Exercising - Generator, that is

I'd like some help regarding exercising our generator. We pretty much park in CG's where the coach is plugged in and when it's stored, we're plugged in to 30 Amp.

I know I need to run the generator now and then to keep it fresh and happy.

1. How often?

2. How do I put it under load? (Since there is power to the coach from the Shore Power, I assume there is no load on the generator.) Do I unplug or turn off the Shore Power and then what should be sure is running to create a reasonable load?

Thanks - I have trouble changing light bulbs so this is really rocket science for me.
__________________

__________________
Cheryl, Emerson and Rascal (Attack Yorkie)
2018 Cornerstone 45Y
2015 Enclave
Saltydog44 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-31-2014, 07:40 AM   #2
Senior Member
 
brobox's Avatar


 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 18,284
The manual says to exercise every thirty days, but I do mine about every 60 days. I do un-plug for two reasons, one to load the generator, also I don't like to throw the load on the transfer switch. I know they are designed for that, but they also wear out and fail, so I don't run shore power and generator at the same time.. Start the generator and let it run for a couple of minutes to warm up before putting a load on it. To load the generator, run the A/C's, but I live in FL and that is easy. For those in cold weather, turn on everything electric and might even plug in a space heater set on full blast. I normally let it run for 20 minutes while I am checking that everything is working.

Before shutting down, turn everything electrical off, let the generator cool down for 2 minutes before turning the generator off. This step should be done anytime the generator is used.
__________________

__________________
Chuck in SW FL
A "Digital" 2019 Cornerstone "B"
A "Classic" 2014 Anthem 42 RBQ---Sold
2016 Colorado Z71 PU
brobox is online now   Reply With Quote
Old 01-31-2014, 07:52 AM   #3
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 13,463
Typically once a month for 30-60 minutes with load. Load being a heavy load, such as air conditioning. So you get to exercise and check the AC as well.

Leaving the shore power connected is ok, just don't have the heavy load operating while transferring to/from the generator.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 01-31-2014, 08:00 AM   #4
Senior Member
 
glenda1908's Avatar
 
Winnebago Owners Club
Join Date: Jun 2004
Location: Virginia Beach, VA
Posts: 676
Quote:
Originally Posted by brobox View Post
The manual says to exercise every thirty days, but I do mine about every 60 days. I do un-plug for two reasons, one to load the generator, also I don't like to throw the load on the transfer switch. I know they are designed for that, but they also wear out and fail, so I don't run shore power and generator at the same time.. Start the generator and let it run for a couple of minutes to warm up before putting a load on it. To load the generator, run the A/C's, but I live in FL and that is easy. For those in cold weather, turn on everything electric and might even plug in a space heater set on full blast. I normally let it run for 20 minutes while I am checking that everything is working.

Before shutting down, turn everything electrical off, let the generator cool down for 2 minutes before turning the generator off. This step should be done anytime the generator is used.
This is the best way. Also, we sometimes run the generator on the road. Depending on if we want heat or air conditioning. About an hour before we reach our destination for the day, turn on the generator set heat or air to give it a load, then your coach temp. Is comfortable front to rear when you park.
glenda1908 is offline   Reply With Quote
Old 01-31-2014, 08:05 AM   #5
Senior Member
 
glenda1908's Avatar
 
Winnebago Owners Club
Join Date: Jun 2004
Location: Virginia Beach, VA
Posts: 676
Forgot to add . TURN OFF ANY SYSTEM YOU ARE USING, LET THE GENERATOR COOL DOWN, THEN TURN OFF YOUR GENERATOR BEFORE PLUGGING IN TO SHORE POWER.
glenda1908 is offline   Reply With Quote
Old 01-31-2014, 09:43 AM   #6
Senior Member
 
Saltydog44's Avatar


 
Entegra Owners Club
Join Date: Oct 2009
Location: Lenoir, NC
Posts: 1,993
Thanks all - Reading is good, but insights from smart people who have practical experience is better.
__________________
Cheryl, Emerson and Rascal (Attack Yorkie)
2018 Cornerstone 45Y
2015 Enclave
Saltydog44 is offline   Reply With Quote
Old 01-31-2014, 10:05 AM   #7
Senior Member
 
Join Date: Jun 2010
Location: Anacortes, WA (Stick & Brick)
Posts: 2,642
It depends to some extent whether the generator is carburetor equipped or EFI. If it's a carb, definitely exercise it every 4 to 6 weeks. In Dec 2011, I had to have cardiac surgery and was out of any serious activity for about 3 months. The generator hasn't run since!

Since we're FHU campers, it hasn't been an issue, but I'll have to get it fixed before we sell the rig.
__________________
Frank Damp -Anacortes, WA,(DW- Eileen)
ex-pat Brits (1968) and ex-RVers.
frankdamp is offline   Reply With Quote
Old 01-31-2014, 07:20 PM   #8
Junior Member
 
drgary's Avatar
 
Join Date: Feb 2006
Posts: 26
Hi IRV2 Friends,

In the "For What It's Worth" Department...

