Generator question when we have a power outage

When power goes out at the pedestal for a few minutes he generator automatically starts. When power comes back in the generator should shut off and go back to regular power.

Problem is the generator still runs and I have to shut it off to be back on regular power

I do not have a Vega touch but I do have the Energy Command 30

I am sure it is just a simple setting just not sure which one.
__________________

__________________
BBQ-Guy
philnail is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-11-2019, 04:19 PM   #2
Senior Member


 
Join Date: Jan 2016
Location: Montgomery, TX (Home Sweet Home)
Posts: 2,332
Hi Phil, for some reason I want to say that if the AGS fired, and later shore power was restored, that you would have to manually shut down the generator and reset the AGS.

If you didnít have shore power at all, and had the AGS set, and it started the generator, it would also shut the generator down when it was satisfied.

Let me test mine and see what happens..

-Matt
__________________

__________________
2017 Entegra Aspire 44R (bunks) towing 2015 F-150
2012 Tiffin Phaeton 40QKH (Our Phaeton was so nice, we bought it twice)
2016 Open Range RF376FBH (Sold)
Matt D is offline   Reply With Quote
Old 07-11-2019, 04:39 PM   #3
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 5,620
Blog Entries: 1
Phil

My memory of this issue is that the AGS will start the genny when commercial power goes out. However, there is nothing on the coach that will turn it off again when commercial power come back on.

My memory is that there is a relay that was never installed which would do that, and as I remember, there was a modification that could be done to the coach to provide that capability. Some very careful searching of this forum around 2015-2016 should find the threads. This was discussed and I am pretty sure that someone posted the modification that showed what to add and how to do it.

Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5Fi
Gary.Jones is offline   Reply With Quote
Old 07-11-2019, 06:32 PM   #4
Senior Member
 
Join Date: May 2017
Posts: 1,313
Starting in 2020 generator will shutdown when pedestal power restored. All previous years you have to stop generator manually after pedestal power restored. Pita
__________________
2017 Cornerstone 45W, 2020 45W Cornerstone on order
2019 Ram Longhorn
Rollin101 is online now   Reply With Quote
Old 07-11-2019, 06:34 PM   #5
Senior Member
 
Join Date: May 2017
Posts: 1,313
Quote:
Originally Posted by Gary.Jones View Post
Phil

My memory of this issue is that the AGS will start the genny when commercial power goes out. However, there is nothing on the coach that will turn it off again when commercial power come back on.

My memory is that there is a relay that was never installed which would do that, and as I remember, there was a modification that could be done to the coach to provide that capability. Some very careful searching of this forum around 2015-2016 should find the threads. This was discussed and I am pretty sure that someone posted the modification that showed what to add and how to do it.

Gary
Gary I think the mod youíre talking about was to start the generator not shut it down.
__________________
2017 Cornerstone 45W, 2020 45W Cornerstone on order
2019 Ram Longhorn
Rollin101 is online now   Reply With Quote
Old 07-11-2019, 07:32 PM   #6
Senior Member


 
Entegra Owners Club
Spartan Chassis
Join Date: Aug 2015
Posts: 414
The EC30 (or VegaTouch) has control of the generator once it is triggered by the shore power outage. Actually, my understanding is it is not the outage that triggers, but the climate or battery voltage status that does. If the AC is running and shore power goes out, then there is a AGS call for generator to start in the absence of shore power. Once the generator has started then the parameters in the EC30 or VegaTouch needs to be satisfied before the generator will turn off even if shore power has restored. Once turned off it will not restart with shore power available.

Unfortunately with the EC30 and current VegaTouch not having the relay Gary mentioned there seems to be no way for the AGS to know shore power has been restored. I believe the AGS will have to turn off the generator after satisfying the call before AGS will return to the status of idle when there is shore power.

