Well, you learn something new every day. From a discussion of the same topic on another forum, I found the Minnesota Electrical Code is available on line in a number of formats, including as a PDF, On-Line Reader (Better than the one used by the NEC), Text, Kindle, etc. Since it is based on the 2008 NEC with additions be the state, and includes the 2008 version of the NEC, it is an easier way to view the code.

Minnesota Electrical Code
__________________
Jon Vermilye
vermilye is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-31-2010, 09:30 AM   #30
Senior Member
 
Monaco Owners Club
Join Date: Jul 2004
Posts: 1,386
I agree with installing 50amp but may I suggest something else to consider while the ditch is open. This may apply more to winter situations, I know you said you would not be there, but could also help at other times of the year. Run another cable that would allow your generator to connect with a transfer switch providing power to the house during power outages. I didn't think of this until after my 50amp installation was done.
__________________
Bob Russo
Formerly had 07 Neptune 36PDQ, ISB 325, Allison 2500, Source Trailing Arms and Ride Enhancement Kit, Demco KarKaddy 460SS.
Currently no Motorhome
Nonno is offline   Reply With Quote
Old 08-31-2010, 02:02 PM   #31
Registered User
 
Newmar Owners Club
Join Date: Nov 2008
Posts: 2,899
OK - First if the power in the house/barn is there enough spare amps to support it. If so do the 50AMP receptacle.

Next RV's are different when hooking up RV plug than a regular home, so you must make sure the electrician knows the differences, because if it's not wired correctly, you can fry all your coaches’ electrical systems.

http://www.myrv.us/electric/ - See this link and understand it well.

This link explains the differences, so I will try not to confuse his description. Just remember the ground and neutral do NOT BOND in the RV. They bond at the pedestal (shore power post in RV park) or in this case at the electrical panel where the power comes from. If you run separate line from street, you will also need a new meter base, etc, pay an additional meter reading charge, and maybe more.

Hope this helps.
Renipladlo is offline   Reply With Quote
Old 08-31-2010, 06:15 PM   #32
Senior Member
 
Jocat54's Avatar
 
Monaco Owners Club
Join Date: Oct 2008
Location: Leakey, Tx (Texas Hill Country)
Posts: 109
Quote:
Originally Posted by JohnQ View Post
I just completed the job you are contemplating. The concern for the "Supplying Panel" is spot on, make sure that when you are installing the subpanel (that is what you are installing), the main panel has the "Juice" to coin a pun. I came out of my Main Panel with a 50 AMP 220 Breaker. The wire is 10/3 UF, no need for conduit, 105 feet to a "Mallard RV Subpanel" that I had one of the 220 hot leads (makes it a 110) to a 110 30 amp RV plug, and the other 220 hot lead feeds my wife's green house thereby killing 2 birds with one stone and a lotta Wifey Brownie points. I would also suggest that since you have a trench dug & open you also install a water line with a Frost Proof faucet (if you are in Southern Maxisnowta, and forget it if you are in Nordern Maxisnowta - Born and raised in Burrrrrrrrrrmidji). The 30 amp service is more than adequate for my coach here at home (hardly ever need a/c).

Hi John,
Am I reading this wrong? 10/3 is only good for 30 amps and you have a 50 amp breaker on the line? Not meaning to start anything here--it just caught my eye when I read the post.

John
__________________
John & Kathy & Gizmo (Maltipoo)
1999 38ft Monaco Diplomat DP
Jocat54 is offline   Reply With Quote
Old 09-01-2010, 07:15 AM   #33
Junior Member
 
Join Date: Nov 2008
Posts: 26
One thing to consider when you look at the available service, if it will not support 50 amp service, you can consider installing 30 amp service (4 wire) wired like it was a 50 amp service. 30 amp two pole breaker, smaller wire, 50 plug outside. Still can put a 20 amp recepticle outside. Remember most generators only put out 120 volts from two windings. For 7.5 kW generator, each winding is only good for 31 amps, for a total of 62 amps. What size is your generator and what size are the output breakers?