From the Cummins/Onan RV Generator Handbook:

"To prevent problems, it is recommended to run gasoline generators
at a minimum of 50 percent capacity (2000-watts, or one air
conditioner for a 4000-watt set) for two hours once every four
weeks. This is necessary to help keep moving parts lubricated,
expel moisture and control fuel varnishing in the carburetor.
A long two-hour exercise period is preferable to several short periods.
While traveling, this can be accomplished by running the air conditioning.
If you own a diesel generator, regular exercising can help reduce
internal condensation and helps keep seals
lubricated."

Cheers,
Gary & Carol
__________________
2013 Aspire 42RBQ/IFS Honda CR-V
Just Us 2 + Mr. Riley/Maltese & Harold/Havanese
drgary is offline   Reply With Quote
Old 02-01-2014, 11:42 AM   #9
Junior Member
 
Join Date: Jan 2014
Posts: 13
Since you do not dry camp, I always found that running the generator while driving down the road to cool down your coach or??? is the best way to exercise it.
beachbum480 is offline   Reply With Quote
Old 02-01-2014, 12:11 PM   #10
Senior Member
 
Join Date: Nov 2005
Posts: 3,537
It all depends on the type of generator you have. We have the 5500 Marquis Gold gasoline powered generator. The manual says:
EXERCISING THE GENSET
Exercise the genset at least 1 hour each month if
use is infrequent. Run the genset at approximately
1/2 rated power. See LOADING THE GENSET
(Page 9). A single exercise period is better than
several shorter periods.
Exercising a genset drives off moisture, re-lubricates
the engine, replaces stale fuel in fuel lines and
carburetor and removes oxides from electrical contacts
and generator slip rings. The result is better
starting, more reliable operation and longer engine life.

I would take them at their word. We religiously ran the one in our old motorhome according to the procedure outlined in the manual. When we did we never had a problem. One winter we went on a cruise and didn't get back for an extended time period. The next spring I tried to start it and had all kinds of problems. It only had about 160 hours but needed some very expensive repairs.
We make sure to run the one in our new motorhome regularly according to the published procedure.

On Edit: Our problem was not with the gasoline engine. A film of corrosion had formed on the slip rings. The brushes got caught on the corrosion when I tried to start the generator. 1 Brush broke taking the holder with it. The whole mess got caught up in the armature and peeled off a few segments. The generator had to be removed and disassembled. It required a new armature, brush set and holders, as well as a couple hours to clean all the broken junk out so it didn't damage anything else.
__________________
Hikerdogs
2013 Adventurer 32H
Hikerdogs is offline   Reply With Quote
Old 02-01-2014, 12:20 PM   #11
Registered User
 
Join Date: Mar 2013
Posts: 1,919
If the motorhome is in storage or not fueled up at regular basis, I would be using premium fuel and stabil in the fuel tank to help prevent fuel degradation. Gasoline will start to loose octane ratings the longer is sits. Higher octane fuel will help with having a higher octane rating in fuel after months of storage and the Stabil will also help prevent the fuel from degrading the octane rating also. I use Stabil every winter in all my toys and I have never had any fuel system issue with anything I own. Even after years of storage.
jamesrxx951 is offline   Reply With Quote
Old 02-01-2014, 02:45 PM   #12
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,022
How often: Monthly, Pick a date 1-28 (do not pick 29,30 or 31)

How to exercise: Shut off everything, You have two ways to do this, one is to trip the main breaker inside the motor home.

Start generator,,, Wait for 2 or 3 minutes or till you hear the transfer switch transfer (NOTE: Read the generator owner's manual, even if you have to download it first, for proper starting procedure.. On mine the manual is off just a bit.. It says to hold STOP till the light comes on then press start,, Hold STOP 2 seconds longer).

Once you hear the switch transfer (or are sure it has) turn main breaker back on.

Alternate to main breaker (How I do it) turn off all big loads (Water heater, A/C, Space heaters,, I even kill the fridge) turn off PARK power breaker.. Start generator,, When transfer happens lights and/or vent/furnace fans will speed up and get brighter, THEN turn on space heaters or A/C's to provide at least 1/2 load on the Genny.. TWO A/C units or two space heaters will provide 24-30 amps of load.. About right for a 5500 watt generator. (or one of each)

Returning to shore power.

Same procedure, Turn off all big loads.. Then stop generator, then turn on park breaker then restore loads.
__________________

__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Exercising RV Systems With Adco Cover On NC Rob Class A Motorhome Discussions 1 07-20-2013 08:58 PM
Exercising engine and generator? Seagrouch Class A Motorhome Discussions 10 06-13-2013 08:34 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:22 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.