Strange breaker problem

I have a 85 Elandan 31' with a 30 amp system. The breaker problem I am having is the 15amp breaker that supplies power to the water heater "trips" when not in use??? If i plug in the water heater and or any other appliances, it works fine as long as it has a load on it. It trips when everything is unplugged with no load. I made sure there is no load with my multimeter. It does not trip right away but at various times(sometimes 2 minutes and up to 20 minutes after everything is unplugged. That breaker also supplies power to the outside 110 receptacles and If I plug in, say a drill or a light. it will trip the breaker immediately even though the drill or light is turned off and causing no load.
Anyone have any advise on what to do about this?
Thanks in advance, Cappy
__________________

__________________
Cappy58 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-03-2014, 06:43 PM   #2
Senior Member
 
gemini5362's Avatar
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Apr 2012
Posts: 2,078
this is a very weird problem. Not sure what it could be. The tripping when no load applied is pretty much impossible. You have to have current going through the breaker to trip it unless the breaker is bad and that would trip even when something is plugged into it. I would first remove power to the camper. I would then take my multimeter and check for a short to ground from either the neutral line or the hot line. I do not see how that could be the problem you are seeing but the fact that when you plug something else into the outside receptacles it trips immediately whether or not they are turned on makes me think the wiring to them has a short that when you plug something in it makes a complete path to the hot and tripping the breaker.
__________________

__________________
gemini5362 is offline   Reply With Quote
Old 02-03-2014, 06:48 PM   #3
Senior Member
 
Sammie's Avatar
 
Tiffin Owners Club
Join Date: Jun 2006
Location: Southern California
Posts: 1,779
Sounds like you might have a bad plug outlet or GFI outlet gone bad.

Sammie
__________________
2015 Tiffin Bus 37AP
2016 Ford Explorer
"A Job Begun is Half Done"
Sammie is offline   Reply With Quote
Old 02-03-2014, 06:58 PM   #4
Junior Member
 
Cappy58's Avatar
 
Join Date: Jun 2013
Posts: 29
Thanks. I am going to pull apart the outside receptacle in the morning and replace it and check the wires as well. I am an experienced electrician somewhat but have never experienced a breaker tripping without a load on it. I will update as soon as I replace the outlet.
Thanks again
__________________
Cappy58 is offline   Reply With Quote
Old 02-03-2014, 07:28 PM   #5
Community Moderator
 
"007"'s Avatar


 
Nor'easters Club
Workhorse Chassis Owner
iRV2 No Limits Club
Join Date: Oct 2004
Posts: 26,804
Outside outlets when they get wet and if they have a sponge seal that holds water the wiring will corrode and short and possibly trip a GFI outlet usually feeding it.
__________________
98KSCA, 99MACA, 03 KSCA-3740- 8.1 Chev-- ALLISON Trans, now in good hands
VISIT the NEWMAR QUICK TIPS & EASYMODS 1 & 2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS --- TECH INFORMATION
"007" is offline   Reply With Quote
Old 02-03-2014, 07:29 PM   #6
Member
 
Spizzer's Avatar
 
Join Date: Sep 2013
Posts: 97
Try swapping the breaker out for one of the other ones to see if the problem moves with it.

Jeff
__________________
Spizzer is offline   Reply With Quote
Old 02-03-2014, 07:54 PM   #7
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 11,803
Quote:
Originally Posted by Spizzer View Post
Try swapping the breaker out for one of the other ones to see if the problem moves with it. Jeff
Agree. Swap around the breaker or load circuit wire and see if the problem moves or not and go from there.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 02-03-2014, 08:12 PM   #8
Senior Member
 
Join Date: May 2004
Location: Auburn, CA, Havasu, AZ & Mulege, BCS
Posts: 5,217
I'm guessing the breaker trips with the rig plugged in but no loads (rather than rig unplugged & therefore no electricity), based on description of plugging loads into exterior plug on rig.

I'd suspect an intermittent short between hot & ground or hot & neutral, and that its related to the outside outlet(s). Its acting like the interior load subtends the draw on the circuit so the tweaky action at the potential short isn't contacting to cause the trip, but if you get more directly to the area of the short (which might be in one of the ext. outlets or in that part of the circuit) then you get a solid trip.

