires or outlets for past 5 years.
2001 Horizon 2004 jeep GC
autofish is offline   Reply With Quote
Old 02-20-2012, 03:10 AM   #20
Senior Member
SteveSkinner's Avatar
Monaco Owners Club
Join Date: Jun 2011
Location: Montana
Posts: 795
I installed 2 small ceramic heaters in the wet bays which are via inverter. They draw 10 amps between them according to the gauge but only run for a short time because it's only a small area.
Surely if you want to forgo propane use, the easiest way would be to run an extension cord from a second outlet from the post at the camp site. I wouldn't be risking damage.
Also I mistakenly purchased a kettle that keeps the water warm. Ive regularly forgotten to turn it off on departing a campground ( disconnect shore power)
I can tell you the inverter gets angry and finally trips requiring a reset.
It's. It that hard to get to 50 Amps so a second shore power connection seems logical to me
2005 Monaco Signature Castle 1V
2013 Subaru Outback Toad
SteveSkinner is offline   Reply With Quote
Old 02-20-2012, 07:15 AM   #21
Senior Member
trainsktg's Avatar
Join Date: Feb 2011
Location: Pacific NW
Posts: 153
To further muddy the waters, the NEC stipulates that a circuit, unless specifically designed for full amperage use, can only be run at 80% of its rated capacity when using a 'continuous load'. Meaning that a 15 amp circuit can only be run at 12 amps and a 20 amp circuit can only be run at 16 amps, unless its just for a short duration. How long this time period is depends on the load's 'duty cycle'. Don't expect to run a 14 amp load day and night on a 15 amp circuit and not expect problems.

To clarify my earlier statement about using 750/1500W heaters in winter, I ran both at 750 continuous, one in front and one in back, and only ran one or the other at 1,500 if I had to get the place a little warmer, ie shower time.

'99 Bounder 30E with V10 and '06 Wrangler tow (no more dolly )
trainsktg is offline   Reply With Quote
Old 02-20-2012, 08:03 AM   #22
Senior Member
bobmac's Avatar
Winnebago Owners Club
Freightliner Owners Club
Join Date: Mar 2008
Location: Southern Ontario
Posts: 675
We experienced the same problem running two heaters - tripping the 30 amp breaker on the inverter panel. I have a 50amp service, and ended up connecting the second heater in the bedroom to the outlet installed for the washer/dryer (we don't have one) and problem solved.
09 Journey 39Z
Southern Ontario
bobmac is online now   Reply With Quote
Old 02-20-2012, 08:24 AM   #23
Senior Member
George Schweikle's Avatar
Join Date: Apr 2004
Posts: 1,791

I have mentioned the 80% breaker load rating several times, but it's great that you did it again. I worked many years in product design for Square D Company and can offer this:

The National Electric Code (NEC) defines how electrical equipment is installed. Underwriters Laboratories (UL) defines how the equipment is designed and tested. UL has "Hold-in, Trip-out" tables for circuit breakers. This is the duty cycle you mentioned, and has time values for when a breaker must hold or trip at different load and overloads. A residential breaker is actually required to hold 100% of it's rating, but this is tested at 65 degrees ambient temperature. Breakers trip two ways; magnetically for short circuits, and thermally for current overloads. The internal bimetal strip that regulates thermal tripping also creates some heat. Because of this, in the real world application, breaker enclosures / loadcenters will be much hotter than 65 degrees inside the enclosure where the breakers are mounted and this is included in the UL test required for all products. This is why the recommended load is 80% - so the breakers will not thermally "nuisance trip".

Circuit breakers are not designed to protect people, they are to protect wiring and wire insulation. GFI breakers are to protect people. A breaker will trip under a short circuit, or current overload, and should be perfectly safe with a space heater on the circuit - assuming the load is within 80% of the breaker rating.

