Old 01-26-2017, 09:12 PM   #1
Junior Member
 
Entegra Owners Club
Join Date: Jul 2012
Location: Cedar Rapids, Iowa
Posts: 19
Aqua Hot 1/2 bath heat

We have a 2016 Cornerstone model 45A. My question is that in the 1/2 bath with the heat on with the Aqua heat is it normal for the 1/2 bath to get extremely hot? I have the thermostat set at 70 but if you leave the door closed in the 1/2 bath it gets to 81*. In the bathroom with door closed. Realizing that the Aqua Hot is directly below the 1/2 bathroom I'm just wondering if that's the norm or do I have a recirculating pump not working? Just got the coach back from the factory and they replaced all 3 Aqua Hot pumps. Maybe it's the normal and I realize we can leave the door open to help distribute the heat..Entagra should have marketed this coach with a sauna in midship??
rnorthway is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-26-2017, 09:36 PM   #2
Senior Member
 
FreshAir's Avatar
 
Workhorse Chassis Owner
Entegra Owners Club
Join Date: Dec 2004
Location: UT/AZ
Posts: 1,417
Quote:
Originally Posted by rnorthway View Post
We have a 2016 Cornerstone model 45A. My question is that in the 1/2 bath with the heat on with the Aqua heat is it normal for the 1/2 bath to get extremely hot? I have the thermostat set at 70 but if you leave the door closed in the 1/2 bath it gets to 81*. In the bathroom with door closed. Realizing that the Aqua Hot is directly below the 1/2 bathroom I'm just wondering if that's the norm or do I have a recirculating pump not working? Just got the coach back from the factory and they replaced all 3 Aqua Hot pumps. Maybe it's the normal and I realize we can leave the door open to help distribute the heat..Entagra should have marketed this coach with a sauna in midship??
That's normal with my RBQ. It has it's own floor register and the thermostat is in another room. Leave the door open to share it's heat with the rest of the coach. Unfortunately with it's own heat register you can't partially close off a register vent.
__________________
Pat & Denise
2016 Entegra Aspire RBQ
18 Silverado
FMCA 212171
FreshAir is offline   Reply With Quote
Old 01-26-2017, 09:46 PM   #3
Junior Member
 
Entegra Owners Club
Join Date: Jul 2012
Location: Cedar Rapids, Iowa
Posts: 19
Thank you for piece of mind
rnorthway is offline   Reply With Quote
Old 01-27-2017, 03:53 AM   #4
Senior Member
 
Johnnypac's Avatar
 
Entegra Owners Club
Join Date: Oct 2014
Posts: 147
Quote:
Originally Posted by rnorthway View Post
We have a 2016 Cornerstone model 45A. My question is that in the 1/2 bath with the heat on with the Aqua heat is it normal for the 1/2 bath to get extremely hot? I have the thermostat set at 70 but if you leave the door closed in the 1/2 bath it gets to 81*. In the bathroom with door closed. Realizing that the Aqua Hot is directly below the 1/2 bathroom I'm just wondering if that's the norm or do I have a recirculating pump not working? Just got the coach back from the factory and they replaced all 3 Aqua Hot pumps. Maybe it's the normal and I realize we can leave the door open to help distribute the heat..Entagra should have marketed this coach with a sauna in midship??

Not sure of the 45 A floor plan but is there a register directly on the other side of the bathroom register ? There was a coach in for service at the factory that had the heat exchanger installed backwards so it was blowing into the half bath instead of the main living area.
__________________
John P 2015 Aspire 44U
Johnnypac is offline   Reply With Quote
Old 01-27-2017, 06:03 AM   #5
Senior Member
 
Mwoodofd's Avatar


 
Entegra Owners Club
Join Date: Apr 2013
Location: Las Colinas, Texas
Posts: 2,040
I didn't think the registers were supposed to blow into the half baths as well, unless that changed on the newer Entegras? Mine does not, but is a 13 "Classic".
__________________
Mark & Debra Wood, Las Colinas, TX.
2013 Entegra Aspire 42RBQ
2023 Jeep Wrangler Sahara 4XE
2013 Thor Challenger 37DT - Sold
Mwoodofd is offline   Reply With Quote
Old 01-27-2017, 06:07 AM   #6
Senior Member
 
brobox's Avatar
 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,729
On my 14 it is a gravity flow vent, but it still gets warm in the 1/2 bath along with freezing with the A/C. I have the ceiling vent almost closed. Open the door for a minute and everything is fine.
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
brobox is offline   Reply With Quote
Old 01-27-2017, 06:20 AM   #7
Senior Member
 
Hayman's Avatar
 
Join Date: Jul 2012
Location: Port Charlotte , Fl
Posts: 1,497
rnorthway, We have a 16 Anthem A and YES our 1/2 bath gets very warm also both from the register as well as the aquahot radiating through the floor. There are 2 fans on each heater and with ours in the 1/2 bath 1 fan blows through the heater into the 1/2 bath while the 2nd fan pulls air and blows into the plumbing chase.

