First time Aquahot user need help

Hello everybody, I have the Gen on, the burner on, thermostat on low heat gas on 3 zones, but show active zone 3 only. On the aquahot, heating zone status light 1,2 and 5 on green. all pump on green, Heating status on green. I have heat at the floor level but cold on the ceiling vents. What is I'm doing wrong? is the heat from aquahot is only from the floor vent? if yes, how do I stop the cold air from the ceiling? thanks for your help.
__________________
Michel and Sylvie
2017 Aspire 44B
2023 Grand Cherokee Overland
mbaril is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-24-2016, 12:26 PM   #2
Senior Member
 
fegans02's Avatar
 
Join Date: May 2015
Location: Richmond, VA
Posts: 166
Quote:
Originally Posted by mbaril View Post
Hello everybody, I have the Gen on, the burner on, thermostat on low heat gas on 3 zones, but show active zone 3 only. On the aquahot, heating zone status light 1,2 and 5 on green. all pump on green, Heating status on green. I have heat at the floor level but cold on the ceiling vents. What is I'm doing wrong? is the heat from aquahot is only from the floor vent? if yes, how do I stop the cold air from the ceiling? thanks for your help.
Our AquaHot only blows from the floor - sounds like you need to turn the heat pumps off so cold air stops blowing from the ceiling - on our thermostat you can switch it heat pump or aqua
__________________
Adrienne Fegans
2015 Newmar London Aire
Richmond, VA
fegans02 is offline   Reply With Quote
Old 10-24-2016, 12:28 PM   #3
Senior Member
 
Tall Tex's Avatar
 
Join Date: Feb 2016
Location: San Antonio, TX
Posts: 635
Aqua hot is floor vent only. The ac fan will blow when you select gas heat and low, high, or auto for fan speed. Do not select a fan speed, then ac fan will stop. Been there done that.
__________________
Larry and Stacey
2016 Entegra Anthem 42 RBQ
2016 Jeep Cherokee Trailhawk
Tall Tex is offline   Reply With Quote
Old 10-24-2016, 12:34 PM   #4
Senior Member
 
Tall Tex's Avatar
 
Join Date: Feb 2016
Location: San Antonio, TX
Posts: 635
In addition, zone 1 is the front and kitchen, 2 is the floor heat, zone 3 is bedroom and rear bath depending on floor plan. If you have engine preheat (not sure if Aspire has that) I believe that is zone 5. Basement heat is zone 4. I may have 4 and 5 reversed, not sure.
__________________
Larry and Stacey
2016 Entegra Anthem 42 RBQ
2016 Jeep Cherokee Trailhawk
Tall Tex is offline   Reply With Quote
Old 10-24-2016, 02:06 PM   #5
Moderator Emeritus
 
Cruzer's Avatar
 
Join Date: Oct 2002
Location: Sheboygan, WI
Posts: 5,641
Engine preheat is a standalone feature and does not use any zone.
__________________
Mark & Leann Quasius
2016 Cornerstone 45A
2020 Jeep Gladiator Rubicon
2021 Jeep Wrangler Rubicon
Cruzer is offline   Reply With Quote
Old 10-24-2016, 02:09 PM   #6
Senior Member
 
Join Date: Jun 2014
Location: Pollock Pines, CA
Posts: 1,100
Quote:
Originally Posted by Tall Tex View Post
In addition, zone 1 is the front and kitchen, 2 is the floor heat, zone 3 is bedroom and rear bath depending on floor plan. If you have engine preheat (not sure if Aspire has that) I believe that is zone 5. Basement heat is zone 4. I may have 4 and 5 reversed, not sure.
You have it correct, Tex, with the exception of engine preheat, which comes on with the switch.

Agree, you have the fan on circulating cold air, AH just works from the floor. Turn off your heat pumps, the cold air will quit.


In addition to the Zone 2 radiant heating (which you will want to keep at a heat level a few degrees above the other inside zones), Zone 1 has fan driven radiator/boiler style heating under the center dash, at the kitchen baseboard, and at the back wall, and Zone 3 has two fan driven radiator/boiler style heating units, one at the baseboard on the back wall of the bedroom by the bathroom door, and one at the baseboard below the vanity.


I think that is right.
__________________
John Arenz N6YBH
2017 Cornerstone 45B, 2012 JK Rubicon in tow
2014 Anthem 44B (sold)
RubiconTrail is offline   Reply With Quote
Old 10-24-2016, 02:18 PM   #7
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 11,530
Blog Entries: 1
Entegra says that zone 2 should be 6 to 7 degrees higher than your temperature settings on the other zones.

Otherwise, the information you are getting is spot on.

Has this helped your situation??

Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Old 10-24-2016, 03:07 PM   #8
Senior Member
 
EVsCoach's Avatar
 
Join Date: Aug 2014
Location: Las Vegas, NV
Posts: 572
And turn on that fireplace to circulate some hot air if possible.



