Thermostat or furnace ??????

Happy New Year to all !!!!!

We left home in -17f a couple weeks ago and since the dash heat wasn't enough I started the furnace and she ran all the way till evening. She ran for about 10 hrs. the next day all was fine, no furnace running. 2 days after while driving, the smoke alarm went off, what a nerv wracking for a few seconds while wife went to look. I stopped the MH in a secure area and didn't smell smoke but realize that fan on furnace was running. Thermostat was on position with all on off modes but fan kept running. I switched the under slid button to off and it didn't stop. I had to unplug the wires from heater. Now if I turn the under switch to on and put furnace on only blower goes on but no flame. If I turn selection to Off and under switch to off, fan won't stop without unplugging the wires from furnace.

Would it be a thermostat problem or furnace ??????

I have the 5 button Comfort Control thermostat and a Hydro Flame 8520IV furnace.

All other functions ( heat pump front and back, AC front and back,rear heat) seems to work OK

1- Can I do a Thermostat reset ???? Is it do-able ???? Will I loose all other functions ????

2- Would it be a burner problem on furnace ????? Why doesn't it shut down with remote???

3- The smoke detector going off, ( right above thermostat) would it be the thermostat shorted out only on one section (furnace) ???



Any input would be greatly appreciated
__________________
Roger & Lynne
2006 Mandalay 40 F 2232 400 ISL Allison 3000
2007 Toyota Camry SE Toad 4 down
High Ball is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-01-2018, 07:58 AM   #2
Senior Member
 
WeatherTodd's Avatar
 
Monaco Owners Club
Workhorse Chassis Owner
Join Date: Nov 2009
Posts: 1,363
check the control board and the propane fitting.
WeatherTodd is offline   Reply With Quote
Old 01-01-2018, 08:09 AM   #3
Senior Member
 
FatChance's Avatar
 
Join Date: Mar 2015
Posts: 2,984
Is there propane in the tank?
__________________
'04 Newmar Mountain Aire 4016
400ISL/Freightliner
FatChance is offline   Reply With Quote
Old 01-01-2018, 08:16 AM   #4
Senior Member
 
Triker56's Avatar
 
Fleetwood Owners Club
Join Date: Jun 2009
Posts: 4,031
If you left a couple weeks ago and headed south.
You should no longer need to use a furnace. And be in a warm area that only the AC is needed.
Or you are driving too slow every day.
__________________
99 Discovery 34Q ISB
2014 MKS AWD EcoBoost Toad
Fulltime Since "99"
Triker56 is offline   Reply With Quote
Old 01-01-2018, 08:44 AM   #5
Senior Member
 
Join Date: Nov 2017
Location: Citra, Florida
Posts: 1,396
Quote:
Originally Posted by Triker56 View Post
If you left a couple weeks ago and headed south.
You should no longer need to use a furnace. And be in a warm area that only the AC is needed.
Or you are driving too slow every day.
You kidding we are in Ocala Fl. and it is in the forties
__________________
Good Luck and keep us posted please. "Q"
1999 Newmar, Mountain Aire 3768, V-10, CAI, Headers.
"Spending our kids inheritance one trip at a time"
Quincy is offline   Reply With Quote
Old 01-01-2018, 08:50 AM   #6
Senior Member
 
Join Date: Nov 2017
Location: Citra, Florida
Posts: 1,396
The short answer is with all the pc boards and electronic controllers connected to the furnaces nowadays who knows what the problem could be.

Now after relieving your stress with the above comment... I believe it could be the stat or the furnace ie, fan relay (someone posted a while ago that some units use a sail switch on even newer rigs.) Stat could be shorted or the wiring could also be shorted, which is really unlikely.Just give the blower motor time to shut off as it does not go off when the stat is satisfied but after it has removed all the warm air from the ducts.

Good luck and keep us posted.
__________________
Good Luck and keep us posted please. "Q"
1999 Newmar, Mountain Aire 3768, V-10, CAI, Headers.
"Spending our kids inheritance one trip at a time"
Quincy is offline   Reply With Quote
Old 01-01-2018, 08:50 AM   #7
Senior Member
 
OLYLEN's Avatar
 
Monaco Owners Club
Join Date: Jan 2008
Location: Olympia, Wa
Posts: 2,772
How is the battery level, charge? With the alarm going off low voltage? As to the furnace take the thermostat off the wall unplug and telling. Do the same with all connections at furnace also. A reset might help also and should not affect operation.

LEN
__________________
2004 Clss C 31' Winnebgo
OLYLEN is offline   Reply With Quote
Old 01-01-2018, 08:56 AM   #8
Senior Member
 
tmw188's Avatar
 
Monaco Owners Club
National RV Owners Club
Workhorse Chassis Owner
Join Date: Dec 2013
Location: St. Charles MO
Posts: 4,920
Send a message via AIM to tmw188
Thermostat or furnace ??????

