Aqua-Hot 450D Info

FWIW, I thought this information might be helpful to diesel aquahot owners with coaches having Vega Touch. Most threads seem to apply to the LP version. We had a heating problem where the diesel side would only operate when manually turning it on from the Vega Touch - and then it would run for an hour at most regardless of the thermostat setting. It would not fire automatically when the Vega Touch thermostat callled for heat. Due to the cold temperatures the electric side would not keep up but the whole system seemed to be erratic, so I thought Vega Touch might also be part of the problem.

I provided Aqua-Hot with a chart showing the lights on the Electronic Controller under various conditions. Due to the zones and pumps that the controller showed were active Aqua-Hot kept saying that it should not be doing what it showed. Meantime it was 50 degrees in the coach each morning. After getting to NIRVC to get eyes on it and going through the diagnostics it finally turned out to be a bad burner controller. That seemed to have corrected all the problems we were having with the heat (hope this doesn't jinx that).

The point of this post (and according to the NIRVC tech) is that Entegra apparently wires the Aqua-Hot controller differently then what is considered the norm. The technician at NIRVC verified that the lights on my controller were the same as other newer coaches with Vega Touch. So if you have an Aqua-Hot problem and are looking at the controller to see what is operating it may not be what the folks at Aqua-Hot expect to see. It would seem to be a problem if you are trying to diagnose a malfunction with the folks at Aqua-Hot. Sorry aboout the length and hope this makes sense to someone.
__________________
Roger & Donna
2021 Anthem 44Z
2023 GMC Canyon Denali
roger8070 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-16-2017, 07:44 AM   #2
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 11,531
Blog Entries: 1
Roger

That information is disturbing, particularly since it is not clear what the different wiring does. Can you explain what the techs at NiRVC told you was the issue and the difference from what is standard wiring?

Entegras, sometimes, have had several of their systems mis-wired and the issue to me is, is this simply a mistake that some person on the line made in connectding the wires, or is this an intentional difference in wiring that Entegra has adopted? If it is intentional, then I would think that they need to be communicating with AH techs so that those notations are in their service books. If it is a mistake, then Entegra customer service needs to know about the error since your coach is probably not the only one with the problem.

Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Old 12-16-2017, 08:41 AM   #3
Moderator Emeritus
 
Cruzer's Avatar
 
Join Date: Oct 2002
Location: Sheboygan, WI
Posts: 5,644
I know my way around Aqua-Hot pretty well and haven't seen any difference in the way the burner controller is wired. Actually, the burner controller is directly connected to the electronic controller panel via the Aqua-Hot harness so it really can't be wired any other way.

The biggest difference I've seen is the Aqua-Hot heating zones. They do not always match up with the interior thermostat zones. But I can see why this would be. Entegra is unique in that they have a hydronic heated floor rather than an electric grid. Circulation pump #1 handles heating zones 1 and 5 while circulation pump #2 handles zones 2, 3 and 4. The bedroom and in-floor heat are on pump #1 while the bedroom and basement are on pump #2. So that requires swapping the heating zones around to differ from the thermostat zones for best effectiveness.

But none of that would affect burner operation - only fluid circulation.
__________________
Mark & Leann Quasius
2016 Cornerstone 45A
2020 Jeep Gladiator Rubicon
2021 Jeep Wrangler Rubicon
Cruzer is offline   Reply With Quote
Old 12-16-2017, 08:45 AM   #4
Senior Member
 
roger8070's Avatar
 
Join Date: Jan 2013
Location: Webster, FL
Posts: 180
Gary,

I wish I could provide more definitive information. The technician is not here today being Saturday but I will try to get more on Monday. All he told me was that the Aqua-Hot provides a 2 wire connection and Entegra uses only 1. What that means who knows. He tried to get a schematic that shows how the Vega Touch is interfaced with the Aqua-Hot but no luck. He was referred to Firefly. I believe he was thinking it was miswired also but his check of another similar coach found the controller was operating the same. Since the heating seems to be working correctly now one might assume that Entegra has adopted a different wiring scheme.
__________________
Roger & Donna
2021 Anthem 44Z
2023 GMC Canyon Denali
roger8070 is offline   Reply With Quote
Old 12-17-2017, 12:51 PM   #5
Senior Member
 
Franko Foto's Avatar
 
Join Date: Jun 2015
Location: Wilmington NC
Posts: 157
I have had an similar ongoing problem with Aqua-Hot that appears to be getting worse.

