Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > THE OWNER'S CORNER FORUMS > Entegra Owner's Forum
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 03-31-2015, 05:42 AM   #1
Senior Member
 
brobox's Avatar
 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,733
Float charge rate?

I noticed on another post that AGM's should not be float charged more than 13.3 volts. Mine are Float charging at 13.7.

I am keeping an eye on Wineman's MH while it is is storage. He had new AGM's installed last year and I noticed they have his float rate set at 12.9V.

Are mine being over charged and how do you change the setting if they are?
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
brobox is online now   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-31-2015, 06:51 AM   #2
Senior Member
 
hawgguy's Avatar
 
Join Date: Jun 2011
Location: College Station, Texas
Posts: 2,841
I will be paying attention to this thread. Mine float at 13.6.

This reference suggests that the ambient temperatures influence the recommended float charge rate.

FTA:
As with all gelled and sealed units, AGM batteries are sensitive to overcharging. These batteries can be charged to 2.40V/cell (and higher) without problem; however, the float charge should be reduced to between 2.25 and 2.30V/cell (summer temperatures may require lower voltages).

2.25-2.3V/cell would be 13.5-13.8V
__________________
Bob in College Station, TX
2015 Entegra Cornerstone 45K
2012 Jeep Rubicon, 1994 FXLR
hawgguy is offline   Reply With Quote
Old 03-31-2015, 07:14 AM   #3
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
I think with AGM batteries, owners need to do a little homework, to find out what float voltage their batteries need. Every manufacturer will probably have slightly different suggestions.

Many people buy them, hook them up and all is good. A few years latter, they are wondering why they're dead.
twinboat is offline   Reply With Quote
Old 03-31-2015, 08:45 AM   #4
Senior Member
 
TerryO's Avatar
 
Entegra Owners Club
Join Date: Feb 2012
Location: Midland, Texas
Posts: 606
It depends on the temperature. I've attached page 19 of the Lifeline manual.
Attached Thumbnails
Click image for larger version

Name:	image.jpg
Views:	201
Size:	386.6 KB
ID:	90143  
__________________
Terry & Gloria O, Midland, Texas
2020 Entegra Aspire 44W, 2022 F250 King Ranch
2012 Entegra Aspire 42RBQ Traded
TerryO is offline   Reply With Quote
Old 03-31-2015, 11:27 AM   #5
Senior Member
 
757driver's Avatar


 
Entegra Owners Club
Join Date: Jun 2004
Location: Bayfield, Ontario
Posts: 5,470
Quote:
Originally Posted by brobox View Post
I noticed on another post that AGM's should not be float charged more than 13.3 volts. Mine are Float charging at 13.7.

I am keeping an eye on Wineman's MH while it is is storage. He had new AGM's installed last year and I noticed they have his float rate set at 12.9V.

Are mine being over charged and how do you change the setting if they are?
Chuck,

If you have the Discover AGM's (or any other brand) then you need to go to their website and get the charge graphs for your model of battery. If they are the Discovery EVGC6A-B then they can be floated at 2.27vpc at 25C. If the temperature is above this, the voltage will be less and greater voltage if below 25C because we have temperature compensation from the Magnum inverters.

12.9v is rather low for float voltage but each manufacturer is different, can't say without knowing the brand.

No, you are not over charging your batteries, in fact you are under charging them if they are set to AGM2 under setting 04 which gives an absorb voltage of 14.5v.
If you want to change the setting of float or absorb they you need to go into the settings menu on the Magnum inverters "04 Battery Type" and set this to custom. If you have the Discovery EVGC6A's then the Absorb setting should be 14.7v, float up to 13.6v (I have mine at 13.4v) and Equalize 14.7v (no you will not equalizing them). The 14.7v for equalize is so that if the batteries did get put into an equalize charge they would not be hurt by it. Also charge rate in settings "05 Charge Rate" should be 80% to best take advantage of generator run time when and if you use it.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring

1300W Solar, 1200AH LiFePO4 FMCA F443497
757driver is offline   Reply With Quote
Old 03-31-2015, 11:38 AM   #6
Senior Member
 
757driver's Avatar


 
Entegra Owners Club
Join Date: Jun 2004
Location: Bayfield, Ontario
Posts: 5,470
Her is the link for Discover Batteries graph.

