Roof AC problem

Searched this Forum and didn't find much about this. Maybe you AC mechanics will know.

My front roof AC is giving signals that it may be low on freon, I know it's not actually freon now-a-days, but I'll call it that. When it first comes on, after being off overnight, the compressor runs for about 10 seconds and then cuts off. It stays off for 2 minutes and 10 seconds, (compressor delay protector I think) and comes back on and runs for 20 seconds and cuts off, and it stays off for the 2 minutes, 10 seconds, etc. This cycling continues and each time the compressor runs for a little longer period, finally running for up to 1 minute before cutting off, and then it does the cycle routine. When the compressor does run, it blows cold air. I'm thinking it must be low on freon and the pressure switch in the freon line low side cuts the compressor off. The pressure then builds up a bit keeping it running a little longer each time.....up to a minute. It could also be a bad freon level sensing switch. Does anyone know if these AC's have a port for adding freon? Any suggestions or advice? Rook
__________________

__________________
When you get a chance to dance, or sit this one out......I hope you DANCE!

98 National Tradewinds 7370, powered by a 3126B 300HP CAT Turbo, Freightliner XC chassis
Rook is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-05-2012, 02:59 PM   #2
Senior Member
 
87Rockwood's Avatar
 
Vintage RV Owners Club
Join Date: Apr 2012
Location: Looking here and there.
Posts: 732
Does sound like you are low on freon-For the ac mechanics they need make/model numbers.
__________________

__________________
87Rockwood is offline   Reply With Quote
Old 06-05-2012, 03:45 PM   #3
Senior Member
 
Chaffeekid's Avatar
 
Join Date: Dec 2011
Location: Chaffee, MO.
Posts: 397
Hello Rook, yes is it a Coleman or a Dometic, I'm not an AC mech, but I believe those are closed systems, i.e., they don't have a way to add Refrigerant to the system.
I might be wrong on that, have been in the past
I have fixed my dometic by changing out a bad capacitor, and fixed my dash air, but havn't found any way to add refigerant to those systems.
Now I do believe that an AC mech may be able to tap into the low pressure side and add refrigerant to it, beyond my pay grade

Happy Trails
Jim
__________________
MGySgt USMC(R) 1961-1991
2001 Fleetwood Expedition
2013 Jeep Wrangler Sierra Toad
Chaffeekid is offline   Reply With Quote
Old 06-05-2012, 03:59 PM   #4
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 4,383
there is a fix for this, if it is low freon. It is called a piercing valve. They are available from any AC supply co.
I don't think that is your problem. Most R22 freon AC's don't have low pressure switch's. It sounds like a Electrical problem.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2012 Honda Civic toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
ga traveler is online now   Reply With Quote
Old 06-05-2012, 04:03 PM   #5
Senior Member
 
Rook's Avatar
 
National RV Owners Club
Solo Rvers Club
Freightliner Owners Club
Join Date: Mar 2011
Location: FT for 6 years, NW in the summer, S in winter.
Posts: 1,092
Quote:
Originally Posted by 87Rockwood View Post
Does sound like you are low on freon-For the ac mechanics they need make/model numbers.
It's a Dometic "Brisk Air". Don't know the model or product number yet.......haven't been on top yet. Rook
__________________
When you get a chance to dance, or sit this one out......I hope you DANCE!

98 National Tradewinds 7370, powered by a 3126B 300HP CAT Turbo, Freightliner XC chassis
Rook is offline   Reply With Quote
Old 06-05-2012, 04:08 PM   #6
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 4,383
I have been meaning for months to post the piercing valve information, For those who have low freon in a roof AC. One piercing vale is made by Supco. The part number is BPV31. It fits 1/4, 5/16, and 3/8 tubing.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2012 Honda Civic toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
ga traveler is online now   Reply With Quote
Old 06-05-2012, 04:18 PM   #7
Senior Member
 
Jimooo's Avatar
 
Winnebago Owners Club
Join Date: Jun 2011
Location: Amite, La.
Posts: 289
Yep sounds like it is low on freon. Seems to be short cycling and thermal disc is cutting out compressor, The freon is used to cool the compressor motor with thermisters , also it would have tapped to add freon.which is no biggie. Unless you have a bad leak in your evaporator coil.
__________________
Jimooo is offline   Reply With Quote
Old 06-05-2012, 04:27 PM   #8
Senior Member
 
Jimooo's Avatar
 
Winnebago Owners Club
Join Date: Jun 2011
Location: Amite, La.
Posts: 289
I would never use a piercing valve because they will leak as time goes on due to rubber seal rottening on copper tubing, who ever does it tell them to put you a tap which is permanent and will not leak over time. Hope this helps you.
__________________
Jimooo is offline   Reply With Quote
Old 06-05-2012, 04:52 PM   #9
Moderator Emeritus
 
Mike Canter's Avatar


 
Join Date: Apr 2008
Location: Freeport, ME
Posts: 4,707
It would be very unusual for a roof AC unit to lose freon. They are a hermetically sealed system such as used in a refrigerator, or a window AC unit. They are sealed 100% at the factory. Not saying that it is impossible but most unlikely. The compressor sits inside a sealed tank. This is not like a car AC system that has shaft seals or rubber hoses and couplings and such. If it did leak then there is no point in just putting in freon without fixing the leak. My guess it is some other problem and you would probably save money by having a professional look at it before breaking into that sealed system.
__________________
Mike Canter
"Gunner" USN Retired, Airdale
2004 Monaco Signature 44' Conquest. Detroit 60
Mike Canter is offline   Reply With Quote
Old 06-05-2012, 05:54 PM   #10
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 17,150
Blog Entries: 21
Better than 90% of the A/C problems are NOT low on Freon, but tat is usually the first thing a novice will come up with. As noted, the units are hermetically sealed and there is no place for the refrigerant to leak out unless you have a line crack, a pin hole develop or physically damage the unit.