I first asked about this issue January of this year - http://www.irv2.com/forums/f278/aqua...ch-325006.html - and just figured things were back to normal. About a month ago I noticed the Aquahot had just done the same thing - all the pumps are running, everything seems normal, the lights on the controller are all green - but the green light on "Diesel Heat" on the Vega Touch had turned off.

I touched the icon on Vega Touch of and then on, and the Aquahot immediately came back on and operated normally until about a week ago. Since then it has repeatedly shut off on the Vega Touch and will start again if I touch the icon.

I opened the unit yesterday and cleaned the burner, replaced the nozzle and the fuel filter because Aquahot Tech help refused to discuss anything unless the unit was serviced.

This morning when I checked, the Vega Touch icon was again off - everything was running - I touched the icon to turn it off, touched it again and Aquahot fired right up.

I don't know if this is related to the controller or what the issue might be, but on at least three of the occasions this happened, there was a lingering odor of - as I described earlier - a burning candle that had been snuffed out.

I'll call Aquahot again tomorrow, now that the "service the unit" issue is resolved and see if they have any insight based on this thread.

Frank
__________________
Frank and Ruth
2017 Cornerstone
Franko Foto is offline   Reply With Quote
Old 12-17-2017, 01:00 PM   #6
Senior Member
 
DoggieDaddy's Avatar
 
Join Date: Jul 2013
Location: Where ever we park it
Posts: 1,295
Make sure you jumpers under the light panel are set correctly. Ours came from the factory with the jumpers all wrong. They forgot to set them to the Entegra configuration which shows that they never tested the heating system. We also had to change the burner controller which solved our hot water issue.
__________________
Robert & Holly - "Fulltimers" 8+ years
Schnauzers Augie Doggie and Monty Puppy
2014 Anthem 44B Rad Copper ----- SOLD
DoggieDaddy is offline   Reply With Quote
Old 12-18-2017, 09:59 AM   #7
Senior Member
 
Franko Foto's Avatar
 
Join Date: Jun 2015
Location: Wilmington NC
Posts: 157
I just had a discussion with Aquahot about this problem, and the tech advised me to remove the controller attached to the side of the burner motor, and put it in the freezer for three hours, re-attach and see if the Aquahot ignites. My problems only seem to appear when it's cold so at least this will eliminate, or point to, the controller.

I'll report back as to the results.

Frank
__________________
Frank and Ruth
2017 Cornerstone
Franko Foto is offline   Reply With Quote
Old 12-18-2017, 11:02 AM   #8
Senior Member
 
roger8070's Avatar
 
Join Date: Jan 2013
Location: Webster, FL
Posts: 180
Quote:
Originally Posted by Cruzer View Post
I know my way around Aqua-Hot pretty well and haven't seen any difference in the way the burner controller is wired. Actually, the burner controller is directly connected to the electronic controller panel via the Aqua-Hot harness so it really can't be wired any other way.
I was actually referring to the Aqua-Hot Electronic Controller wiring, but I have tested the system after the burner controller was replaced and all seems to be working correctly now. I can only assume at this point that all the erratic lights being displayed on the main aqua-hot controller were caused by problems with the burner controller. Possible that the technician's comments about the controller wiring were not correct as all the zones and pumps are working as Cruzer has discussed. The only difference I can find is that zone 3 seems to be related to the stir pump (pump 3) as it is not active when anything is running. This is what I observed on the VegaTouch and main controller:

Zone 1 - Front (punp 1)
Zone 2 - Rear (pump 2)
Zone 3 - Stir Pump (pump 3) ?
Zone 4 - Basement (pump 2)
Zone 5 - Floor (pump 1)
__________________
Roger & Donna
2021 Anthem 44Z
2023 GMC Canyon Denali
roger8070 is offline   Reply With Quote
Old 12-18-2017, 12:43 PM   #9
Senior Member
 
Franko Foto's Avatar
 
Join Date: Jun 2015
Location: Wilmington NC
Posts: 157
Put the controller in the freezer for three hours, reconnected and AQ fired right up. Not the cold, apparently.

Frank
__________________
Frank and Ruth
2017 Cornerstone
Franko Foto is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Entegra Aqua Hot 450D brianw8602 Entegra Owner's Forum 36 05-31-2015 06:35 PM
Source for 450D Aqua Hot filters? brobox Entegra Owner's Forum 14 07-23-2014 05:18 PM
Aqua Hot 450D Five2o RV Systems & Appliances 7 05-04-2013 04:50 PM
Which DP's have aqua hot 450D standard? GARRYOWEN Class A Motorhome Discussions 10 09-28-2012 04:06 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:37 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.