Product SearchÂ*|Â*Discover Energy
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring

1300W Solar, 1200AH LiFePO4 FMCA F443497
757driver is offline   Reply With Quote
Old 03-31-2015, 01:46 PM   #7
Senior Member
 
brobox's Avatar
 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,733
Thanks Don. I don't even know which batteries are in the Anthem. I have printed your post and it looks I need to spend a day checking it out. I also appreciate the link. I still don't understand all of the setting for the Magnums.
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
brobox is online now   Reply With Quote
Old 03-31-2015, 03:11 PM   #8
Senior Member
 
MRUSA14's Avatar
 
Entegra Owners Club
Join Date: Nov 2012
Posts: 8,149
Quote:
Originally Posted by 757driver View Post
Also charge rate in settings "05 Charge Rate" should be 80% to best take advantage of generator run time when and if you use it.
This is something I have been wondering about. Why not 100%?
__________________
Marc and Jill, Wellington FL
2013 Entegra Anthem 44SL
2018 Lincoln MKX
MRUSA14 is offline   Reply With Quote
Old 03-31-2015, 04:00 PM   #9
Senior Member
 
Randyman1's Avatar
 
Monaco Owners Club
Join Date: Sep 2013
Location: Nebraska
Posts: 799
I have the Magnum Inverter/Charger set for AGM batteries and my Lifeline AGM's Float at 13.0, I thought that was kind of high until I read TerryO chart. Randy
__________________
Randy & Kathy-n-Auggie
07 HR Navigator 43PBQ, 525hp Cummins ISX, 17 Ford Supercrew Ecoboost King Ranch 4x4
Randyman1 is offline   Reply With Quote
Old 03-31-2015, 04:27 PM   #10
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
You charge to 80% , on generator, because it takes hours for the last 20 %.
That is where a solar panel setup would come in real handy. Even a mid size array would top off the batteries.

That gets back to the AGM , wet cell issue. Wet cells tolerate being charged to 80% much better then AGM. Not an issue if you boondock a few day, then plug in, but not bringing your AGMs up to 100% often, will shorten their life's.
twinboat is offline   Reply With Quote
Old 03-31-2015, 04:54 PM   #11
Senior Member
 
MRUSA14's Avatar
 
Entegra Owners Club
Join Date: Nov 2012
Posts: 8,149
You are referring to the level of charging, but I am looking at charging rate. My inverters came set up to charge at 50%, but according to the Lifeline chart posted by TerryO, you should charge as fast as possible.
__________________
Marc and Jill, Wellington FL
2013 Entegra Anthem 44SL
2018 Lincoln MKX
MRUSA14 is offline   Reply With Quote
Old 03-31-2015, 05:34 PM   #12
Senior Member
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Aug 2014
Posts: 1,899
Quote:
Originally Posted by MRUSA14 View Post
You are referring to the level of charging, but I am looking at charging rate. My inverters came set up to charge at 50%, but according to the Lifeline chart posted by TerryO, you should charge as fast as possible.
50% of what??

Normal charge rate is specified a x times Capacity (like 2C would be 2 amps for a 1 AmpHr battery).

I think most of the inverter manuals use % to specify when the charger switches between Bulk, Absorb, and Float. Each one gets less current (lower applied charge voltage.

Can you point us to the page where you see 50% charge rate?
This is from the Magnum Manual that I have.


Thanks,
Dan
Attached Thumbnails
Click image for larger version

Name:	aa_temp.jpg
Views:	240
Size:	37.6 KB
ID:	90198  
__________________
2014 40QBH Phaeton DP Cummins 380HP ISL, Freightliner XC, 2019 Jeep Grand Cherokee Trailhawk TOAD
Blue Ox Aventa tow bar, SMI Air Force One -Cave Creek, AZ.
dpinvidic is offline   Reply With Quote
Old 03-31-2015, 07:17 PM   #13
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
Thinking about what he said, I think the 50% number, may have come from the 120 volt AC load sharing settings on the inverter. They use that so they don't overload the generator or pop the breakers, when plugged into 20 amp shore power.

Could be wrong
twinboat is offline   Reply With Quote
Old 03-31-2015, 08:09 PM   #14
Registered User
 
Join Date: Apr 2013
Location: NV
Posts: 2,227
johnnyreno is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Peak Final Charge Global testing Hugmongous Monaco Owner's Forum 3 11-13-2014 06:11 PM
Battery charge rate & absorb charge time loisjop Entegra Owner's Forum 0 11-01-2014 01:15 PM
Final Charge - Color of coolant concern Smitty77 Cummins Engines 8 10-14-2014 05:07 PM
Final Charge Coolant Hooligan Cummins Engines 23 09-08-2013 04:03 PM
Xantrex inverter/charger shows full charge at 12.2V michelb Class A Motorhome Discussions 3 07-16-2013 06:04 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:23 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.