a/c issue

i am posting for my sister who just lost her husband. They purchased a Travel Supreme about a year ago. He pretty much took care of everything. Recently she was running both a/c's on the generator when (as she said) both made an "exhaling" sound and shut off and the generator shut down. Now both units will run with the generator (apparently the above problem did no damage ) but the zone 1 (living space) will not run on shore power. Zone 2 (bedroom) runs on both. I am very mechanically inclined but am terrible with electrical and have ZERO experience with motor coaches . It is an '02 Travel Supreme Select DS02 with a 500 Cummins. Any help/suggestions would be greatly appreciated.

Ray
hogtails is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-23-2016, 09:26 PM   #2
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
I'd be inclined to checking the transfer switch gear. Sometimes you can get arching and issues with the terminals and or spring loaded contacts on that device.


Best of luck.
__________________
J & J, DRV Suites ES-38RSSA #9679
GM Denali, 3500HD-Max, 4x CC, 8' DRW,
EZGo-TXT, Clubcar Precedent
MtnTrek is offline   Reply With Quote
Old 08-23-2016, 09:51 PM   #3
Member
 
yackman's Avatar
 
Join Date: Mar 2014
Location: Illinois
Posts: 96
You might check the inverter to see if possibly a breaker has tripped.
__________________
yackman
2008 TS Insignia 42DL24
2010 Ford Edge
yackman is offline   Reply With Quote
Old 08-23-2016, 10:10 PM   #4
Senior Member
 
rag_ftw's Avatar


 
Spartan Chassis
Join Date: Feb 2010
Location: Fort Worth
Posts: 1,590
I would check all AC circuit breakers and then the transfer switch. It sounds like the leg that supplies Sys #1 is not closing on shore power. Take the cover off the transfer switch and check for proper voltage on all the connections. You can find a print for your transfer switch on the internet. Let us know which switch you have and possibly one of us will already have the print.

If you have to get a new transfer switch suggest you get a solid state switch. The new mechanical units are not made in the US and they have a tendency to hum loudly. Since this thing is probably located under the bed that is not a good thing!

Good luck and keep us posted.
__________________
2004 38DS04 Travel Supreme
Cummins 8.3 ISC 350HP CAPS
Spartan Mountain Master
2023 F-150 Towed
rag_ftw is offline   Reply With Quote
Old 08-24-2016, 07:48 AM   #5
Senior Member
 
justaroamer's Avatar
 
Join Date: Oct 2009
Location: Lake OZ,MO summer-RiverBend Motorcoach Resort,FL winter
Posts: 716
What is the power source you refer to as shore power? 50 amp, 30 amp, 15 amp???
Could be the inverter control panel is set to a lower power than 50 amp, even though you may be connected to a 50 amp source. If connected to power source not supplying 50 amp 220v then the zone 1 AC may be on a different leg/buss in the main breaker box....
__________________
♫ Happy Trails... to You ♪....., Until We Meet Again ♪..... ♫
justaroamer is offline   Reply With Quote
Old 08-24-2016, 08:49 AM   #6
Senior Member
 
Join Date: Jul 2014
Posts: 35,413
If it's a 30 amp RV, you may not get both ACs running on shore power. There would be a selector switch for front or rear AC.

The generator will run both because it had a 30 and 20 amp output. They use the 20 amp output for the second AC.

Have her check the plug on the end of the power cord for an amp rating.

2 blades,1 pin = 30 amp

3 blades, 1 pin = 50 amp
twinboat is offline   Reply With Quote
Old 08-24-2016, 12:39 PM   #7
Senior Member
 
justaroamer's Avatar
 
Join Date: Oct 2009
Location: Lake OZ,MO summer-RiverBend Motorcoach Resort,FL winter
Posts: 716
Quote:
Originally Posted by twinboat View Post
If it's a 30 amp RV, you may not get both ACs running on shore power. There would be a selector switch for front or rear AC.

The generator will run both because it had a 30 and 20 amp output. They use the 20 amp output for the second AC.

Have her check the plug on the end of the power cord for an amp rating.

2 blades,1 pin = 30 amp

3 blades, 1 pin = 50 amp
I believe on the coach in question, would not have a generator with "a 30 and 20 amp output" , but an 8kw generator that would be capable of 50 amps 220v. The coach would then have a 4 pin male plug on the supply cord (220v). The question is are they using an adaptor to connect with, which would only give 110v and only be powering one leg/buss on the coach main breaker box.