Sent from my iPhone 70NAM
__________________
Jack & Evelyn
2014 Anthem DLQ
Living the Good Life
EVsCoach is offline   Reply With Quote
Old 10-24-2016, 05:09 PM   #9
Senior Member
 
FreshAir's Avatar
 
Workhorse Chassis Owner
Entegra Owners Club
Join Date: Dec 2004
Location: UT/AZ
Posts: 1,417
Quote:
Originally Posted by mbaril View Post
Hello everybody, I have the Gen on, the burner on, thermostat on low heat gas on 3 zones,
Assuming your 17 is the same as my 16 Aspire. If you have low heat gas showing, then >mode switch to "gas heat" only. Upper left guadrant should be blank. If you have high,low, auto, etc in that area you have your ceiling system active also. As my memory serves me.
pat
__________________
Pat & Denise
2016 Entegra Aspire RBQ
18 Silverado
FMCA 212171
FreshAir is offline   Reply With Quote
Old 10-24-2016, 08:40 PM   #10
Senior Member
 
Tall Tex's Avatar
 
Join Date: Feb 2016
Location: San Antonio, TX
Posts: 635
Quote:
Originally Posted by Cruzer View Post
Engine preheat is a standalone feature and does not use any zone.
The OP stated that his status light was on for zone 5. You are correct that the thermost has zones 1, 2 and 3, however the Aquahot panel in the basement has status lights for 5 zones. 4 is basement heat 5 is engine preheat, both controlled separate from the HVAC thermostat.
__________________
Larry and Stacey
2016 Entegra Anthem 42 RBQ
2016 Jeep Cherokee Trailhawk
Tall Tex is offline   Reply With Quote
Old 10-25-2016, 06:55 AM   #11
Moderator Emeritus
 
Cruzer's Avatar
 
Join Date: Oct 2002
Location: Sheboygan, WI
Posts: 5,641
True, the AquaHot does have 5 zones but they are all heat output zones. The engine preheat is not one of them. It is a heat "input" zone that is a standalone system apart from any of the heating zones. Attached is an excerpt from the service manual showing the zone wiring.
Attached Files
File Type: pdf AHE-450D Service Manual.pdf (292.2 KB, 48 views)
__________________
Mark & Leann Quasius
2016 Cornerstone 45A
2020 Jeep Gladiator Rubicon
2021 Jeep Wrangler Rubicon
Cruzer is offline   Reply With Quote
Old 10-25-2016, 08:01 AM   #12
Senior Member
 
weirba's Avatar
 
Join Date: Sep 2015
Location: wandering
Posts: 207
Quote:
Originally Posted by mbaril View Post
Hello everybody, I have the Gen on, the burner on, thermostat on low heat gas on 3 zones, but show active zone 3 only. On the aquahot, heating zone status light 1,2 and 5 on green. all pump on green, Heating status on green. I have heat at the floor level but cold on the ceiling vents. What is I'm doing wrong? is the heat from aquahot is only from the floor vent? if yes, how do I stop the cold air from the ceiling? thanks for your help.
What are experiencing has nothing to do with the Aquahot, it is the thermostat settings. When you are selecting gas heat you have to cycle through all of the fan speeds (low, med, high, auto and blank). Change yours from low to blank and you will be good.
__________________
2018 Ford F-350 DRW pulling a 2023 LUXE 47FB TH
weirba is offline   Reply With Quote
Old 10-25-2016, 08:20 AM   #13
Senior Member
 
Swerwin's Avatar
 
Join Date: Oct 2013
Location: Northeast Georgia
Posts: 185
I thought the engine loop would add heat to the aquahot if the engine was running and the aquahot would circulate heat to the engine if the engine was turned off. This is done by way of the pump on the rear of the aquahot. This is diesel aquahot only. Did I misunderstand how this works?
__________________
2014 Anthem 44SL
2015 F-150 Toad
Swerwin is offline   Reply With Quote
Old 10-25-2016, 08:41 AM   #14
Moderator Emeritus
 
Cruzer's Avatar
 
Join Date: Oct 2002
Location: Sheboygan, WI
Posts: 5,641
No, that is the way it works. The system is dual directional but uses the coolant hoses to the engine to connect to the boiler instead of the circulating zone pumps and solenoids.
__________________
Mark & Leann Quasius
2016 Cornerstone 45A
2020 Jeep Gladiator Rubicon
2021 Jeep Wrangler Rubicon
Cruzer is offline   Reply With Quote
Reply

Tags
need help



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
First time user Longweekends New Member Check-In 7 04-02-2012 01:47 PM
First time poster, first time owner jimmyq New Member Check-In 5 08-17-2011 09:16 AM
Good Sam ERS - First time user and issue Racedog iRV2.com General Discussion 43 03-10-2011 04:40 PM
First time toad user bugsrv Toads and Motorhome Related Towing 14 10-26-2010 05:07 PM