Transfer switch cutting out

As I'm plugged in to 50 amp shore power, my transfer switch is opening sporadically. I have a TRC Surge Guard. I've sat with my volt meter on the cable into the surge protector when power was interrupted, and there was no variance from the power post. So the problem doesn't seem to be from outside.

Won't happen for two days, then it does it 4 times in an hour. Doesn't seem related to heavy electrical use, nor to any particular equipment (e.g., microwave or hair dryer). Basement isn't hot.

Any ideas?
__________________
[COLOR="Blue"]Doug, Robyn, Ross & Ryan
06 Travel Supreme Select 45'
The Driver is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-07-2012, 03:14 PM   #2
Senior Member
 
justaroamer's Avatar
 
Join Date: Oct 2009
Location: Lake OZ,MO summer-RiverBend Motorcoach Resort,FL winter
Posts: 716
Sounds like you could be right on.
A transfer switch is basicly a contactor, when the contacts arc and deteriorate, they fail to make a positive connection accross the points/contacts. Sometimes more load is better than little load as they arc together.
In any event, have you tried using without the surge protector? The TRC's have a built-in delay when power is lost. Many times park boxes get a bit overloaded, especially if someone runs 3 airs, micro/oven, etc. Just the other night, neighbor was having problem very similar. Trip off breaker back on all ok. Turn on a/c do the same...snap, krackle, pop...the back of the breaker was fried in the parks box. Having owned parks in the past, I have also seen the plugs in the boxes become fried too. If you can detect a pinkish tinge to the contacts in the park plug in or the breaker, then either could be suspect. May not be your transfer switch or in your coach.
__________________
♫ Happy Trails... to You ♪....., Until We Meet Again ♪..... ♫
justaroamer is offline   Reply With Quote
Old 01-07-2012, 03:31 PM   #3
Senior Member
 
The Driver's Avatar
 
Join Date: May 2011
Location: Dayton, Ohio
Posts: 823
Quote:
Originally Posted by justaroamer View Post
....have you tried using without the surge protector?
Leery of trying it, in case it really is intercepting something from the post!
__________________
[COLOR="Blue"]Doug, Robyn, Ross & Ryan
06 Travel Supreme Select 45'
The Driver is offline   Reply With Quote
Old 01-07-2012, 09:56 PM   #4
Senior Member
 
dons2346's Avatar
 
Country Coach Owners Club
Join Date: Dec 2010
Posts: 7,799
It could be voltage spikes. A typical volt meter will not see a spike which will measure time wise, in milliseconds which the TRC will see.

Might want to try another power source in another campground before condemning the transfer switch.

It could also be a problem with the surge guard. You might try using the by pass switch on the TRC and see what happens.
dons2346 is online now   Reply With Quote
Old 01-07-2012, 10:05 PM   #5
Senior Member
 
slabman's Avatar
 
Freightliner Owners Club
Join Date: Oct 2002
Location: Fairview TX
Posts: 2,461
Why not take the transfer switch out of the circuit for starters?
__________________
Slabman
2019 Newmar Ventana 3717
2007 Lexus LX470 Toad
slabman is offline   Reply With Quote
Old 01-08-2012, 04:52 AM   #6
Senior Member
 
justaroamer's Avatar
 
Join Date: Oct 2009
Location: Lake OZ,MO summer-RiverBend Motorcoach Resort,FL winter
Posts: 716
Quote:
Originally Posted by The Driver View Post
Leery of trying it, in case it really is intercepting something from the post!
If you are currently in a park, then I would assume you have neighbors and some are not using a surge protector, right? A surge protector only protects from voltage surge, not drop, so you could remove it for a test unless your neighbors are experiencing similar problems. If you fear a surge in power, then everyone on the same transformer will have it too, a power surge will not single out one pedistal in a park. Parks are more likely to experience voltage drops than surges. Today, lightning is the biggest cause of surges or spikes. I would take the TRC out of the loop and see if that makes any difference.
__________________
♫ Happy Trails... to You ♪....., Until We Meet Again ♪..... ♫
justaroamer is offline   Reply With Quote
Old 01-08-2012, 06:18 AM   #7
Senior Member
 
The Driver's Avatar
 
Join Date: May 2011
Location: Dayton, Ohio
Posts: 823
Quote:
Originally Posted by slabman View Post
Why not take the transfer switch out of the circuit for starters?
How to do that?
__________________
[COLOR="Blue"]Doug, Robyn, Ross & Ryan
06 Travel Supreme Select 45'
The Driver is offline   Reply With Quote
Old 01-08-2012, 06:24 AM   #8
Senior Member
 