Originally Posted by trainsktg View Post
To further muddy the waters, the NEC stipulates that a circuit, unless specifically designed for full amperage use, can only be run at 80% of its rated capacity when using a 'continuous load'. Meaning that a 15 amp circuit can only be run at 12 amps and a 20 amp circuit can only be run at 16 amps, unless its just for a short duration. How long this time period is depends on the load's 'duty cycle'. Don't expect to run a 14 amp load day and night on a 15 amp circuit and not expect problems. Keith
George Schweikle Lexington, KY
1999 Safari TREK 2830, FMCA 190830, Safari International chapter
1995 Safari TREK 2630, 1983 Winnebago Chieftain, 1976 Midas Mini
George Schweikle is offline   Reply With Quote
Old 02-20-2012, 08:57 AM   #24
LAT-LON's Avatar
Winnebago Owners Club
Join Date: Apr 2010
Location: Milton, FL
Posts: 91
Having worked for many years as an electrical engineer, I agree with George. He has offered some excellent references and advise on AC breakers.

Winnebago owners can visit the Winnebago/Itasca web site and download the AC Electrical schematics for their coach. These drawings will show which AC outlets in your particular coach are powered via your inverter. In my case only outlets that power the entertainment electronics and one in the cockpit area are powered through the inverter. I haven't visited other manufacturer's web sites, but hopefully they offer this information to their customers as well.
2011 Itasca Suncruiser 32H, Blue OX TigerTrak, Steer Safe
2004 Jeep Wranger
LAT-LON is offline   Reply With Quote
Old 02-20-2012, 09:02 AM   #25
Senior Member
okie-dokie's Avatar
Fleetwood Owners Club
Freightliner Owners Club
Join Date: Nov 2010
Posts: 362
I've been using my space heater every year for the past 3 years with no problems.
however I only use one 1500 watt heater. If I'm on 30 amp shore power. I will use it on the low setting. If I'm hooked up to 50amp. I will use it on the high setting. I am conservative with the other appliances. If my amperage draw is getting close to the 30amp total. I will turn something off.
Bill, enrolled member of Choctaw Tribe. 2005 Fleetwood/Revolution,AFE Filter,Aero Exhaust,Koni FSD shocks,KarKaddy SS. Progressive HW-50C.
okie-dokie is offline   Reply With Quote
Old 02-20-2012, 04:28 PM   #26
Senior Member
CharlieTwo's Avatar
Join Date: Nov 2010
Posts: 232
If you don't have an inverter and just a converter, does any of that apply?
95 Winnebago Brave Sport. 27'
94 33' Fleetwood Wilderness
CharlieTwo is offline   Reply With Quote
Old 02-20-2012, 04:32 PM   #27
Senior Member
Join Date: Sep 2011
Posts: 982
Originally Posted by CharlieTwo View Post
If you don't have an inverter and just a converter, does any of that apply?
A converter does not supply 120v it uses it to convert 120VAC to 12VDC. So basically no except for all the NEC (electric code) discussions above which applies to ALL RVIA certified RVs (which is pretty much all of them).
ottffss is offline   Reply With Quote
Old 02-21-2012, 09:13 AM   #28
Senior Member
Join Date: Oct 2005
Location: Oh.
Posts: 519
Fellows, something is wrong either with my coach or some of the information provided. I did exactly what Gary recommended i.e. turn off the inverter breaker then test all the outlets to see which outlet still has power and that will tell you it does not run off the inverter. Well, all my outlets still worked with the inverter turned off! What gives here??????? Did I do something wrong? Thanks

fun time is offline   Reply With Quote


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
"Made In America" fights back. Possum Just Conversation 71 12-19-2012 09:54 PM
If you are in FL or are coming to FL where will you be? Billieg Camping Locations, Plans & Trip Reports 77 03-26-2012 03:25 AM
Campgrounds in Texas JMJCSIM Texas Boomers 9 02-26-2012 11:29 AM
Battery problems redneckbiker Fleetwood Products Owner's Forum 3 02-20-2012 07:08 AM
Ladder Storage in 99 Chieftain 35U corvettec3 Winnebago Industries Owner's Forum 10 02-19-2012 06:01 AM

» Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities

Copyright 2002-2015 Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 04:59 PM.

Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, vBulletin Solutions, Inc.