If the coach is unplugged & the breaker trips, then either 1) there is a discharging capacitor in the AC circuit (I doubt this), 2) somebody's messing with you, or 3) you have a ghost messing with you.
__________________
Baja-tested '08 2-slide 36'
Alpine: The Ultimate DIY'er Project
EngineerMike is offline   Reply With Quote
Old 02-04-2014, 10:21 AM   #9
Senior Member
 
Stealth01's Avatar


 
Newmar Owners Club
Join Date: Jun 2013
Location: MidWest
Posts: 817
From what you're describing, you must have a GFCI breaker that's popping. If in deed it's a GFCI, they can be finicky OR you have a low amplitude leak (to ground) in the circuit. First, I'd replace the GFCI breaker. If it repeats then you're going to have to find where you have a leak to ground. I would star with the hot water circuit!
__________________
Ken & Anita 2011 Newmar Essex,4522,Cummins 500 ISM,2013 CRV,RVI2 Brake with TPMS **Our Travel WebSite**
<a href=https://i1129.photobucket.com/albums/m512/kengallagher/copper_a_zps0e12153d.jpg target=_blank>https://i1129.photobucket.com/albums...ps0e12153d.jpg</a>
Stealth01 is offline   Reply With Quote
Old 02-04-2014, 11:58 PM   #10
Member
 
Spizzer's Avatar
 
Join Date: Sep 2013
Posts: 97
Quote:
Originally Posted by Stealth01 View Post
From what you're describing, you must have a GFCI breaker that's popping. If in deed it's a GFCI, they can be finicky OR you have a low amplitude leak (to ground) in the circuit. First, I'd replace the GFCI breaker. If it repeats then you're going to have to find where you have a leak to ground. I would star with the hot water circuit!
If it is the GFCI tripping, why would the breaker feeding it pop? If anything, it seems it could be a GFCI that has a fault and is not tripping but shorting to ground. If there is a GFCI in the circuit in question, I would trip it with the test button, and then see if that changes the problem. If the test button does not trip it, then remove it and see if all is normal.

Jeff
__________________
Spizzer is offline   Reply With Quote
Old 02-05-2014, 01:22 AM   #11
Junior Member
 
Join Date: Sep 2012
Posts: 28
Breakers can get 'weak' with age. Try swapping it out with a good one and see if that solves the problem. You can also get a feel of the breaker by cycling it, then do the same on another known good one. Do they feel the same, or does one feel 'mushy' A mushy breaker is weak, thus bad and needs replacement.
__________________
Richardk is offline   Reply With Quote
Old 02-05-2014, 11:45 AM   #12
Senior Member
 
Stealth01's Avatar


 
Newmar Owners Club
Join Date: Jun 2013
Location: MidWest
Posts: 817
Quote:
Originally Posted by Spizzer View Post
If it is the GFCI tripping, why would the breaker feeding it pop? If anything, it seems it could be a GFCI that has a fault and is not tripping but shorting to ground. If there is a GFCI in the circuit in question, I would trip it with the test button, and then see if that changes the problem. If the test button does not trip it, then remove it and see if all is normal.

Jeff
Jeff,
There are multiple ways to protect a circuit.. one method is a GFCI "outlet" that protects a number of outlets in a daisy chain circuit... OR, you can use a GFCI breaker, where the GFCI protection is built into the breaker. Since the breaker in question is feeding a hot water tank, I'm assuming (yes I know a dangerous thing to do) but I'm assuming the breaker protecting the water tank is a GFCI breaker. My experience with these type breakers is they are VERY FINICKY and have a high failure rate.
__________________
Ken & Anita 2011 Newmar Essex,4522,Cummins 500 ISM,2013 CRV,RVI2 Brake with TPMS **Our Travel WebSite**
<a href=https://i1129.photobucket.com/albums/m512/kengallagher/copper_a_zps0e12153d.jpg target=_blank>https://i1129.photobucket.com/albums...ps0e12153d.jpg</a>
Stealth01 is offline   Reply With Quote
Old 02-05-2014, 11:40 PM   #13
Member
 
Spizzer's Avatar
 
Join Date: Sep 2013
Posts: 97
Quote:
Originally Posted by Stealth01 View Post
Jeff, There are multiple ways to protect a circuit.. one method is a GFCI "outlet" that protects a number of outlets in a daisy chain circuit... OR, you can use a GFCI breaker, where the GFCI protection is built into the breaker. Since the breaker in question is feeding a hot water tank, I'm assuming (yes I know a dangerous thing to do) but I'm assuming the breaker protecting the water tank is a GFCI breaker. My experience with these type breakers is they are VERY FINICKY and have a high failure rate.
Aah!! Now that makes a lot more sense. If the breaker is indeed a GFCI then I would put my money on that being the culprit. I was thinking just one of the outlet GFCIs.

Thanks for the explanation.

Jeff
__________________
Spizzer is offline   Reply With Quote
Old 02-06-2014, 12:51 PM   #14
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,829
How to tell if a breaker is a GFCI or not.

Does it have a TEST button on it? IF so, GFCI.
__________________

__________________
wa8yxm is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dash warning light/ignition problem BCCanuk Monaco Owner's Forum 15 02-04-2014 08:01 AM
Fridge Problem Rossi6998 Winnebago Industries Owner's Forum 22 01-10-2014 09:02 AM
Help, tripped a breaker somewhere Rusty years Class A Motorhome Discussions 9 12-11-2013 01:08 AM
Inverter install problem captd RV Systems & Appliances 1 11-19-2013 05:41 PM
Please help! New fulltimer with distressing electrical problem! ocipura Class A Motorhome Discussions 67 09-18-2013 02:41 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 12:00 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.