Mike Canter's Avatar
 
Join Date: Apr 2008
Location: Freeport, ME
Posts: 4,707
Does it do it when running off the generator only?
__________________
Mike Canter
"Gunner" USN Retired, Airdale
2004 Monaco Signature 44' Conquest. Detroit 60
Mike Canter is offline   Reply With Quote
Old 01-08-2012, 07:00 AM   #9
Moderator Emeritus
 
"007"'s Avatar
 
Nor'easters Club
Workhorse Chassis Owner
iRV2 No Limits Club
Join Date: Oct 2004
Posts: 30,785
I would check all your wiring connections in transfer switch and to your Surge Guard for loose screws.
Stranded wire will loosen due to vibrations while on the road and cause high resistance connections and possible melting of wire insulation.
__________________
98KSCA, 99MACA, 03 KSCA-3740- 8.1 Chev-- ALLISON Trans
VISIT the NEWMAR QUICK TIPS & EASYMODS 1 & 2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS --- TECH INFORMATION
"007" is offline   Reply With Quote
Old 01-08-2012, 07:09 AM   #10
Senior Member
 
The Driver's Avatar
 
Join Date: May 2011
Location: Dayton, Ohio
Posts: 823
Quote:
Originally Posted by Mike Canter View Post
Does it do it when running off the generator only?
Don't know...started doing this after a few days at cg, and we're here for another week. Thought of running genny for a while today to see, but the problem is so sporadic it might not happen right then anyway!
__________________
[COLOR="Blue"]Doug, Robyn, Ross & Ryan
06 Travel Supreme Select 45'
The Driver is offline   Reply With Quote
Old 01-08-2012, 10:11 AM   #11
Senior Member
 
dons2346's Avatar
 
Country Coach Owners Club
Join Date: Dec 2010
Posts: 7,799
Quote:
Originally Posted by slabman View Post
Why not take the transfer switch out of the circuit for starters?
And how would he do that and make anything work?
dons2346 is online now   Reply With Quote
Old 01-08-2012, 10:48 AM   #12
Senior Member
 
slabman's Avatar
 
Freightliner Owners Club
Join Date: Oct 2002
Location: Fairview TX
Posts: 2,461
To disconnect the transfer switch, just loosen the strain relief at the bottom where the supply power comes in, loosen the screws on the associated contactor (Not where the generator line comes in, of course) and pull the cable out of the box. Re-attach it to the terminals at the top where the power exits the box and it's bypassed! I believe I also used a zip tie to give some strain relief, but you can run indefinitely that way as long as you don't need to generate.

And yes, you can also bypass the surge protector in the same manner...just take it apart and it'll become obvious. When I took both out of the circuit I also took the feed cable into the surge protector and hard-wired it to the top of the transfer switch in the same manner as above. Be sure the power is off, of course, and guard against any bare wires shorting against something.
__________________
Slabman
2019 Newmar Ventana 3717
2007 Lexus LX470 Toad
slabman is offline   Reply With Quote
Old 01-08-2012, 04:16 PM   #13
Senior Member
 
The Driver's Avatar
 
Join Date: May 2011
Location: Dayton, Ohio
Posts: 823
Slabman, I'm going to bypass both the surge guard & transfer switch tomorrow. I'll report back here....
__________________
[COLOR="Blue"]Doug, Robyn, Ross & Ryan
06 Travel Supreme Select 45'
The Driver is offline   Reply With Quote
Old 01-08-2012, 05:27 PM   #14
Senior Member
 
Rich and Cork's Avatar
 
Join Date: Jan 2006
Posts: 1,163
Hopefully you do 007's suggestion first and verify all your connections are tight.

Good luck.
__________________
2014 Phaeton 36gh
2008 Jeep Rubicon or 2012 Ford F150 4x4 Lariat towds
or a couple of different trailers
Retired in Apple Valley, California
Rich and Cork is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
LPT50CA Transfer Switch RedHotSoup Alpine Coach Owner's Forum 7 04-29-2011 09:24 AM
Transfer switch hums djhinds Class A Motorhome Discussions 1 12-04-2010 07:54 AM
Transfer Switch SC RV'er Alpine Coach Owner's Forum 12 03-24-2010 10:58 AM
Transfer switch and 110v plug??? azloafer MH-General Discussions & Problems 11 12-18-2009 06:09 PM
Electrical Transfer Switch OldForester Alpine Coach Owner's Forum 18 08-05-2008 11:27 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:32 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.