Turn off the 12v power to the house that should turn off that fan, then turn the 12v power back on again and that should at least cancel out that fan, sort of a reset. If the fan comes back on it could be the stat or a relay whatever controls that. Then try to do a start up again with the furnace to see what happens. If that doesn't work maybe a flame sensor? Look in your manual for trouble shooting.
__________________
2002 Monaco Windsor 40PST 2019 Equinox 1.5L, Blue OX Aventa LX tow bar, Roadmaster EZ5 baseplate, SMI Stay-In-Play Duo, TireSafeGuard TPMS
tmw188 is offline   Reply With Quote
Old 01-01-2018, 11:52 AM   #9
Senior Member
 
High Ball's Avatar
 
Join Date: Nov 2014
Location: Ottawa, Ontario, Canada
Posts: 177
Thanks to all for the replies.
yes propane tank is at 3/4 and all others propane appliances are working
I have enough voltage 12.8-13
I did shut off main power, un plug thermostat, re tried and same thing. No flame and blower keeps on running.
I took outside panel off, took main board partially off and un plug all wires, re plug, play tried to see if some of resistors, relays and other things on board if they were slack and re install board. Can't seem to find sail switch by following wires.
tried furnace again twice and for now all seems good.
bring temp up, furnace and burner starts, bring temp down , burner off and blower off.
guess if I have further problems it will be time for new card.

thanks again for all info, Greatly appreciated.
__________________
Roger & Lynne
2006 Mandalay 40 F 2232 400 ISL Allison 3000
2007 Toyota Camry SE Toad 4 down
High Ball is offline   Reply With Quote
Old 01-01-2018, 12:15 PM   #10
Senior Member
 
Pepper2's Avatar
 
Winnebago Owners Club
Join Date: Nov 2011
Location: Seeing the USA
Posts: 2,646
Pulling the wires off the terminals and reinstalling them may have cured a poor contact on one of them.

We are in the RGV and woke up to 36 degree temps. Brrr...
__________________
Neal and Deb + Mya and Gizmo, the pup's
2003 Winnebago Sightseer 30B

May the roads rise up to meet you, May the winds be always at your back...
Pepper2 is offline   Reply With Quote
Old 01-01-2018, 01:50 PM   #11
Senior Member
 
tmw188's Avatar
 
Monaco Owners Club
National RV Owners Club
Workhorse Chassis Owner
Join Date: Dec 2013
Location: St. Charles MO
Posts: 4,920
Send a message via AIM to tmw188
You have an Attwood furnace correct? Do you have the manual for it?


Sent from my iPhone using iRV2 - RV Forum
__________________
2002 Monaco Windsor 40PST 2019 Equinox 1.5L, Blue OX Aventa LX tow bar, Roadmaster EZ5 baseplate, SMI Stay-In-Play Duo, TireSafeGuard TPMS
tmw188 is offline   Reply With Quote
Old 01-02-2018, 06:00 AM   #12
Senior Member
 
Join Date: Nov 2017
Location: Citra, Florida
Posts: 1,396
Sorry I misread your post the first time about no flame. I would pay close attention to the control board since it seems like two different failures at the same time, If you can get a picture or at least a good look at the back of the board you might see a small yellow spot where the board got hot enough to damage the circuit.

keep us posted please.
__________________
Good Luck and keep us posted please. "Q"
1999 Newmar, Mountain Aire 3768, V-10, CAI, Headers.
"Spending our kids inheritance one trip at a time"
Quincy is offline   Reply With Quote
Old 01-02-2018, 02:34 PM   #13
Senior Member
 
High Ball's Avatar
 
Join Date: Nov 2014
Location: Ottawa, Ontario, Canada
Posts: 177
Since we are going to get a few nights of under 40 decided to try furnace today and same symptoms. Played with wires and stuff on board but just blower goes on and won't stop until I unplug main one on furnace. Just order new Electronic board for furnace. will only get it next week then will see if this is really the problem
__________________
Roger & Lynne
2006 Mandalay 40 F 2232 400 ISL Allison 3000
2007 Toyota Camry SE Toad 4 down
High Ball is offline   Reply With Quote
Old 01-04-2018, 02:42 PM   #14
Senior Member
 
WeatherTodd's Avatar
 
Monaco Owners Club
Workhorse Chassis Owner
Join Date: Nov 2009
Posts: 1,363
funny thing... my board went out. I always keep a couple of electric space heaters in the coach out of habit. Glad I did. Temps dipped into the 30s... and the coach thermometer showed it being 48 inside! Didnt help someone left the windows open while pulling down the night shades.
WeatherTodd is offline   Reply With Quote
Reply

Tags
ace, furnace, thermostat



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Remote thermostat for roof air residential thermostat swap?? supertramp Travel Trailer Discussion 6 01-12-2017 08:39 PM
Upgrade Duo-Therm thermostat to a Honeywell RTH230B Thermostat Ray Wallace RV Systems & Appliances 7 12-07-2009 08:22 PM
AC, Furnace Thermostat Problems EngineerMike Alpine Coach Owner's Forum 0 02-03-2009 12:26 PM
furnace or thermostat problem georgetown350 MH-General Discussions & Problems 12 05-02-2007 03:57 PM
Propane thermostat vs. True-Air electronic thermostat John_Canfield Winnebago Industries Owner's Forum 5 10-18-2005 02:32 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:12 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.