We also usually leave the 1/2 bath door open to disperse the heat but while at factory service in early November some owners asked techs to disconnect the fans on the 1/2 bath heater and my understanding was they did. I'm not recommending you do that just expressing what I observed.
__________________
Sue & Brian Ashworth & Rizzy( adopted Boxer)

No RV anymore !
Hayman is offline   Reply With Quote
Old 01-27-2017, 08:46 AM   #8
Senior Member
 
weirba's Avatar
 
Join Date: Sep 2015
Location: wandering
Posts: 207
In our 16 Anthem 44A, the mid bath gets much warmer. Some from what others have mentioned, also cooler with the A/C. We just try to leave the door open. We also find the vanity cabinet gets very hot and sometimes leave that door open.
__________________
2018 Ford F-350 DRW pulling a 2023 LUXE 47FB TH
weirba is offline   Reply With Quote
Old 01-27-2017, 09:12 AM   #9
Junior Member
 
kaisooba's Avatar
 
Join Date: May 2008
Location: North Bend (Coos Bay) OR
Posts: 21
Yu can install a resistor switch that will cut the heat in half. Very easy to do.
__________________
Andrew & Linda
2009 Camelot 42' PDQ
N6ZPK N6ZPL
kaisooba is offline   Reply With Quote
Old 01-27-2017, 09:34 AM   #10
Senior Member
 
757driver's Avatar


 
Entegra Owners Club
Join Date: Jun 2004
Location: Bayfield, Ontario
Posts: 5,470
Just so most others do not go looking for a heat register blowing heat in the 1/2 bath I believe the 2016 45A and 44A was the only model that Entegra experimented with on putting a blower and heat register in the 1/2 bath. For most of us with a 1/2 bath there is a register grate to get residual heat from the one in the living area but no additional heating unit and fan.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring

1300W Solar, 1200AH LiFePO4 FMCA F443497
757driver is offline   Reply With Quote
Old 01-27-2017, 09:59 AM   #11
Moderator Emeritus
 
Cruzer's Avatar
 
Join Date: Oct 2002
Location: Sheboygan, WI
Posts: 5,644
We had the same thing. The heat exchanger in the half-bath does blow out lots of heat for that small area and the thermostat is in the front because they are all part of zone 1.

What I did was install a temperature controller. I mounted the controller in the cabinet next to the G5 fuse panel in the mid-bath. The temperature probe was run to a point just beneath the vanity countertop where you can't see it but will accurately read the temperature in the room. The controller has normally open or closed contacts so I just ran the two wires to the fan on the heat exchanger beneath the vanity and intercepted the fan wires. I also added a small mini rocker switch to control the 12 VDC power to the controller so that I could turn it on or off as desired - mainly for storage. I set the temperature controller to the desired temperature and whenever the bathroom reaches that temperature the fan shuts off.

I bought the controller on Amazon, was an easy install, looks good and works great.

https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1
__________________
Mark & Leann Quasius
2016 Cornerstone 45A
2020 Jeep Gladiator Rubicon
2021 Jeep Wrangler Rubicon
Cruzer is offline   Reply With Quote
Old 01-27-2017, 05:40 PM   #12
Senior Member
 
Jalisa's Avatar
 
Join Date: Mar 2016
Posts: 194
Thanks for that info Don, I actually asked that question this morning! Nice meeting you in Quartzsite😊
Lisa
__________________
Lisa
2016 Anthem 44B
Jalisa is offline   Reply With Quote
Old 01-27-2017, 05:51 PM   #13
Senior Member
 
DoggieDaddy's Avatar
 
Join Date: Jul 2013
Location: Where ever we park it
Posts: 1,295
Just to note here. If you are full timing, you should have your roof vents running constantly, especially in cold weather. I run mine at 10% 24/7/365. We are full timers. If you read the documentation these coach are not designed for full time occupancy and moisture will build up which may causer an unsafe condition with mold, mildew, and etc. The heating in the midship bath may be set up to compensate for that. And then maybe not. Can't trust those engineers.
__________________
Robert & Holly - "Fulltimers" 8+ years
Schnauzers Augie Doggie and Monty Puppy
2014 Anthem 44B Rad Copper ----- SOLD
DoggieDaddy is offline   Reply With Quote
Old 01-27-2017, 06:29 PM   #14
Senior Member
 
FreshAir's Avatar
 
Workhorse Chassis Owner
Entegra Owners Club
Join Date: Dec 2004
Location: UT/AZ
Posts: 1,417
Two fans, side by side, in a black plastic box with plumbing in and out of it located below the sink in the 1/2 bath in my 2016 RBQ Aspire. It's of a different design than the other typical registers in the coach as it does not blow thru a radiator type exchanger in front of the fans. ? Whatever.
__________________
Pat & Denise
2016 Entegra Aspire RBQ
18 Silverado
FMCA 212171
FreshAir is offline   Reply With Quote
Reply

Tags
heat



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aqua Hot solution to my hot, cold, hot water problem JeffK Entegra Owner's Forum 38 06-25-2017 03:54 PM
Aqua Hot furnace vs. Heat Pumps for heat S-n-L RV Systems & Appliances 14 12-17-2015 06:36 PM
Coachman Mirada Bath and half vs Fleetwood Bounder Bath and Half retiring1day Class A Motorhome Discussions 18 09-03-2015 08:06 PM
Hydro Hot & Aqua Hot, Air but no Heat at Register EngineerMike Alpine Coach Owner's Forum 7 01-15-2012 09:07 AM
Aqua Hot basement heat dshogman Alpine Coach Owner's Forum 18 02-28-2010 05:11 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:31 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.