Quote:
Originally Posted by epj View Post
I have a Norcold four door unit. I took the motorhome out to the semi local state park the other day when a campsite became available. I did a quick level job which wasn't probably much better than just leaving it alone. Anyway, the refrigerator was popping the GFI. The local repair guys told me to replace the GFI. I will do that when I get to the campground this afternoon. In the meantime, I did a more through job of leveling. Question is, is the unit being out of level a possible cause of the GFI tripping?

That is most generally an indication that the electric heating element has gone bad and is shorting to its metal housing. A quick test is to disconnect the element (two black wires to the control board) and see if it still trips the GFCI.


Sent from my iPad using iRV2 - RV Forum
TravellingRVDoctor, LLC
__________________

__________________
shiggs68 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-24-2015, 08:56 PM   #30
Senior Member
 
Join Date: Feb 2010
Posts: 4,493
Yup...gfi is telling you that you have an issue that needs repair and it refuses to risk your safety until fixed.
__________________

__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 09-25-2015, 04:38 PM   #31
Member
 
the trainguy's Avatar


 
Newmar Owners Club
Nor'easters Club
Join Date: Jul 2014
Location: upstate new york
Posts: 225
Quote:
Originally Posted by Gary RVRoamer View Post
You can also use your meter check for voltage or current in the ground wire. If there is any at all, then the GFCI was just doing its job the way it is supposed to. "Working as designed", they call it.
I'm curious as to how you would do this.
How can you check for current and/or voltage through a grounded ground wire?

Can't check for voltage with the circuit powered up as you'd get 120vac- fairly pointless.

Can't check for current across those same two points with the circuit live or you'll need a new meter.

The only test you can make with the circuit powered down is resistance as no volts/no amps with no power.

Bob
__________________
the trainguy is offline   Reply With Quote
Old 09-25-2015, 05:35 PM   #32
Senior Member
Commercial Member
 
Join Date: Aug 2012
Posts: 608
Refer tripping GFI

Quote:
Originally Posted by the trainguy View Post
I'm curious as to how you would do this.

How can you check for current and/or voltage through a grounded ground wire?



Can't check for voltage with the circuit powered up as you'd get 120vac- fairly pointless.



Can't check for current across those same two points with the circuit live or you'll need a new meter.



The only test you can make with the circuit powered down is resistance as no volts/no amps with no power.



Bob

A GFCI outlet does not check for voltage or current on the ground wire. It simply checks that the current on the hot lead is the same on the neutral lead. If not than the current is leaking somewhere. The leakage could be in the sink to the water.


Sent from my iPad using iRV2 - RV Forum
TravellingRVDoctor, LLC
__________________
shiggs68 is offline   Reply With Quote
Old 09-25-2015, 05:51 PM   #33
Member
 
the trainguy's Avatar


 
Newmar Owners Club
Nor'easters Club
Join Date: Jul 2014
Location: upstate new york
Posts: 225
If the current being used does not match the current being returned(via the neutral) then it has to be draining to ground somewhere.

Air does not conduct electricity ,the ground does.

That makes a properly grounded ground wire a valid test point to check for leakage(ohms) between the load side hot wire and the ground wire .

I wasn't explaining how a gfci device works.

I was explaining how to test the circuit to see whether you actually have a leakage problem or just a faulty gfci.

Bob
__________________
the trainguy is offline   Reply With Quote
Old 09-25-2015, 07:31 PM   #34
Senior Member
 
National RV Owners Club
Join Date: Apr 2012
Location: Virginia Beach Va.
Posts: 110
Send a message via Skype™ to Vaflatlander
I would start my search by checking how many recepticles and appliances are affected by the tripped gfi. Next if it is a recepticle mounted gfi I would diconnect the downstream wire from the back of the gfi . Power that circuit back up and see if it trips, no load,if not see if it trips with a load directly in the gfi., hair dryer or some plug in load. This will tell you if the proplem is the gfi or a downstream fault, and if you inventoried the circuit you now have a check list to follow. Good luck.
__________________
Ed & Sharon Ward ,Virginia Beach, Va.
2000 National RV, 37' Tradewinds
3126 Cat 300hp Allison 6spd Fl xc chassis
Vaflatlander is online now   Reply With Quote
Old 09-26-2015, 08:24 AM   #35
Senior Member
 
FreedomDream's Avatar
 
Join Date: Aug 2012
Location: fulltiming
Posts: 294
Quote:
Originally Posted by Gary RVRoamer View Post
You can also use your meter check for voltage or current in the ground wire. If there is any at all, then the GFCI was just doing its job the way it is supposed to. "Working as designed", they call it.

I've never been able to comprehend why people are so ready to blame a GFCI trip on a faulty GFCI instead of an actual ground fault? Sure, any device can fail, but is it so hard believe that it might also be telling the truth? I chalk it up to ignorance of what a ground fault really is, and why we have GFCI's in the first place.
+1 on "why people are so ready to blame a GFCI trip on a faulty GFCI".
My DW opened the fridge door and a bottle of white wine fell on the ceramic floor and broke. We quickly mopped up the disaster but some of the liquid found its way to the labyrinth of wires below the floor and the next morning I noticed a GFCI trip near where the accident occurred. It would trip a few seconds after resetting. Not connecting the two events, I went and purchased a new GFCI outlet and installed it. It worked. By then my slow little gray cells had put the two events together and I reinstalled the old GFCI outlet. And it worked. The liquid had dried around the place where it caused the short. So it was indeed NOT a bad GFCI.
__________________
Bob & Joan Alexander, 2010 Tiffin Phaeton 36 QSH, 2013 Jeep Wrangler (toad)
Lobo & Juniper (woof, woof)
FreedomDream is offline   Reply With Quote
Old 09-26-2015, 03:59 PM   #36
Senior Member
Commercial Member
 
Join Date: Aug 2012
Posts: 608
Quote:
Originally Posted by the trainguy View Post
If the current being used does not match the current being returned(via the neutral) then it has to be draining to ground somewhere.



Air does not conduct electricity ,the ground does.



That makes a properly grounded ground wire a valid test point to check for leakage(ohms) between the load side hot wire and the ground wire .



I wasn't explaining how a gfci device works.



I was explaining how to test the circuit to see whether you actually have a leakage problem or just a faulty gfci.



Bob

The leakage to ground does not necessarily have to be thru the ground wire. It can leak because of a short thru many paths.

As I indicated before, the most common is the fridges electric heating element is shorted to its mounting bracket. Second most common is the ice maker if you have one. Just unplug the fridge to test if that eliminates the problem.


Sent from my iPad using iRV2 - RV Forum
TravellingRVDoctor, LLC
__________________

__________________
shiggs68 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Tripping GFI Mrfoto iRV2.com General Discussion 6 06-24-2015 06:15 PM
GFI tripping, with inverter and transfer switch pokgunner RV Systems & Appliances 4 05-30-2015 03:50 PM
84' Holiday Rambler, Need help locating GFI Gump Vintage RV's 10 01-24-2015 11:44 PM
No power to refer or hot water tank GlenB RV Systems & Appliances 13 07-16-2014 04:38 PM
BUZZZZZ went the GFI pumper9x9 Country Coach Owners Forum 2 02-23-2014 11:15 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:36 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.