I’ve thought of testing this, but annoying my neighbors won’t be my first option.
__________________
Tom and Jodie
2017 Entegra Cornerstone 44B
2013 Jeep Wrangler Unlimited
Tom78418 is offline   Reply With Quote
Old 07-11-2019, 07:35 PM   #7
Senior Member
 
Hayman's Avatar
 
Join Date: Jul 2012
Location: On The Road to Somewhere
Posts: 1,209
Our 16 Anthem w/EC 30 when set on AUTO will start the generator on loss of shore power if AC's are needed or if SOC falls below set point. In both cases when shore power returns the generator will shut down BUT not until a certain SOC is reached and AC's cycle off.
I tested the system several times ( shortly after our purchase ) because of our concern over loss of AC's with our dog in the coach and as I recall once the AC's shut down it took about 15 minutes to reach a SOC that allowed the generator to shut down and shore power take over. I always set the EC 30 to auto and just the other day due to maintenance at our location shore power was lost and the generator started due to AC's.
__________________
Sue & Brian Ashworth, Full Time on the road
2016 Anthem 44A, 2018 GMC Canyon Denali
2012 Fatboy, HydraLift
Hayman is offline   Reply With Quote
Old 07-11-2019, 07:38 PM   #8
Senior Member
 
Marcosdad's Avatar
 
Entegra Owners Club
Join Date: Apr 2012
Location: Green Valley, AZ
Posts: 1,347
Just guessing here, but on my Vega Touch I have a minumum run time for the AGS. Maybe, the system is just doing what it was told. So, it runs until all requirement are met and THEN what ever you have as min run time.
__________________
Stew and Diane (and Marco)
2018 Entegra Cornerstone 45X
Formerly: 2015 Entegra Cornerstone 45B, 2013 Entegra Aspire DEQ IFS, 2004 DSDP; all sold
Marcosdad is offline   Reply With Quote
Old 07-11-2019, 07:41 PM   #9
Senior Member
 
Magic-carpet's Avatar
 
Join Date: Apr 2012
Location: Washington, Pennsylvania
Posts: 858
Quote:
Originally Posted by Rollin101 View Post
Starting in 2020 generator will shutdown when pedestal power restored. All previous years you have to stop generator manually after pedestal power restored. Pita
It is a PITA but on my 2017 the generator will shutdown after 2 hours and check for shore power. If it doesn't see shore power it starts the generator again. The VT can be set for anything between 2 and 12 hours. Of course you can always shut it off if you are there and know that you have shore power back up. If you reset the AGS and the generator hasn't run for 2 hours, it will dump shore power and restart the generator. Its got a timer in the code. The only way to kill the timer is to reboot the 12V system.

At least that is how my system is operating at this point.
__________________
Jeanne & Rosko
2017 Cornerstone 45B
2014 Anthem 44B Classic (traded)
Magic-carpet is offline   Reply With Quote
Old 07-11-2019, 07:46 PM   #10
Senior Member
 
Entegra Owners Club
Join Date: Mar 2012
Posts: 156
Quote:
Originally Posted by Gary.Jones View Post
Phil

My memory of this issue is that the AGS will start the genny when commercial power goes out. However, there is nothing on the coach that will turn it off again when commercial power come back on.

My memory is that there is a relay that was never installed which would do that, and as I remember, there was a modification that could be done to the coach to provide that capability. Some very careful searching of this forum around 2015-2016 should find the threads. This was discussed and I am pretty sure that someone posted the modification that showed what to add and how to do it.