I have 50 amp service in the RV and use the 30 amp method at home. I could pull the wires out of the conduit to the garage, put in new wires (legal fill in conduit), and put an outlet in the garage. Garage now has 240/120 Volt, 30 amp service.
__________________
2003 Fleetwood Discovery 39S
2011Cadillac SRX
vectra96 is offline   Reply With Quote
Old 09-01-2010, 08:04 AM   #34
Moderator Emeritus
 
RickO's Avatar


 
Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 10,530
Quote:
Originally Posted by vectra96 View Post
One thing to consider when you look at the available service, if it will not support 50 amp service, you can consider installing 30 amp service (4 wire) wired like it was a 50 amp service. 30 amp two pole breaker, smaller wire, 50 plug outside. Still can put a 20 amp recepticle outside. Remember most generators only put out 120 volts from two windings. For 7.5 kW generator, each winding is only good for 31 amps, for a total of 62 amps. What size is your generator and what size are the output breakers?

I have 50 amp service in the RV and use the 30 amp method at home. I could pull the wires out of the conduit to the garage, put in new wires (legal fill in conduit), and put an outlet in the garage. Garage now has 240/120 Volt, 30 amp service.
Thanks Vectra. Actually, this may be the best approach for me but I'll wait to see what I find when I can inspect the panel. If nothing else it could provide an option to use 6/3 grounded wire rather than 4/3. I had heard others refer to this option in the past but didn't understand it until these past few days of education.

Is your reference to the generator to make the point that this approach with 30 amp would provide virtually the same power? Mine is an Onan 8000.
__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
RickO is offline   Reply With Quote
Old 09-01-2010, 09:15 AM   #35
Junior Member
 
Join Date: Nov 2008
Posts: 26
Yes, for the generator at 8 kW, you get 33.5 amps per side available. You could even consider a 35 amp main breaker because of the larger cabling, due to voltage drop.
__________________
2003 Fleetwood Discovery 39S
2011Cadillac SRX
vectra96 is offline   Reply With Quote
Old 09-03-2010, 07:50 AM   #36
Senior Member
 
Bob86ZZ4's Avatar
 
Join Date: Feb 2009
Location: St. Paul, MN
Posts: 412
Rent a trencher. You want to go at least 18", better to go 2'. Easy work with a rented trencher. Except the rocks and roots will slow you down. I'm in St. Paul if there's anything I can do to help. I'd even come out and set up a lawn chair to cheer you on from. If you're close to the cities I've got a buddy that's a licensed electrician too. Might be able to get him to come out if not too far.
__________________
www.bobwinsor.com
MN is home for now.
Bob86ZZ4 is offline   Reply With Quote
Old 09-03-2010, 08:22 AM   #37
Moderator Emeritus
 
RickO's Avatar


 
Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 10,530
Thanks so much Bob but we're near Windom... about 180 miles from you. My FIL has an electrician who wired the new barn he put up and I'm going to talk to him about the job. thanks again...
__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
RickO is offline   Reply With Quote
Old 09-03-2010, 08:37 AM   #38
Senior Member
 
Join Date: Jul 2000
Posts: 4,034
I am about to install a 50 amp service as well. A few cautions. #10 wire is way too small if you are going to run any heaters or AC. The receptacle that one poster suggested is correct but with one caveat. You should have a disconnect close to the receptacle as you should never connect or disconnect your rv from a live circuit. You can buy the box with a 50 amp and a 20 amp receptacle complete with breakers at Home Depot online for $109.00.
__________________
Moisheh
2008 Dynasty 42' Diamond IV
1988 Bluebird PT38
2009 Silverado Toad
moisheh is offline   Reply With Quote
Old 09-03-2010, 06:46 PM   #39
Senior Member
 
OneRVer's Avatar
 
Triple E Owners Club
Join Date: Aug 2010
Location: Pacific Northwest
Posts: 732
50 amp. You will have to run a insulated ground wire, neutral wire, and two hot wires from the main breaker. At the new panel you have to have a ground rod connected to the new panel. Keep the Neutral bar/bus isolated from the GROUND bar/bus and connect the ground rod to this ground bar. If you do not do this, you will have a ground loop which will cause problems. In the new panel connect the insulated ground wire and the neutral wire to the neutral bar. Connect all white wires, neutral, to the neutral bar, connect all green or bar wires, ground, to the ground bar. DO NOT MIX GROUND WIRES WITH NEUTRAL WIRES. If you do this mixing and have it inspected by L & I you will have to start all over. Not Good.

Question: Is your motor home set up for 50 amp service or 30 amp service. I am assuming your home is set up for 50 amps.

For a 100 foot run I would not go any smaller then 2 ga copper. In the box I believe 8 ga. for 50 amp and 10 ga. for 30 amp.