Start by pulling the inside cover and check the evaporator for dirt and lint. The air filters need to be cleaned about every 14 days of use. Next get a volt meter and an amp meter and check the volts and amps at the compressor.

Next, you may have a start capacitor that may be going bad. They can be checked, but it takes a special meter. Capacitors are pretty inexpensive, so you might pick one up and change it.

Low voltage (below 108 volts) and a bad start capacitor can keep you from starting.

The last thing is the unit is 14 years old by the age of your coach. It may have a compressor going bad and time to replace it.

Generally, that age unit is not worth the cost of properly recharging it. The piercing valve, more commonly called a saddle clamp or saddle valve will leak. It is not a matter of if, but when. They are a temporary fix and used to diagnose a problem. The unit needs to be completely evacuated, purged with nitrogen and Schrader valves soldered into the lines for a proper fix. Then the unit need to be evacuated and recharged with refrigerant. You will spend half the cost of a new unit unless you can do the work yourself.

Ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is offline   Reply With Quote
Old 06-05-2012, 07:28 PM   #11
Senior Member
 
Rook's Avatar
 
National RV Owners Club
Solo Rvers Club
Freightliner Owners Club
Join Date: Mar 2011
Location: FT for 6 years, NW in the summer, S in winter.
Posts: 1,092
Rethinking the problem

Thanks for all the comments.....some good points have been stated, causing me to rethink the problem.

1) I didn't realize that the system was "hermetically sealed"......thereby making the loss of refrigerant very unlikely. There is no physical damage, either. And.... there is no "low-side" pressure switch in these units, so that's not what's cutting the compressor off after 10 seconds.
2) The compressor starts easily....but initially only runs for about 10 seconds and then "something" cuts it off! Then after 2 minutes 10 seconds (the fixed period compressor delay), it starts right up again and runs for about 20 seconds and then "something" cuts it off! And.....eventually it will run for up to a minute before "something" cuts it off. That does not sound like a starting capacitor would cause this. Could it?
3) So. what is the "something"? Question: What else besides the thermostat has the ability to cut the compressor off? Rook
__________________
When you get a chance to dance, or sit this one out......I hope you DANCE!

98 National Tradewinds 7370, powered by a 3126B 300HP CAT Turbo, Freightliner XC chassis
Rook is offline   Reply With Quote
Old 06-05-2012, 07:38 PM   #12
Senior Member
 
Jeff753's Avatar


 
Monaco Owners Club
Coastal Campers
Join Date: Mar 2012
Posts: 1,681
It would be worth checking, if you have floor ducting, a rug over a vent can cause short cycles


Quote:
Originally Posted by Rook
Thanks for all the comments.....some good points have been stated, causing me to rethink the problem.

1) I didn't realize that the system was "hermetically sealed"......thereby making the loss of refrigerant very unlikely. There is no physical damage, either. And.... there is no "low-side" pressure switch in these units, so that's not what's cutting the compressor off after 10 seconds.
2) The compressor starts easily....but initially only runs for about 10 seconds and then "something" cuts it off! Then after 2 minutes 10 seconds (the fixed period compressor delay), it starts right up again and runs for about 20 seconds and then "something" cuts it off! And.....eventually it will run for up to a minute before "something" cuts it off. That does not sound like a starting capacitor would cause this. Could it?
3) So. what is the "something"? Question: What else besides the thermostat has the ability to cut the compressor off? Rook
__________________
Jeff
2001 Monaco Dynasty tag axle
2006 Jeep Wrangler
Jeff753 is offline   Reply With Quote
Old 06-05-2012, 07:49 PM   #13
Senior Member
 
Rook's Avatar
 
National RV Owners Club
Solo Rvers Club
Freightliner Owners Club
Join Date: Mar 2011
Location: FT for 6 years, NW in the summer, S in winter.
Posts: 1,092
Quote:
Originally Posted by Jeff753 View Post
It would be worth checking, if you have floor ducting, a rug over a vent can cause short cycles
The ducting is in the roof and also used by the rear AC......and the rear AC works just fine. Initially, the Compressor does not run long enough (10 seconds, 20 seconds, etc.) to get anything hot! Rook
__________________
When you get a chance to dance, or sit this one out......I hope you DANCE!

98 National Tradewinds 7370, powered by a 3126B 300HP CAT Turbo, Freightliner XC chassis
Rook is offline   Reply With Quote
Old 06-05-2012, 08:09 PM   #14
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 17,150
Blog Entries: 21
Rook have you check the amps and volts and compared them to the rear A/C?

ken
__________________

__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is offline   Reply With Quote
Reply

Tags
roof



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:58 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.