Gary
I am not sure if it is still this way, but on my 14 the EC30 requires a shore power sense wire to know when shore power has been restored. Mine did not come wired with one. I added it to my coach and it will shut down after shore power has been restored and the generator has satisfied what triggered it in the first place (low battery, thermostat, etc). To work properly the EC30 requires a low voltage AC or DC current from the shore power side of the transfer switch to sense when shore power is available. I wired a door bell transformer to the incoming shore power side of the transfer switch and ran door bell wire from the transformer to the EC30. I never understood why the factory would install an AGS but not run the wire to allow it to sense shore power. It would not be a very expensive addition.
__________________
James and Diana
2014 Entegra Coach Aspire 44B
jherrin99 is online now   Reply With Quote
Old 07-11-2019, 07:54 PM   #11
Senior Member


 
Entegra Owners Club
Spartan Chassis
Join Date: Aug 2015
Posts: 414
Brian, you just saved my neighbors form my testing. Interesting we recently had an issue where the Progressive Ind surge protector drop L1 due to low voltage and the AGS started the generator. In that case even when L1 returned to an acceptable voltage and the EMS reset, the generator continued to run. It would have been a good test, but it was a hot day and the AC would hav continued for quite some time.
__________________
Tom and Jodie
2017 Entegra Cornerstone 44B
2013 Jeep Wrangler Unlimited
Tom78418 is offline   Reply With Quote
Old 07-11-2019, 08:25 PM   #12
Senior Member


 
Join Date: Jan 2016
Location: Montgomery, TX (Home Sweet Home)
Posts: 2,332
I just tested this on our 2017 Aspire (not VegaTouch equipped.)

I used the thermostat to request the AGS start the generator upon shore power failure.

When I turned off shore power, the AGS fired up the generator and A/C was restored.

Without touching the Command 30, or the manual generator start button I went to the pedestal and turned on the shore power.

After a good long while, well beyond the Progressive Industries delay, the generator continued to happily run, and the Command 30 screen indicated AUTO.

Only after I manually shut down the generator did shore power pass through the Transfer Switch, and to the coach.

-Matt
__________________
2017 Entegra Aspire 44R (bunks) towing 2015 F-150
2012 Tiffin Phaeton 40QKH (Our Phaeton was so nice, we bought it twice)
2016 Open Range RF376FBH (Sold)
Matt D is offline   Reply With Quote
Old 07-11-2019, 08:30 PM   #13
Senior Member


 
Join Date: Jan 2016
Location: Montgomery, TX (Home Sweet Home)
Posts: 2,332
Phil, my suspicion is that your 2013 Anthem has more in common with our Aspire, than with a newer Anthem or Cornerstone.

The question that is forefront in my mind, is how to wire up the sense wire for the Command 30 AGS circuit to sense the restoration of shore power?

In addition, if you have the capability to detect when shore power is restored, must you then reset the AGS to AUTO, seeing as it already triggered a start in my hypothetical scenario?

Thoughts?

-Matt
__________________
2017 Entegra Aspire 44R (bunks) towing 2015 F-150
2012 Tiffin Phaeton 40QKH (Our Phaeton was so nice, we bought it twice)
2016 Open Range RF376FBH (Sold)
Matt D is offline   Reply With Quote
Old 07-11-2019, 08:33 PM   #14
Senior Member
 
philnail's Avatar


 
Entegra Owners Club
Join Date: Aug 2012
Location: Full Time - Most of the time we are lost.
Posts: 375
I actually ran the trigger wire with the doorbell relay. I also have the relay set to a breaker. It seems to me it used to shutdown the generator once power was restored but I just canít remember

I will run some more tests and report back
__________________

__________________
BBQ-Guy
philnail is offline   Reply With Quote
Reply

Tags
generator, power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using RV generator during home power outage Trtomraub RV Systems & Appliances 21 12-02-2018 03:04 PM
Palazzo Generator for home power outage sttom Palazzo Motorhomes 3 02-05-2016 10:37 AM
RV genset to power house during power outage McDanie1 Newmar Owner's Forum 8 07-16-2009 08:54 AM
Ice Storm Power outage - BUT - we kept warm Logthumper Monaco Owner's Forum 4 12-14-2007 02:16 PM
Power outage - using generator questions Audrey & John Alpine Coach Owner's Forum 13 04-20-2006 03:08 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:59 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.