These cable must be at least 24" deep. 36" deep if you have them buried where you can drive over it. Unless in that area you have the cable's run thru a conduit, then 24" is alright.

I hope I covered it all. Good Luck.

I also recommend this panel. It is all set up and the ground bar and neutral bar are already separeted. Connecticut Electric 60 Amp RV Panel with 50A Receptacle, Breakers & GFCI Duplex - CESMPSC55GRHR at The Home Depot
__________________
1997 Triple E Empress, Freightliner Chassis, CAT 3126 w/ 275 horse's.
MD 3600 Tranny, 2011 Ford Escape Hybrid w/Blue Ox tow bar and Roadmaster Base Plate.
Amsoil Synthetic Oil only for my baby.
OneRVer is offline   Reply With Quote
Old 09-03-2010, 07:52 PM   #40
Senior Member
 
Join Date: May 2004
Location: Auburn, CA, Havasu, AZ & Mulege, BCS
Posts: 5,385
I've used this panel twice now. gives me options to connect either a 30 or 50A cord direct w/no adapters, plus the 20A GFI all in one. Feed it from a 50A 2 pole breaker since you don't connect more than one RV at a time.

#2 wire for 100 foot 50A run is overkill. #4 would be more than adequate keeping volt drop to less than 3%. Truthfully an RV could live nicely w/a 5% drop which would be #6, assuming your original house voltage is better than 115V.
__________________
Baja-tested '08 2-slide 36'
Alpine: The Ultimate DIY'er Project
EngineerMike is offline   Reply With Quote
Old 09-03-2010, 10:53 PM   #41
Senior Member
 
OneRVer's Avatar
 
Triple E Owners Club
Join Date: Aug 2010
Location: Pacific Northwest
Posts: 732
Quote:
Originally Posted by EngineerMike View Post
I've used this panel twice now. gives me options to connect either a 30 or 50A cord direct w/no adapters, plus the 20A GFI all in one. Feed it from a 50A 2 pole breaker since you don't connect more than one RV at a time.

#2 wire for 100 foot 50A run is overkill. #4 would be more than adequate keeping volt drop to less than 3%. Truthfully an RV could live nicely w/a 5% drop which would be #6, assuming your original house voltage is better than 115V.
Yep, that is the same panel I installed w/an 80 amp breaker at the main panel. Ran 1 ought aluminum.
I am sure you are right. I have a problem of always over killing when it comes to electricity. Always pay more then what I should also. But I do feel safer going this route. Also during during family reunions I end up using both the 30 and 50 amp breakers.
__________________
1997 Triple E Empress, Freightliner Chassis, CAT 3126 w/ 275 horse's.
MD 3600 Tranny, 2011 Ford Escape Hybrid w/Blue Ox tow bar and Roadmaster Base Plate.
Amsoil Synthetic Oil only for my baby.
OneRVer is offline   Reply With Quote
Old 09-04-2010, 08:06 AM   #42
Registered User


 
Monaco Owners Club
Join Date: May 2009
Posts: 3,198
Quote:
Originally Posted by RickO View Post
Thanks so much Dirk... that's perfect. I was surprised to see that the wire sizing chart calls for #4 wire for a 120v 50amp 100 foot run though. Hmmmm.... they seem to call for a much heavier wire that most on this thread have proposed.
ok good, nothing like some accurate reference material.

I did 50 amp 220 circuits for both an inground pool and a hot tub. (2 complete circuits) Used 6 guage wire, longest run was 30 feet.

The 10 gauge mentioned in other posts is WAY TOO SMALL for 50 amp, even for a 10 foot run. A hundred feet plus, you need some BIG wire.

It will cost you a grand for enough 4 conductor 4 gauge to reach 150 feet.

You "may" be able to skip the 4rth conductor. We did with the pool / hot tub. Oddly, code for a house says one and only one ground, at the main panel, everything else grounded off of that, but code for a pool says a separate bonding wire with a ground rod 10 feet into the ground.

So the cable coming out of the house is 2 hots and a neutral. (times 2)
JimM68 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 amp power versus 50 amp question Paul T Winnebago Industries Owner's Forum 17 07-14-2010 06:53 AM
30 amp power tedward1555 iRV2.com General Discussion 8 06-23-2010 06:13 PM
Power Inverter install? cgau Damon 3 04-20-2010 07:46 PM
1996 Adventurer--running both A/C from shore power DannyLong Winnebago Industries Owner's Forum 7 08-29-2006 11:04 AM