If they are connecting to "shore power" via a down size adapter (i.e. 50 amp 220v (4 pin) coach cord adapted down to 30 amp (110v) or even down to 15/20 amp then the problem would be as I stated previously.
Really need to know what their power source is and how the power is supplied to the coach. If they are connecting via full 50 amp connection,
then the supply breaker could have a bad leg in the breaker or the buss connection at the supply side pedestal side.
__________________
♫ Happy Trails... to You ♪....., Until We Meet Again ♪..... ♫
justaroamer is offline   Reply With Quote
Old 08-24-2016, 02:20 PM   #8
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
These are all plausible scenarios in the event that the coach had been moved re-connected etc., etc.
OP reads as if there was a sudden loss of power or the generator dropped out with a "humph". There may heat pumps (with reversing valves) up there that make that distinctive sound. Perhaps we'll get an update from OP'r


Be well.
__________________
J & J, DRV Suites ES-38RSSA #9679
GM Denali, 3500HD-Max, 4x CC, 8' DRW,
EZGo-TXT, Clubcar Precedent
MtnTrek is offline   Reply With Quote
Old 08-24-2016, 05:03 PM   #9
Junior Member
 
Join Date: Aug 2016
Posts: 3
Thank you all for your replies . I went to the coach today and found the transfer switch but as i said i am horrible with electrical. The coach is hooked up to 50 amp service with no adapters. Unfortunately my sister was not around so i could not get inside. I do know the control panel is set for 50 amp. There is a breaker box in the control cabinet with i believe 3 20 amp and 1 50 amp breakers. Are there other locations i need to find ?Ask me to tear down a chevy 350 and rebuild it and it would be done , but this motor home is like brain surgery to me i don't have a clue . Again ,thank you all
hogtails is offline   Reply With Quote
Old 08-24-2016, 05:18 PM   #10
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,400
OK--lots of shots in the dark here but think rag-ftw is on target. Since both units run on genset but not on shore power, it basically means all upstream components are working. So need to target/focus on x-fer switch. Genset has priority on most x-fer switches so those contactors are normally closed. Fact that front unit doesn't work on SP suggests that when x-fer switch transfers to SP, one of the SP contactors [one of two separate 120volt legs] isn't closing. This can all be verified with a voltmeter at the x-fer switch but based on your concerns about "all things electrical," you probably aren't the guy to do it [smile].
PS--if so equipped, surge protector could an issue but since original shut down occurred while on genset, symptoms point back to x-fer switch!
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 08-24-2016, 09:55 PM   #11
Senior Member
 
rag_ftw's Avatar


 
Spartan Chassis
Join Date: Feb 2010
Location: Fort Worth
Posts: 1,590
Can you identify a brand and model number of your transfer switch?

Once you have that you can get a print and the testing part is really pretty easy. You would be measuring AC voltage across a couple bolt heads inside the transfer switch.

If you are willing to work with us there is enough knowledge in this group to talk you through some basic troubleshooting.
__________________
2004 38DS04 Travel Supreme
Cummins 8.3 ISC 350HP CAPS
Spartan Mountain Master
2023 F-150 Towed
rag_ftw is offline   Reply With Quote
Old 08-24-2016, 11:11 PM   #12
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
T/S primer

Here is a generic overview of a MH and a typical flow diagram.

Depending on layout you may find the T/S in or through a bulkhead wall adjoining or close to the main breaker panel. Follow the leads from either you can see. Some coaches they're under the bed.

In the T/S itself (grey box) is often a pair of mechanically interlocking contactors. one is N.O. the other is N.C.
With all the power off you can often work the contactors spring loaded plungers / interlock with a screw driver and check for binding etc.
Likewise the contacts are spring loaded metal slugs.
Check all the connection lug screws & contacts for alignment. Burnt wire?
Spray it with contact cleaner if available. Discoloring will require investigation.

The control board becomes more difficult to diagnose, not so serviceable.
Attached Thumbnails
Click image for larger version

Name:	coach power layout.png
Views:	85
Size:	233.7 KB
ID:	137055   Click image for larger version

Name:	transfer contactors.png
Views:	74
Size:	77.2 KB
ID:	137056  

Attached Images
 
MtnTrek is offline   Reply With Quote
Old 09-01-2016, 04:11 PM   #13
Junior Member
 
Join Date: Aug 2016
Posts: 3
Thank you all again for your help. rag ftw was spot on. Although i was told by 2 different people ( my sister and quite competent brother - in -law ) that the circuit breakers were not tripped, low and behold i looked and, surprise, the breaker for the front a/c was tripped. I do remember being told many times KEEP IT SIMPLE STUPID. I am sure i will post again since the help is quite abundant here.
hogtails is offline   Reply With Quote
Old 09-01-2016, 04:34 PM   #14
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
A 50 amp service is TWO 50 amp breakers for 12,000 watts so an 8KW gen will not supply the full 50 amps.
A correctly wired 30 amp adapter will supply power to both legs of a 50 amp plug but you will be limited to 30 amps (3,600 watts) total
30 amps = 120 X 30 = 3,600 watts
66.67 amps = 8,000 watts
50 amps = 50 X 2 X 120 or 12,000 watts.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Slight oil leak...Issue or non Issue? Speedjester Cummins Engines 6 09-03-2015 07:17 AM
AGS Issue: 2010 Paeton 40-QTH AGS Issue gjw Tiffin Owner's Forum 1 09-06-2013 04:46 PM
Slide Controller Issue, but maybe slide motor issue also Corwin Newmar Owner's Forum 8 07-16-2012 11:41 AM
Southwind 36D Issue after issue after issue.... fixn2gocamp Fleetwood Owner's Forum 4 10-21-2009 07:05 PM
Interesting Workhorse Brake-Issue Information at NHTSA.gov Richard 34A Workhorse and Chevrolet Chassis Motorhome Forum 6 12-09-2008 01:08 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:01 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.